- These are the results:
Immergas - Zone 2 min CH? candidate (near R08 3003) (3004) 1
Immergas - Zone 2⁄3 CH candidate (gap 4351-4356) (4352) NA
Immergas - Zone 2⁄3 CH candidate (gap 4351-4356) (4353) NA
Immergas - Zone 2⁄3 candidate (near R08) (3005) NA
Immergas - Zone 2⁄3 cooling candidate (gap 4351-4356) (4354) NA
Immergas - Zone 2⁄3 cooling candidate (gap 4351-4356) (4355) NA
With some error on the log:
13:30:34 [W] [modbus:247]
Error function code: 0x83 exception: 2, address: 11, 17ms after last send
13:30:34 [E] [modbus_controller:097]
Modbus error function code: 0x3 exception: 2
13:30:34 [E] [modbus_controller:104]
Modbus error - last command: function code=0x3 register address = 0x11C7 registers count=1 payload size=0
13:30:34 [W] [modbus:247]
Error function code: 0x83 exception: 2, address: 11, 22ms after last send
13:30:34 [E] [modbus_controller:097]
Modbus error function code: 0x3 exception: 2
13:30:34 [E] [modbus_controller:104]
Modbus error - last command: function code=0x3 register address = 0xBBD registers count=1 payload size=0
13:30:34 [W] [modbus:247]
Error function code: 0x83 exception: 2, address: 11, 25ms after last send
13:30:34 [E] [modbus_controller:097]
Modbus error function code: 0x3 exception: 2
13:30:34 [E] [modbus_controller:104]
Modbus error - last command: function code=0x3 register address = 0x11CA registers count=1 payload size=0
13:30:34 [W] [modbus:247]
Error function code: 0x83 exception: 2, address: 11, 29ms after last send
13:30:34 [E] [modbus_controller:097]
Modbus error function code: 0x3 exception: 2
13:30:34 [E] [modbus_controller:104]
Modbus error - last command: function code=0x3 register address = 0x1100 registers count=1 payload size=0
13:30:34 [W] [modbus:247]
Error function code: 0x83 exception: 2, address: 11, 25ms after last send
13:30:34 [E] [modbus_controller:097]
Modbus error function code: 0x3 exception: 2
13:30:34 [E] [modbus_controller:104]
Modbus error - last command: function code=0x3 register address = 0x11CD registers count=1 payload size=0
13:30:34 [W] [modbus:247]
Error function code: 0x83 exception: 2, address: 11, 31ms after last send
13:30:34 [E] [modbus_controller:097]
Modbus error function code: 0x3 exception: 2
13:30:34 [E] [modbus_controller:104]
Modbus error - last command: function code=0x3 register address = 0x1101 registers count=1 payload size=0
13:30:35 [W] [modbus:247]
Error function code: 0x83 exception: 2, address: 11, 22ms after last send
13:30:35 [E] [modbus_controller:097]
Modbus error function code: 0x3 exception: 2
13:30:35 [E] [modbus_controller:104]
Modbus error - last command: function code=0x3 register address = 0x11E9 registers count=1 payload size=0
13:30:35 [W] [modbus:247]
Error function code: 0x83 exception: 2, address: 11, 27ms after last send
13:30:35 [E] [modbus_controller:097]
Modbus error function code: 0x3 exception: 2
13:30:35 [E] [modbus_controller:104]
Modbus error - last command: function code=0x3 register address = 0x1102 registers count=1 payload size=0
13:30:35 [W] [modbus:247]
Error function code: 0x83 exception: 2, address: 11, 24ms after last send
13:30:35 [E] [modbus_controller:097]
Modbus error function code: 0x3 exception: 2
13:30:35 [E] [modbus_controller:104]
Modbus error - last command: function code=0x3 register address = 0x11F8 registers count=1 payload size=0
13:30:35 [W] [modbus:247]
Error function code: 0x83 exception: 2, address: 11, 28ms after last send
13:30:35 [E] [modbus_controller:097]
Modbus error function code: 0x3 exception: 2
13:30:35 [E] [modbus_controller:104]
Modbus error - last command: function code=0x3 register address = 0x1103 registers count=1 payload size=0
13:30:35 [E] [modbus_helpers:087]
not enough data for value type=1 offset=2 size=2 required=2
13:30:35 [E] [modbus_helpers:076]
not enough data for value type=1 offset=4 size=2
13:30:35 [E] [modbus_helpers:087]
not enough data for value type=1 offset=2 size=2 required=2
- I can Attach the log
Done: reg 0-999, found 1
Done: reg 1000-1999, found 0
Done: reg 2000-2999, found 6
Done: reg 3000-3999, found 13
Done: reg 4000-4999, found 28
Done: reg 5000-5999, found 0
Done: reg 6000-6999, found 15
