solved
Baud Rate 9600 and everything go well
Hi Mattie
I have a question.
How did you setup energy dashboard? I mean battery storage. SRNE inverter doesnāt give data in kWh. Mathematic is simple but I donāt know how to setup it in HA:(
Hi! You were right about the colors, my bad. Actually I think I have them the other way around, I dont really think it matters? I tried a lot in the beginning when I didnt get any data so I guess I just left them as that when it finally worked.
As for the energy dashboard I got influx and grafana if you wanna go and do those handsome graphs.
And in hassio I have been testing out different calculations for my template sensors, Iām sticking with these at the moment, the battery charge/discharge actually seems pretty acurate even tho I use a non changing 24.8 for voltage, I have been thinking about making an input_number that gets populated by the current voltage every hour to make these calculations instead in the future:
inverter_overhead_daily:
friendly_name: Inverter Overhead
device_class: energy
unit_of_measurement: 'kWh'
value_template: >
{{ (states('sensor.daily_inverter_ac') | float(0) + states('sensor.inverter_battery_discharge_ah_daily') | float(0) - states('sensor.inverter_battery_charge_ah_daily') | float(0) - states('sensor.daily_energy_ac') | float(0) - states('sensor.daily_soluttag_energy') | float(0) - states('sensor.daily_studioserver_energy') | float(0)) | round(1) }}
inverter_battery_charge_ah_daily:
friendly_name: Batteri laddat idag
icon_template: mdi:battery-high
value_template: >
{{ (states('sensor.daily_inverter_battery_charge_ah') | float(0) * 27.8 / 1000 | float) | round(2) }}
inverter_battery_discharge_ah_daily:
friendly_name: Batteri urladdat idag
value_template: >
{{ (states('sensor.daily_inverter_battery_discharge_ah') | float(0) * 24.8 / 1000 | float) | round(2) }}
inverter_battery_charge_energy:
friendly_name: Batteri laddat Increasing
value_template: >
{{ (states('sensor.modbus_inverter_battery_charge') | float(0) * 24.8 / 1000 | float) | round(2) }}
inverter_battery_discharge_energy:
friendly_name: Batteri urladdat Increasing
value_template: >
{{ (states('sensor.modbus_inverter_battery_discharge') | float(0) * 24.8 / 1000 | float) | round(2) }}
inverter_battery_power:
friendly_name: Batteribank effekt
device_class: power
unit_of_measurement: 'W'
icon_template: mdi:flash
value_template: >
{{ (states('sensor.modbus_inverter_batteryv') | float(0) * states('sensor.modbus_inverter_batterya') | float) | round(1) }}
inverter_battery_power_kwh:
friendly_name: Batteribank effekt kWh
device_class: power
value_template: >
{{ (states('sensor.inverter_battery_power') | float(0) / 1000 | float(0) ) | round(2) }}
I use the battery charge discharge in Ah from modbus
#Accumulated battery charge AH
- name: Modbus_Inverter_battery_charge
unique_id: Modbus_Inverter_battery_charge
scan_interval: 245
unit_of_measurement: ah
state_class: total_increasing
scale: 1
precision: 1
slave: 1
address: 61492
input_type: holding
#Accumulated battery discharge AH
- name: Modbus_Inverter_battery_discharge
unique_id: Modbus_Inverter_battery_discharge
scan_interval: 260
scale: 1
precision: 1
slave: 1
address: 61494
input_type: holding
My latest version of the solar-dashboard looks like this:
Do you get any unavailable states when the sun is out from your modbus waveshare gateway? My current problem is that when the sun is out I get āunavailableā state very often, this only happens when the sun is out, almost as if the inverter prioritizes the internal mppt calculation and not the modbus protocol when it has to āwork moreā
Wow
Thanks for you Mattie I learned what is template sensor. Game changer I have to say.
I have no problem with states. After 3 days its looks solid.
Did you connected GND wire to waveshare gateway because you didnāt mention about it. Or try my baud rate settings.
Ps. Do you have SRNE address book, I want to look inside
Yes templatesensors solve many issues!
Actually I havenāt connected the GND at this point, maybe Iāll give it a try. Of course I have plenty of modbus requests also, at least 20 different sensors polling the gateway even though some are grouped into one. It is possible that Iām on thr limit of what the inverter interface can deliver also.
Iāve pasted the modbus address index in this post. Enjoy
Easyupload.io - Upload files for free and transfer big files easily. (Link available for 30 days)
Never forget the GND!
Everything seems fine now! Thanks for reminding me! Also I had the colors right, I just fat fingered in my initial post here
ha! good to hear that:)
Nice
I control my SRNE with HA writing registers to control charging mode and source mode. I have an integration polling the electricity price forecast that sets an automation to start charging batteries on the lowest cost hour. Works great, I also have an automation controlling the load so that the battery never goes beyond 24.4V on my 6p2s batterybank. When the voltage gets close the automation sets charge to āPV onlyā and Source to āmainsā. I posted about writing registers a few posts up here, just use script
What SRNE model do you use exactly? I see that you got almost 3kWh from solar. And I already need to upgrade⦠
Also where did you buy it? Anything you could recommend?
Hi Mattie
My model is 5k older SRNE
Iām not super turbo extra happy about it because of minimum battery voltage which I cannot setup property. They got software limitation to 40V and I cant go lower with it
They selling it on AliExpress and I sow that they got new model. Iām living in Sicilly and from 10 panels and this inverter I got more power that I need during the day and generally Iām very happy about this setup
Actually Iām looking at this model now, did you order from Ali? Was it all good?
no no, I bring it from Poland, Iām polish guy who moved to Sicily. But a lot of my friends ordered from Ali. You have to wait a little but its working well
Actually Iām also from Poland but live in Sweden.
where did you get it from?? You could dm me!
Edit, saw your dm now
Can I also read this out with ESPHOME (ESP32)? I have an RS232 at the inverter and could read that via Modbus, right?
As long as you communicate with the same protocol you should be able to use esphome to do it with the code above. Iāve seen a few videos on yt where ppl do it. It seems like a more troublesome way though. The waveshare unit costs about 25$ and itās pretty much plug and play
I already have two of them to a srne and a epever tracer (differens modbus addresses ofc)
Works pretty good
Mattie and others thanks for the great information in this thread. I own the 3000w SRNE hybrid inverter, and the waveshare gateway linked in the initial post by Mattie(My inverter is the 110v version since I live in Japan(I am Danish though). It was dead easy to set up thanks to this thread. I know how to make scripts in HA however I lack the reference to the registers. What I am trying to accomplish is something like what Mattie is doing ie change the working mode between CSO/OSO etc in setting ā6ā in the inverter display. I saw that you shared a pdf with those Mattie but the Link has expired could you repost it or can I dm you with my e-mail and have you mail it to me? I could ask SRNE support and I have tried but they dont seam to respond Thanks in advance Best regards Anders
I envy you, I LOVE Japan and would like to travel there sometime
Send me your email address in dm here and Iāll send you the file when I wake up tomorrow, itās 01.00 here in Sweden. Or if you want I can give you my whole config. I have two different models now and it works like a charm on both of them
Thanks a lot for the kind words and your quick reply. I canāt make dmās for some reason however, so I will type my e-mail it is: xxxxxxxxxxx. I would love to have a look at you config files if possible and not to much trouble. I am very impressed with your setup. Thanks again I really appreciate it. Tack sĆ„ mycket!
Figured I might as well paste my raw updated code here. Excuse the mess in the code, much trial and error so Iāve commented some parts away that I dont use but may wanna get back to. Take what you need
# MODBUS
modbus:
# SRNE HYBRID - 1600W
- type: rtuovertcp
host: 192.168.1.30
port: 8888
sensors:
- name: "Main Battery"
address: 256
slave: 1
count: 3
scan_interval: 10
data_type: custom
structure: ">3H"
- name: "Main Panel"
address: 263
slave: 1
count: 3
scan_interval: 11
data_type: custom
structure: ">3H"
- name: "Main Usage"
address: 61487
slave: 1
count: 2
scan_interval: 12
data_type: custom
structure: ">2H"
- name: "Main Info"
address: 540
slave: 1
count: 10
scan_interval: 13
data_type: custom
structure: ">10h"
#Load active power phase A
- name: Modbus_Inverter_Power
unique_id: Modbus_Inverter_Power
scan_interval: 11
unit_of_measurement: W
scale: 1
slave: 1
address: 539
input_type: holding
#Battery current
- name: Modbus_Inverter_BatteryA
unique_id: Modbus_Inverter_BatteryA
scan_interval: 63
unit_of_measurement: A
scale: 0.1
precision: 1
slave: 1
address: 258
input_type: holding
#Total charge power, include charge power by mains and pv
- name: Modbus_Inverter_Charge_power
unique_id: Modbus_Inverter_Charge_power
scan_interval: 64
scale: 1
slave: 1
address: 270
input_type: holding
#Charge state
- name: Modbus_Inverter_battery_chargestate
unique_id: Modbus_Inverter_battery_chargestate
scan_interval: 65
unit_of_measurement: state
scale: 1
slave: 1
address: 267
input_type: holding
#Current state of the machine
- name: Modbus_Inverter_Operation
unique_id: Modbus_Inverter_Operation
scan_interval: 60
scale: 1
slave: 1
address: 528
input_type: holding
#Battery side current by PV charging
- name: Modbus_Inverter_PV_charge_current
unique_id: Modbus_Inverter_PV_charge_current
scan_interval: 63
scale: 0.1
precision: 1
slave: 1
address: 548
input_type: holding
# RĆKNARE
#Accumulated PV power generation
- name: Modbus_Inverter_PV_Generated
unique_id: Modbus_Inverter_PV_Generated
scan_interval: 240
unit_of_measurement: kWh
scale: 0.1
precision: 1
slave: 1
address: 61496
input_type: holding
scan_interval: 245
device_class: power
scale: 1
precision: 1
slave: 1
address: 61492
input_type: holding
scan_interval: 260
device_class: power
scale: 1
precision: 1
slave: 1
address: 61494
input_type: holding
#Power consumption by load from mains of today
- name: Modbus_Inverter_Main_load_power_daily
unique_id: Modbus_Inverter_Main_load_power_daily
scan_interval: 280
scale: 0.1
precision: 1
slave: 1
address: 61501
input_type: holding
#Output Priority
- name: Modbus_Inverter_output_priority
unique_id: Modbus_Inverter_output_priority
scan_interval: 34
scale: 1
slave: 1
address: 57860
input_type: holding
#Charge Priority
- name: Modbus_Inverter_charge_priority
unique_id: Modbus_Inverter_charge_priority
scan_interval: 35
scale: 1
slave: 1
address: 57871
input_type: holding
#Mains Charge Limit
- name: Modbus_Inverter_mains_charge_limit
unique_id: Modbus_Inverter_mains_charge_limit
scan_interval: 30
unit_of_measurement: 'A'
scale: 0.1
slave: 1
address: 57861
input_type: holding
# SRNE HYBRID - 4000W
- type: rtuovertcp
host: 192.168.1.29
port: 8888
sensors:
- name: "Main Battery 500v"
address: 256
slave: 1
count: 3
scan_interval: 10
data_type: custom
structure: ">3H"
- name: "Main Panel 500v"
address: 263
slave: 1
count: 3
scan_interval: 11
data_type: custom
structure: ">3H"
- name: "Main Usage 500v"
address: 61487
slave: 1
count: 2
scan_interval: 12
data_type: custom
structure: ">2H"
- name: "Main Info 500v"
address: 540
slave: 1
count: 10
scan_interval: 13
data_type: custom
structure: ">10h"
- name: Modbus_Inverter_500v_Power
unique_id: Modbus_Inverter_500v_Power
scan_interval: 11
scale: 1
slave: 1
address: 539
input_type: holding
#Battery current
- name: Modbus_Inverter_500v_BatteryA
unique_id: Modbus_Inverter_500v_BatteryA
scan_interval: 63
scale: 0.1
precision: 1
slave: 1
address: 258
input_type: holding
- name: Modbus_Inverter_500v_Charge_power
unique_id: Modbus_Inverter_500v_Charge_power
scan_interval: 64
scale: 1
slave: 1
address: 270
input_type: holding
#Charge state
- name: Modbus_Inverter_500v_battery_chargestate
unique_id: Modbus_Inverter_500v_battery_chargestate
scan_interval: 65
scale: 1
slave: 1
address: 267
input_type: holding
- name: Modbus_Inverter_500v_Operation
unique_id: Modbus_Inverter_500v_Operation
scan_interval: 60
scale: 1
slave: 1
address: 528
input_type: holding
- name: Modbus_Inverter_500v_PV_charge_current
unique_id: Modbus_Inverter_500v_PV_charge_current
scan_interval: 63
scale: 0.1
precision: 1
slave: 1
address: 548
input_type: holding
# RĆKNARE
- name: Modbus_Inverter_500v_PV_Generated
unique_id: Modbus_Inverter_500v_PV_Generated
scan_interval: 240
scale: 0.1
precision: 1
slave: 1
address: 61496
input_type: holding
scan_interval: 245
device_class: power
scale: 1
precision: 1
slave: 1
address: 61492
input_type: holding
- name: Modbus_Inverter_500v_battery_discharge
unique_id: Modbus_Inverter_500v_battery_discharge
scan_interval: 260
device_class: power
scale: 1
precision: 1
slave: 1
address: 61494
input_type: holding
- name: Modbus_Inverter_500v_Main_load_power_daily
unique_id: Modbus_Inverter_500v_Main_load_power_daily
scan_interval: 280
scale: 0.1
precision: 1
slave: 1
address: 61501
input_type: holding
#Output Priority
- name: Modbus_Inverter_500v_output_priority
unique_id: Modbus_Inverter_500v_output_priority
scan_interval: 34
scale: 1
slave: 1
address: 57860
input_type: holding
#Charge Priority
- name: Modbus_Inverter_500v_charge_priority
unique_id: Modbus_Inverter_500v_charge_priority
scan_interval: 35
scale: 1
slave: 1
address: 57871
input_type: holding
#Mains Charge Limit
- name: Modbus_Inverter_500v_mains_charge_limit
unique_id: Modbus_Inverter_500v_mains_charge_limit
scan_interval: 30
scale: 0.1
slave: 1
address: 57861
input_type: holding
# TEMPLATE SENSORER
sensors:
daily_solar_total_energy:
unique_id: daily_solar_total_energy
friendly_name: Sol Totalt Idag
value_template: >
{{ (states('sensor.daily_inverter_pv') | float(0) + states('sensor.daily_inverter_500v_pv') | float(0) + states('sensor.daily_epever_energy') | float(0)) | round(1) }}
#Main power bƄda inverters
inverters_ac_power:
unique_id: inverters_ac_power
friendly_name: "Inverters AC Totalt"
device_class: power
value_template: "{{ (states('sensor.inverter_ac_power') | float(0) + states('sensor.inverter_500v_ac_power') | float(0)) | round(0) }}"
#Fƶrbrukare bƄda inverters
inverters_power:
unique_id: inverters_power
friendly_name: "Fƶrbrukare Totalt"
device_class: power
value_template: "{{ (states('sensor.modbus_inverter_power') | float(0) + states('sensor.modbus_inverter_500v_power') | float(0)) | round(0) }}"
solar_total_power:
unique_id: solar_total_power
friendly_name: "Sol Totalt"
device_class: power
value_template: "{{ (states('sensor.modbus_inverter_pv_power') | float(0) + states('sensor.modbus_inverter_500v_pv_power') | float(0) + states('sensor.epever_array_power_template') | float(0)) | round(0) }}"
solar_total_power_kwh:
unique_id: solar_total_power_kwh
device_class: power
value_template: "{{ ((states('sensor.modbus_inverter_pv_power') | float(0) + states('sensor.modbus_inverter_500v_pv_power') | float(0) + states('sensor.epever_array_power_template') | float(0)) / 1000) | round(1) }}"
batterybank_shelly_template:
unique_id: batterybank_shelly_template
friendly_name: "Batteribank"
unit_of_measurement: 'V'
icon_template: mdi:car-battery
value_template: "{{ states('sensor.batterybank_low_adc') | float(0) + states('sensor.shelly_uni_batteri_adc') | float(0) | round(1) }}"
# inverter_forbrukare_energy:
# friendly_name: "Inverter Fƶrbrukare -Batteri"
# device_class: energy
# unit_of_measurement: 'kWh'
# icon_template: mdi:power-socket-eu
# value_template: "{{ (states('sensor.daily_soluttag_energy') | float + states('sensor.daily_satoshi') | float + states('sensor.daily_energy_ac') | float + states('sensor.inverter_battery_charge_ah_daily') | float(0) + states('sensor.daily_energy_studioserver') | float) | round(1) }}"
# + states('sensor.daily_energy_studioserver') | float
soluttag_total_daily_energy:
unique_id: soluttag_total_daily_energy
friendly_name: Soluttag Totalt
value_template: >
{{ (states('sensor.daily_energy_ac') | float(0) + states('sensor.daily_satoshi') | float(0) + states('sensor.daily_soluttag_energy') | float(0) + states('sensor.daily_energy_studioserver') | float) | round(1) }}
# SRNE 1600W Templates
modbus_inverter_batterylevel:
friendly_name: "Main Battery SOC"
unit_of_measurement: '%'
value_template: "{{ (states('sensor.main_battery').split(',')[0]) }}"
modbus_inverter_batteryv:
friendly_name: "Main Battery Voltage"
unit_of_measurement: V
value_template: "{{ (states('sensor.main_battery').split(',')[1]|float * 0.1)|round(1) }}"
# modbus_inverter_batterya:
# friendly_name: "Main Battery Current"
# unit_of_measurement: A
# value_template: "{{ (states('sensor.main_battery').split(',')[2]|float * 0.1)|round(1) }}"
modbus_inverter_pv_voltage:
friendly_name: "Main Panel Voltage"
value_template: "{{ (states('sensor.main_panel').split(',')[0]|float * 0.1)|round(1) }}"
modbus_inverter_pv_current:
friendly_name: "Main Panel Current"
value_template: "{{ (states('sensor.main_panel').split(',')[1]|float * 0.1)|round(1) }}"
modbus_inverter_pv_power:
unique_id: modbus_inverter_pv_power
friendly_name: 'Main Panel Power'
value_template: "{{ (states('sensor.main_panel').split(',')[2]) }}"
modbus_inverter_pv_power_kwh:
unique_id: modbus_inverter_pv_power_kwh
value_template: "{{ (states('sensor.main_panel').split(',')[2]|float / 1000) | round(2) }}"
#ANVĆNDS??
main_power_generated:
friendly_name: "Main Power Generated"
#state_class: total_increasing
value_template: "{{ (states('sensor.main_usage').split(',')[0]|float * 0.1)|round(1) }}"
main_power_consumed:
friendly_name: "Main Power Consumed"
value_template: "{{ (states('sensor.main_usage').split(',')[1]|float * 0.1)|round(1) }}"
# main_load_power:
# friendly_name: "Main Load Power"
# unit_of_measurement: W
# value_template: "{{ (states('sensor.main_load').split(',')[0]) }}"
# main_load_percent:
# friendly_name: "Main Load Percentage"
# unit_of_measurement: '%'
# value_template: "{{ (states('sensor.main_load').split(',')[3]) }}"
modbus_inverter_main_charge_current_new:
friendly_name: "Main Charge Current"
value_template: "{{ (states('sensor.main_info').split(',')[2]|float * 0.1) }}"
modbus_inverter_loadratio:
value_template: "{{ (states('sensor.main_info').split(',')[3]) }}"
modbus_inverter_dcdc_temp:
friendly_name: "DC-DC"
unit_of_measurement: '°C'
value_template: "{{ (states('sensor.main_info').split(',')[4]|float * 0.1) }}"
modbus_inverter_dcac_temp:
friendly_name: "DC-AC"
value_template: "{{ (states('sensor.main_info').split(',')[5]|float * 0.1) }}"
modbus_inverter_translator_temp:
friendly_name: "Translator"
value_template: "{{ (states('sensor.main_info').split(',')[6]|float * 0.1) }}"
# modbus_inverter_pv_charge_current_new:
# friendly_name: "PV Charge Current"
# unit_of_measurement: 'A'
# value_template: "{{ (states('sensor.main_info').split(',')[8]|float * 0.1) }}"
# SRNE 4000W Templates
modbus_inverter_500v_batterylevel:
value_template: "{{ (states('sensor.main_battery_500v').split(',')[0]) }}"
modbus_inverter_500v_batteryv:
value_template: "{{ (states('sensor.main_battery_500v').split(',')[1]|float * 0.1)|round(1) }}"
# modbus_inverter_500v_batterya:
# value_template: "{{ (states('sensor.main_battery_500v').split(',')[2]|float * 0.1)|round(1) }}"
modbus_inverter_500v_pv_voltage:
value_template: "{{ (states('sensor.main_panel_500v').split(',')[0]|float * 0.1)|round(1) }}"
modbus_inverter_500v_pv_current:
value_template: "{{ (states('sensor.main_panel_500v').split(',')[1]|float * 0.1)|round(1) }}"
modbus_inverter_500v_pv_power:
unique_id: modbus_inverter_500v_pv_power
value_template: "{{ (states('sensor.main_panel_500v').split(',')[2]) }}"
modbus_inverter_500v_pv_power_kwh:
unique_id: modbus_inverter_500v_pv_power_kwh
value_template: "{{ (states('sensor.main_panel_500v').split(',')[2]|float / 1000) | round(2) }}"
#ANVĆNDS??
main_500v_power_generated:
value_template: "{{ (states('sensor.main_usage_500v').split(',')[0]|float * 0.1)|round(1) }}"
main_500v_power_consumed:
value_template: "{{ (states('sensor.main_usage_500v').split(',')[1]|float * 0.1)|round(1) }}"
modbus_inverter_500v_main_charge_current_new:
value_template: "{{ (states('sensor.main_info_500v').split(',')[2]|float * 0.1) }}"
modbus_inverter_500v_loadratio:
value_template: "{{ (states('sensor.main_info_500v').split(',')[3]) }}"
modbus_inverter_500v_dcdc_temp:
value_template: "{{ (states('sensor.main_info_500v').split(',')[4]|float * 0.1) }}"
modbus_inverter_500v_dcac_temp:
value_template: "{{ (states('sensor.main_info_500v').split(',')[5]|float * 0.1) }}"
modbus_inverter_500v_translator_temp:
value_template: "{{ (states('sensor.main_info_500v').split(',')[6]|float * 0.1) }}"
# inverter_mains_power:
# friendly_name: Inverter Mains Power
# unit_of_measurement: 'W'
# value_template: >
# {{ states('sensor.modbus_grid_voltage') | float(0) * states('sensor.modbus_grid_current') | float(0) }}
inverter_batterybank_soc:
friendly_name: Batteribank SOC
value_template: >
{{ (100 - ((states('sensor.inverter_battery_discharge_ah_daily2') | float(0) / 9 ) * 100)) | round(0) }}
inverter_batterybank_soc2:
value_template: >
{{ (100 - ((states('sensor.inverter_battery_laddat_net_idag') | float(0) / 9 ) * 100)) | round(0) }}
# Utility Meter Tracking - tracks specific state time of a device/counter
utility_meter:
daily_epever_energy:
source: sensor.epever_total_generated_energy
cycle: daily
daily_inverter_battery_charge_ah:
source: sensor.modbus_inverter_battery_charge
cycle: daily
daily_inverter_battery_discharge_ah:
source: sensor.modbus_inverter_battery_discharge
cycle: daily
daily_inverter_500v_battery_charge_ah:
source: sensor.modbus_inverter_500v_battery_charge
cycle: daily
daily_inverter_500v_battery_discharge_ah:
source: sensor.modbus_inverter_500v_battery_discharge
cycle: daily
daily_soluttag_energy:
unique_id: daily_soluttag_energy
source: sensor.soluttag_energy
cycle: daily
daily_inverter_pv:
unique_id: daily_inverter_pv
source: sensor.modbus_inverter_pv_generated
cycle: daily
daily_inverter_500v_pv:
unique_id: daily_inverter_500v_pv
source: sensor.modbus_inverter_500v_pv_generated
cycle: daily
daily_inverter_ac:
source: sensor.inverter_ac_energy
cycle: daily
monthly_inverter_ac:
cycle: monthly