sorry no support in proxy for PAC-WF010-E
it does a different handshake, but I don’t have a unit to test and to make it work unfortunately
Can you test one thing for me, attach proxy with melcloud.
And http://esp_ip, turn on the “uart debug” switch
Can you copy paste a couple of message sequences for me? It might contain enough info to make it work
New release with some additions for AA
- AA: Allow overshoot compensation. Use this setting to compensate for overshooting in your thermostat
- AA: Predictive Short-Cycle prevention. Heating offset will be raised by 0.5c when delta between requested and actual feed temp is above 1.0c for the min duration of 4 minutes. This mode is always enabled in Auto Adaptive. In fixed flow heating it can be enabled manually via the switch. the
High Delta detection durationis editable [1m-5m, default 4m] - AA: Only enforce saturation prevention when in active heating/cooling
- AA: Implement dual heating slope for heating. When it gets cold (
< 5c) an additional factor is multiplied with the slope. Setting can now be set in steps of 0.05c - AA: Allow adjustable min flow temp for heating. Override if you are hitting min output capacity during mild weather. [24.0c - 40.0c, default: 25c]
- Add floor dry up, cool compensation curve mode (only works for ftc7+)
- AA: Widen dead zone for UFH profiles during the night
@rokic
Would you be willing to test my .merged.bin version - to see if proxy works for you?
yeah please try @F1p bin. Just to rule out.
I use 9600 baud per default, and that might mess things up.
@gekkekoe, I will try today with UART debug and post what I will get out.
@F1p, I will try. Hopefully already this week ![]()
Also try this, with uart. It should support unsupported messages at 9600, or at least should print more with uart logging so i can hopefully fixed it
OK, I checked a few things and I think that there is an compatibility issue with PAC-WF010-E.
- Proxy connection - with Atom s3 and proxy adapter and Melcloud adapter → Melcloud adapter LED2 is constantly blinking, which means “Server communication or access point communication failed, and ecodan unit communication failed”.
- Only Melcloud adapter connected to port CN105 → everything is OK. Communication works and also Melcloud app is working fine.
- Proxy setup without S3 atom → only proxy adapter between Melcloud adapter and Ecodan CN105. The same error as on 1st point.
- Proxy setup with adapter and S3 atom (without Melcloud adapter on EXT port) → esp32s3-proxy2-z1-en-2025-09-03.1 (ESPHome 2025.7.5) and with esp32s3-proxy2-z1-en-2025-10-12.5 (ESPHome 2025.7.5) all data visible, but I can not start the Ecodan (Off mode by Melcloud) as it is in “slave mode”.
So, I can conclude that with PAC-WF010-E and adapter for proxy setup are some compatibility issues. I don’t think it’s worth to continue investigating.
But I still have some issue with “nomal mode” (non proxy setup) temperature settings. If I have “Selected operating mode” in “Heat target temperature” I can normally adjust “Zone 1 Room Temp” and communication works. If I select “Compensation curve” neither Zone 1 Room Temp or Zone 1 Flow Temp are reacting to changes. If I modify the temperature value, it stays there for approx. 1 minute and then returns back to its original setting. It’s ard to show tis via “Uart logging” because there are to many rows of code. If there is a possibility to export the history of 2 minutes it would be great.
Thanks for help.
Below two logs if something help you out. This is with “non-proxy” setup.
