Finally... I believe a table that many Home assistant users have been searching for!
Below is the Goodwe GM3000 Smart Power Meter table of modbus registers (and likely similar or the same for the GW1000 - the single phase version - though untested).
Notes on use:
The default modbus/RS485 address of the GW3000 is 3. It is likely changeable in the registers above Decimal 120 - but that is beyond the scope of this post.
The correct modbus function code to read the GW3000 is "03 Read Holding Registers (4x)" or equivalent.
Check the hints below the code. Ive added a few tips that I trust may help your HA/ESPHome + modbus journey. See below.
for your convenience i have added both the ESPHome and Home Assistant code.
First, Home Assistant code:
# this code is lifted straight from the modbus section of a Home Assistant configuration.yaml
- name: "PwrMtr" # use your own name for your power meter here
type: tcp # TCP of course! if you are using a serial port, change accordingly
host: 192.168.xxx.xxx # LAN IP address of your transparent tcp to RS485 slave
port: 8899 # NOTE: the most common default port is 509.
#### adjust your code to match your network####
delay: 0 # standard settings here, use what suits your network.
message_wait_milliseconds: 200
timeout: 5
sensors:
# PwrMtr sensors
- name: "PwrMtr Active Energy Consumption" # As per table. Change if you wish
unique_id: PwrMtr_Active_Energy_Consumption
slave: 3 # default address for the GW3000
address: 0x0047 # Starting register. Decimal 71.
input_type: holding
data_type: float32
scale: 0.001 #edit to suit your use
unit_of_measurement: "kWh"
precision: 1
slave_count: 2 # the first four registers are 32 bit. ie 2 registers give the correct reading
state_class: total_increasing # you must use this class for the sensor to read correctly
scan_interval: 60 # Poll this specific sensor every 60 seconds # See hints below
- name: "PwrMtr Active Energy Production"
unique_id: PwrMtr_Active_Energy_Production # there are four 32 bit registers. seperated here for ease
slave: 3
address: 0x0049
input_type: holding
data_type: float32
scale: 0.001
precision: 1
slave_count: 2
- name: "Reactive Energy"
unique_id: Reactive_Energy
slave: 3
address: 0x004B
input_type: holding
data_type: float32
scale: 0.001
unit_of_measurement: "kVArh"
precision: 1
slave_count: 2
- name: "Capacitive Energy"
unique_id: Capacitive_Energy
slave: 3
address: 0x004D
input_type: holding
data_type: float32
scale: 0.001
precision: 1
slave_count: 2
- name: "PwrMtr 5" # remaining tabled registers can be read with one query.
unique_id: PwrMtr_5 # Enter separately if you want to name directly from modbus
slave: 3
address: 0x0061
input_type: holding
scale: 0.1
unit_of_measurement: "°C"
precision: 1
slave_count: 22
state_class: measurement
- Now for the ESPHome yaml code
## The following code is from a Kincony KC868 v3 wifi unit. it is not the complete code, retaining only the sections required for RS485 and the GW3000. with only a few modifications it runs the excellent Waveshare ESP32-S3 8 relay wifi unit. this code IS for wifi, change as necessary if using ethernet.
esphome:
name: kincony-board # match to your board
friendly_name: S1HControl # use your name for this device
platformio_options:
board_build.extra_flags:
# WIFI_CONTROL_SELF_MODE = 0
# WIFI_CONTROL_SELF_MODE = 1
- "-DWIFI_CONTROL_SELF_MODE=1"
external_components:
- source: # use the correct links for your device
type: git
url: https://github.com/hzkincony/esphome-tuya-wifi-mcu
ref: v1.3.1
esp32:
board: esp32-s3-devkitc-1 # all specific to your board - use the correct details!!
framework:
type: arduino
api:
encryption:
key: "xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx=" #ESPHome will specify this key
ota:
- platform: esphome # required for OTA (Over The Air) updates to your code
logger:
#ethernet: # ethernet disabled here. adjust together with wifi to match your network.
