You are mixing 2 systems together.
Node Red is not needed to read the data.
The entities you made in Node Red need to be in the configuration.yaml file.
There you first make a modbus group, then a sensor group and in that group you put the entities you want to have visible in HA.
For example see my working solution in an earlier post.
Hello, can you Post what device you have take to have this UI?
Hey Niels nice work! Can you say me what device you have take to control you eco forest heat pump?
I am only reading the BMS port but can be controlled with the same device. I am using a USB to rs485 interface. But any rs485 interface (ie. Ethernet/TCP) can work.
Hello Nielss i was on holiday. Ok i don’t know the modbus protocol. Can I only read the data or can I command(turn on the HP, change the temperature)? Nice Day
I have spent some time to figure out if I can control the HP. I got some progress but did not work out well with HA talking to the bus.
I enabled the Modbus control in the HP via the installermenu and it looks like the heatpump does work with BMS and external control (Digital inputs for DG1, SG2-4) simultaneous.
With HA I switched on the DHW but then the start temperature changes to -5 C and could not change it to something different. Turning off changed it back to the earlier start temperature.
So if anybody else would give it a try to control it by Modbus, you’re welcome
I got some progress in controlling the heatpump via the bus.
First note: controlling the heatpump by bus AND digital inputs for heating/cooling works!
Second note: before the heatpump responds to commands via Modbus, you first need to enable ‘remote control by bus’ in the installer menu.
Then you need to send via Modbus that you want to ‘control by bus’: send a ‘1’ to address 5221. (To disable it you can send a ‘0’ )
I got the DHW working by enabling parameter 5222 (set it to ‘1’ to enable DHW demand)
Then you need to set the target temperature at parameter 134 with the desired value.
A thing I mentioned while enabling the control by bus is that the combined heating and cooling demand switched to heating only. I could not figure out what to set to make it combined and/or to cooling. If anyone finds the parameter or knows how to control, you’re welcome.
I also found a few parameters that are not documented by Ecoforest:
- name: Heatpump Thermal Power DHW Min
unit_of_measurement: "%"
scale: 0.1
slave: 17
address: 74
lazy_error_count: 10
data_type: int16
- name: Heatpump Thermal Power DHW Max
scale: 0.1
slave: 17
address: 75
data_type: int16
- name: Heatpump Thermal Power Heating Min
scale: 0.1
slave: 17
address: 76
data_type: int16
- name: Heatpump Thermal Power Heating Max
scale: 0.1
slave: 17
address: 77
data_type: int16
- name: Heatpump Thermal Power Cooling Min
scale: 0.1
slave: 17
address: 78
data_type: int16
- name: Heatpump Thermal Power Cooling Max
scale: 0.1
slave: 17
address: 79
data_type: int16
- name: Heatpump Thermal Power Pool Min
scale: 0.1
slave: 17
address: 80
data_type: int16
- name: Heatpump Thermal Power Pool Max
scale: 0.1
slave: 17
address: 81
data_type: int16
(not sure if int16 is ok in this setup)
And for the distribution pumps:
- name: Heatpump Production Pump
scale: 0.1
slave: 17
address: 5033
data_type: int16
- name: Heatpump Brine Pump
scale: 0.1
slave: 17
address: 5034
data_type: int16
(I have added the lazye error counts to suppress the no_data read from bus errors and giving ‘unavailable’ as value in the logs.)
Almost a year later, I have an ecoforest on order, And also have got a list of modbus registers for the Ecoair and Ecogeo from an installer here. Wont be able to properly work at things until I actually get it installed.
I am still fairly new to homeassistant and yaml Have the basics down but still learning. but have worked with others work with modbus (mainly the sofar2mqtt project.)
I have HA running in a VM but have access to Pi’s and esp32’s that can do the RS485. I have also some experience with ESPhome.
Just looking for some advice moving forwards. I suppose a ESPhome could be more turnkey for other users (although would require building some hardware.)