Done: reg 7000-7999, found 0
Done: reg 8000-8999, found 0
Done: reg 9000-9999, found 0
[14:34:51.353][I][T_PDU_SCAN:071]: OK reg=512 value=0
[14:37:23.525][I][T_PDU_SCAN:071]: OK reg=2000 value=1
[14:37:25.128][I][T_PDU_SCAN:071]: OK reg=2010 value=0
[14:37:25.281][I][T_PDU_SCAN:071]: OK reg=2011 value=0
[14:37:38.729][I][T_PDU_SCAN:071]: OK reg=2095 value=500
[14:37:39.530][I][T_PDU_SCAN:071]: OK reg=2100 value=0
[14:37:39.845][I][T_PDU_SCAN:071]: OK reg=2102 value=0
[14:41:18.748][I][T_PDU_SCAN:071]: OK reg=3000 value=563
[14:41:18.904][I][T_PDU_SCAN:071]: OK reg=3001 value=543
[14:41:19.054][I][T_PDU_SCAN:071]: OK reg=3002 value=310
[14:41:19.214][I][T_PDU_SCAN:071]: OK reg=3003 value=0
[14:41:21.315][I][T_PDU_SCAN:071]: OK reg=3016 value=583
[14:41:23.066][I][T_PDU_SCAN:071]: OK reg=3027 value=0
[14:41:23.225][I][T_PDU_SCAN:071]: OK reg=3028 value=0
[14:41:23.380][I][T_PDU_SCAN:071]: OK reg=3029 value=32768
[14:41:27.212][I][T_PDU_SCAN:071]: OK reg=3053 value=0
[14:41:27.380][I][T_PDU_SCAN:071]: OK reg=3054 value=0
[14:41:27.699][I][T_PDU_SCAN:071]: OK reg=3056 value=458
[14:41:28.488][I][T_PDU_SCAN:071]: OK reg=3061 value=0
[14:41:28.659][I][T_PDU_SCAN:071]: OK reg=3062 value=0
[14:44:31.551][I][T_PDU_SCAN:071]: OK reg=4011 value=0
[14:45:01.960][I][T_PDU_SCAN:071]: OK reg=4201 value=1
[14:45:02.113][I][T_PDU_SCAN:071]: OK reg=4202 value=9
[14:45:25.785][I][T_PDU_SCAN:071]: OK reg=4350 value=42
[14:45:25.961][I][T_PDU_SCAN:071]: OK reg=4351 value=50
[14:45:26.753][I][T_PDU_SCAN:071]: OK reg=4356 value=12
[14:45:26.903][I][T_PDU_SCAN:071]: OK reg=4357 value=7
[14:45:34.129][I][T_PDU_SCAN:071]: OK reg=4402 value=4
[14:45:34.278][I][T_PDU_SCAN:071]: OK reg=4403 value=1
[14:45:35.550][I][T_PDU_SCAN:071]: OK reg=4411 value=0
[14:45:41.638][I][T_PDU_SCAN:071]: OK reg=4449 value=0
[14:45:41.959][I][T_PDU_SCAN:071]: OK reg=4451 value=1
[14:45:42.120][I][T_PDU_SCAN:071]: OK reg=4452 value=236
[14:45:42.271][I][T_PDU_SCAN:071]: OK reg=4453 value=0
[14:45:42.439][I][T_PDU_SCAN:071]: OK reg=4454 value=1
[14:45:42.598][I][T_PDU_SCAN:071]: OK reg=4455 value=231
[14:45:44.674][I][T_PDU_SCAN:071]: OK reg=4468 value=120
[14:45:44.844][I][T_PDU_SCAN:071]: OK reg=4469 value=180
[14:45:46.433][I][T_PDU_SCAN:071]: OK reg=4479 value=4
[14:45:57.961][I][T_PDU_SCAN:071]: OK reg=4551 value=310
[14:45:58.462][I][T_PDU_SCAN:071]: OK reg=4554 value=386
[14:45:58.910][I][T_PDU_SCAN:071]: OK reg=4557 value=2000
[14:45:59.097][I][T_PDU_SCAN:071]: OK reg=4558 value=0
[14:46:03.399][I][T_PDU_SCAN:071]: OK reg=4585 value=396
[14:46:03.550][I][T_PDU_SCAN:071]: OK reg=4586 value=0
[14:46:03.710][I][T_PDU_SCAN:071]: OK reg=4587 value=0
[14:46:03.876][I][T_PDU_SCAN:071]: OK reg=4588 value=0
[14:46:05.800][I][T_PDU_SCAN:071]: OK reg=4600 value=0
[14:47:45.476][I][T_PDU_SCAN:071]: OK reg=6000 value=3
[14:47:45.803][I][T_PDU_SCAN:071]: OK reg=6002 value=0
[14:47:47.085][I][T_PDU_SCAN:071]: OK reg=6010 value=70
[14:47:47.241][I][T_PDU_SCAN:071]: OK reg=6011 value=100
[14:47:47.561][I][T_PDU_SCAN:071]: OK reg=6013 value=1
[14:47:47.723][I][T_PDU_SCAN:071]: OK reg=6014 value=0
[14:49:05.500][I][T_PDU_SCAN:071]: OK reg=6500 value=300
[14:49:05.656][I][T_PDU_SCAN:071]: OK reg=6501 value=200
[14:49:05.821][I][T_PDU_SCAN:071]: OK reg=6502 value=0
[14:49:05.969][I][T_PDU_SCAN:071]: OK reg=6503 value=0
[14:49:06.129][I][T_PDU_SCAN:071]: OK reg=6504 value=0
[14:49:06.296][I][T_PDU_SCAN:071]: OK reg=6505 value=83
[14:49:06.443][I][T_PDU_SCAN:071]: OK reg=6506 value=14
[14:49:06.597][I][T_PDU_SCAN:071]: OK reg=6507 value=1
[14:49:07.086][I][T_PDU_SCAN:071]: OK reg=6510 value=1
- About status Codes: i use the heat pump only for heating and hot water.
Maybe this evening i can try to force it to start also in cooling for a short time and see the status.
D99 = 1 When Z2 cooling request
D99 = 6 When Z2 Heating request
D99 = 61 When DHW with solar boost input
D99 = 64 When DHW with electric heater (not heatpump)
D97 = 342 When Z2 cooling request
Anyway if could be useful my zone 1 have classic thermostat on-off. Zone 2 have Immergas Remote Zone Panel.
If you need i have full dump but Was easyer paste here only OK Messages