# type: W5500
# clk_pin: GPIO1
# mosi_pin: GPIO2
# miso_pin: GPIO41
# cs_pin: GPIO42
# interrupt_pin: GPIO43
# reset_pin: GPIO44
wifi:
ssid: !secret wifi_ssid
manual_ip: # set for your network. suggest you do use a static IP
static_ip: 192.168.xx.xx
gateway: 192.168.xx.xx
subnet: 255.255.255.0
dns1: 192.168.xxx.xxx
##use_address: 192.168.xxx.xxx # not relevant to GW3000. Use when reprogramming board to a new IP
#dns2: The backup DNS server to use.
i2c: # configure for your board
- id: bus_a
sda: 8
scl: 18
scan: true
frequency: 400kHz
pcf8574: # this is an extension board mounted on the KC838. # configure for your board
- id: 'pcf8574_hub_out_1' # for output channel 0-7| input channel 8-15
i2c_id: bus_a
address: 0x22
pcf8575: true
uart:
- id: uart_1 #RS485
tx_pin: 39
rx_pin: 38
baud_rate: 9600 # baud rate is pretty standard on code ive seen....
# dummy_receiver: true # you must add data bits, parity and stop bits
# after:
# timeout: 10ms
data_bits: 8
parity: NONE
stop_bits: 1
modbus:
- id: modbus1
uart_id: uart_1
modbus_controller:
- id: S1H_Temps # I left this here so can see how to add another modbus slave
address: 0x0B ## (dec 11) address of the Modbus slave device on the bus
modbus_id: modbus1
setup_priority: -10
- id: S1H_PwrMtr
address: 0x03 ## (dec 5) address of the Modbus slave device on the bus
modbus_id: modbus1
setup_priority: -10
#### Actual GW3000 code below #################################################
- platform: modbus_controller # again, use your names
modbus_controller_id: S1H_PwrMtr
name: "S1HPwrMtr Active Energy Cnsmptn." # S1HPwrMtr is my device name, and register name abbreviated
# change to your own naming format.
register_type: holding
address: 0x47 ## address of the register
value_type: FP32 # note the 32 bit register
register_count: 2
accuracy_decimals: 1 #adjust the scales to suit
filters:
- multiply: 0.001
name: "S1HPwrMtr Active Energy Prod." # Register name abbreviated
address: 0x49 ## address of the register
value_type: FP32
register_count: 2
filters:
- multiply: 0.001
name: "S1HPwrMtr Reactive Energy" # Register name abbreviated
address: 0x4B ## address of the register
value_type: FP32
register_count: 2
filters:
- multiply: 0.001
name: "S1HPwrMtr Cap. Energy" # Register name abbreviated
address: 0x4D ## address of the register
value_type: FP32
register_count: 2
filters:
- multiply: 0.001
#### below, the registers numbered decimal 98 thru 120 only yields 13 useful values. despite being able to query the full 22 register series using modbus, ESPHome requires query for each register.