Looks like the geothermal and airsource seem to have slightly different modbus addresses for some things, Need to keep an eye on.that.
For me it is figuring out how to control the heatpump via modbus. There is not a lot of info on the internet. With the info I can find I will post it here after figuring out which parameters have which function.
How to proceed with the information: let’s figure out together and see what is possible.
To me, WiFi is not stable enough to fully control a machine. But if ESPHome can run stand-alone, then why not? Then all logic needs to be in ESPHome and makes it more difficult to maintain.
For me the datalogging was the first approach. Second is controlling the system remote.
If somebody has advise or ideas, let’s put them together.
Some progress!
I have figured out that many parameters for reading are also for writing.
At first the full addresslist I have discovered and tested:
modbus:
- name: "ecoforest"
delay: 5
type: serial
method: rtu
port: /dev/serial/by-id/usb-Prolific_Technology_Inc._USB-Serial_Controller-if00-port0
baudrate: 19200
stopbits: 2
bytesize: 8
parity: N
binary_sensors:
- name: heatpump_alarm
slave: 17
address: 50
- name: Heatpump Summer
slave: 17
address: 127
- name: Heatpump Winter
slave: 17
address: 128
- name: Heatpump on/off control by BUS
slave: 17
address: 53
sensors:
- name: Heatpump Buitentemperatuur
unit_of_measurement: °C
scale: 0.1
precision: 1
slave: 17
address: 11
data_type: int16
- name: Heatpump Boiler
scale: 0.1
precision: 1
slave: 17
address: 8
data_type: int16
- name: Heatpump Pressure Brine
unit_of_measurement: Bar
scale: 0.1
precision: 1
slave: 17
address: 13
data_type: int16
- name: Heatpump Pressure Heating
scale: 0.1
precision: 1
slave: 17
address: 14
data_type: int16
- name: Heatpump Brine air outlet
scale: 0.1
precision: 1
slave: 17
address: 29
data_type: int16
- name: Heatpump Brine out
scale: 0.1
precision: 1
slave: 17
address: 1
data_type: int16
- name: Heatpump Brine in
scale: 0.1
precision: 1
slave: 17
address: 2
data_type: int16
- name: Heatpump Heating out
scale: 0.1
precision: 1
slave: 17
address: 3
data_type: int16
- name: Heatpump Heating in
scale: 0.1
precision: 1
slave: 17
address: 4
data_type: int16
- name: Heatpump Compressor suction temperature
scale: 0.1
precision: 1
slave: 17
address: 5
data_type: int16
- name: Heatpump Compresor suction pressure
scale: 0.1
precision: 1
slave: 17
address: 6
data_type: int16
- name: Heatpump Compressor discharge pressure
scale: 0.1
precision: 1
slave: 17
address: 7
data_type: int16
- name: Heatpump Condensation temperature
scale: 0.1
precision: 1
slave: 17
address: 94
data_type: int16
scale: 0.1
slave: 17
address: 74
data_type: int16
#set and get
scale: 0.1
slave: 17
address: 75
data_type: int16
#set and get
scale: 0.1
slave: 17
address: 76
data_type: int16
#set and get
scale: 0.1
slave: 17
address: 77
data_type: int16
#set and get
scale: 0.1
slave: 17
address: 78
data_type: int16
#set and get
scale: 0.1
slave: 17
address: 79
data_type: int16
#set and get
scale: 0.1
slave: 17
address: 80
data_type: int16
#set and get
scale: 0.1
slave: 17
address: 81
data_type: int16
#set and get
- name: Heatpump Superheat
scale: 0.1
precision: 1
slave: 17
address: 132
data_type: int16
- name: Heatpump Expansion valve position
slave: 17
address: 133
data_type: int16
- name: Heatpump BUS DHW Setpoint
scale: 0.1
precision: 1
slave: 17
address: 134
data_type: int16
#set and get
- name: Heatpump BUS Heating DG1 Setpoint
scale: 0.1
precision: 1
slave: 17
