I wanted to share an update for those using follow me action. I’ve created a pull request on ESPHome that improves the functionality of the Follow Me action for Midea AC units, specifically allowing temperature updates to be sent in Fahrenheit. This should resolve an issue where Midea AC units would switch to Celsius by default when receiving updates from ESPHome, which was inconvenient for users who prefer Fahrenheit.
The action, midea_ac.follow_me, now supports temperature input in Fahrenheit. Here’s a quick example of the YAML setup:
temperature: Sets the external room temperature for the AC to use.
use_fahrenheit: When set to true, sends temperature in Fahrenheit (defaults to false, Celsius).
beeper: Optionally enables a beep on each update (defaults to false).
I’d love some help testing this to ensure it works well across various Midea based AC models. If anyone here is able to test it and share feedback here or on github pull request, it would be greatly appreciated!
For more info how to test it, take a look at pull request external component example. Syslog is not needed.
For HAHB it do not think that it is that complicated as described in the document, but that the power is taken from the 2 wires over a transformer that blocks modulated differential signals from other sources and that there is enough dampening by capacitors, that the power-consumption ripples are much lower than the communication patterns.
I’m happy to help with both hardware development and testing for xye and pqe and ha-hb interface. Just i need some intro about hardware required. I’ve got minisplit inverter ac that’s midea under the hood. I posted photo of indoor wiring diagram in #1218 above but i only have display board currently. What’s exact part number for multifunction board?
This module is shipped with 2 wiring harnesses which are the same BUT does not have the adapter cable that connects the plug on the AC’s main control board pcb (CN32) with the harness (because Bosch unit come preinstalled?)
On my unit at home i use a kit that is almost the same as the Bosch.
At my unit the 12V (CN32) cable was not already mounted and shipped with the board, but i had to fully disassemble the unit to plug it into the right connector.
–>The wiring between CN32 (main control board) and CN43 (multifunction/adapter board) is split into 2 cables.
(My unit: Midea All easy Blue == Xtreme Save Blue)
My module was sold as MFB-C and is shipped with the missing 12V cable (for me the other wiring looked the same incl. same poliarity as the bosch labeled, PCB has same ID sticker!)
The bad thing is, that i need the box formfactor like the bosch module has, but MFB-C is some other formfactor. If i have some time in the next days, then i print a housing.
@DjordjeMandic thanks a lot for your investigation! You added another brandlabel for that kind of AC - i was not aware that Midea is behind some Samsung variants too…
For the AR12TXHQASINEU AR3500 mini-split, operating at 23°C in heating mode with a maximum airflow of 540 m³/h, we can estimate airflow at different fan speeds based on proportional RPM scaling. This approach gives us the following approximate values:
Fan Speed and Corresponding Airflow Rates (approximately)
Mode
IF Parameter (HEX)
Indoor Fan (DEC)
RPM
Approximate Airflow (m³/h)
Silence
41-42
65-66
650-660 RPM
~280 m³/h
Low
47-48
71-72
710-720 RPM
~305 m³/h
Medium
5B-5C
91-92
910-920 RPM
~390 m³/h
High
6F-70
111-112
1110-1120 RPM
~475 m³/h
Boost/Turbo
7D-7F
125-127
1250-1270 RPM
~540 m³/h
Calculating Power Transfer and COP
With measurements of inlet and outlet air temperature, humidity, pressure, and airflow, you can calculate the power transferred to the air using:
P = density × flow rate × specific heat × ΔT
Here:
Power Transferred to Air (or Power Output) can be calculated from airflow and temperature difference.
Power Input can be read directly from an electricity meter.
For instance, with an airflow of 540 m³/h in turbo mode, my manual calculation (using only ΔT and airflow) resulted in a power output of 4.16 kW at 2°C outdoor temperature, while drawing approximately 1.3 kW from the wall, yielding a COP of ~3.2.
Inquiry Mode and Accessing RPM Data
These fan speeds were obtained manually using the IF parameter in inquiry mode. I’m exploring whether there’s a way to read RPM directly via UART or XYE/Modbus protocols.
While the unit has a built-in fan RPM sensor that could be tapped for direct readings, there may be a simpler way to access this data. If anyone has experience with accessing RPM values through these protocols or knows whether COP and EER are directly reported by the unit, that information would be helpful.