#### IMPORTANT NOTICE: THE GW3000 REGISTERS numbered dec 98 THRU 120 ON THE MANUFACTURERS TABLE ARE ACTUALLY 97 THRU 119. YOU MUST SUBTRACT decimal 1 FROM EVERY REGISTER IN THAT RANGE ....####
#### Grey and half bald from ripping your hair out? Join the ESPHome Home Assistant Modbus Sufferers Club. Where we expect incompatibility, non functionality, non-interchangeability, change of compatibilities and namings and reinvent the same wheel several times over, required many focused searches, until we find the required code in a dark shady corner of the internet, Happy because the sensor finally works, not so happy because irreparably, early heart failure has already made its dark mark on the DNA of the believing.. And with all due respects, if HA and ESPHome dont achieve the goal of removing your hair and sanity, the device manufacturers are in cahoots and will finish the job on behalf of the afore-mentioned. :( \ :( [sword fight] :p [some hair] X| [no hair, potentially DOA]. Please forgive one's morbid outlook. I love all you volunteer guys and stand in absolute awe of of your incalculable efforts. HA, ESPHome have never been better, but the adoption of slightly more technical devices is challenging ####
#### All comments without prejudice or presonal accusation, purely constructive criticism ####
#### Right, thats out of the way, moving right on.....####
name: "S1HPwrMtr L1-N Voltage" # Register name abbreviated
address: 0x61 ## address of the register
unit_of_measurement: "V"
#value_type: FP32 # all these are 16 bit. you should need value_type at all
register_count: 1 # read 8 registers
filters:
- multiply: 0.1
name: "S1HPwrMtr L2-N Voltage" # Register name abbreviated
address: 0x62 ## address of the register
filters:
- multiply: 0.1
name: "S1HPwrMtr L3-N Voltage1" # Register name abbreviated
address: 0x63 ## address of the register
filters:
- multiply: 0.1
name: "S1HPwrMtr L1 Current" # Register name abbreviated
address: 0x64 ## address of the register
unit_of_measurement: "A"
filters:
- multiply: 0.01
name: "S1HPwrMtr L2 Current" # Register name abbreviated
address: 0x65 ## address of the register
filters:
- multiply: 0.01
name: "S1HPwrMtr L3 Current" # Register name abbreviated
address: 0x66 ## address of the register
filters:
- multiply: 0.001
name: "S1HPwrMtr L1 ActPwr" # Register name abbreviated
address: 0x67 ## address of the register
unit_of_measurement: "kW"
accuracy_decimals: 2
filters:
- multiply: 1
name: "S1HPwrMtr L2 ActPwr" # Register name abbreviated
address: 0x68 ## address of the register
filters:
- multiply: 1
name: "S1HPwrMtr L3 ActPwr" # Register name abbreviated
address: 0x69 ## address of the register
filters:
- multiply: 1
name: "S1HPwrMtr Total Active Power"
address: 0x6A ## address of the register
filters:
- multiply: 0.0001
name: "S1HPwrMtr Reactive Power"
address: 0x6B ## address of the register
unit_of_measurement: "kVAr"
filters:
- multiply: 0.01
name: "S1HPwrMtr Apparent Power"
address: 0x6F ## address of the register
unit_of_measurement: "kVA"
filters:
- multiply: 0.001
name: "S1HPwrMtr Frequency"
address: 0x77 ## address of the register
unit_of_measurement: "Hz"
filters:
- multiply: 0.01
#### Actual GW3000 code above #################################################
### the below registers are not relevant to the GW3000, included as an example of reading the second slave noted above, in this case an 8 channel temperature acquisition device.
modbus_controller_id: S1H_Temps
name: "S1H Temp 3"
register_type: read
address: 0x0192 ## address of the register inside the Modbus slave device
unit_of_measurement: "C"
value_type: U_WORD
filters:
- multiply: 0.1
name: "S1H Temp 4"
register_type: read
address: 0x0193 ## address of the register inside the Modbus slave device
value_type: U_WORD
filters:
- multiply: 0.1
name: "S1H Temp 5"
register_type: read
address: 0x0194 ## address of the register inside the Modbus slave device
value_type: U_WORD
filters:
- multiply: 0.1
name: "S1H Temp 6"
register_type: read
address: 0x0195 ## address of the register inside the Modbus slave device
value_type: U_WORD
filters:
- multiply: 0.1
name: "S1H Temp 7"
register_type: read
address: 0x0196 ## address of the register inside the Modbus slave device
value_type: U_WORD
filters:
- multiply: 0.1
register_type: read
address: 0x0197 ## address of the register inside the Modbus slave device
value_type: U_WORD
filters:
- multiply: 0.1
web_server:
port: 80
font:
- file: "gfonts://Roboto"
display:
- platform: ssd1306_i2c
i2c_id: bus_a
model: "SSD1306 128x64"
address: 0x3C
lambda: |-
it.printf(0, 0, id(roboto), "KinCony kinconyboard");
Suggestions and hints for bringing modbus devices online with either Home Assistant or ESPHome:
DO bench test your device before installing. Get a usb to serial conversion device - cheap from your local electronics store. Connect this on your PC, have a power supply handy and get your device live. Then use a program like Modbus Poll to connect direct from the PC to the device. This exercise can be exceptionally frustrating to get your PC and device talking, particularly when you are new to Home Assistant, modbus, how to read modbus tables. Believe me, its much easier to troubleshoot , record required functions, then test your yaml at your desk than when the device is installed in roof space and your desk is two floors lower. once communicating you can check each function so you are 100% certain the device is working. (Disclaimer: I get no kickbacks from the Modbus Poll software writers
I am the biggest software scrooge there is and greatly appreciate the inestimable efforts of the open source/freeware community, but the small cost for Modbus Poll is one of the best investments you will make) -
Use Modbus Poll to work through all the expected functions of your slave devices. note the device address, register addresses, which function is needed for each register. Having this information will be useful for when you are writing your YAML
Finally write your YAML for the device and live operate/read all functions. because once the device is in the field and your trying to connect via wifi, you soon find ESPHome and Home Assistant have none of the useful tools to operate the device that Modbus Poll has. Modbus Poll is also very useful for once in a lifetime operations like changing the device address.
