Integrate Modbus smart meter with Home Assistant Energy
I had the same problem. In my case I had to remove
unique_id: xxxx
to solve this problem.
@miroslavpetrov followed your example to connect to a Eastron SDM230 Modbus, using an 8266 D1 Mini + same RS485 (using MAX495 chip) as you. But keep getting lots of “Modbus CRC Check failed!” errors. Are you encountering same ? Eventually (random) I get all values from the SDM230, rest of time is all errors. Dont think issue is with physical connections (using all jumper cables). Tried switching to the modbus_controller instead of sdm_meter and getting same results more or less. Ground from SDM230 is connected to the Ground of the esp8266 and then to the RS485. Tested using hardware and software UART pins on 8266 with same result. Saw some complaining of this issues coming after some ESPHome version, but all were on ESP32 not 8266 not sure if it affects also 8266. ESPHome version 2022.11.5 seems to work fine, but not sure how to revert to that version only for this esp8266. The phone symbol on SDM230 is blinking, this was not same when I had my inverter connected to SDM230.
I use the Modbus USB Stick
Works great with eastron kwh meter
IMG_5256
This is my yaml file
  • type: serial
    method: rtu
    port: /dev/ttyUSB2
    baudrate: 9600
    stopbits: 1
    bytesize: 8
    parity: N
    sensors:
    • name: eastron
      unique_id: eastronkwh
      address: 12
      scan_interval: 1
      input_type: input
      count: 2
      slave: 2
      precision: 2
      data_type: float32
      device_class: energy
      state_class: total_increasing
      unit_of_measurement: ‘W’
Hello @miroslavpetrov . Sorry for jumping in here. But I was hoping you might be able to help me with something.
I have a daisy-chain of 1x Eastron SDM230 and 3x Eastron SDM120 all connecting to a USB/RS485 converter.
I know it all works as I had them working well with an Open Energy Monitor (emonCMS) setup. But I’m now moving away from that to solely HA.
I’m waning to create a modbus.yaml which contains sensors for the read-only values on each of the Eastrons. But, being a novice, I’m struggling, especially with the addresses to read on teh Eastrons.
Would you be kind enough to share your specific sections of your modbus setup for reading the Eastrons (if you’re still using those)?
Any help is greatly appreciated.
Thanks in advance.
@smoketabs
First you should set different addresses of the two meters, but you should know that since you got them working before. This example should work for you if one of the meters is with address 1 and the other address 2. Change the value of slave: accordingly if your values are different.
Thanks. And yes, the IDs are unique.
Are you pulling any other data from the meters? For example, current, volts, PF, etc.?
I was hoping to build out a list of possible sensors for reading instantaneous readings, and then as you’ve got in your code, cumulative kWh.
In my emonCMS config, I had the following. But I’m not sure how best to represent these in HA, and also the addresses to read:
            [[[[[sdm230a]]]]]
                address = 010
                registers = 0,6,12,18,30,70,72,74,76
                names = V,I,P,VA,PF,FR,EI,EE,RI
                precision = 2,3,1,1,3,3,3,3,3
            [[[[[sdm120a]]]]]
                address = 011
Again, any help is greatly received.
Best.
Roland.
Sorry for the mistake in my previous post, the value of the address for active energy is wrong because I was helping another person.
I am giving you my config for SDM630 which is a 3 phase meter, so you need to remove the lines for phase 2 and 3.
modbus:
  - name: hub1
    type: serial
    baudrate: 9600
    bytesize: 8
    method: rtu
    parity: N
    port: /dev/ttyUSB0
    stopbits: 1
    sensors:
    - name: sdm630_total_active_energy
      address: 342
      input_type: input
      count: 2
      slave: 1
      precision: 2
      data_type: float
      unit_of_measurement: kWh
    - name: sdm630_p1_voltage
      slave: 1
      address: 0
      input_type: input
      count: 2
      precision: 2
      data_type: float
      unit_of_measurement: V
      device_class: voltage
    - name: sdm630_p2_voltage
      slave: 1
      address: 2
      input_type: input
      count: 2
      precision: 2
      data_type: float
    - name: sdm630_p3_voltage
      slave: 1
      address: 4
      input_type: input
      count: 2
      precision: 2
      data_type: float
    - name: sdm630_p1_current
      slave: 1
      address: 6
      input_type: input
      count: 2
      precision: 3
      data_type: float
      unit_of_measurement: A
      device_class: current
    - name: sdm630_p2_current
      slave: 1
      address: 8
      input_type: input
      count: 2
      precision: 3
      data_type: float
    - name: sdm630_p3_current
      slave: 1
      address: 10
      input_type: input
      count: 2
      precision: 3
      data_type: float
    - name: sdm630_p1_active_power
      slave: 1
      address: 12
      input_type: input
      count: 2
      precision: 3
      scale: 0.001
      data_type: float
      device_class: power
    - name: sdm630_p2_active_power
      slave: 1
      address: 14
      input_type: input
      count: 2
      precision: 3
      scale: 0.001
      data_type: float
      device_class: power
    - name: sdm630_p3_active_power
      slave: 1
      address: 16
      input_type: input
      count: 2
      precision: 3
      scale: 0.001
      data_type: float
      device_class: power
    - name: sdm630_sum_current
      slave: 1
      address: 48
      input_type: input
      count: 2
      precision: 3
      data_type: float
    - name: sdm630_sum_active_power
      slave: 1
      address: 52
      input_type: input
      count: 2
      precision: 3
      scale: 0.001
      data_type: float
      device_class: power
    - name: sdm630_sum_apparant_power
      slave: 1
      address: 56
      input_type: input
      count: 2
      precision: 2
      data_type: float
      unit_of_measurement: VA
      device_class: power
    - name: sdm630_sum_reactive_power
      slave: 1
      address: 60
      input_type: input
      count: 2
      precision: 2
      data_type: float
      unit_of_measurement: VAr
      device_class: power
    - name: sdm630_sum_pf
      slave: 1
      address: 62
      input_type: input
      count: 2
      precision: 2
      data_type: float
      unit_of_measurement: cosф
      device_class: power_factor
here is also a table with the addresses of the registers. I see that voltage is missing but its “0”.