address: 135
data_type: int16
#set and get
- name: Heatpump BUS Heating SG2 Setpoint
scale: 0.1
precision: 1
slave: 17
address: 136
data_type: int16
#set and get
- name: Heatpump BUS Heating SG3 Setpoint
scale: 0.1
precision: 1
slave: 17
address: 137
data_type: int16
#set and get
- name: Heatpump BUS Heating SG4 Setpoint
scale: 0.1
precision: 1
slave: 17
address: 138
data_type: int16
#set and get
- name: Heatpump BUS Cooling DG1 Setpoint
scale: 0.1
precision: 1
slave: 17
address: 139
data_type: int16
#set and get
- name: Heatpump BUS Cooling SG2 Setpoint
scale: 0.1
precision: 1
slave: 17
address: 140
data_type: int16
#set and get
- name: Heatpump BUS Cooling SG3 Setpoint
scale: 0.1
precision: 1
slave: 17
address: 141
data_type: int16
#set and get
- name: Heatpump BUS Cooling SG4 Setpoint
scale: 0.1
precision: 1
slave: 17
address: 142
data_type: int16
#set and get
- name: Heatpump Supply Temperature SG2
scale: 0.1
precision: 1
slave: 17
address: 194
data_type: int16
- name: Heatpump Supply Temperature SG3
scale: 0.1
precision: 1
slave: 17
address: 195
data_type: int16
- name: Heatpump Supply Temperature SG4
scale: 0.1
precision: 1
slave: 17
address: 196
data_type: int16
- name: Heatpump Start Temperature DHW
scale: 0.1
precision: 1
slave: 17
address: 198
data_type: int16
- name: Heatpump Evaporation temperature
scale: 0.1
precision: 1
slave: 17
address: 199
data_type: int16
- name: Heatpump Compressor discharge temperature
scale: 0.1
precision: 1
slave: 17
address: 203
data_type: int16
- name: Heatpump COP
unit_of_measurement: COP
scale: 0.1
precision: 1
slave: 17
address: 30
data_type: int16
- name: Heatpump EER
unit_of_measurement: EER
scale: 0.1
precision: 1
slave: 17
address: 202
data_type: int16
- name: Heatpump Compressor RPM
unit_of_measurement: RPM
slave: 17
address: 5002
data_type: int16
- name: Heatpump Scroll temperature
slave: 17
address: 5004
data_type: int16
- name: Heatpump Inverter temperature
slave: 17
address: 5005
data_type: int16
- name: Heatpump Working Hours L
slave: 17
address: 5080
data_type: int16
- name: Heatpump Working Hours H
slave: 17
address: 5081
data_type: int16
scale: 0.1
slave: 17
address: 5033
data_type: int16
scale: 0.1
slave: 17
address: 5034
data_type: int16
- name: Heatpump Powerconsumption
unit_of_measurement: W
slave: 17
address: 5082
data_type: int16
- name: Heatpump Condensation capacity
slave: 17
address: 5083
data_type: int16
- name: Heatpump Evaporation capacity
slave: 17
address: 5185
data_type: int16
- name: Heatpump working program by BUS
slave: 17
address: 5221
data_type: int16
#set and get
# 0 - mixed, 1 - heating, 2 - cooling, 3 - off
- name: Heatpump BUS DHW Demand
slave: 17
address: 5222
data_type: int16
#set and get
# 0 - off, 1 - on
- name: Heatpump BUS DG1 Demand
slave: 17
address: 5224
data_type: int16
#set and get
# 0 - off, 1 - on
- name: Heatpump BUS SG2 Demand
slave: 17
address: 5225
data_type: int16
#set and get
# 0 - off, 1 - heating, 2 - cooling
- name: Heatpump BUS SG3 Demand
slave: 17
address: 5226
data_type: int16
#set and get
- name: Heatpump BUS SG4 Demand
slave: 17
address: 5227
data_type: int16
#set and get
- name: Heatpump Condensation Energy january
unit_of_measurement: kWh
slave: 17
address: 5144
data_type: int16
- name: Heatpump Condensation Energy february
slave: 17
address: 5145
data_type: int16
- name: Heatpump Condensation Energy march
slave: 17
address: 5146
data_type: int16
- name: Heatpump Condensation Energy april
slave: 17
address: 5147
data_type: int16
- name: Heatpump Condensation Energy may
slave: 17
address: 5148
data_type: int16
- name: Heatpump Condensation Energy june
slave: 17
address: 5149
data_type: int16
- name: Heatpump Condensation Energy july
slave: 17
address: 5150
data_type: int16
- name: Heatpump Condensation Energy august
slave: 17
address: 5151
data_type: int16
- name: Heatpump Condensation Energy september
slave: 17
address: 5152
data_type: int16
- name: Heatpump Condensation Energy october
slave: 17
address: 5153
data_type: int16
- name: Heatpump Condensation Energy november
slave: 17
address: 5154
data_type: int16
- name: Heatpump Condensation Energy december
slave: 17
address: 5155
data_type: int16
- name: Heatpump Evaporation Energy january
slave: 17
address: 5156
data_type: int16
- name: Heatpump Evaporation Energy february
slave: 17
address: 5157
data_type: int16
- name: Heatpump Evaporation Energy march
slave: 17
address: 5158
data_type: int16
- name: Heatpump Evaporation Energy april
slave: 17
address: 5159
data_type: int16
- name: Heatpump Evaporation Energy may
slave: 17
address: 5160
data_type: int16
- name: Heatpump Evaporation Energy june
slave: 17
address: 5161
data_type: int16
- name: Heatpump Evaporation Energy july
slave: 17
address: 5162
data_type: int16
- name: Heatpump Evaporation Energy august
slave: 17
address: 5163
data_type: int16
- name: Heatpump Evaporation Energy september
slave: 17
address: 5164
data_type: int16
- name: Heatpump Evaporation Energy october
slave: 17
address: 5165
data_type: int16
- name: Heatpump Evaporation Energy november
slave: 17
address: 5166
data_type: int16
- name: Heatpump Evaporation Energy december
slave: 17
address: 5167
data_type: int16
- name: Heatpump Electrical Consumption january
slave: 17
address: 5168
data_type: int16
- name: Heatpump Electrical Consumption february
slave: 17
address: 5169
data_type: int16
- name: Heatpump Electrical Consumption march
slave: 17
address: 5170
data_type: int16
- name: Heatpump Electrical Consumption april
slave: 17
address: 5171
data_type: int16
- name: Heatpump Electrical Consumption may
slave: 17
address: 5172
data_type: int16
- name: Heatpump Electrical Consumption june
slave: 17
address: 5173
data_type: int16
- name: Heatpump Electrical Consumption july
slave: 17
address: 5174
data_type: int16
- name: Heatpump Electrical Consumption august
slave: 17
address: 5175
data_type: int16
- name: Heatpump Electrical Consumption september
slave: 17
address: 5176
data_type: int16
- name: Heatpump Electrical Consumption october
slave: 17
address: 5177
data_type: int16
- name: Heatpump Electrical Consumption november
slave: 17
address: 5178
data_type: int16
- name: Heatpump Electrical Consumption december
slave: 17
address: 5179
data_type: int16
- name: Heatpump Number Of Starts L
slave: 17
address: 5281
data_type: int16
- name: Heatpump Number Of Starts H
slave: 17
address: 5282
data_type: int16
The parameters that are writeable are remarked with extra information.
Be aware that if you send a variable that the value needs to be an integer. ie. temperature like 32.5 degrees needs to be sent like 325.
Also keep in mind that ‘control by bus’ needs to be enabled in the installer menu, otherwise it does not respond to modbus writes. External controls are still working ie Digital inputs. (Th Tune is not tested due to that I removed that unit years ago)
Another thing I discovered is that demanding the zones work but keep in mind that these zones need to be ‘open’ or valves that need to be opened first to have flow.
When demanding zones: have the ‘working program by BUS’ set right for the needs ( both (default), heating or cooling) 0 - mixed, 1 - heating, 2 - cooling, 3 - off
Then the target water temperature for heating and/or cooling set per zone.
If those are set, then you can set the ‘BUS x Demand’ with 0 - off, 1 - heating, 2 - cooling
A nice feature is having the ‘Thermal power’ variables to limit the amount of power of the compressor. This can be used while monitoring your solar power and limit heating up the boiler that nearly all power is sourced from the solar panels.
Be carefull with setting these values! Writing wrong values can damage the heatpump.
Thats great work. Do you have a geothermal or Air to water? (Im getting Air to Water)
ESPhome, would need an esp and a rs485 board, but would be wifi connection. I’m using esp8266 and that for my control of my sofar inverter without issue. ( but not via home assistant, I was using that pre home assistant.)
Mine wont be that close to my HA install which is also running in a VM.
Possibly looking into how the sunsynk addon is doing it. ( Getting Started | Deye/Sunsynk), But that add on is built in python.
Can use mbusd to take a RTU modbus and convert it to TCP.
They do sell a solar excess controller, have been told that it could match the excess coming from solar.
I think what your building currently using the in built modbus in home assistant is currently the best way to go currently to get everything figured out.
Unfortunately cant dabble too much until I get it installed.
How are you writing to the registers within home assistant?
I have an air to water version. Maybe I will convert it to hybrid.
Where I live is the level of ground water within one meter and have a horizontal source.
For writing modbus you can use a service: Modbus Write service.
I am not sure if I am going to use the HA automations. Maybe NodeRed (or a mix of them)
I used a USB to RS485 converter that is on VMWare connected. The twisted pair is around 8 meters to the heatpump. Other devices I read are connected with an EPS8266 for the solarpanels with GoodWeLogger which I maybe switch to an ethernet solution which can control the solarinverter via HA. And a few kWh meters that are also via USB on the VMWare.
I think at some point a github page could be made with the yaml code for all the registers.
I have thrown together a RTU to Modbus TCP bridge with a tasmota and a rs485 board I had to hand, I will keep experimenting with it with the sofar inverter I have to hand. [will need it for a Deye inverter I have ordered anyway]
Started looking into how to create an integration but that is currently beyond me, although a ESPHome device may be doable.
Hello Niels,
Can you confirm the protocol RS232 or RS485?
Because i am on the point to order a converter to TCP
And I have problem with implanting the code on the Yaml maybe you have also a solution for this.
The system cannot restart because the configuration is not valid: Component error: modbus - cannot import name ‘ModbusBaseClient’ from ‘pymodbus.client’ (/usr/local/lib/python3.11/site-packages/pymodbus/client/init.py)
No Hands on here yet, but as far as I know its RS485, Modbus over rs232 is possible but its not the done thing.
What heatpump do you have? the EcoAir+ has slightly different registers than the EcoGeo.
I have put together an untested, readonly esphome device. can put it up on git hub if interested
As mentioned by @graememk it is RS485
Your config looks like there is something missing or has wrong indents.
Can you post your complete yaml? (remove passwords and other personal information)
Hi Niels,
Thanks for the answer about the RS version. And her is my compleet YAML file. Maybe you see the problem.
Loads default set of integrations. Do not remove.
default_config:
Text to speech
tts:
- platform: google_translate
script: !include scripts.yaml
scene: !include scenes.yaml
rflink:
port: /dev/serial/by-id/usb-Arduino__www.arduino.cc__Arduino_Mega_2560_12252601009322316566-if00
wait_for_ack: false
light:
- platform: rflink
automatic_add: true
sensor: - platform: rflink
automatic_add: true
logger:
default: error
logs:
rflink: debug
homeassistant.components.rflink: debug
cover: - platform: rflink
devices:
brelmotor_064770_05:
utility_meter:
util_water_usage_hourly:
source: sensor.water_total
cycle: hourly
util_water_usage_daily:
cycle: daily
util_water_usage_monthly:
cycle: monthly
util_water_usage_yearly:
cycle: yearly
modbus:
- name: "ecoforest"
delay: 5 - name: "hub1"
type: rtuovertcp
host: IP_ADDRESS
port: 502
Can you put the yaml into a ‘preformatted text’ block? You can do that by clicking the </> on top of the editor.
The code is now missing indents and has markups that do not exist in yaml.
# Loads default set of integrations. Do not remove.
default_config:
# Text to speech
tts:
rflink:
wait_for_ack: false
light:
- platform: rflink
automatic_add: true
- platform: rflink
automatic_add: true
logger:
default: error
logs:
rflink: debug
cover:
- platform: rflink
devices:
utility_meter:
cycle: hourly
cycle: daily
cycle: monthly
cycle: yearly
modbus:
- name: "ecoforest"
delay: 5
- name: "hub1"
type: rtuovertcp
host: IP_ADDRESS
port: 502
binary_sensors:
slave: 17
address: 50
slave: 17
address: 127
slave: 17
address: 128
sensors:
scale: 0.1
precision: 1
slave: 17
address: 11
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 8
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 13
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 14
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 29
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 1
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 2
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 3
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 4
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 5
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 6
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 7
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 94
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 132
data_type: int16
slave: 17
address: 133
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 194
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 195
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 196
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 198
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 199
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 203
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 30
data_type: int16
scale: 0.1
precision: 1
slave: 17
address: 202
data_type: int16
slave: 17
address: 5002
data_type: int16
slave: 17
address: 5004
data_type: int16
slave: 17
address: 5005
data_type: int16
slave: 17
address: 5080
data_type: int16
slave: 17
address: 5081
data_type: int16
slave: 17
address: 5082
data_type: int16
slave: 17
address: 5083
data_type: int16
slave: 17
address: 5185
data_type: int16
slave: 17
address: 5144
data_type: int16
slave: 17
address: 5145
data_type: int16
slave: 17
address: 5146
data_type: int16
slave: 17
address: 5147
data_type: int16
slave: 17
address: 5148
data_type: int16
slave: 17
address: 5149
data_type: int16
slave: 17
address: 5150
data_type: int16
slave: 17
address: 5151
data_type: int16
slave: 17
address: 5152
data_type: int16
slave: 17
address: 5153
data_type: int16
slave: 17
address: 5154
data_type: int16
slave: 17
address: 5155
data_type: int16
slave: 17
address: 5156
data_type: int16
slave: 17
address: 5157
data_type: int16
slave: 17
address: 5158
data_type: int16
slave: 17
address: 5159
data_type: int16
slave: 17
address: 5160
data_type: int16
slave: 17
address: 5161
data_type: int16
slave: 17
address: 5162
data_type: int16
slave: 17
address: 5163
data_type: int16
slave: 17
address: 5164
data_type: int16
slave: 17
address: 5165
data_type: int16
slave: 17
address: 5166
data_type: int16
slave: 17
address: 5167
data_type: int16
slave: 17
address: 5168
data_type: int16
slave: 17
address: 5169
data_type: int16
slave: 17
address: 5170
data_type: int16
slave: 17
address: 5171
data_type: int16
slave: 17
address: 5172
data_type: int16
slave: 17
address: 5173
data_type: int16
slave: 17
address: 5174
data_type: int16
slave: 17
address: 5175
data_type: int16
slave: 17
address: 5176
data_type: int16
slave: 17
address: 5177
data_type: int16
slave: 17
address: 5178
data_type: int16
slave: 17
address: 5179
data_type: int16
slave: 17
address: 5281
data_type: int16
slave: 17
address: 5282
data_type: int16