You will find google to be a good friend in finding the right code for a particular operation - it even generates YAML code - take care though, the code will usually not work straight off - it will need tweaking for your specific. Google does generate some ESPHome code that used Home Assistant modbus expressions and actions. Sometimes there not even a direct comparison from one code to the other, which is actually very frustrating. Train yourself to be a logically thinking detective, the code you need will be out there. Keep looking until you find it.
the GW3000 has many more registers numbering up from 120. there is likely a lot of extra functionality available, one of which would be to change the default address from 3. Most people would only be looking for the imported / exported power registers for their energy page in HA.
Modbus use on Home assistant. its excellent ..... up to a certain level of concurrent usage. Beyond that action becomes delayed or missed, and if pushed far enough will actually stop communicating altogether. If that happens you will lose control of your slave devices. If you only have a few slave devices congestion is unlikely to be an issue. Personally i had six wifi-RS485 server devices (the EW11A is cheap and the best of the entire line-up if you want a recommendation) with access to 3 or 4 RS485 slaves on each bus. The slaves were temp sensors, DO and DI, and a VSD/VFD motor drive. I was trying to query 8 temps and the 10 status registers on the VSD 10 seconds. Very Bad Idea. I had to back the temp timing to 20 seconds, and the VSD to 60 seconds. ESP32 devices on ESPHome are proving more efficient.
When using a any modbus device, your top priority will be to get the genuine modbus table for that device. There are far too many variables in modbus for you to try to guess the register addresses and function codes.
carefully connect your RS485 modbus wiring, be sure to use twisted pair cable - shielded if running near heavy electrical mains. Modbus Poll mainly connects as per the manufacturers modbus tables. It the event that you cannot get communication working try/check the following points:
a. try switching the A and B wires. For unknown reasons some devices work correctly when wired with A and B switched. When benchtesting record this anomaly for that device - you will need to wire it with A and B reversed in your final bus.
b. if you have several slave devices on one bus, make sure you connect them in series - a daisy chain. If some of your slave devices wont work, the easiest method to troubleshoot is disconnect the bus after the the closest device to your ESPhome /serial / tcp-modbus server, and get that device working correctly first. The add the remaining devices one by one ensuring functionality after each addition.
c. ensure all slaves powered with correct voltage and polarity
d. ensure the RS485/modbus wires have terminated at every connection correctly.
e. ensure all slave devices have a unique address numbered 1-247. The do not need to be sequentially numbered but must be unique.
f. The A and B may need switching. I have had different brands of devices exhibit different operation than when benchtested once the devices were daisy chained.
g. Remember - you can also you modbus poll to test the daisy chained devices. The is very useful to determine if the lack of functionality is related to the bus of devices, or whether its incorrect YAML
h. note FYI that the esphome / serial / tcp-modbus server device bus address is 0. in exceptionally rare circumstances that may need to be actually coded on your YAML. a fact to file away in the back of your memory, just in case. You will likely never need to action this. -
Before you sit down to work out you modbus devices, get a heavy duty dose of patience. You will need it!