Smart ERV / HRV Controller with IAQ Sensors, Manual Timers, and Efficiency Guardrails
A comprehensive Home Assistant blueprint for automating an Energy Recovery Ventilator (ERV), Heat Recovery Ventilator (HRV), or generic ventilation system. It supports single or dual-speed configurations and intelligently balances sensor inputs, manual overrides, schedules, and minimum hourly baseline runs.
Why Use This Blueprint?
While ERVs are highly efficient, they are not perfect. Even a high-performing ERV that is 80% effective is still 20% ineffective. This means that during the winter, 20% of your conditioned indoor heat is being actively pumped outside while it runs. During the summer, the same percentage of heat and humidity is being pulled in.
To maximize climate efficiency and lower your energy bill, an ERV should only run as much as necessary to keep indoor air levels healthy. Furthermore, traditional systems ventilate blindly. This blueprint introduces a "Do No Harm" outdoor check: if your outdoor sensors indicate the outside air quality is worse than your indoor air quality, the automation will suppress ventilation. There is no efficiency or health benefit to pumping polluted air into your home.
Features & Logic Priority
The automation evaluates conditions continuously in a strict priority order to ensure the ERV is always in the correct state:
- Blockers & Manual Off: Any active blocking entity or a physical "Off" button press immediately stops operation.
- Manual Button Press (Timer Lock): Physical button inputs temporarily lock the system into Regular or Boost mode via a configurable countdown timer helper.
- Sensor-Driven IAQ Logic: Activates Regular or Boost modes based on indoor air quality thresholds. Suppresses automatic ventilation if outdoor air quality is worse than indoors, unless the outdoor air is still below safe thresholds.
- Schedules: Keeps the ERV running at regular speed during configured time windows.
- Minimum Hourly Ventilation: Runs the ERV for a set number of minutes at the top of every hour (e.g., from :00 to :20) to maintain a baseline fresh air exchange when sensors are quiet.
Requirements
To use this blueprint, you must have:
- Regular Speed Relay: A
switchentity controlling your ERV's primary power/low speed.
Optional Requirements (Depending on your features used):
Boost Speed Relay: A second
switchentity for high speed. -
Helpers: * A
timerhelper to track manual run windows. -
A
schedulehelper for scheduled operational hours. -
Sensors: Any combination of indoor (and matching outdoor) environment sensors for CO2, VOC, PM2.5, or NOx.
Buttons:
evententities tied to physical smart buttons/remotes for manual control (Regular, Boost, and Off). -
Blocking Entities: Any
switch,binary_sensor, or other domain that dictates a hard stop (e.g., window open sensors, extreme outdoor AQI alerts).
Configuration Variables
- Trigger Delay: Time (in minutes) an indoor sensor must continuously exceed a threshold before triggering the ERV (prevents short-cycling from spikes).
- Post-Run Delay: Time (in minutes) sensors must remain below thresholds before the ERV turns off.
- Manual Off Cooldown: Suppresses automatic sensor/schedule control for a set period after pressing the physical off button, ensuring the system doesn't immediately flip back on.
- Button Time Increment: Amount of time added to the timer helper per physical button click (cumulative if pressed multiple times).
Blueprint YAML
blueprint:
name: ERV Controller
description: |
# ERV Controller
A Home Assistant blueprint for controlling an Energy Recovery Ventilator (ERV) or similar ventilation device. Designed for single or dual-speed setups (regular and boost), with multiple layers of control that work together automatically.
## How It Works
The automation runs continuously in the background, evaluating conditions in priority order: blockers and manual off first, then manual button presses, then sensor-driven responses, then scheduled and hourly minimum ventilation. The ERV is always in exactly the right state based on whatever is most relevant at the time.
## Features
**Dual-Speed Support**
Separate relays for regular and boost speed. Boost relay is optional — works fine as a single-speed setup.
**Air Quality Sensors**
Monitors up to four sensor types — CO2, VOC, PM2.5, and NOx. Each has independent regular and boost thresholds. If an outdoor sensor is provided, the ERV will only respond when indoor levels exceed outdoor levels (no point ventilating if outside air is worse). Trigger and post-run delays prevent short cycling from momentary spikes.
**Physical Buttons**
Optional regular, boost, and off buttons via Event entities. Each press adds time to a timer helper. Supports click-type filtering (e.g. single vs double press) for buttons that emit multiple event types.
**Schedule**
Optional Schedule helper keeps the ERV running at regular speed during configured time windows.
**Minimum Hourly Ventilation**
Runs the ERV for a set number of minutes at the top of every hour, regardless of sensor readings — useful for maintaining baseline fresh air exchange. Respects blocking entities like everything else.
**Blocking Entities**
Any switch, binary sensor, or other entity in the 'on' state can block all ERV operation — useful for outdoor air quality alerts, open window detection, or any other condition where ventilation should be suppressed.
**Manual Off Cooldown**
Pressing the off button suppresses automatic control for a configurable period, so sensors or schedules don't immediately undo a manual off.
domain: automation
input:
section_relays:
icon: mdi:power-plug
collapsed: true
input:
regular_relay:
name: Regular Speed Relay
selector: { entity: { domain: switch } }
boost_relay:
name: Boost Speed Relay (Optional)
default: ""
section_helpers:
icon: mdi:creation
collapsed: true
input:
manual_timer:
name: Timer Helper (Optional)
description: >
A Timer helper used to track manual button presses. When a Regular or Boost
button is pressed, this timer runs for the configured increment. The ERV stays
on until the timer finishes.
default: ""
selector: { entity: { domain: timer } }
custom_schedule:
name: Schedule Helper (Optional)
description: >
A Schedule helper that keeps the ERV running at regular speed whenever
the schedule is active. Create a Schedule helper in Settings → Helpers.
default: ""
selector: { entity: { domain: schedule } }
section_overrides:
name: "Controls & Safety"
icon: mdi:shield-alert-outline
collapsed: true
input:
blocking_entities:
name: Blocking Entities (Optional)
description: >
When any of these entities are 'on', the ERV will be forced off and will not
run for any reason — including the hourly minimum, sensors, or schedule.
Useful for outdoor air quality alerts, window/door sensors, or manual overrides.
default: []
selector: { entity: { multiple: true } }
btn_regular:
name: Regular Speed Button (Optional)
description: >
An Event entity tied to a physical button. Each press adds time to the timer
at Regular speed.
default: ""
selector: { entity: { domain: event } }
btn_regular_type:
name: Regular Button — Click Type
description: >
Filter to a specific click type (e.g. single_press, double_press). Leave blank
to trigger on any event from that button. To find the event type, go to
Developer Tools → States, find your button entity, and look at the
'event_type' attribute after pressing the button.
default: ""
btn_boost:
name: Boost Speed Button (Optional)
description: >
at Boost speed.
default: ""
btn_boost_type:
name: Boost Button — Click Type
description: >
default: ""
btn_off:
name: Off Button (Optional)
description: >
An Event entity tied to a physical button. Pressing this cancels the timer
and turns the ERV off for the configured cooldown period.
default: ""
btn_off_type:
name: Off Button — Click Type
description: >
default: ""
section_timing:
icon: mdi:timer-cog-outline
collapsed: true
input:
trigger_dur:
description: >
How long a sensor must remain above its threshold before the ERV turns on.
Helps avoid short spurts from momentary sensor spikes.
default: 2
selector: { number: { min: 0, max: 30, unit_of_measurement: min } }
post_run_dur:
description: >
How long sensors must remain below their thresholds before the ERV turns off.
Keeps the ERV running a little longer after air quality recovers.
default: 3
min_run_time:
name: Minimum Hourly Ventilation
description: >
The ERV will run for at least this many minutes at the start of every hour
(e.g. 20 = runs from :00 to :20 each hour). Set to 0 to disable.
Blocking entities will prevent this from running, just like any other mode.
default: 0
selector: { number: { min: 0, max: 60, unit_of_measurement: min } }
manual_inc:
name: Button Time Increment
description: >
Each button press adds this many minutes to the timer. If the ERV is already
running in the same mode, presses are cumulative.
default: 10
selector: { number: { min: 1, max: 60, unit_of_measurement: min } }
off_cooldown:
name: Manual Off Cooldown
description: >
After pressing the Off button, the ERV will stay off for this many minutes
before normal automatic control (sensors, schedule, hourly minimum) can turn
it back on. Does not block emergency overrides or blocker entities.
default: 30
selector: { number: { min: 0, max: 180, unit_of_measurement: min } }
section_co2:
icon: mdi:molecule-co2
collapsed: true
input:
co2_in:
default: ""
selector: { entity: { domain: sensor, device_class: carbon_dioxide } }
co2_out:
default: ""
co2_reg:
name: Regular Threshold
default: 1000
selector: { number: { min: 400, max: 5000, mode: box } }
co2_bst:
name: Boost Threshold
default: 2000
section_voc:
icon: mdi:scent
collapsed: true
input:
voc_in:
default: ""
selector: { entity: { domain: sensor } }
voc_out:
default: ""
voc_reg:
default: 300
selector: { number: { min: 0, max: 2000, mode: box } }
voc_bst:
default: 1000
section_pm:
icon: mdi:blur
collapsed: true
input:
pm_in:
default: ""
selector: { entity: { domain: sensor, device_class: pm25 } }
pm_out:
default: ""
pm_reg:
default: 15
selector: { number: { min: 0, max: 500, mode: box } }
pm_bst:
default: 55
section_nox:
icon: mdi:smog
collapsed: true
input:
nox_in:
default: ""
nox_out:
default: ""
nox_reg:
default: 30
nox_bst:
default: 100
mode: restart
variables:
reg_relay: !input regular_relay
bst_relay: !input boost_relay
manual_timer: !input manual_timer
manual_inc: !input manual_inc
min_run_time: !input min_run_time
off_cooldown: !input off_cooldown
blocking_entities: !input blocking_entities
custom_schedule: !input custom_schedule
btn_reg_type: !input btn_regular_type
btn_bst_type: !input btn_boost_type
btn_off_type: !input btn_off_type
btn_regular: !input btn_regular
btn_boost: !input btn_boost
btn_off: !input btn_off
ev_type: "{{ trigger.to_state.attributes.event_type | default('') if trigger.platform == 'state' and trigger.to_state is not none else '' }}"
match_off: "{{ trigger.id == 'trig_btn_off' and (btn_off_type == '' or ev_type == btn_off_type) }}"
match_bst: "{{ trigger.id == 'trig_btn_bst' and (btn_bst_type == '' or ev_type == btn_bst_type) }}"
match_reg: "{{ trigger.id == 'trig_btn_reg' and (btn_reg_type == '' or ev_type == btn_reg_type) }}"
# Sensor Eval Logic
co2_in: !input co2_in
co2_out: !input co2_out
co2_reg: !input co2_reg
co2_bst: !input co2_bst
voc_in: !input voc_in
voc_out: !input voc_out
voc_reg: !input voc_reg
voc_bst: !input voc_bst
pm_in: !input pm_in
pm_out: !input pm_out
pm_reg: !input pm_reg
pm_bst: !input pm_bst
nox_in: !input nox_in
nox_out: !input nox_out
nox_reg: !input nox_reg
nox_bst: !input nox_bst
# === "Do No Harm" Safe Outdoor Check ===
# Only allow automatic ventilation if outdoor air is NOT worse for ANY pollutant,
# UNLESS that outdoor pollutant is still below its regular safety threshold.
safe_to_ventilate: >
{% set ns = namespace(safe=true) %}
{% set sensors = [
(co2_in, co2_out, co2_reg),
(voc_in, voc_out, voc_reg),
(pm_in, pm_out, pm_reg),
(nox_in, nox_out, nox_reg)
{% for s_in, s_out, thresh in sensors %}
{% if s_in != '' and s_out != '' and states(s_in)|is_number and states(s_out)|is_number %}
{% set in_val = states(s_in)|float %}
{% set out_val = states(s_out)|float %}
{% if out_val > in_val and out_val >= thresh|float %}
{% set ns.safe = false %}
{% endif %}
{% endif %}
{% endfor %}
{{ ns.safe }}
eval_boost_needed: >
{% set ns = namespace(needs_boost=false) %}
{% if safe_to_ventilate | trim | bool(false) %}
{% set sensors = [(co2_in, co2_out, co2_bst), (voc_in, voc_out, voc_bst), (pm_in, pm_out, pm_bst), (nox_in, nox_out, nox_bst)] %}
{% if s_in != '' and states(s_in)|is_number %}
{% if in_val >= thresh|float %}
{% if s_out == '' or not states(s_out)|is_number or in_val > states(s_out)|float %}
{% set ns.needs_boost = true %}
{% endif %}
{% endif %}
{% endif %}
{% endfor %}
{% endif %}
{{ ns.needs_boost }}
eval_regular_needed: >
{% set ns = namespace(needs_regular=false) %}
{% set sensors = [(co2_in, co2_out, co2_reg), (voc_in, voc_out, voc_reg), (pm_in, pm_out, pm_reg), (nox_in, nox_out, nox_reg)] %}
{% set ns.needs_regular = true %}
{% endif %}
{% endif %}
{% endif %}
{% endfor %}
{% endif %}
{{ ns.needs_regular }}
# Physical button event triggers
- platform: state
