No response from modbus slave 2, register 0
There are still at least 2 issues open on github:
As for progress, there’s been none as far as I know in terms of fixing the component’s timing or allowing configurable delays between commands.
The only progress I’m aware of is a work-in-progress pull request from 12 days ago to allow multiple hubs:
Personally, I don’t have any hope that there will be a timely resolution for the issue (from the group of volunteer programmers we have) so I got a modbus RTU->TCP/IP converter a month or two ago, and the Modbus TCP/IP component seems to work fine. Or, as another user pointed out, you could try reading it in through NodeRed i suppose…
Hi
I have the ‘No response from Modbus Slave…’ issue too. (SDM230 and SDM120 power meters connected to USB on the Pi. SDM120 gives continuous errors. SDM230 is fine)
Would you share your hardware/software setup?
Thank you.
The node red modbus implementation works fine for me, I am reading 18 push buttons, four temperature sensors and six SDM120 power meters. The push buttons are read every 200 ms and the others a bit less frequent. I am then publishing these to MQTT sensors which home assistant picks up. It is very fast and I have no errors. I am also writing coils and registers from node red to my PLC. I can recommend this approach.
Yes it seems like Node-red is the way to go.
Would you share your flow?
Sorry for late reply, I have been kind of busy lately… But here is a copy of one of my flows for reading data from a SDM120 power meter. I am using modbus RTU over ethernet so you will have to change that to use serial if that is what you are using.
[{“id”:“3ff3c8de.aec258”,“type”:“inject”,“z”:“151c0cc5.f5da43”,“name”:“10 sec injector”,“topic”:“”,“payload”:“”,“payloadType”:“date”,“repeat”:“10”,“crontab”:“”,“once”:false,“onceDelay”:0.1,“x”:180,“y”:180,“wires”:[[“287acab3.2791a6”]]},{“id”:“287acab3.2791a6”,“type”:“function”,“z”:“151c0cc5.f5da43”,“name”:“Read 14 registers from slave 1”,“func”:“msg.payload = {\n ‘fc’: 4, \n ‘unitid’: 1, \n ‘address’: 0 ,\n ‘quantity’: 14 \n};\nreturn msg;”,“outputs”:1,“noerr”:0,“x”:170,“y”:220,“wires”:[[“12c70b26.040335”]]},{“id”:“12c70b26.040335”,“type”:“modbus-flex-getter”,“z”:“151c0cc5.f5da43”,“name”:“voltage”,“showStatusActivities”:false,“showErrors”:false,“logIOActivities”:false,“server”:“47e72f12.61fc5”,“useIOFile”:false,“ioFile”:“”,“useIOForPayload”:false,“x”:120,“y”:280,“wires”:[[“444e31ff.fe70a”],]},{“id”:“444e31ff.fe70a”,“type”:“function”,“z”:“151c0cc5.f5da43”,“name”:“splitter”,“func”:“var x = [0,0,0,0,0,0,0,0,0,0,0,0,0,0];\nvar msg_o = [0,0,0,0,0,0,0,0,0,0,0,0,0,0];\nfor(i=0;i<14; i++){\n msg_o[i] = {payload: msg.payload[i]}; \n}\nreturn msg_o;”,“outputs”:14,“noerr”:0,“x”:410,“y”:260,“wires”:[[“fcae43a4.eaa99”],[“fcae43a4.eaa99”],,,,,[“7c2709b6.f7f588”],[“7c2709b6.f7f588”],,,,,[“e36ec90b.af1458”],[“e36ec90b.af1458”]],“outputLabels”:[“coil 100 livingroom1”,“coil 101”,“coil 102”,“coil 103”,“”,“”,“”,“”,null,null,null,null,null,null]},{“id”:“fcae43a4.eaa99”,“type”:“join”,“z”:“151c0cc5.f5da43”,“name”:“”,“mode”:“custom”,“build”:“array”,“property”:“payload”,“propertyType”:“msg”,“key”:“topic”,“joiner”:“\n”,“joinerType”:“str”,“accumulate”:false,“timeout”:“”,“count”:“2”,“reduceRight”:false,“reduceExp”:“”,“reduceInit”:“”,“reduceInitType”:“”,“reduceFixup”:“”,“x”:570,“y”:180,“wires”:[[“5bb317c7.4ac088”]]},{“id”:“7c2709b6.f7f588”,“type”:“join”,“z”:“151c0cc5.f5da43”,“name”:“”,“mode”:“custom”,“build”:“array”,“property”:“payload”,“propertyType”:“msg”,“key”:“topic”,“joiner”:“\n”,“joinerType”:“str”,“accumulate”:false,“timeout”:“”,“count”:“2”,“reduceRight”:false,“reduceExp”:“”,“reduceInit”:“”,“reduceInitType”:“”,“reduceFixup”:“”,“x”:570,“y”:240,“wires”:[[“1a80b27b.0efefe”]]},{“id”:“e36ec90b.af1458”,“type”:“join”,“z”:“151c0cc5.f5da43”,“name”:“”,“mode”:“custom”,“build”:“array”,“property”:“payload”,“propertyType”:“msg”,“key”:“topic”,“joiner”:“\n”,“joinerType”:“str”,“accumulate”:false,“timeout”:“”,“count”:“2”,“reduceRight”:false,“reduceExp”:“”,“reduceInit”:“”,“reduceInitType”:“”,“reduceFixup”:“”,“x”:570,“y”:300,“wires”:[[“5cbb0f4b.4d56d”]]},{“id”:“5bb317c7.4ac088”,“type”:“function”,“z”:“151c0cc5.f5da43”,“name”:“convert to float”,“func”:“var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\n\nmsg.payload = parseFloat(fltView[0]).toFixed(1);\nmsg.payload = Number(msg.payload);\n\nreturn msg;”,“outputs”:1,“noerr”:0,“x”:740,“y”:180,“wires”:[[“5e854b4.e15a6b4”]]},{“id”:“1a80b27b.0efefe”,“type”:“function”,“z”:“151c0cc5.f5da43”,“name”:“convert to float”,“func”:“var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\n\nmsg.payload = parseFloat(fltView[0]).toFixed(1);\nmsg.payload = Number(msg.payload);\n\nreturn msg;”,“outputs”:1,“noerr”:0,“x”:740,“y”:240,“wires”:[[“4782900e.d6d67”]]},{“id”:“5cbb0f4b.4d56d”,“type”:“function”,“z”:“151c0cc5.f5da43”,“name”:“convert to float”,“func”:“var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\n\nmsg.payload = parseFloat(fltView[0]).toFixed(1);\nmsg.payload = Number(msg.payload);\n\nreturn msg;”,“outputs”:1,“noerr”:0,“x”:740,“y”:300,“wires”:[[“25e56.c9a981aa4”]]},{“id”:“5e854b4.e15a6b4”,“type”:“mqtt out”,“z”:“151c0cc5.f5da43”,“name”:“bathroom floor heating Voltage”,“topic”:“home/bathroom/floor_heating/voltage”,“qos”:“”,“retain”:“”,“broker”:“122d308f.7370af”,“x”:1010,“y”:180,“wires”:},{“id”:“4782900e.d6d67”,“type”:“mqtt out”,“z”:“151c0cc5.f5da43”,“name”:“bathroom floor heating current”,“topic”:“home/bathroom/floor_heating/current”,“qos”:“”,“retain”:“”,“broker”:“122d308f.7370af”,“x”:1010,“y”:240,“wires”:},{“id”:“25e56.c9a981aa4”,“type”:“mqtt out”,“z”:“151c0cc5.f5da43”,“name”:“bathroom floor heating power”,“topic”:“home/bathroom/floor_heating/power”,“qos”:“”,“retain”:“”,“broker”:“122d308f.7370af”,“x”:1000,“y”:300,“wires”:},{“id”:“47e72f12.61fc5”,“type”:“modbus-client”,“z”:“”,“name”:“ADM5850”,“clienttype”:“tcp”,“bufferCommands”:true,“stateLogEnabled”:false,“tcpHost”:“192.168.42.185”,“tcpPort”:“502”,“tcpType”:“DEFAULT”,“serialPort”:“/dev/ttyUSB”,“serialType”:“RTU-BUFFERD”,“serialBaudrate”:“9600”,“serialDatabits”:“8”,“serialStopbits”:“1”,“serialParity”:“none”,“serialConnectionDelay”:“100”,“unit_id”:1,“commandDelay”:1,“clientTimeout”:1000,“reconnectTimeout”:2000},{“id”:“122d308f.7370af”,“type”:“mqtt-broker”,“z”:“”,“name”:“Mosquitto”,“broker”:“192.168.42.187”,“port”:“1883”,“clientid”:“”,“usetls”:false,“compatmode”:true,“keepalive”:“60”,“cleansession”:true,“birthTopic”:“”,“birthQos”:“0”,“birthPayload”:“”,“closeTopic”:“”,“closeQos”:“0”,“closePayload”:“”,“willTopic”:“”,“willQos”:“0”,“willPayload”:“”}]
I don’t think this is the most elegant way to do things but it seems to work fine for me.
Thank you for the flow.
I’m having some trouble importing it to my node red. Don’t know what is wrong.
Did you add the node-red-contrib-modbus module? I. Don’t know anything else, I’m not very good with node red… Maybe there are some errors in a log somewhere?
Yes I have a couple of other Modbus flows.
I’m not too familiar with node red either.
I’ve just noticed that HA 0.87 has updated pymodbus to 1.5.2 (https://www.home-assistant.io/blog/2019/02/06/release-87/)
Not sure if anyone has tried that to see if it helps.
I’m also getting the same issue with my modbus system, so I will try the above update and see if it helps.
Failing that, I do like the idea of sending messages between HA and node-red via mqtt and using node-red to send the modbus signals. I’ll probably give that a try as well.
Thanks,
Steven
No it doesn’t.
Still getting 'No Response from Modbus slave 2
Agreed. I just tried the update and it still randmonly failed. Think I might have to give up with that at the moment.
I have just tried node-red, and mqtt switch, and nodered-contribute-modbus and so far it seems to be working quite well.
I’ve got the following simple flow working. Pierre, you might want to try this and see if it work. I’m using a modbus switch, so I’m using FC5 (force coil). I’m not doing anything with the output and no checking is done, but it’s a good first step.
[{"id":"4a3dc7c7.c90d1","type":"modbus-write","z":"eec9f23a.75d41","name":"","showStatusActivities":true,"showErrors":true,"unitid":"1","dataType":"Coil","adr":"1","quantity":"1","server":"94658b38.62cb6","x":600,"y":260,"wires":[["bed394fa.a1ec58"],["55ee8f1a.561cc"]]},{"id":"4e484671.44fc28","type":"inject","z":"eec9f23a.75d41","name":"","topic":"","payload":"65280","payloadType":"num","repeat":"","crontab":"","once":false,"onceDelay":0.1,"x":250,"y":180,"wires":[["4a3dc7c7.c90d1"]]},{"id":"e9b7c093.4650b","type":"inject","z":"eec9f23a.75d41","name":"","topic":"","payload":"0","payloadType":"num","repeat":"","crontab":"","once":false,"onceDelay":0.1,"x":250,"y":240,"wires":[["4a3dc7c7.c90d1"]]},{"id":"bed394fa.a1ec58","type":"modbus-response","z":"eec9f23a.75d41","name":"","registerShowMax":20,"x":830,"y":240,"wires":[]},{"id":"2943fb10.9f0454","type":"mqtt in","z":"eec9f23a.75d41","name":"","topic":"home/bedroom/switch1/set","qos":"2","broker":"a54831d3.55237","x":150,"y":100,"wires":[["232e73d6.50e254"]]},{"id":"232e73d6.50e254","type":"function","z":"eec9f23a.75d41","name":"","func":"if (msg.payload == \"ON\"){\n    msg.payload = 0xFF00;\n}\nelse{\n    msg.payload = 0;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":400,"y":140,"wires":[["4a3dc7c7.c90d1"]]},{"id":"55ee8f1a.561cc","type":"debug","z":"eec9f23a.75d41","name":"","active":true,"tosidebar":true,"console":false,"tostatus":false,"complete":"true","x":800,"y":320,"wires":[]},{"id":"94658b38.62cb6","type":"modbus-client","z":"","name":"","clienttype":"serial","bufferCommands":true,"stateLogEnabled":true,"tcpHost":"127.0.0.1","tcpPort":"502","tcpType":"DEFAULT","serialPort":"/dev/ttyUSB0","serialType":"RTU-BUFFERD","serialBaudrate":"19200","serialDatabits":"8","serialStopbits":"1","serialParity":"even","serialConnectionDelay":"100","unit_id":"1","commandDelay":"100","clientTimeout":"1000","reconnectTimeout":"2000"},{"id":"a54831d3.55237","type":"mqtt-broker","z":"","name":"","broker":"localhost","port":"1883","clientid":"","usetls":false,"compatmode":true,"keepalive":"60","cleansession":true,"birthTopic":"","birthQos":"0","birthPayload":"","closeTopic":"","closeQos":"0","closePayload":"","willTopic":"","willQos":"0","willPayload":""}]
Also, in my configuration file:
switch:
    - platform: mqtt
      command_topic: "home/bedroom/switch1/set"
To all those who have been having trouble with ‘No Response from Modbus slave 2’,
I’ve got this:
using this flow:
[{"id":"cf294862.7e8b68","type":"tab","label":"SDM","disabled":false,"info":""},{"id":"39fe0e66.c9799a","type":"comment","z":"cf294862.7e8b68","name":"SDM230 Energy Meter","info":"","x":160,"y":80,"wires":[]},{"id":"94d8cc20.dddda8","type":"modbus-read","z":"cf294862.7e8b68","name":"SDM 230 Voltage","topic":"","showStatusActivities":true,"logIOActivities":false,"showErrors":true,"unitid":"1","dataType":"InputRegister","adr":"0","quantity":"2","rate":"15","rateUnit":"s","delayOnStart":false,"startDelayTime":"","server":"8a72579f.202908","useIOFile":false,"ioFile":"","useIOForPayload":false,"x":160,"y":140,"wires":[["8e5f6d2b.cfc398"],[]]},{"id":"8e5f6d2b.cfc398","type":"function","z":"cf294862.7e8b68","name":"Voltage","func":"var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\nmsg.payload = parseFloat(fltView[0].toFixed(1));\nmsg.topic = \"voltage\";\n\nnode.status({fill:\"blue\",shape:\"ring\",text:msg.topic + \":\" + msg.payload});    \n\nreturn msg;","outputs":1,"noerr":0,"x":380,"y":140,"wires":[["9f73b54.da6f348","755cac29.d21844"]]},{"id":"9f73b54.da6f348","type":"ui_text","z":"cf294862.7e8b68","group":"52e8e5ce.130db4","order":1,"width":0,"height":0,"name":"","label":"Voltage","format":"{{msg.payload}} V","layout":"row-spread","x":560,"y":140,"wires":[]},{"id":"2d92317c.0c8ff6","type":"modbus-read","z":"cf294862.7e8b68","name":"SDM 230 Current","topic":"","showStatusActivities":true,"logIOActivities":false,"showErrors":true,"unitid":"1","dataType":"InputRegister","adr":"6","quantity":"2","rate":"15","rateUnit":"s","delayOnStart":false,"startDelayTime":"","server":"8a72579f.202908","useIOFile":false,"ioFile":"","useIOForPayload":false,"x":160,"y":200,"wires":[["ffab16d2.30bce8"],[]]},{"id":"ffab16d2.30bce8","type":"function","z":"cf294862.7e8b68","name":"Current","func":"var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\nmsg.payload = parseFloat(fltView[0].toFixed(1));\nmsg.topic = \"current\";\n\nnode.status({fill:\"blue\",shape:\"ring\",text:msg.topic + \":\" + msg.payload});    \n\nreturn msg;","outputs":1,"noerr":0,"x":380,"y":200,"wires":[["3dce87d7.a582d","755cac29.d21844"]]},{"id":"3dce87d7.a582d","type":"ui_text","z":"cf294862.7e8b68","group":"52e8e5ce.130db4","order":2,"width":0,"height":0,"name":"","label":"Current","format":"{{msg.payload}} A","layout":"row-spread","x":560,"y":200,"wires":[]},{"id":"dd502269.cf075","type":"modbus-read","z":"cf294862.7e8b68","name":"SDM 230 Power","topic":"","showStatusActivities":true,"logIOActivities":false,"showErrors":true,"unitid":"1","dataType":"InputRegister","adr":"12","quantity":"2","rate":"15","rateUnit":"s","delayOnStart":false,"startDelayTime":"","server":"8a72579f.202908","useIOFile":false,"ioFile":"","useIOForPayload":false,"x":160,"y":260,"wires":[["7c9ac9f6.45e8c"],[]]},{"id":"7c9ac9f6.45e8c","type":"function","z":"cf294862.7e8b68","name":"Power","func":"var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\nmsg.payload = parseFloat(fltView[0].toFixed(1));\nmsg.topic = \"power\";\n\nnode.status({fill:\"blue\",shape:\"ring\",text:msg.topic + \":\" + msg.payload});    \n\nreturn msg;","outputs":1,"noerr":0,"x":370,"y":260,"wires":[["ecdf6f70.f8cf8","755cac29.d21844"]]},{"id":"ecdf6f70.f8cf8","type":"ui_text","z":"cf294862.7e8b68","group":"52e8e5ce.130db4","order":3,"width":0,"height":0,"name":"","label":"Power","format":"{{msg.payload}} W","layout":"row-spread","x":550,"y":260,"wires":[]},{"id":"2a33780f.6c1dc8","type":"modbus-read","z":"cf294862.7e8b68","name":"SDM 230 Energy Imp","topic":"","showStatusActivities":true,"logIOActivities":false,"showErrors":true,"unitid":"1","dataType":"InputRegister","adr":"72","quantity":"2","rate":"15","rateUnit":"s","delayOnStart":false,"startDelayTime":"","server":"8a72579f.202908","useIOFile":false,"ioFile":"","useIOForPayload":false,"x":180,"y":320,"wires":[["39e8800a.b2141"],[]]},{"id":"39e8800a.b2141","type":"function","z":"cf294862.7e8b68","name":"Import","func":"var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\nmsg.payload = (parseFloat(fltView[0]) * 1.00361 + 36481.26).toFixed(2) ;\nmsg.topic = \"import\";\n\nnode.status({fill:\"blue\",shape:\"ring\",text:msg.topic + \":\" + msg.payload});    \n\nreturn msg;","outputs":1,"noerr":0,"x":370,"y":320,"wires":[["6860a00d.4d03","755cac29.d21844"]]},{"id":"6860a00d.4d03","type":"ui_text","z":"cf294862.7e8b68","group":"52e8e5ce.130db4","order":4,"width":0,"height":0,"name":"","label":"Energy Import","format":"{{msg.payload}} kWh","layout":"row-spread","x":580,"y":320,"wires":[]},{"id":"7a47858b.2a485c","type":"modbus-read","z":"cf294862.7e8b68","name":"SDM 230 Energy Exp","topic":"","showStatusActivities":true,"logIOActivities":false,"showErrors":true,"unitid":"1","dataType":"InputRegister","adr":"74","quantity":"2","rate":"15","rateUnit":"s","delayOnStart":false,"startDelayTime":"","server":"8a72579f.202908","useIOFile":false,"ioFile":"","useIOForPayload":false,"x":180,"y":380,"wires":[["f8a5e4dd.65dd4"],[]]},{"id":"f8a5e4dd.65dd4","type":"function","z":"cf294862.7e8b68","name":"Export","func":"var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\nmsg.payload = (parseFloat(fltView[0]) * 1.00229 + 10274.41).toFixed(2);\nmsg.topic = \"export\";\n\nnode.status({fill:\"blue\",shape:\"ring\",text:msg.topic + \":\" + msg.payload});    \n\nreturn msg;","outputs":1,"noerr":0,"x":370,"y":380,"wires":[["386c164e.4bbc1a","755cac29.d21844"]]},{"id":"386c164e.4bbc1a","type":"ui_text","z":"cf294862.7e8b68","group":"52e8e5ce.130db4","order":5,"width":0,"height":0,"name":"","label":"Energy Export","format":"{{msg.payload}} kWh","layout":"row-spread","x":580,"y":380,"wires":[]},{"id":"9f8b2c57.5d5a3","type":"comment","z":"cf294862.7e8b68","name":"SDM120 Energy Meter","info":"","x":160,"y":460,"wires":[]},{"id":"a6cb9467.69a86","type":"modbus-read","z":"cf294862.7e8b68","name":"SDM 120 Voltage","topic":"","showStatusActivities":true,"logIOActivities":false,"showErrors":true,"unitid":"2","dataType":"InputRegister","adr":"0","quantity":"2","rate":"15","rateUnit":"s","delayOnStart":false,"startDelayTime":"","server":"8a72579f.202908","useIOFile":false,"ioFile":"","useIOForPayload":false,"x":160,"y":520,"wires":[["5a8f390e.8a6918"],[]]},{"id":"5a8f390e.8a6918","type":"function","z":"cf294862.7e8b68","name":"Voltage","func":"var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\nmsg.payload = parseFloat(fltView[0].toFixed(1));\nmsg.topic = \"voltage\";\n\nnode.status({fill:\"blue\",shape:\"ring\",text:msg.topic + \":\" + msg.payload});    \n\nreturn msg;","outputs":1,"noerr":0,"x":380,"y":520,"wires":[["97ca0cdb.71eb2","7ee2add0.e052cc"]]},{"id":"97ca0cdb.71eb2","type":"ui_text","z":"cf294862.7e8b68","group":"519e323e.f5f804","order":1,"width":0,"height":0,"name":"","label":"Voltage","format":"{{msg.payload}} V","layout":"row-spread","x":560,"y":520,"wires":[]},{"id":"70f61194.d2be9","type":"modbus-read","z":"cf294862.7e8b68","name":"SDM 120 Current","topic":"","showStatusActivities":true,"logIOActivities":false,"showErrors":true,"unitid":"2","dataType":"InputRegister","adr":"6","quantity":"2","rate":"15","rateUnit":"s","delayOnStart":false,"startDelayTime":"","server":"8a72579f.202908","useIOFile":false,"ioFile":"","useIOForPayload":false,"x":160,"y":580,"wires":[["29bb0407.d78ee4"],[]]},{"id":"29bb0407.d78ee4","type":"function","z":"cf294862.7e8b68","name":"Current","func":"var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\nmsg.payload = parseFloat(fltView[0].toFixed(1));\nmsg.topic = \"current\";\n\nnode.status({fill:\"blue\",shape:\"ring\",text:msg.topic + \":\" + msg.payload});    \n\nreturn msg;","outputs":1,"noerr":0,"x":380,"y":580,"wires":[["17f9b22e.8513be","7ee2add0.e052cc"]]},{"id":"17da4ae.2fe14b5","type":"modbus-read","z":"cf294862.7e8b68","name":"SDM 120 Power","topic":"","showStatusActivities":true,"logIOActivities":false,"showErrors":true,"unitid":"2","dataType":"InputRegister","adr":"12","quantity":"2","rate":"15","rateUnit":"s","delayOnStart":false,"startDelayTime":"","server":"8a72579f.202908","useIOFile":false,"ioFile":"","useIOForPayload":false,"x":160,"y":640,"wires":[["a63fa0d5.975f4"],[]]},{"id":"a63fa0d5.975f4","type":"function","z":"cf294862.7e8b68","name":"Power","func":"var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\nmsg.payload = parseFloat(fltView[0].toFixed(1));\nmsg.topic = \"power\";\n\nnode.status({fill:\"blue\",shape:\"ring\",text:msg.topic + \":\" + msg.payload});    \n\nreturn msg;","outputs":1,"noerr":0,"x":370,"y":640,"wires":[["9862b54a.ce90d8","7ee2add0.e052cc"]]},{"id":"9862b54a.ce90d8","type":"ui_text","z":"cf294862.7e8b68","group":"519e323e.f5f804","order":3,"width":0,"height":0,"name":"","label":"Power","format":"{{msg.payload}} W","layout":"row-spread","x":550,"y":640,"wires":[]},{"id":"162178a0.2804af","type":"modbus-read","z":"cf294862.7e8b68","name":"SDM 120 Energy Sol","topic":"","showStatusActivities":true,"logIOActivities":false,"showErrors":true,"unitid":"2","dataType":"InputRegister","adr":"72","quantity":"2","rate":"15","rateUnit":"s","delayOnStart":false,"startDelayTime":"","server":"8a72579f.202908","useIOFile":false,"ioFile":"","useIOForPayload":false,"x":180,"y":700,"wires":[["82d22530.e1375","8ec5d960.4ca1d8"],[]]},{"id":"82d22530.e1375","type":"function","z":"cf294862.7e8b68","name":"Solar","func":"var rawData = new ArrayBuffer(4);\nvar intView = new Uint16Array(rawData);\nvar fltView = new Float32Array(rawData);\n\nintView[0] = msg.payload[1]; //low\nintView[1] = msg.payload[0]; //high\n\nmsg.payload = parseFloat(fltView[0] * 1.00099 + 21326.51).toFixed(2);\nmsg.topic = \"solar\";\n\nnode.status({fill:\"blue\",shape:\"ring\",text:msg.topic + \":\" + msg.payload});    \n\nreturn msg;","outputs":1,"noerr":0,"x":370,"y":700,"wires":[["f5ea2005.21f028","7ee2add0.e052cc"]]},{"id":"f5ea2005.21f028","type":"ui_text","z":"cf294862.7e8b68","group":"519e323e.f5f804","order":4,"width":0,"height":0,"name":"","label":"Energy Solar","format":"{{msg.payload}} kWh","layout":"row-spread","x":570,"y":700,"wires":[]},{"id":"17f9b22e.8513be","type":"ui_text","z":"cf294862.7e8b68","group":"519e323e.f5f804","order":2,"width":0,"height":0,"name":"","label":"Current","format":"{{msg.payload}} A","layout":"row-spread","x":560,"y":580,"wires":[]},{"id":"b4d90c81.c15988","type":"modbus-queue-info","z":"cf294862.7e8b68","name":"SDM120_queue","topic":"","unitid":"2","queueReadIntervalTime":"5000","lowLowLevel":"1","lowLevel":75,"highLevel":150,"highHighLevel":300,"server":"5642d1a0.fe87f8","errorOnHighLevel":false,"x":520,"y":900,"wires":[["ffd37a29.367e28"]]},{"id":"76179178.c5d938","type":"inject","z":"cf294862.7e8b68","name":"","topic":"","payload":"","payloadType":"date","repeat":"","crontab":"","once":false,"x":149.00000762939453,"y":901.0000247955322,"wires":[["606911.9f3c9ef"]]},{"id":"606911.9f3c9ef","type":"change","z":"cf294862.7e8b68","name":"Reset