Blockquote
18:12:55 [D] [uart_debug:114]
<<< FC 62 02 7A 10 A3 00 07 00 00 00 00 00 00 00 00 00 00 00 00 00 68
18:12:56 [D] [sensor:104]
‘Heap Free’: Sending state 185232.00000 B with 0 decimals of accuracy
18:12:56 [D] [sensor:104]
‘Loop Time’: Sending state 29.00000 ms with 0 decimals of accuracy
18:12:56 [D] [uart_debug:114]FC 42 02 7A 10 A3 00 07 00 00 00 00 00 00 00 00 00 00 00 00 00 88 FC 42 02 7A 10 A3 00 07 00 00 00 00 00 00 00 00 00 00 00 00 00 88
18:12:56 [D] [sensor:104]
‘Outside Unit Two Phase Pipe Temp’: Sending state 7.00000 °C with 1 decimals of accuracy
18:12:56 [D] [uart_debug:114]
<<< FC 62 02 7A 10 A3 00 07 02 07 00 00 00 00 00 00 00 00 00 00 00 5F
18:12:56 [D] [uart_debug:114]
FC 42 02 7A 10 0F 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 23
18:12:57 [D] [uart_debug:114]
FC 42 02 7A 10 10 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 22
18:12:57 [D] [uart_debug:114]
<<< FC 62 02 7A 10 10 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 02
18:12:57 [D] [uart_debug:114]
FC 42 02 7A 10 13 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 1F
18:12:57 [D] [sensor:104]
‘Operating Runtime’: Sending state 21306.00000 h with 0 decimals of accuracy
18:12:57 [D] [uart_debug:114]
<<< FC 62 02 7A 10 13 01 00 06 00 D5 00 00 00 00 00 00 00 00 00 00 23
18:12:57 [D] [text_sensor:069]
‘Operation Mode’: Sending state ‘Space Heating’
18:12:58 [D] [uart_debug:114]
FC 42 02 7A 10 15 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 1D
18:12:58 [I] [ecodan.component:040]
Could not publish state of sensor ‘status_three_way_valve_2’ with value: ‘1’
18:12:58 [I] [ecodan.component:040]
Could not publish state of sensor ‘status_water_pump_3’ with value: ‘0’
18:12:58 [I] [ecodan.component:018]
Could not publish state of sensor ‘status_mixing_valve’ with value: ‘4.000000’
18:12:58 [I] [ecodan.component:018]
Could not publish state of sensor ‘mixing_valve_step’ with value: ‘0.000000’
18:12:58 [D] [uart_debug:114]
<<< FC 62 02 7A 10 15 01 00 44 01 00 00 01 00 00 00 04 00 00 00 00 B2
18:12:58 [D] [uart_debug:114]
FC 42 02 7A 10 14 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 1E
18:12:58 [D] [sensor:104]
‘Flow Rate’: Sending state 0.00000 L/min with 0 decimals of accuracy
18:12:58 [D] [sensor:104]
‘Estimated Output Power’: Sending state 0.00000 kW with 3 decimals of accuracy
18:12:58 [D] [sensor:104]
‘Estimated Total Daily Energy Produced’: Sending state 0.00000 kWh with 3 decimals of accuracy
18:12:58 [D] [uart_debug:114]
<<< FC 62 02 7A 10 14 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 FE
18:12:59 [D] [uart_debug:114]
FC 42 02 7A 10 26 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 0C
18:12:59 [D] [sensor:104]
‘H/C status’: Sending state 2.00000 with 0 decimals of accuracy
18:12:59 [I] [ecodan.component:018]
Could not publish state of sensor ‘status_heating_cooling_z2’ with value: ‘1.000000’
18:12:59 [D] [sensor:104]
‘DHW Setpoint Value’: Sending state 50.00000 °C with 1 decimals of accuracy
18:12:59 [D] [uart_debug:114]
<<< FC 62 02 7A 10 26 00 00 01 02 00 02 01 13 88 0E 10 07 D0 00 00 56
18:12:59 [D] [uart_debug:114]
FC 42 02 7A 10 28 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 0A
18:12:59 [D] [text_sensor:069]
‘Dip Switch 2 (8-1)’: Sending state ‘00001100’
18:12:59 [D] [climate:396]
‘Zone 1 Flow Temp’ - Sending state:
18:12:59 [D] [climate:399]
Mode: HEAT
18:12:59 [D] [climate:401]
Action: HEATING
18:12:59 [D] [climate:419]
Current Temperature: 36.00°C
18:12:59 [D] [climate:425]
Target Temperature: 36.00°C
18:12:59 [I] [ecodan.component:040]
Could not publish state of sensor ‘status_prohibit_heating_z2’ with value: ‘0’
18:12:59 [I] [ecodan.component:040]
Could not publish state of sensor ‘status_prohibit_cool_z2’ with value: ‘0’
18:12:59 [I] [ecodan.component:040]
Could not publish state of sensor ‘status_server_control_prohibit_heating_z2’ with value: ‘0’
18:12:59 [I] [ecodan.component:040]
Could not publish state of sensor ‘status_server_control_prohibit_cool_z2’ with value: ‘0’
18:12:59 [D] [uart_debug:114]
<<< FC 62 02 7A 10 28 00 00 00 00 01 00 00 00 00 01 00 00 00 00 00 E8
18:12:59 [D] [sensor:104]
‘WiFi Signal dB’: Sending state -64.00000 dBm with 0 decimals of accuracy
18:12:59 [D] [sensor:104]
‘WiFi Signal %’: Sending state 72.00000 % with 0 decimals of accuracy
18:13:00 [D] [uart_debug:114]
FC 42 02 7A 10 A1 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 91
18:13:00 [D] [uart_debug:114]
<<< FC 62 02 7A 10 A1 19 0A
18:13:00 [D] [uart_debug:114]
<<< 0C 00 0B 0A
18:13:00 [D] [sensor:104]
‘Heating Consumed’: Sending state 11.10000 kWh with 2 decimals of accuracy
18:13:00 [D] [sensor:104]
‘Cool Consumed’: Sending state 0.00000 kWh with 2 decimals of accuracy
18:13:00 [D] [sensor:104]
‘DHW Consumed’: Sending state 0.00000 kWh with 2 decimals of accuracy
Blockquote
Time Level Tag Message
18:05:53 [D] [climate:396]
‘Zone 1 Room Temp’ - Sending state:
18:05:53 [D] [climate:399]
Mode: HEAT
18:05:53 [D] [climate:401]
Action: HEATING
18:05:53 [D] [climate:419]
Current Temperature: 17.00°C
18:05:53 [D] [climate:425]
Target Temperature: 28.00°C
18:05:53 [I] [ecodan.component:040]
Could not publish state of sensor ‘status_three_way_valve_2’ with value: ‘1’
18:05:53 [I] [ecodan.component:040]
Could not publish state of sensor ‘status_water_pump_3’ with value: ‘0’
18:05:53 [I] [ecodan.component:018]
Could not publish state of sensor ‘status_mixing_valve’ with value: ‘4.000000’
18:05:53 [I] [ecodan.component:018]
Could not publish state of sensor ‘mixing_valve_step’ with value: ‘0.000000’
18:05:53 [D] [uart_debug:114]
<<< FC 62 02 7A 10 15 01 00 45 01 00 00 01 00 00 00 04 00 00 00 00 B1
18:05:53 [D] [climate:396]
‘Zone 1 Room Temp’ - Sending state:
18:05:54 [D] [climate:399]
Mode: HEAT
18:05:54 [D] [climate:401]
Action: HEATING
18:05:54 [D] [climate:419]
Current Temperature: 17.00°C
18:05:54 [D] [climate:425]
Target Temperature: 28.00°C
18:05:54 [D] [uart_debug:114]FC 42 02 7A 10 14 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 1E
18:05:54 [D] [climate:396]
‘Zone 1 Room Temp’ - Sending state:
18:05:54 [D] [climate:399]
Mode: HEAT
18:05:54 [D] [climate:401]
Action: HEATING
18:05:54 [D] [climate:419]
Current Temperature: 17.00°C
18:05:54 [D] [climate:425]
Target Temperature: 28.00°C
18:05:54 [D] [sensor:104]
‘Flow Rate’: Sending state 0.00000 L/min with 0 decimals of accuracy
18:05:54 [D] [sensor:104]
‘Estimated Output Power’: Sending state 0.00000 kW with 3 decimals of accuracy
18:05:54 [D] [sensor:104]
‘Estimated Total Daily Energy Produced’: Sending state 0.00000 kWh with 3 decimals of accuracy
18:05:54 [D] [uart_debug:114]
<<< FC 62 02 7A 10 14 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 FE
18:05:54 [D] [climate:396]
‘Zone 1 Room Temp’ - Sending state:
18:05:54 [D] [climate:399]
Mode: HEAT
18:05:54 [D] [climate:401]
Action: HEATING
18:05:54 [D] [climate:419]
Current Temperature: 17.00°C
18:05:54 [D] [climate:425]
Target Temperature: 28.00°C
18:05:54 [D] [uart_debug:114]
FC 42 02 7A 10 26 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 0C
18:05:54 [D] [text_sensor:069]
‘Operation Mode’: Sending state ‘Space Heating’
18:05:54 [D] [climate:396]
‘Zone 1 Room Temp’ - Sending state:
18:05:54 [D] [climate:399]
Mode: HEAT
18:05:54 [D] [climate:401]
Action: HEATING
18:05:54 [D] [climate:419]
Current Temperature: 17.00°C
18:05:54 [D] [climate:425]
Target Temperature: 28.00°C
18:05:54 [D] [sensor:104]
‘WiFi Signal dB’: Sending state -64.00000 dBm with 0 decimals of accuracy
18:05:54 [D] [sensor:104]
‘WiFi Signal %’: Sending state 72.00000 % with 0 decimals of accuracy
18:05:54 [D] [sensor:104]
‘H/C status’: Sending state 2.00000 with 0 decimals of accuracy
18:05:54 [I] [ecodan.component:018]
Could not publish state of sensor ‘status_heating_cooling_z2’ with value: ‘1.000000’
18:05:54 [D] [sensor:104]
‘DHW Setpoint Value’: Sending state 50.00000 °C with 1 decimals of accuracy
18:05:54 [D] [uart_debug:114]
<<< FC 62 02 7A 10 26 00 00 01 02 00 02 01 13 88 0E 10 07 D0 00 00 56
18:05:54 [D] [climate:396]
‘Zone 1 Room Temp’ - Sending state:
18:05:55 [D] [climate:399]
Mode: HEAT
18:05:55 [D] [climate:401]
Action: HEATING
18:05:55 [D] [climate:419]
Current Temperature: 17.00°C
18:05:55 [D] [climate:425]
Target Temperature: 28.00°C
18:05:55 [D] [uart_debug:114]
FC 42 02 7A 10 28 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 0A
18:05:55 [D] [switch:016]
‘UART Logging’ Turning OFF.
please try this file: https://github.com/gekkekoe/esphome-ecodan-hp/releases/download/2025-10-17.1/esp32s3-proxy2-z1-en-2025-10-17.1.ota.bin
Should match your config. flash it via http://esp_ip, at the bottom of the page
I hope it will fix your proxy issue. Please verify for us, since there are not a lot of users with PAC-WF010-E to test.
non proxy setup works fine no need to test that ![]()
@rokic latest release should support your wifi adapter
Hi,
just tested, but no success.
As I wrote before. As soon as I connect Melcloud adapter to “proxy adapter” it has no communication anymore. LED2 is constantly blinking, which means “Server communication or access point communication failed, and ecodan unit communication failed”.
No matter if there is ESP installed or not.
Also Melcloud app somehow sees that there is a communication ("Last communication… time/date from few second before), but anything I try to do in Melcloud app does not respond.
Commands from HASS works, but I don’t see any temperature. Basically everything under Sensors and Diagnostic is “unkown” or “0”.
I enabled UART if something helps you:
| 18:56:31 | [D] | [uart_debug:114] | >>> 01_00_40_00_00_06_02_7A_00_00_B5 |
|---|---|---|---|
| 18:56:31 | [D] | [uart_debug:114] | >>> 02 FF FF 00 00 00 00 02 |
| 18:56:31 | [D] | [uart_debug:114] | <<< 02_FF_FF_00_00_00_00_02 |
| 18:56:31 | [D] | [uart_debug:114] | <<< 02 FF FF 80 00 00 0A |
| 18:56:31 | [D] | [uart_debug:114] | >>> 02_FF_FF_80_00_00_0A |
| 18:56:31 | [D] | [sensor:104] | ‘WiFi Signal dB’: Sending state -62.00000 dBm with 0 decimals of accuracy |
| 18:56:31 | [D] | [sensor:104] | ‘WiFi Signal %’: Sending state 76.00000 % with 0 decimals of accuracy |
| 18:56:31 | [D] | [uart_debug:114] | <<< 01 00 40 00 00 06 02 7A 00 00 B5 |
| 18:56:31 | [D] | [uart_debug:114] | >>> 01_00_40_00_00_06_02_7A_00_00_B5 |
| 18:56:31 | [D] | [uart_debug:114] | >>> 02 FF FF 00 00 00 00 02 |
| 18:56:31 | [D] | [uart_debug:114] | <<< 02_FF_FF_00_00_00_00_02 |
| 18:56:31 | [D] | [text_sensor:069] | ‘Operation Mode’: Sending state ‘Unknown’ |
| 18:56:31 | [D] | [sensor:104] | ‘ESP Uptime’: Sending state 571.73798 s with 0 decimals of accuracy |
| 18:56:31 | [D] | [uart_debug:114] | <<< 02 FF FF 80 00 00 0A |
| 18:56:31 | [D] | [uart_debug:114] | >>> 02_FF_FF_80_00_00_0A |
| 18:56:32 | [D] | [uart_debug:114] | <<< 01 00 40 00 00 06 02 7A 00 00 B5 |
| 18:56:32 | [D] | [uart_debug:114] | >>> 01_00_40_00_00_06_02_7A_00_00_B5 |
| 18:56:32 | [D] | [uart_debug:114] | >>> 6E 02 |
| 18:56:32 | [D] | [uart_debug:114] | <<< 6E_02 |
| 18:56:33 | [D] | [uart_debug:114] | >>> 6E 02 |
| 18:56:33 | [D] | [uart_debug:114] | <<< 6E_02 |
| 18:56:33 | [D] | [sensor:104] | ‘Estimated COP’: Sending state 0.00000 with 2 decimals of accuracy |
| 18:56:33 | [D] | [uart_debug:114] | >>> 6E 02 |
| 18:56:33 | [D] | [uart_debug:114] | <<< 6E_02 |
| 18:56:34 | [D] | [uart_debug:114] | >>> 02 FF FF 00 00 00 00 02 |
| 18:56:34 | [D] | [uart_debug:114] | <<< 02_FF_FF_00_00_00_00_02 |
| 18:56:34 | [D] | [uart_debug:114] | <<< 02 FF FF 80 00 00 0A |
| 18:56:34 | [D] | [uart_debug:114] | >>> 02_FF_FF_80_00_00_0A |
| 18:56:34 | [D] | [uart_debug:114] | <<< 01 00 40 00 00 06 02 7A 00 00 B5 |
| 18:56:35 | [D] | [uart_debug:114] | >>> 01_00_40_00_00_06_02_7A_00_00_B5 |
| 18:56:35 | [D] | [text_sensor:069] | ‘Operation Mode’: Sending state ‘Unknown’ |
| 18:56:35 | [D] | [uart_debug:114] | >>> 02 FF FF 00 00 00 00 02 |
| 18:56:35 | [D] | [uart_debug:114] | <<< 02_FF_FF_00_00_00_00_02 |
| 18:56:35 | [D] | [uart_debug:114] | <<< 02 FF FF 80 00 00 0A |
| 18:56:35 | [D] | [uart_debug:114] | >>> 02_FF_FF_80_00_00_0A |
| 18:56:35 | [D] | [uart_debug:114] | <<< 01 00 40 00 00 06 02 7A 00 00 B5 |
| 18:56:35 | [D] | [uart_debug:114] | >>> 01_00_40_00_00_06_02_7A_00_00_B5 |
| 18:56:35 | [D] | [uart_debug:114] | >>> 02 FF FF 00 00 00 00 02 |
| 18:56:35 | [D] | [uart_debug:114] | <<< 02_FF_FF_00_00_00_00_02 |
| 18:56:35 | [D] | [light:052] | ‘Led’ Setting: |
| 18:56:35 | [D] | [light:069] | Brightness: 50% |
| 18:56:35 | [D] | [light:076] | Red: 0%, Green: 100%, Blue: 0% |
| 18:56:35 | [D] | [light:103] | Transition length: 1.0s |
| 18:56:35 | [D] | [uart_debug:114] | <<< 02 FF FF 80 00 00 0A |
| 18:56:35 | [D] | [uart_debug:114] | >>> 02_FF_FF_80_00_00_0A |
| 18:56:35 | [D] | [uart_debug:114] | <<< 01 00 40 00 00 06 02 7A 00 00 B5 |
| 18:56:35 | [D] | [uart_debug:114] | >>> 01_00_40_00_00_06_02_7A_00_00_B5 |
| 18:56:36 | [D] | [sensor:104] | ‘Heap Free’: Sending state 183620.00000 B with 0 decimals of accuracy |
| 18:56:36 | [D] | [sensor:104] | ‘Loop Time’: Sending state 41.00000 ms with 0 decimals of accuracy |
| 18:56:36 | [D] | [switch:016] | ‘UART Logging’ Turning OFF. |
@rokic
Try Release Minor release (proxy fixes) · gekkekoe/esphome-ecodan-hp · GitHub
I found some timing issues that should have been resolved in this one
- Run serial IO on the
sparecore for low latency, refactor proxy - Add esp core 0 and 1 monitoring
- wifi: Remove
fast_connectoption - AA: Add efficiency probe during dead zone to find a more efficient offset (probe only active while heating)
- Use work around for espidf 5.4.2 UART issues. Upgrading to Esphome 2025.10.2
- Adds proper retry and timeout for cmd sent to the heatpump
- Throttle get service code results (less spamming)
changelog:
- Reverted uart workaround and upgraded to esphome 2025.10.3 (it has been fixed in esphome 2025.10.3)
- AA: Fixed enforcing safety cap of heating offset
- AA: Allow override of outdoor temp sensor
- AA: Allow predictive cycle prevention to be turned off during AA
- AA: Temporary allow manual editing of offsets (Don’t depend on this, will be removed when algorithm is working stable)
- AA: Increased efficiency probe from 0.01 to 0.02 (
speedupdecay) - Add 0x0f condensing temp fallback if we encounter stuck
40.57value - Proxy: handle 0x28 byte 11 clear when in proxy
- AA: Use multi zone status to ensure that zones are actually operating (for independent zones)
- Adjust timeout settings for heatpump and proxy to ensure there’s no overlapping
- Use controller day of the year to avoid double counting in the forever increasing counters
- Remove sntp usage in the
delta_energy_consumed_increasingsensor (use the controller day of the year instead) - Only handle Off → On and On → Off compressor transitions. Ignore the unknown states
- Remember states for
reported daily consumptionandestimated COP(will not be reset after reboot) - AA: adjust z1 and z2 offset independently when boosting
Found a regression, Estimated Total Daily Energy Produced was not reset properly.
- remove sntp requirement and use the time from the heatpump to detect day transitions (all external dependencies have been removed)
- fixed issue where
daily_computed_output_powersensor was not reset on day transition
Pre-release: Add alternative auto adaptive based on delta T profile. Should be much easier to work with and almost no parameters needed.
Release 2025-11-04.3 · gekkekoe/esphome-ecodan-hp
upgraded to esphome 2025.10.4 AA: Add alternative heating strategy: Delta T control AA: Delta T, handle defrost weather by reducing delta T to minimum of the selected profile
documentation: esphome-ecodan-hp/docs/auto-adaptive-delta-t.md at main · gekkekoe/esphome-ecodan-hp · GitHub
Hi,
Maybe I missed the information somewhere but I cannot understand whether I need logic level shifters between cn105 and Grove port on Atom S3 Lite. From the instructions I can see that the connection is done directly between the devices. But what I found as information is that cn105 port provides logic level 5V (RX/TX) and Atom S3 Lite Grove port is 3.3V. Is there any logic level shifter embedded in Atom S3 Lite? Is it safe connecting directly both devices without logic level shifter?
not needed you can connect the s3 lite directly as shown in the docs
new release:
- upgraded to esphome 2025.10.4
- AA: Add alternative heating strategy: Delta T control. Please test/use/migrate to this strategy, it will replace the
self learning curvein the next release. It should have superior performance. use the simulator to choose the correct profile - AA: Delta T, handle defrost weather by reducing delta T to minimum of the selected profile
- AA: Ensure auto adaptive loop (if enabled) is executed on compressor off → on transition
- AA: Use z1/z2 return temp instead of primary when using multi zones
- Short cycle: handle lockout restore periodically, fixes lockout state stuck when rebooting during lockout
- AA: Derive max error range from floor type, ufh = 1.5, hybrid = 2.0, radiator = 2.5
- AA: Handle predictive cycle boost when using Delta T strategy
- Add Pump consumption, speed setting
For my unit Heating delivered, DHW delivered and Cool delivered are not reported. Is there specific configuration somewhere for this.
Also I have a question about the consumed energy. As I understand at the end of the day the total consumed energy for the day is reported. This means that the value that I have in Heating Consumed entry in fact is the value for the previous day. Is this correct? I’m trying to understand how to build correct history graph with the consumption per day