entity_id: !input btn_regular
not_to: [ "unknown", "unavailable" ]
- platform: state
entity_id: !input btn_boost
- platform: state
entity_id: !input btn_off
# Heartbeat Trigger: Evaluates the entire automation every 60 seconds
# Fixes the bug where transitioning past the hourly runtime limit failed to trigger a shutoff
- platform: time_pattern
minutes: "/1"
# Sensor Active Trigger: Fires when IAQ thresholds are exceeded continuously for 'trigger_dur' minutes
value_template: "{{ eval_boost_needed | trim | bool(false) or eval_regular_needed | trim | bool(false) }}"
for:
minutes: !input trigger_dur
# All Clear Trigger: Fires when air quality drops below thresholds for 'post_run_dur' minutes
value_template: "{{ not (eval_boost_needed | trim | bool(false)) and not (eval_regular_needed | trim | bool(false)) }}"
for:
minutes: !input post_run_dur
# Housekeeping Triggers: Re-evaluates on timer expiration, blocker changes, or system restarts
- platform: state
entity_id: !input manual_timer
to: 'idle'
- platform: state
entity_id: !input blocking_entities
- platform: homeassistant
event: start
- platform: event
event_type: automation_reloaded
- choose:
# --- OFF / BLOCKERS ---
- conditions: >
{% set blocker_active = expand(blocking_entities) | selectattr('state', 'eq', 'on') | list | length > 0 %}
{{ match_off or blocker_active }}
sequence:
- if: "{{ manual_timer != '' }}"
then:
- service: timer.cancel
target: { entity_id: "{{ manual_timer }}" }
- service: switch.turn_off
target: { entity_id: ["{{ reg_relay }}", "{{ bst_relay }}"] }
- if: "{{ match_off and off_cooldown > 0 }}"
then:
- delay:
minutes: "{{ off_cooldown }}"
# --- BOOST BUTTON ---
- conditions: "{{ match_bst }}"
sequence:
then:
- service: timer.start
duration: >
{% set is_already_bst = is_state(bst_relay, 'on') if bst_relay != '' else false %}
{% set rem = state_attr(manual_timer, 'remaining') %}
{% set current_sec = (rem.split(':')[0]|int * 3600 + rem.split(':')[1]|int * 60 + rem.split(':')[2]|int) if is_state(manual_timer, 'active') and rem else 0 %}
{{ (manual_inc * 60) + (current_sec if is_already_bst else 0) }}
- if: "{{ bst_relay != '' }}"
then:
- service: switch.turn_on
# --- REGULAR BUTTON ---
- conditions: "{{ match_reg }}"
sequence:
then:
duration: >
{% set is_already_reg = is_state(reg_relay, 'on') and (is_state(bst_relay, 'off') if bst_relay != '' else true) %}
{{ (manual_inc * 60) + (current_sec if is_already_reg else 0) }}
target: { entity_id: "{{ reg_relay }}" }
then:
target: { entity_id: "{{ bst_relay }}" }
# --- SYSTEM EVALUATION ---
# Automatically triggers when a specific physical button interaction hasn't intercepted the flow
default:
- choose:
# PRIORITY 1: MANUAL TIMER LOCK
# If the remote's timer is running, STOP evaluating and leave the relays exactly as the remote set them!
- conditions: "{{ manual_timer != '' and is_state(manual_timer, 'active') }}"
sequence:
- stop: "Manual remote timer is active. Yielding control."
# PRIORITY 2: BOOST SPEED SENSORS
# If high-severity IAQ sensor thresholds are crossed, run boost speed and regular speed
# DO NO HARM: Yields to bad outdoor air.
- conditions: "{{ eval_boost_needed | trim | bool(false) and safe_to_ventilate | trim | bool(false) and bst_relay != '' }}"
sequence:
# PRIORITY 3: REGULAR SPEED CONDITIONS
# Turns on regular speed if standard sensor thresholds are breached, a custom schedule is on,
# OR the current clock minute is below the target hourly runtime.
- conditions: >
{% set sched_active = custom_schedule != '' and is_state(custom_schedule, 'on') %}
{% set hourly_active = min_run_time > 0 and now().minute < min_run_time %}
{% set auto_ventilation = eval_regular_needed | trim | bool(false) or sched_active or hourly_active %}
{{ auto_ventilation and safe_to_ventilate | trim | bool(false) }}
sequence:
then:
# DEFAULT FALLBACK: TURN EVERYTHING OFF
# Runs when all other criteria above fail (e.g., the exact minute the hourly runtime window closes)
default: