Hello Klangen82,
Thank you VERY much for your examples! I copied them and after some tweaking they work on my installation as designed (Full Charge / Full Discharge / Stop Activities).
What I still do not understand, after many hours of trial and error and checking many different forums, is why those numbers (60933 and 4603)?. All I found out is that they add up to the the value of 65536 which is Hex FFFF+1.
The reason I am asking is twofold:
- I want to optimize my consumption from the grid and
- I have 2 different inverters connected to a separate EVU. Hence I need to control the charge/discharge seamlessly and based on values from my EVU.
Now I am trying to setup a node-red automation, feeding the GEN24 10 Plus with the required values to keep the grid consumption at +/- 0.
The Fronius register map talks about +/- 1000 for the OutWRte and InWRte, but your values are much different. Am I right assuming (float setting assumed) that one number always need to be 65535 - the other value? Ideally I would want to keep the StorCtl_Mod always at 3?
Do you know where I can find more details on the topic?
Many thanks
Heinz