https://www.aggsoft.com/serial-data-logger/tutorials/modbus-data-logging/eastron-sdm230.htm
hope this helps.
Thanks @miroslavpetrov - greatly appreciated.
I’ve lifted just one for now, and tried it. It doesn’t like the “float” data_type. The check config says this:
“Invalid config for [modbus]: value must be one of [<DataType.CUSTOM: ‘custom’>, <DataType.FLOAT16: ‘float16’>, <DataType.FLOAT32: ‘float32’>, <DataType.FLOAT64: ‘float64’>, <DataType.INT16: ‘int16’>, <DataType.INT32: ‘int32’>, <DataType.INT64: ‘int64’>, <DataType.INT8: ‘int8’>, <DataType.STRING: ‘string’>, <DataType.STRING: ‘string’>, <DataType.UINT16: ‘uint16’>, <DataType.UINT32: ‘uint32’>, <DataType.UINT64: ‘uint64’>, <DataType.UINT8: ‘uint8’>] for dictionary value @ data[‘modbus’][0][‘sensors’][0][‘data_type’]. Got ‘float’.”
Sorry to be a pain. Any help would be welcome.
But thank you, all the same.
Roland.
Just checked it out, its because there was a breaking change in version 2022.4 I think. You need to change float to float32 and it should be fine. I am no longer using this config because I am now reading my Eastron meters using ESPHome and I have not updated my archives :smiley:
Thanks @miroslavpetrov. That’s fixed it. I can now see voltage from one of my SDM120s.
Thanks again - greatly appreciated.
For everyone else’s benefit, I’ll paste my working code when I’ve completed testing.
Thanks again,
Roland.
Hello all.
With the help of @miroslavpetrov I’ve got my Eastrons working as I hoped. So as promised, here’s a copy of my modbus config for all those others out there who are “new” to this.
My setup:
1x Eastron SDM230
3x Eastron SDM120
1x Industrial Modbus RS485 to USB Adaptor
1x IntelNUC (i5; 8Gb RAM; 128Gb SSD) flashed for HA only
  • Daisy-chained using a single pair taken from a CAT6 cable.
  • No GND cable
  • No Terminating resistor
  1. My configuration.yaml calls a separate file in the same directory as the config.yaml called “modbusUSB.yaml”.
modbus: !include modbusUSB.yaml
  1. contents of “modbusUSB.yaml”.
I’m able to read the following data on all of the individual meters:
  • Active Energy (kWh)
  • Voltage (V)
  • Current (A)
  • Active Power (W)
  • Power Factor
- name: HomeModbus1
  type: serial
  baudrate: 9600
  bytesize: 8
  method: rtu
  parity: N
  port: /dev/ttyACM0
  stopbits: 1
  sensors:
    - name: "EPS Active Energy"
      unique_id: eps_active_energy
      address: 342
      input_type: input
      count: 2
      slave: 200
      precision: 2
      data_type: float32
    - name: "EPS Voltage"
      unique_id: eps_voltage
      slave: 200
      address: 0
      input_type: input
      count: 2
      precision: 2
      data_type: float32
    - name: "EPS Current"
      unique_id: eps_current
      slave: 200
      address: 6
      input_type: input
      count: 2
      precision: 3
      data_type: float32
    - name: "EPS Active Power"
      unique_id: eps_active_power
      slave: 200
      address: 12
      input_type: input
      count: 2
      precision: 3
      scale: 0.001
      data_type: float32
      device_class: power
    - name: "EPS Power Factor"
      unique_id: eps_power_factor
      slave: 200
      address: 30
      input_type: input
      count: 2
      precision: 2
      data_type: float32
    - name: "Non-EPS Active Energy"
      unique_id: non_eps_active_energy
      address: 342
      input_type: input
      count: 2
      slave: 100
      precision: 2
      data_type: float32
    - name: "Non-EPS Voltage"
      unique_id: non_eps_voltage
      slave: 100
      address: 0
      input_type: input
      count: 2
      precision: 2
      data_type: float32
    - name: "Non-EPS Current"
      unique_id: non_eps_current
      slave: 100
      address: 6
      input_type: input
      count: 2
      precision: 3
      data_type: float32
    - name: "Non-EPS Active Power"
      unique_id: non_eps_active_power
      slave: 100
      address: 12
      input_type: input
      count: 2
      precision: 3
      scale: 0.001
      data_type: float32
      device_class: power
    - name: "Non-EPS Power Factor"
      unique_id: non_eps_power_factor
      slave: 100
      address: 30
      input_type: input
      count: 2
      precision: 2
      data_type: float32
    - name: "Hob Active Energy"
      unique_id: hob_active_energy
      address: 342
      input_type: input
      count: 2
      slave: 101
      precision: 2
      data_type: float32
    - name: "Hob Voltage"
      unique_id: hob_voltage
      slave: 101
      address: 0
      input_type: input
      count: 2
      precision: 2
      data_type: float32
    - name: "Hob Current"
      unique_id: hob_current
      slave: 101
      address: 6
      input_type: input
      count: 2
      precision: 3
      data_type: float32
    - name: "Hob Active Power"
      unique_id: hob_active_power
      slave: 101
      address: 12
      input_type: input
      count: 2
      precision: 3
      scale: 0.001
      data_type: float32
      device_class: power
    - name: "Hob Power Factor"
      unique_id: hob_power_factor
      slave: 101
      address: 30
      input_type: input
      count: 2
      precision: 2
      data_type: float32
    - name: "Immersion Active Energy"
      unique_id: immersion_active_energy
      address: 342
      input_type: input
      count: 2
      slave: 102
      precision: 2
      data_type: float32
    - name: "Immersion Voltage"
      unique_id: immersion_voltage
      slave: 102
      address: 0
      input_type: input
      count: 2
      precision: 2
      data_type: float32
    - name: "Immersion Current"
      unique_id: immersion_current
      slave: 102
      address: 6
      input_type: input
      count: 2
      precision: 3
      data_type: float32
    - name: "Immersion Active Power"
      unique_id: immersion_active_power
      slave: 102
      address: 12
      input_type: input
      count: 2
      precision: 3
      scale: 0.001
      data_type: float32
      device_class: power
    - name: "Immersion Power Factor"
      unique_id: immersion_power_factor
      slave: 102
      address: 30
      input_type: input
      count: 2
      precision: 2
      data_type: float32
With the above, I’m able to get kWh (Active Energy) from each meter, so no need to write script to change power to energy.
These meters are not placed to monitor import/export - I’ll be using a solar inverter (Fox-ESS H1 6kW) for that.
I will also be adding further Eastrons over time.
I also pull in other energy data from various Shelly plus1PMs and a Shelly Pro4PM.
I also have a Hildebrand GLOW In House Display (IHD) reading my SMETS2 and sending data via MQTT to my HA instance. This allows me to track tariff rates and import/export consumption at the boundary line. (This is a UK setup).
Hope the above is of use to someone out there.
Thanks.
Roland.
hi. i have inverter connected to DTSU666 via RS485 to logger. could i connect to the same connector another rs485 to ttl converter in parallel so i could integrate power meter data it to home assistant with ESPhome?
Hi, I am getting the same issue with the float error on checking the config.
modbus:
  - name: modhub1
    type: serial
    baudrate: 9600
    bytesize: 8
    method: rtu
    parity: N
    port: /dev/ttyUSB1
    stopbits: 1
    sensors:
      - name: "sdm230_active_power"
        unique_id: sdm230_active_power
        slave: 1
        address: 12
        input_type: input
        count: 2
        precision: 4
        data_type: float32
        unit_of_measurement: W
        device_class: power
I am on OS 12.2 and Core 2024.4.4
Configuration warnings
Invalid config for ‘modbus’ at configuration.yaml, line 186: sdm230_active_power: count illegal with data_type: float32 ‘modbus->0->sensors->0’, got {‘name’: ‘sdm230_active_power’, ‘unique_id’: ‘sdm230_active_power’, ‘slave’: 1, ‘address’: 12, ‘input_type’: ‘input’, ‘count’: 2, ‘precision’: 4, ‘data_type’: ‘float32’, ‘unit_of_measurement’: ‘W’, ‘device_class’: ‘power’}
Any idea what’s wrong? I have tried float, float16 and float32
I managed to fix it by removing count: 2 and am getting now getting readings. But they seem much less frequent that how often the meter itself changes - and it goes unavailable every so often too.
Hi I have used your example and corrected a new parameters (I will share soon) but I have come across and issue with a missing device_class called “reactive_energy”. I have opened an enhacement request, could you vote/comment on it if needed:
Once i have something with this fix I will share my complete config.
Thanks!
I have the same question :slight_smile: