Danfoss Ally TRV with ZigBee2MQTT - Lovelace temperature changes set TRV occupied_heating_setpoint, but are not reflected in the Lovelace GUI
Is this a problem in my setup, or is this a HA bug?
Everything done with a freshly paired Danfoss Ally TRV. The Z2M log at the end of the question.
I have paired my TRV with Z2M and named it trv.uf_office. In the Z2M map it shows properly connected with a high LQI:
In the developer tools it represents like this:
In the dashboard I have got a Entities Card with the climate.trv_uf_office (values here allready after update, details below):
Assume the TRV was set to 18 degrees. When I change the occupied_heating_setpoint of the TRV in the Lovelace dashboard to e.g. 23 now, then shows 23 for some seconds and then the occupied_heating_setpoint in the dashboard jumps back to 18.
But the TRV is set to 23 degrees and starts to heat after some seconds. When I check the Z2M logs, I clearly see the correct MQTT messages sent.
When I go to the Z2M Devices page, open up the view of the TRV → Exposes it shows all the values N/A or Null.
When I press the load value buttons (circulating arrows) for occupied_heating_setpoint and local_temperature then it sends the get MQTT messages and updates the vallues in the Z2M expose page and also the Lovelace dashboard.
But I would expect this to happen automatically when I change the temperature in the dashboard, and also when an autmation changes them.
To me it sounds like HA should send out the Received MQTT message on 'zigbee2mqtt/trv.uf_office/get' with data '{"occupied_heating_setpoint":""}' message whenever a change in the dashboard entitiy happens. This shouldn’t have to be done manually.
Is this a bug? Or just a PITA?
Z2M log:
warn  2022-10-23 16:31:35: Device 'trv.uf_office' left the network
info  2022-10-23 16:31:36: MQTT publish: topic 'zigbee2mqtt/bridge/event', payload '{"data":{"friendly_name":"trv.uf_office","ieee_address":"0xccccccfffe1da77a"},"type":"device_leave"}'
info  2022-10-23 16:32:03: Device 'trv.uf_office' joined
info  2022-10-23 16:32:03: MQTT publish: topic 'zigbee2mqtt/bridge/event', payload '{"data":{"friendly_name":"trv.uf_office","ieee_address":"0xccccccfffe1da77a"},"type":"device_joined"}'
info  2022-10-23 16:32:03: Starting interview of 'trv.uf_office'
info  2022-10-23 16:32:03: MQTT publish: topic 'zigbee2mqtt/bridge/event', payload '{"data":{"friendly_name":"trv.uf_office","ieee_address":"0xccccccfffe1da77a","status":"started"},"type":"device_interview"}'
debug 2022-10-23 16:32:21: Device 'trv.uf_office' announced itself
info  2022-10-23 16:32:21: MQTT publish: topic 'zigbee2mqtt/bridge/event', payload '{"data":{"friendly_name":"trv.uf_office","ieee_address":"0xccccccfffe1da77a"},"type":"device_announce"}'
debug 2022-10-23 16:32:23: Received Zigbee message from 'trv.uf_office', type 'readResponse', cluster 'genPollCtrl', data '{"checkinInterval":1200}' from endpoint 1 with groupID 0
info  2022-10-23 16:32:23: Successfully interviewed 'trv.uf_office', device has successfully been paired
info  2022-10-23 16:32:23: Device 'trv.uf_office' is supported, identified as: Danfoss Ally thermostat (014G2461)
info  2022-10-23 16:32:23: MQTT publish: topic 'zigbee2mqtt/bridge/event', payload '{"data":{"definition":{"description":"Ally thermostat","exposes":[{"access":1,"description":"Remaining battery in %","name":"battery","property":"battery","type":"numeric","unit":"%","value_max":100,"value_min":0},{"access":7,"description":"Enables/disables physical input on the device","name":"keypad_lockout","property":"keypad_lockout","type":"enum","values":["unlock","lock1","lock2"]},{"access":7,"description":"Controls how programming affects the thermostat. Possible values: setpoint (only use specified setpoint), schedule (follow programmed setpoint schedule). Changing this value does not clear programmed schedules.","name":"programming_operation_mode","property":"programming_operation_mode","type":"enum","values":["setpoint","schedule","eco"]},{"access":5,"description":"Is the unit in mounting mode. This is set to `false` for mounted (already on the radiator) or `true` for not mounted (after factory reset)","name":"mounted_mode_active","property":"mounted_mode_active","type":"binary","value_off":false,"value_on":true},{"access":7,"description":"Set the unit mounting mode. `false` Go to Mounted Mode or `true` Go to Mounting Mode","name":"mounted_mode_control","property":"mounted_mode_control","type":"binary","value_off":false,"value_on":true},{"access":7,"description":"Thermostat Orientation. This is important for the PID in how it assesses temperature. `false` Horizontal or `true` Vertical","name":"thermostat_vertical_orientation","property":"thermostat_vertical_orientation","type":"binary","value_off":false,"value_on":true},{"access":7,"description":"Viewing/display direction, `false` normal or `true` upside-down","name":"viewing_direction","property":"viewing_direction","type":"binary","value_off":false,"value_on":true},{"access":7,"description":"Not clear how this affects operation. However, it would appear that the device does not execute any motor functions if this is set to false. This may be a means to conserve battery during periods that the heating system is not energized (e.g. during summer). `false` No Heat Available or `true` Heat Available","name":"heat_available","property":"heat_available","type":"binary","value_off":false,"value_on":true},{"access":5,"description":"Whether or not the unit needs warm water. `false` No Heat Request or `true` Heat Request","name":"heat_required","property":"heat_required","type":"binary","value_off":false,"value_on":true},{"access":1,"description":"Values observed are `0` (manual), `1` (schedule) or `2` (externally)","name":"setpoint_change_source","property":"setpoint_change_source","type":"enum","values":["manual","schedule","externally"]},{"features":[{"access":7,"description":"Temperature setpoint","name":"occupied_heating_setpoint","property":"occupied_heating_setpoint","type":"numeric","unit":"°C","value_max":35,"value_min":5,"value_step":0.5},{"access":5,"description":"Current temperature measured on the device","name":"local_temperature","property":"local_temperature","type":"numeric","unit":"°C"},{"access":1,"description":"Position of the valve (= demanded heat) where 0% is fully closed and 100% is fully open","name":"pi_heating_demand","property":"pi_heating_demand","type":"numeric","unit":"%","value_max":100,"value_min":0},{"access":7,"description":"Mode of this device","name":"system_mode","property":"system_mode","type":"enum","values":["heat"]},{"access":1,"description":"The current running state","name":"running_state","property":"running_state","type":"enum","values":["idle","heat"]}],"type":"climate"},{"access":7,"description":"If `radiator_covered` is `true`: Set at maximum 30 minutes interval but not more often than every 5 minutes and 0.1 degrees difference. Resets every 35 minutes to standard. If `radiator_covered` is `false`: Set at maximum 3 hours interval but not more often than every 30 minutes and 0.1 degrees difference. Resets every 3 hours to standard. Value 21C = 2100 (-8000=undefined).","name":"external_measured_room_sensor","property":"external_measured_room_sensor","type":"numeric","value_max":3500,"value_min":-8000},{"access":7,"description":"Set if the TRV should solely rely on external_measured_room_sensor or operate in offset mode. `false` = Auto Offset Mode or `true` = Room Sensor Mode","name":"radiator_covered","property":"radiator_covered","type":"binary","value_off":false,"value_on":true},{"access":7,"description":"Whether or not the window open feature is enabled","name":"window_open_feature","property":"window_open_feature","type":"binary","value_off":false,"value_on":true},{"access":5,"description":"0=Quarantine, 1=Windows are closed, 2=Hold - Windows are maybe about to open, 3=Open window detected, 4=In window open state from external but detected closed locally","name":"window_open_internal","property":"window_open_internal","type":"numeric","value_max":4,"value_min":0},{"access":7,"description":"Set if the window is open or close. This setting will trigger a change in the internal window and heating demand. `false` (windows are closed) or `true` (windows are open)","name":"window_open_external","property":"window_open_external","type":"binary","value_off":false,"value_on":true},{"access":7,"description":"Exercise day of week: 0=Sun...6=Sat, 7=undefined","name":"day_of_week","property":"day_of_week","type":"enum","values":["sunday","monday","tuesday","wednesday","thursday","friday","saturday","away_or_vacation"]},{"access":7,"description":"Exercise trigger time. Minutes since midnight (65535=undefined). Range 0 to 1439","name":"trigger_time","property":"trigger_time","type":"numeric","value_max":65535,"value_min":0},{"access":7,"description":"Scale factor of setpoint filter timeconstant (\"aggressiveness\" of control algorithm) 1= Quick ...  5=Moderate ... 10=Slow","name":"algorithm_scale_factor","property":"algorithm_scale_factor","type":"numeric","value_max":10,"value_min":1},{"access":7,"description":"Whether or not the thermostat acts as standalone thermostat or shares load with other thermostats in the room. The gateway must update load_room_mean if enabled.","name":"load_balancing_enable","property":"load_balancing_enable","type":"binary","value_off":false,"value_on":true},{"access":7,"description":"Mean radiator load for room calculated by gateway for load balancing purposes (-8000=undefined)","name":"load_room_mean","property":"load_room_mean","type":"numeric","value_max":2000,"value_min":-8000},{"access":5,"description":"Load estimate on this radiator","name":"load_estimate","property":"load_estimate","type":"numeric","value_max":3600,"value_min":-8000},{"access":5,"description":"Specific for pre-heat running in Zigbee Weekly Schedule mode","name":"preheat_status","property":"preheat_status","type":"binary","value_off":false,"value_on":true},{"access":5,"description":"Status of adaptation run: None (before first run), In Progress, Valve Characteristic Found, Valve Characteristic Lost","name":"adaptation_run_status","property":"adaptation_run_status","type":"enum","values":["none","in_progress","found","lost"]},{"access":7,"description":"Automatic adaptation run enabled (the one during the night)","name":"adaptation_run_settings","property":"adaptation_run_settings","type":"binary","value_off":false,"value_on":true},{"access":7,"description":"Adaptation run control: Initiate Adaptation Run or Cancel Adaptation Run","name":"adaptation_run_control","property":"adaptation_run_control","type":"enum","values":["none","initiate_adaptation","cancel_adaptation"]},{"access":7,"description":"Regulation SetPoint Offset in range -2.5°C to 2.5°C in steps of 0.1°C. Value 2.5°C = 25.","name":"regulation_setpoint_offset","property":"regulation_setpoint_offset","type":"numeric","value_max":25,"value_min":-25},{"access":1,"description":"Link quality (signal strength)","name":"linkquality","property":"linkquality","type":"numeric","unit":"lqi","value_max":255,"value_min":0}],"model":"014G2461","options":[],"supports_ota":true,"vendor":"Danfoss"},"friendly_name":"trv.uf_office","ieee_address":"0xccccccfffe1da77a","status":"successful","supported":true},"type":"device_interview"}'
debug 2022-10-23 16:32:23: Retrieving state of 'trv.uf_office' after reconnect
debug 2022-10-23 16:33:08: Received Zigbee message from 'trv.uf_office', type 'commandQueryNextImageRequest', cluster 'genOta', data '{"fieldControl":0,"fileVersion":274,"imageType":256,"manufacturerCode":4678}' from endpoint 1 with groupID 0
debug 2022-10-23 16:33:08: Device 'trv.uf_office' requested OTA
debug 2022-10-23 16:33:11: Received Zigbee message from 'trv.uf_office', type 'commandQueryNextImageRequest', cluster 'genOta', data '{"fieldControl":0,"fileVersion":274,"imageType":256,"manufacturerCode":4678}' from endpoint 1 with groupID 0
debug 2022-10-23 16:33:11: Device 'trv.uf_office' requested OTA
debug 2022-10-23 16:33:14: Received Zigbee message from 'trv.uf_office', type 'commandQueryNextImageRequest', cluster 'genOta', data '{"fieldControl":0,"fileVersion":274,"imageType":256,"manufacturerCode":4678}' from endpoint 1 with groupID 0
debug 2022-10-23 16:33:14: Device 'trv.uf_office' requested OTA
debug 2022-10-23 16:33:17: Received Zigbee message from 'trv.uf_office', type 'commandQueryNextImageRequest', cluster 'genOta', data '{"fieldControl":0,"fileVersion":274,"imageType":256,"manufacturerCode":4678}' from endpoint 1 with groupID 0
debug 2022-10-23 16:33:17: Device 'trv.uf_office' requested OTA
debug 2022-10-23 16:33:20: Received Zigbee message from 'trv.uf_office', type 'commandQueryNextImageRequest', cluster 'genOta', data '{"fieldControl":0,"fileVersion":274,"imageType":256,"manufacturerCode":4678}' from endpoint 1 with groupID 0
debug 2022-10-23 16:33:20: Device 'trv.uf_office' requested OTA
debug 2022-10-23 16:36:39: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 16:41:40: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 16:46:42: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 16:51:45: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 16:56:47: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 17:01:49: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 17:06:52: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 17:11:54: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 17:15:22: Received MQTT message on 'zigbee2mqtt/trv.uf_office/set/occupied_heating_setpoint' with data '23.5'
debug 2022-10-23 17:15:22: Publishing 'set' 'occupied_heating_setpoint' to 'trv.uf_office'
debug 2022-10-23 17:16:04: Received MQTT message on 'zigbee2mqtt/trv.uf_office/set/occupied_heating_setpoint' with data '23.0'
debug 2022-10-23 17:16:04: Publishing 'set' 'occupied_heating_setpoint' to 'trv.uf_office'
debug 2022-10-23 17:16:56: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 17:21:58: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 17:27:01: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 17:32:03: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
debug 2022-10-23 17:32:26: Received MQTT message on 'zigbee2mqtt/trv.uf_office/get' with data '{"occupied_heating_setpoint":""}'
debug 2022-10-23 17:32:26: Publishing get 'get' 'occupied_heating_setpoint' to 'trv.uf_office'
debug 2022-10-23 17:32:33: Received Zigbee message from 'trv.uf_office', type 'readResponse', cluster 'hvacThermostat', data '{"occupiedHeatingSetpoint":2300}' from endpoint 1 with groupID 0
info  2022-10-23 17:32:33: MQTT publish: topic 'zigbee2mqtt/trv.uf_office', payload '{"adaptation_run_control":null,"adaptation_run_settings":null,"adaptation_run_status":null,"algorithm_scale_factor":null,"battery":null,"day_of_week":null,"external_measured_room_sensor":null,"heat_available":null,"heat_required":null,"keypad_lockout":null,"linkquality":163,"load_balancing_enable":null,"load_estimate":null,"load_room_mean":null,"mounted_mode_active":null,"mounted_mode_control":null,"occupied_heating_setpoint":23,"pi_heating_demand":null,"preheat_status":null,"programming_operation_mode":null,"radiator_covered":null,"regulation_setpoint_offset":null,"running_state":null,"setpoint_change_source":null,"thermostat_vertical_orientation":null,"trigger_time":null,"update":{"state":null},"update_available":null,"viewing_direction":null,"window_open_external":null,"window_open_feature":null,"window_open_internal":null}'
debug 2022-10-23 17:32:52: Received MQTT message on 'zigbee2mqtt/trv.uf_office/get' with data '{"local_temperature":""}'
debug 2022-10-23 17:32:52: Publishing get 'get' 'local_temperature' to 'trv.uf_office'
debug 2022-10-23 17:32:55: Received Zigbee message from 'trv.uf_office', type 'readResponse', cluster 'hvacThermostat', data '{"localTemp":2422}' from endpoint 1 with groupID 0
info  2022-10-23 17:32:55: MQTT publish: topic 'zigbee2mqtt/trv.uf_office', payload '{"adaptation_run_control":null,"adaptation_run_settings":null,"adaptation_run_status":null,"algorithm_scale_factor":null,"battery":null,"day_of_week":null,"external_measured_room_sensor":null,"heat_available":null,"heat_required":null,"keypad_lockout":null,"linkquality":167,"load_balancing_enable":null,"load_estimate":null,"load_room_mean":null,"local_temperature":24.22,"mounted_mode_active":null,"mounted_mode_control":null,"occupied_heating_setpoint":23,"pi_heating_demand":null,"preheat_status":null,"programming_operation_mode":null,"radiator_covered":null,"regulation_setpoint_offset":null,"running_state":null,"setpoint_change_source":null,"thermostat_vertical_orientation":null,"trigger_time":null,"update":{"state":null},"update_available":null,"viewing_direction":null,"window_open_external":null,"window_open_feature":null,"window_open_internal":null}'
debug 2022-10-23 17:37:05: Received Zigbee message from 'trv.uf_office', type 'commandCheckIn', cluster 'genPollCtrl', data '{}' from endpoint 1 with groupID 0
Also found this error in my HA logs, which might be related:
2022-10-24 10:43:32.574 WARNING (MainThread) [homeassistant.helpers.template] Template variable warning: 'dict object' has no attribute 'system_mode' when rendering '{{ value_json.system_mode }}'
2022-10-24 10:43:32.575 ERROR (MainThread) [homeassistant.components.mqtt.climate] Invalid modes mode:
Edit: included a short screencast of the issue: Home Assistant - MQTT entity update problem - YouTube
I am having the same issue. Seems to be as of the october or september update of both HA and Z2M, but am not sure.
Good to know. Thanks.
Seems to be the same issue as in Popp/Danfoss TRVs become unresponsive with CC2652P · Issue #13478 · Koenkk/zigbee2mqtt (github.com)