queue","rules":[{"t":"set","p":"resetQueue","pt":"msg","to":"true","tot":"bool"}],"action":"","property":"","from":"","to":"","reg":false,"x":318.00000762939453,"y":901.0000114440918,"wires":[["b4d90c81.c15988"]]},{"id":"cddb4c9d.baf348","type":"function","z":"cf294862.7e8b68","name":"reset on HighHigh","func":"if(\"high high level reached\" === msg.state) {\n    msg.resetQueue = true;\n    return msg;\n}\n","outputs":1,"noerr":0,"x":392.8571548461914,"y":1031.1428470611572,"wires":[["b4d90c81.c15988","ee028367.4ac758"]]},{"id":"44043ade.580f5c","type":"catch","z":"cf294862.7e8b68","name":"Catch queue errors","scope":["b4d90c81.c15988"],"x":154.8571548461914,"y":1031.1428470611572,"wires":[["cddb4c9d.baf348"]]},{"id":"c3715613.168cc8","type":"comment","z":"cf294862.7e8b68","name":"Error handling","info":"","x":120.8571548461914,"y":986.1428470611572,"wires":[]},{"id":"ee028367.4ac758","type":"function","z":"cf294862.7e8b68","name":"Diagnostic input message structure","func":"// setting a global flag that the solar system is down\n\nmsg.payload = \"SDM120 modbus queue reached high level, resetting. (\" + msg.state + \")\";\nmsg.system = 4; // System id, use 1 for Dummy\n//msg.state = 1; // specify if the message is to change system status\nmsg.severity = 1; // 0: information, 1: warning, 2: error\nmsg.email = false; // if separate email should be sent\n//msg.emailtext = \"Clean up step of the SAIA log backup has failed\";\nreturn msg;","outputs":1,"noerr":0,"x":692.8571548461914,"y":1030.1428470611572,"wires":[["390172ec.6edbce"]]},{"id":"390172ec.6edbce","type":"link out","z":"cf294862.7e8b68","name":"","links":["13e089a7.73cb46"],"x":878.8571548461914,"y":1030.1428470611572,"wires":[]},{"id":"5f3cd465.3b374c","type":"catch","z":"cf294862.7e8b68","name":"Modbus read errors","scope":["70f61194.d2be9","162178a0.2804af","17da4ae.2fe14b5","a6cb9467.69a86","9f8b2c57.5d5a3"],"x":154.8571548461914,"y":1074.1428470611572,"wires":[["ee788b69.b501d8"]]},{"id":"ee788b69.b501d8","type":"function","z":"cf294862.7e8b68","name":"Diagnostic input message structure","func":"// setting a global flag that the solar system is down\n\nmsg.payload = \"SDM120 modbus error: \" + msg.error.message;\nmsg.system = 4; // System id, use 1 for Dummy\n//msg.state = 1; // specify if the message is to change system status\nmsg.severity = 1; // 0: information, 1: warning, 2: error\nmsg.email = false; // if separate email should be sent\n//msg.emailtext = \"Clean up step of the SAIA log backup has failed\";\nreturn msg;","outputs":1,"noerr":0,"x":443.8571548461914,"y":1074.1428470611572,"wires":[["237b54e8.3c67bc"]]},{"id":"237b54e8.3c67bc","type":"link out","z":"cf294862.7e8b68","name":"","links":["13e089a7.73cb46"],"x":629.8571548461914,"y":1074.1428470611572,"wires":[]},{"id":"ffd37a29.367e28","type":"debug","z":"cf294862.7e8b68","name":"","active":false,"tosidebar":true,"console":false,"tostatus":false,"complete":"payload","x":720.8571548461914,"y":899.1428470611572,"wires":[]},{"id":"8ec5d960.4ca1d8","type":"function","z":"cf294862.7e8b68","name":"Health check","func":"var devicename = \"sdm120\"; // Device name used for context variable\nvar system_id = 4; // System id number for diagnostic update\nvar online_threshold = 10; // Seconds between updates under which the device is considered online\nvar offline_threshold = 30; // Seconds between updates above which the device is considered offline\n\nvar temp = context.get(devicename+\"_update\");\nvar current = new Date();\nmsg.payload = \"No data\";\nmsg.warning = false;\nif (msg.topic!==\"timecheck\") {\n    // Do not update the context if it is triggered by the check inject node\n    context.set(devicename+\"_update\",current);\n}\nif (temp===undefined) {\n    // this will be the case when node-red is booting up or redeployed\n    context.set(devicename+\"_update\",current);\n}\n\nif (temp!==undefined) {\n    current = current - temp;\n    current = Math.floor(current/1000);\n    var minute = Math.floor(current/60);\n    var hour = Math.floor(minute/60);\n    var day = Math.floor(hour/24);\n    if (current>24*60*60) {\n        msg.payload = \"Last update \" + day + \" days, \" + hour%24 + \" hours, \" + minute%60 + \" minutes, \" + current%60 + \" seconds ago\";\n    } else if (current>60*60) {\n        msg.payload = \"Last update \" + hour%24 + \" hours, \" + minute%60 + \" minutes, \" + current%60 + \" seconds ago\";\n    } else if (current>60) {\n        msg.payload = \"Last update \" + minute%60 + \" minutes, \" + current%60 + \" seconds ago\";\n    } else {\n        msg.payload = \"Last update \" + current%60 + \" seconds ago\";\n    }\n\n    if (context.get(devicename+\"_state\")!==1) {\n        if (current<online_threshold) {\n            msg.payload = \"SDM120 is now online\";\n            msg.system = system_id; // System id, use 1 for Dummy\n            msg.state = 1; // specify if the message is to change system status\n            msg.severity = 0; // 0: information, 1: warning, 2: error\n            //msg.email = true; // if separate email should be sent\n            //msg.emailtext = \"\"; this a long text which goes into the email  \n            msg.warning = true;\n            context.set(devicename+\"_state\",1);\n        }\n    } else {\n        if (current>offline_threshold) {\n            msg.payload = \"SDM120 is not transmitting\";\n            msg.system = system_id; // System id, use 1 for Dummy\n            msg.state = 99; // specify if the message is to change system status\n            msg.severity = 2; // 0: information, 1: warning, 2: error\n            //msg.email = true; // if separate email should be sent\n            //msg.emailtext = \"\"; this a long text which goes into the email            \n            msg.warning = true;\n            context.set(devicename+\"_state\",99);\n        }\n    }\n    \n    \n}\n\nnode.status({fill:\"blue\",shape:\"ring\",text:msg.payload});\n\nreturn msg;","outputs":1,"noerr":0,"x":390,"y":780,"wires":[["6cea0c6a.628304"]]},{"id":"ab080220.2b2ab8","type":"inject","z":"cf294862.7e8b68","name":"Check","topic":"timecheck","payload":"","payloadType":"date","repeat":"1","crontab":"","once":false,"x":140,"y":780,"wires":[["8ec5d960.4ca1d8"]]},{"id":"6cea0c6a.628304","type":"switch","z":"cf294862.7e8b68","name":"Update diag?","property":"warning","propertyType":"msg","rules":[{"t":"true"}],"checkall":"true","outputs":1,"x":585,"y":780,"wires":[["b3c5cd90.09b32"]]},{"id":"b3c5cd90.09b32","type":"link out","z":"cf294862.7e8b68","name":"","links":["13e089a7.73cb46"],"x":704.3015727996826,"y":779.571403503418,"wires":[]},{"id":"42364693.260b28","type":"modbus-queue-info","z":"cf294862.7e8b68","name":"SDM230_queue","topic":"","unitid":"1","queueReadIntervalTime":"5000","lowLowLevel":"1","lowLevel":75,"highLevel":150,"highHighLevel":300,"server":"5642d1a0.fe87f8","errorOnHighLevel":false,"x":520,"y":1160,"wires":[["dfb73b19.107e18"]]},{"id":"79d3e78d.d2d238","type":"inject","z":"cf294862.7e8b68","name":"","topic":"","payload":"","payloadType":"date","repeat":"","crontab":"","once":false,"x":149.00000762939453,"y":1161.0000247955322,"wires":[["6e42ae1a.04f558"]]},{"id":"6e42ae1a.04f558","type":"change","z":"cf294862.7e8b68","name":"Reset queue","rules":[{"t":"set","p":"resetQueue","pt":"msg","to":"true","tot":"bool"}],"action":"","property":"","from":"","to":"","reg":false,"x":318.00000762939453,"y":1161.0000114440918,"wires":[["42364693.260b28"]]},{"id":"40512c9f.ca430c","type":"function","z":"cf294862.7e8b68","name":"reset on HighHigh","func":"if(\"high high level reached\" === msg.state) {\n    msg.resetQueue = true;\n    return msg;\n}\n","outputs":1,"noerr":0,"x":392.8571548461914,"y":1291.1428470611572,"wires":[["42364693.260b28","2fe0a353.be909c"]]},{"id":"cb6ecebf.2473","type":"catch","z":"cf294862.7e8b68","name":"Catch queue errors","scope":["42364693.260b28"],"x":154.8571548461914,"y":1291.1428470611572,"wires":[["40512c9f.ca430c"]]},{"id":"438810a9.d9bb28","type":"comment","z":"cf294862.7e8b68","name":"Error handling","info":"","x":120.8571548461914,"y":1246.1428470611572,"wires":[]},{"id":"2fe0a353.be909c","type":"function","z":"cf294862.7e8b68","name":"Diagnostic input message structure","func":"// setting a global flag that the solar system is down\n\nmsg.payload = \"SDM120 modbus queue reached high level, resetting. (\" + msg.state + \")\";\nmsg.system = 4; // System id, use 1 for Dummy\n//msg.state = 1; // specify if the message is to change system status\nmsg.severity = 1; // 0: information, 1: warning, 2: error\nmsg.email = false; // if separate email should be sent\n//msg.emailtext = \"Clean up step of the SAIA log backup has failed\";\nreturn msg;","outputs":1,"noerr":0,"x":692.8571548461914,"y":1290.1428470611572,"wires":[["3ff9ed9f.31f832"]]},{"id":"3ff9ed9f.31f832","type":"link out","z":"cf294862.7e8b68","name":"","links":["13e089a7.73cb46"],"x":878.8571548461914,"y":1290.1428470611572,"wires":[]},{"id":"e85a26d5.e99ea8","type":"catch","z":"cf294862.7e8b68","name":"Modbus read errors","scope":["2d92317c.0c8ff6","7a47858b.2a485c","2a33780f.6c1dc8","dd502269.cf075","94d8cc20.dddda8","39fe0e66.c9799a"],"x":154.8571548461914,"y":1334.1428470611572,"wires":[["f880d888.e379f8"]]},{"id":"f880d888.e379f8","type":"function","z":"cf294862.7e8b68","name":"Diagnostic input message structure","func":"// setting a global flag that the solar system is down\n\nmsg.payload = \"SDM120 modbus error: \" + msg.error.message;\nmsg.system = 4; // System id, use 1 for Dummy\n//msg.state = 1; // specify if the message is to change system status\nmsg.severity = 1; // 0: information, 1: warning, 2: error\nmsg.email = false; // if separate email should be sent\n//msg.emailtext = \"Clean up step of the SAIA log backup has failed\";\nreturn msg;","outputs":1,"noerr":0,"x":443.8571548461914,"y":1334.1428470611572,"wires":[["93665473.948328"]]},{"id":"93665473.948328","type":"link out","z":"cf294862.7e8b68","name":"","links":["13e089a7.73cb46"],"x":629.8571548461914,"y":1334.1428470611572,"wires":[]},{"id":"dfb73b19.107e18","type":"debug","z":"cf294862.7e8b68","name":"","active":false,"tosidebar":true,"console":false,"tostatus":false,"complete":"payload","x":720.8571548461914,"y":1159.1428470611572,"wires":[]},{"id":"7ee2add0.e052cc","type":"function","z":"cf294862.7e8b68","name":"Build object","func":"watch_topic = \"solar\";\nvar output = {};\n\ncontext.set(msg.topic,msg.payload);\n\nif (context.get(\"voltage\")!==undefined) {\n    output.voltage = context.get(\"voltage\");\n}\nif (context.get(\"current\")!==undefined) {\n    output.current = context.get(\"current\");\n}\nif (context.get(\"power\")!==undefined) {\n    output.power = context.get(\"power\");\n}\nif (context.get(\"solar\")!==undefined) {\n    output.solar = context.get(\"solar\");\n}\nmsg.payload = output;\n\nif (msg.topic===watch_topic) {\n    msg.topic = \"sdm120\";\n    return msg;\n}","outputs":1,"noerr":0,"x":810,"y":600,"wires":[["d795a631.b276e8","e649422c.1df178"]]},{"id":"d795a631.b276e8","type":"debug","z":"cf294862.7e8b68","name":"","active":false,"tosidebar":true,"console":false,"tostatus":false,"complete":"true","x":970,"y":600,"wires":[]},{"id":"e649422c.1df178","type":"mqtt out","z":"cf294862.7e8b68","name":"SDM120","topic":"sdm120","qos":"","retain":"","broker":"eb79ed91.8ce1a8","x":980,"y":540,"wires":[]},{"id":"755cac29.d21844","type":"function","z":"cf294862.7e8b68","name":"Build object","func":"watch_topic = \"export\";\nvar output = {};\n\ncontext.set(msg.topic,msg.payload);\n\nif (context.get(\"voltage\")!==undefined) {\n    output.voltage = context.get(\"voltage\");\n}\nif (context.get(\"current\")!==undefined) {\n    output.current = context.get(\"current\");\n}\nif (context.get(\"power\")!==undefined) {\n    output.power = context.get(\"power\");\n}\nif (context.get(\"import\")!==undefined) {\n    output.import = context.get(\"import\");\n}\nif (context.get(\"export\")!==undefined) {\n    output.export = context.get(\"export\");\n}\nmsg.payload = output;\n\nif (msg.topic===watch_topic) {\n    msg.topic = \"sdm230\";\n    return msg;\n}","outputs":1,"noerr":0,"x":810,"y":260,"wires":[["88577a71.23e0a8","ae174f35.284c3"]]},{"id":"88577a71.23e0a8","type":"debug","z":"cf294862.7e8b68","name":"","active":false,"tosidebar":true,"console":false,"tostatus":false,"complete":"true","x":970,"y":260,"wires":[]},{"id":"ae174f35.284c3","type":"mqtt out","z":"cf294862.7e8b68","name":"SDM230","topic":"sdm230","qos":"","retain":"","broker":"eb79ed91.8ce1a8","x":980,"y":200,"wires":[]},{"id":"8a72579f.202908","type":"modbus-client","z":"","name":"Serial_9600_8_N_1","clienttype":"serial","bufferCommands":true,"stateLogEnabled":false,"tcpHost":"127.0.0.1","tcpPort":"502","tcpType":"DEFAULT","serialPort":"/dev/ttyUSB0","serialType":"RTU-BUFFERD","serialBaudrate":"9600","serialDatabits":"8","serialStopbits":"1","serialParity":"none","serialConnectionDelay":"100","unit_id":"","commandDelay":30,"clientTimeout":2000,"reconnectTimeout":5000},{"id":"52e8e5ce.130db4","type":"ui_group","z":"","name":"SDM 230 Energy Meter","tab":"543f66f3.88086","order":2,"disp":true,"width":"6","collapse":false},{"id":"519e323e.f5f804","type":"ui_group","z":"","name":"SDM 120 Energy Meter","tab":"543f66f3.88086","order":2,"disp":true,"width":"6","collapse":false},{"id":"5642d1a0.fe87f8","type":"modbus-client","z":"","name":"Serial_9600_8_N_1","clienttype":"serial","bufferCommands":true,"stateLogEnabled":false,"tcpHost":"127.0.0.1","tcpPort":"502","tcpType":"DEFAULT","serialPort":"/dev/ttyUSB0","serialType":"RTU-BUFFERD","serialBaudrate":"9600","serialDatabits":"8","serialStopbits":"1","serialParity":"none","serialConnectionDelay":"100","unit_id":"","commandDelay":"30","clientTimeout":"2000","reconnectTimeout":"5000"},{"id":"eb79ed91.8ce1a8","type":"mqtt-broker","z":"","name":"Mosquitto","broker":"192.168.1.200","port":"1883","clientid":"","usetls":false,"compatmode":true,"keepalive":"60","cleansession":true,"birthTopic":"","birthQos":"0","birthRetain":"false","birthPayload":"","closeTopic":"","closeQos":"0","closeRetain":"false","closePayload":"","willTopic":"","willQos":"0","willRetain":"false","willPayload":""},{"id":"543f66f3.88086","type":"ui_tab","z":"","name":"Modbus","icon":"memory","order":15}]
and this custom card:
and much insight from:
by Csongor Varga for my SDM120 (solar power) and SDM230 (grid import/export).
Hope it helps.
Hi guys. Is it still an issue?
If yes, I would like to help you.
Please add those lines to configuration yaml, and post the result here.
logger:
  default: info
  logs:
    homeassistant.components.modbus: debug
    pymodbus: debug
Thank you for your email. I’ve switched to a Node-red implementation which gives me more flexibility.
If I decide to switch back I will get back to you.
Hi @pavlo.tsiupka,
I’m using 3 modbus devices. Running the default modbus component, and 2 copies of the orginal modbus component as custom_components(Modbus over TCP/UDP).
I’m getting this issue very often(On all 3).
It seems like it occurs more often if using Modbus TCP rather than Modbus UDP.
At the end of this log you can see the error message:
No response from hub default, slave 1, register 1104
It feels like there should be some delay between the queries, it seems like it sends all queries at the same time, flooding the modbus unit.
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] Running transaction 204
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] SEND: 0x0 0xcc 0x0 0x0 0x0 0x6 0x1 0x4 0x4 0x51 0x0 0x1
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.client.sync] New Transaction state 'SENDING'
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] Changing transaction state from 'SENDING' to 'WAITING FOR REPLY'
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] Incomplete message received, Expected 1024 bytes Recieved 11 bytes !!!!
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] Changing transaction state from 'WAITING FOR REPLY' to 'PROCESSING REPLY'
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] RECV: 0x0 0xcc 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x0 0x2
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.framer.socket_framer] Processing: 0x0 0xcc 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x0 0x2
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.factory] Factory Response[ReadInputRegistersResponse: 4]
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] Adding transaction 204
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] Getting transaction 204
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.transaction] Running transaction 205
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.transaction] SEND: 0x0 0xcd 0x0 0x0 0x0 0x6 0x1 0x4 0x3 0xee 0x0 0x1
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.client.sync] New Transaction state 'SENDING'
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.transaction] Changing transaction state from 'SENDING' to 'WAITING FOR REPLY'
2019-04-16 22:25:00 DEBUG (SyncWorker_0) [pymodbus.transaction] Incomplete message received, Expected 1024 bytes Recieved 11 bytes !!!!
2019-04-16 22:25:00 DEBUG (SyncWorker_0) [pymodbus.transaction] Changing transaction state from 'WAITING FOR REPLY' to 'PROCESSING REPLY'
2019-04-16 22:25:00 DEBUG (SyncWorker_0) [pymodbus.transaction] RECV: 0x0 0x3c 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x8 0x34
2019-04-16 22:25:00 DEBUG (SyncWorker_0) [pymodbus.framer.socket_framer] Processing: 0x0 0x3c 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x8 0x34
2019-04-16 22:25:00 DEBUG (SyncWorker_0) [pymodbus.factory] Factory Response[ReadHoldingRegistersResponse: 3]
2019-04-16 22:25:00 DEBUG (SyncWorker_0) [pymodbus.transaction] Adding transaction 60
2019-04-16 22:25:00 DEBUG (SyncWorker_0) [pymodbus.transaction] Getting transaction 60
2019-04-16 22:25:00 DEBUG (SyncWorker_0) [pymodbus.transaction] Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.transaction] Incomplete message received, Expected 1024 bytes Recieved 11 bytes !!!!
2019-04-16 22:25:00 DEBUG (SyncWorker_2) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.transaction] Changing transaction state from 'WAITING FOR REPLY' to 'PROCESSING REPLY'
2019-04-16 22:25:00 DEBUG (SyncWorker_2) [pymodbus.transaction] Running transaction 61
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.transaction] RECV: 0x0 0xcd 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x9 0x60
2019-04-16 22:25:00 DEBUG (SyncWorker_2) [pymodbus.transaction] SEND: 0x0 0x3d 0x0 0x0 0x0 0x6 0x1 0x3 0x0 0xd5 0x0 0x1
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.framer.socket_framer] Processing: 0x0 0xcd 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x9 0x60
2019-04-16 22:25:00 DEBUG (SyncWorker_2) [pymodbus.client.sync] New Transaction state 'SENDING'
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.factory] Factory Response[ReadInputRegistersResponse: 4]
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.transaction] Adding transaction 205
2019-04-16 22:25:00 DEBUG (SyncWorker_2) [pymodbus.transaction] Changing transaction state from 'SENDING' to 'WAITING FOR REPLY'
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.transaction] Getting transaction 205
2019-04-16 22:25:00 DEBUG (SyncWorker_4) [pymodbus.transaction] Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.transaction] Running transaction 206
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.transaction] SEND: 0x0 0xce 0x0 0x0 0x0 0x6 0x1 0x4 0x5 0x18 0x0 0x1
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.client.sync] New Transaction state 'SENDING'
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.transaction] Changing transaction state from 'SENDING' to 'WAITING FOR REPLY'
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.transaction] Incomplete message received, Expected 1024 bytes Recieved 11 bytes !!!!
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.transaction] Changing transaction state from 'WAITING FOR REPLY' to 'PROCESSING REPLY'
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.transaction] RECV: 0x0 0xce 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x0 0x64
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.framer.socket_framer] Processing: 0x0 0xce 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x0 0x64
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.factory] Factory Response[ReadInputRegistersResponse: 4]
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.transaction] Adding transaction 206
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.transaction] Getting transaction 206
2019-04-16 22:25:00 DEBUG (SyncWorker_9) [pymodbus.transaction] Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] Running transaction 207
2019-04-16 22:25:00 DEBUG (SyncWorker_5) [pymodbus.transaction] SEND: 0x0 0xcf 0x0 0x0 0x0 0x6 0x1 0x4 0x7 0xd5 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Incomplete message received, Expected 1024 bytes Recieved 11 bytes !!!!
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Changing transaction state from 'WAITING FOR REPLY' to 'PROCESSING REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] RECV: 0x0 0x3d 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0xba
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.framer.socket_framer] Processing: 0x0 0x3d 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0xba
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.factory] Factory Response[ReadHoldingRegistersResponse: 3]
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Adding transaction 61
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Getting transaction 61
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] Running transaction 62
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] SEND: 0x0 0x3e 0x0 0x0 0x0 0x6 0x1 0x3 0x0 0xcb 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.client.sync] New Transaction state 'SENDING'
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Incomplete message received, Expected 1024 bytes Recieved 11 bytes !!!!
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Changing transaction state from 'WAITING FOR REPLY' to 'PROCESSING REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] RECV: 0x0 0xcf 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x0 0x3
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.framer.socket_framer] Processing: 0x0 0xcf 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x0 0x3
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] Changing transaction state from 'SENDING' to 'WAITING FOR REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.factory] Factory Response[ReadInputRegistersResponse: 4]
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Adding transaction 207
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Getting transaction 207
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Running transaction 208
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] SEND: 0x0 0xd0 0x0 0x0 0x0 0x6 0x1 0x4 0x7 0xc 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.client.sync] New Transaction state 'SENDING'
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Changing transaction state from 'SENDING' to 'WAITING FOR REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Incomplete message received, Expected 1024 bytes Recieved 11 bytes !!!!
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Changing transaction state from 'WAITING FOR REPLY' to 'PROCESSING REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] RECV: 0x0 0xd0 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x0 0x64
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.framer.socket_framer] Processing: 0x0 0xd0 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x0 0x64
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.factory] Factory Response[ReadInputRegistersResponse: 4]
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Adding transaction 208
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Getting transaction 208
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] Running transaction 209
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] SEND: 0x0 0xd1 0x0 0x0 0x0 0x6 0x1 0x4 0xa 0x2e 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.client.sync] New Transaction state 'SENDING'
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] Changing transaction state from 'SENDING' to 'WAITING FOR REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] Incomplete message received, Expected 1024 bytes Recieved 11 bytes !!!!
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] Changing transaction state from 'WAITING FOR REPLY' to 'PROCESSING REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] RECV: 0x0 0xd1 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x2 0xbc
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.framer.socket_framer] Processing: 0x0 0xd1 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x2 0xbc
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.factory] Factory Response[ReadInputRegistersResponse: 4]
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] Adding transaction 209
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] Getting transaction 209
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] Running transaction 210
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] SEND: 0x0 0xd2 0x0 0x0 0x0 0x6 0x1 0x4 0x8 0x39 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.client.sync] New Transaction state 'SENDING'
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] Changing transaction state from 'SENDING' to 'WAITING FOR REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] Incomplete message received, Expected 1024 bytes Recieved 11 bytes !!!!
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] Changing transaction state from 'WAITING FOR REPLY' to 'PROCESSING REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] RECV: 0x0 0x3e 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x0
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.framer.socket_framer] Processing: 0x0 0x3e 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x0
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.factory] Factory Response[ReadHoldingRegistersResponse: 3]
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] Adding transaction 62
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] Getting transaction 62
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Running transaction 63
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] SEND: 0x0 0x3f 0x0 0x0 0x0 0x6 0x1 0x3 0x0 0x64 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.client.sync] New Transaction state 'SENDING'
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Changing transaction state from 'SENDING' to 'WAITING FOR REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] Incomplete message received, Expected 1024 bytes Recieved 11 bytes !!!!
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] Changing transaction state from 'WAITING FOR REPLY' to 'PROCESSING REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] RECV: 0x0 0xd2 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x0 0x4
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.framer.socket_framer] Processing: 0x0 0xd2 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x0 0x4
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.factory] Factory Response[ReadInputRegistersResponse: 4]
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] Adding transaction 210
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] Getting transaction 210
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Running transaction 211
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] SEND: 0x0 0xd3 0x0 0x0 0x0 0x6 0x1 0x4 0x9 0x2 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.client.sync] New Transaction state 'SENDING'
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Changing transaction state from 'SENDING' to 'WAITING FOR REPLY'
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] RECV: 0x0 0xd3 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x8 0x98
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.framer.socket_framer] Processing: 0x0 0xd3 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x8 0x98
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Adding transaction 211
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Getting transaction 211
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Running transaction 212
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] SEND: 0x0 0xd4 0x0 0x0 0x0 0x6 0x1 0x4 0x8 0x35 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] RECV: 0x0 0xd4 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x9 0x4c
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.framer.socket_framer] Processing: 0x0 0xd4 0x0 0x0 0x0 0x5 0x1 0x4 0x2 0x9 0x4c
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Adding transaction 212
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Getting transaction 212
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] RECV: 0x0 0x3f 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x2
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.framer.socket_framer] Processing: 0x0 0x3f 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x2
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] Running transaction 213
2019-04-16 22:25:01 DEBUG (SyncWorker_4) [pymodbus.transaction] SEND: 0x0 0xd5 0x0 0x0 0x0 0x6 0x1 0x4 0x4 0x50 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Adding transaction 63
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Getting transaction 63
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] Running transaction 64
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] SEND: 0x0 0x40 0x0 0x0 0x0 0x6 0x1 0x3 0x2 0x58 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] RECV: 0x0 0x40 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0xc
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.framer.socket_framer] Processing: 0x0 0x40 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0xc
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] Adding transaction 64
2019-04-16 22:25:01 DEBUG (SyncWorker_0) [pymodbus.transaction] Getting transaction 64
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] Running transaction 65
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] SEND: 0x0 0x41 0x0 0x0 0x0 0x6 0x1 0x3 0x0 0xd6 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] RECV: 0x0 0x41 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0xe1
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.framer.socket_framer] Processing: 0x0 0x41 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0xe1
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.factory] Factory Response[ReadHoldingRegistersResponse: 3]
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] Adding transaction 65
2019-04-16 22:25:01 DEBUG (SyncWorker_9) [pymodbus.transaction] Getting transaction 65
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Running transaction 66
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] SEND: 0x0 0x42 0x0 0x0 0x0 0x6 0x1 0x3 0x0 0xc9 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] RECV: 0x0 0x42 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.framer.socket_framer] Processing: 0x0 0x42 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.factory] Factory Response[ReadHoldingRegistersResponse: 3]
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Adding transaction 66
2019-04-16 22:25:01 DEBUG (SyncWorker_5) [pymodbus.transaction] Getting transaction 66
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Running transaction 67
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] SEND: 0x0 0x43 0x0 0x0 0x0 0x6 0x1 0x3 0x1 0x7c 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] RECV: 0x0 0x43 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x18
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.framer.socket_framer] Processing: 0x0 0x43 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x18
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.factory] Factory Response[ReadHoldingRegistersResponse: 3]
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Adding transaction 67
2019-04-16 22:25:01 DEBUG (SyncWorker_8) [pymodbus.transaction] Getting transaction 67
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Running transaction 68
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] SEND: 0x0 0x44 0x0 0x0 0x0 0x6 0x1 0x3 0x0 0xd9 0x0 0x1
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] RECV: 0x0 0x44 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0xa
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.framer.socket_framer] Processing: 0x0 0x44 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0xa
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Adding transaction 68
2019-04-16 22:25:01 DEBUG (SyncWorker_2) [pymodbus.transaction] Getting transaction 68
2019-04-16 22:25:02 INFO (MainThread) [volvooncall.volvooncall] Updating
2019-04-16 22:25:04 DEBUG (SyncWorker_4) [pymodbus.transaction] Transaction failed. (timed out)
2019-04-16 22:25:04 DEBUG (SyncWorker_4) [pymodbus.framer.socket_framer] Processing:
2019-04-16 22:25:04 DEBUG (SyncWorker_4) [pymodbus.transaction] Getting transaction 213
2019-04-16 22:25:04 DEBUG (SyncWorker_4) [pymodbus.transaction] Changing transaction state from 'PROCESSING REPLY' to 'TRANSACTION_COMPLETE'
2019-04-16 22:25:04 ERROR (SyncWorker_4) [custom_components.modbus1.sensor] No response from hub default, slave 1, register 1104
The switch can act by the command, but no response for read state:
modbus:
type: rtuovertcp
host: 192.168.31.246
port: 8899
switch:
platform: modbus
coils:
- name: switch1
hub: hub1
slave: 1
coil: 0
- name: switch2
hub: hub1
slave: 1
coil: 1
- name: switch3
hub: hub1
slave: 1
coil: 2
- name: switch4
hub: hub1
slave: 1
coil: 3
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.transaction] Running transaction 11
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.transaction] SEND: 0x1 0x5 0x0 0x0 0xff 0x0 0x8c 0x3a
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.framer.rtu_framer] Changing state to IDLE - Last Frame End - 1556633598.135601, Current Time stamp - 1556633615.755921
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.client.sync] New Transaction state ‘SENDING’
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.transaction] Changing transaction state from ‘SENDING’ to ‘WAITING FOR REPLY’
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.transaction] Changing transaction state from ‘WAITING FOR REPLY’ to ‘PROCESSING REPLY’
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.transaction] RECV: 0x1 0x5 0x0 0x0 0xff 0x0 0x8c 0x3a
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.framer.rtu_framer] Getting Frame - 0x5 0x0 0x0 0xff 0x0
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.factory] Factory Response[WriteSingleCoilResponse: 5]
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.framer.rtu_framer] Frame advanced, resetting header!!
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.transaction] Adding transaction 11
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.transaction] Getting transaction 11
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-12) [pymodbus.transaction] Changing transaction state from ‘PROCESSING REPLY’ to ‘TRANSACTION_COMPLETE’
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-21) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-21) [pymodbus.transaction] Running transaction 12
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-21) [pymodbus.transaction] SEND: 0x1 0x1 0x0 0x0 0x0 0x1 0xfd 0xca
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-21) [pymodbus.framer.rtu_framer] Changing state to IDLE - Last Frame End - 1556633615.831405, Current Time stamp - 1556633615.867966
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-21) [pymodbus.client.sync] New Transaction state ‘SENDING’
Apr 30 22:13:35 raspberrypi hass[30580]: 2019-04-30 22:13:35 DEBUG (Thread-21) [pymodbus.transaction] Changing transaction state from ‘SENDING’ to ‘WAITING FOR REPLY’
Apr 30 22:13:38 raspberrypi hass[30580]: 2019-04-30 22:13:38 DEBUG (Thread-21) [pymodbus.transaction] Transaction failed. (Modbus Error: [Invalid Message] Incomplete message received, expected at least 2 bytes (0 received))
Apr 30 22:13:38 raspberrypi hass[30580]: 2019-04-30 22:13:38 DEBUG (Thread-21) [pymodbus.framer.rtu_framer] Frame - [b’’] not ready
Apr 30 22:13:38 raspberrypi hass[30580]: 2019-04-30 22:13:38 DEBUG (Thread-21) [pymodbus.transaction] Getting transaction 12
Apr 30 22:13:38 raspberrypi hass[30580]: 2019-04-30 22:13:38 DEBUG (Thread-21) [pymodbus.transaction] Changing transaction state from ‘PROCESSING REPLY’ to ‘TRANSACTION_COMPLETE’
Apr 30 22:13:38 raspberrypi hass[30580]: 2019-04-30 22:13:38 ERROR (Thread-21) [homeassistant.components.modbus.switch] No response from hub hub1, slave 1, coil 0
Apr 30 22:13:38 raspberrypi hass[30580]: 2019-04-30 22:13:38 DEBUG (Thread-3) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
Apr 30 22:13:38 raspberrypi hass[30580]: 2019-04-30 22:13:38 DEBUG (Thread-3) [pymodbus.transaction] Running transaction 13
Apr 30 22:13:38 raspberrypi hass[30580]: 2019-04-30 22:13:38 DEBUG (Thread-3) [pymodbus.transaction] SEND: 0x1 0x1 0x0 0x3 0x0 0x1 0xd 0xca
Apr 30 22:13:38 raspberrypi hass[30580]: 2019-04-30 22:13:38 DEBUG (Thread-3) [pymodbus.framer.rtu_framer] Changing state to IDLE - Last Frame End - 1556633618.873639, Current Time stamp - 1556633618.944335
Apr 30 22:13:38 raspberrypi hass[30580]: 2019-04-30 22:13:38 DEBUG (Thread-3) [pymodbus.client.sync] New Transaction state ‘SENDING’
Apr 30 22:13:38 raspberrypi hass[30580]: 2019-04-30 22:13:38 DEBUG (Thread-3) [pymodbus.transaction] Changing transaction state from ‘SENDING’ to ‘WAITING FOR REPLY’
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.transaction] Incomplete message received, Expected 6 bytes Recieved 0 bytes !!!
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.transaction] Changing transaction state from ‘WAITING FOR REPLY’ to ‘PROCESSING REPLY’
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.transaction] RECV:
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.framer.rtu_framer] Frame - [b’’] not ready
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.transaction] Getting transaction 13
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.transaction] Changing transaction state from ‘PROCESSING REPLY’ to ‘TRANSACTION_COMPLETE’
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 ERROR (Thread-3) [homeassistant.components.modbus.switch] No response from hub hub1, slave 1, coil 3
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.transaction] Running transaction 14
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.transaction] SEND: 0x1 0x1 0x0 0x1 0x0 0x1 0xac 0xa
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.framer.rtu_framer] Changing state to IDLE - Last Frame End - 1556633621.954821, Current Time stamp - 1556633621.972448
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.client.sync] New Transaction state ‘SENDING’
Apr 30 22:13:41 raspberrypi hass[30580]: 2019-04-30 22:13:41 DEBUG (Thread-3) [pymodbus.transaction] Changing transaction state from ‘SENDING’ to ‘WAITING FOR REPLY’
Apr 30 22:13:44 raspberrypi hass[30580]: 2019-04-30 22:13:44 DEBUG (Thread-3) [pymodbus.transaction] Incomplete message received, Expected 6 bytes Recieved 0 bytes !!!
Apr 30 22:13:44 raspberrypi hass[30580]: 2019-04-30 22:13:44 DEBUG (Thread-3) [pymodbus.transaction] Changing transaction state from ‘WAITING FOR REPLY’ to ‘PROCESSING REPLY’
Apr 30 22:13:44 raspberrypi hass[30580]: 2019-04-30 22:13:44 DEBUG (Thread-3) [pymodbus.transaction] RECV:
Apr 30 22:13:44 raspberrypi hass[30580]: 2019-04-30 22:13:44 DEBUG (Thread-3) [pymodbus.framer.rtu_framer] Frame - [b’’] not ready
Apr 30 22:13:44 raspberrypi hass[30580]: 2019-04-30 22:13:44 DEBUG (Thread-3) [pymodbus.transaction] Getting transaction 14
Apr 30 22:13:44 raspberrypi hass[30580]: 2019-04-30 22:13:44 DEBUG (Thread-3) [pymodbus.transaction] Changing transaction state from ‘PROCESSING REPLY’ to ‘TRANSACTION_COMPLETE’
Apr 30 22:13:44 raspberrypi hass[30580]: 2019-04-30 22:13:44 ERROR (Thread-3) [homeassistant.components.modbus.switch] No response from hub hub1, slave 1, coil 1
Apr 30 22:13:44 raspberrypi hass[30580]: 2019-04-30 22:13:44 DEBUG (Thread-7) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
Apr 30 22:13:44 raspberrypi hass[30580]: 2019-04-30 22:13:44 DEBUG (Thread-7) [pymodbus.transaction] Running transaction 15
Apr 30 22:13:44 raspberrypi hass[30580]: 2019-04-30 22:13:44 DEBUG (Thread-7) [pymodbus.transaction] SEND: 0x1 0x1 0x0 0x2 0x0 0x1 0x5c 0xa
Apr 30 22:13:45 raspberrypi hass[30580]: 2019-04-30 22:13:44 DEBUG (Thread-7) [pymodbus.framer.rtu_framer] Changing state to IDLE - Last Frame End - 1556633624.976122, Current Time stamp - 1556633624.998606
Apr 30 22:13:45 raspberrypi hass[30580]: 2019-04-30 22:13:45 DEBUG (Thread-7) [pymodbus.client.sync] New Transaction state ‘SENDING’
Apr 30 22:13:45 raspberrypi hass[30580]: 2019-04-30 22:13:45 DEBUG (Thread-7) [pymodbus.transaction] Changing transaction state from ‘SENDING’ to ‘WAITING FOR REPLY’
Apr 30 22:13:48 raspberrypi hass[30580]: 2019-04-30 22:13:48 DEBUG (Thread-7) [pymodbus.transaction] Incomplete message received, Expected 6 bytes Recieved 0 bytes !!!
Apr 30 22:13:48 raspberrypi hass[30580]: 2019-04-30 22:13:48 DEBUG (Thread-7) [pymodbus.transaction] Changing transaction state from ‘WAITING FOR REPLY’ to ‘PROCESSING REPLY’
Apr 30 22:13:48 raspberrypi hass[30580]: 2019-04-30 22:13:48 DEBUG (Thread-7) [pymodbus.transaction] RECV:
Apr 30 22:13:48 raspberrypi hass[30580]: 2019-04-30 22:13:48 DEBUG (Thread-7) [pymodbus.framer.rtu_framer] Frame - [b’’] not ready
Apr 30 22:13:48 raspberrypi hass[30580]: 2019-04-30 22:13:48 DEBUG (Thread-7) [pymodbus.transaction] Getting transaction 15
Apr 30 22:13:48 raspberrypi hass[30580]: 2019-04-30 22:13:48 DEBUG (Thread-7) [pymodbus.transaction] Changing transaction state from ‘PROCESSING REPLY’ to ‘TRANSACTION_COMPLETE’
Apr 30 22:13:48 raspberrypi hass[30580]: 2019-04-30 22:13:48 ERROR (Thread-7) [homeassistant.components.modbus.switch] No response from hub hub1, slave 1, coil 2
Apr 30 22:14:07 raspberrypi hass[30580]: 2019-04-30 22:14:07 DEBUG (Thread-13) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
Apr 30 22:14:07 raspberrypi hass[30580]: 2019-04-30 22:14:07 DEBUG (Thread-13) [pymodbus.transaction] Running transaction 16
Apr 30 22:14:07 raspberrypi hass[30580]: 2019-04-30 22:14:07 DEBUG (Thread-13) [pymodbus.transaction] SEND: 0x1 0x1 0x0 0x3 0x0 0x1 0xd 0xca
Apr 30 22:14:07 raspberrypi hass[30580]: 2019-04-30 22:14:07 DEBUG (Thread-13) [pymodbus.framer.rtu_framer] Changing state to IDLE - Last Frame End - 1556633628.006112, Current Time stamp - 1556633647.013301
Apr 30 22:14:07 raspberrypi hass[30580]: 2019-04-30 22:14:07 DEBUG (Thread-13) [pymodbus.client.sync] New Transaction state ‘SENDING’
Apr 30 22:14:07 raspberrypi hass[30580]: 2019-04-30 22:14:07 DEBUG (Thread-13) [pymodbus.transaction] Changing transaction state from ‘SENDING’ to ‘WAITING FOR REPLY’
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-13) [pymodbus.transaction] Incomplete message received, Expected 6 bytes Recieved 0 bytes !!!
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-13) [pymodbus.transaction] Changing transaction state from ‘WAITING FOR REPLY’ to ‘PROCESSING REPLY’
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-13) [pymodbus.transaction] RECV:
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-13) [pymodbus.framer.rtu_framer] Frame - [b’’] not ready
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-13) [pymodbus.transaction] Getting transaction 16
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-13) [pymodbus.transaction] Changing transaction state from ‘PROCESSING REPLY’ to ‘TRANSACTION_COMPLETE’
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 ERROR (Thread-13) [homeassistant.components.modbus.switch] No response from hub hub1, slave 1, coil 3
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-16) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-16) [pymodbus.transaction] Running transaction 17
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-16) [pymodbus.transaction] SEND: 0x1 0x1 0x0 0x2 0x0 0x1 0x5c 0xa
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-16) [pymodbus.framer.rtu_framer] Changing state to IDLE - Last Frame End - 1556633650.017537, Current Time stamp - 1556633650.036253
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-16) [pymodbus.client.sync] New Transaction state ‘SENDING’
Apr 30 22:14:10 raspberrypi hass[30580]: 2019-04-30 22:14:10 DEBUG (Thread-16) [pymodbus.transaction] Changing transaction state from ‘SENDING’ to ‘WAITING FOR REPLY’
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-16) [pymodbus.transaction] Incomplete message received, Expected 6 bytes Recieved 0 bytes !!!
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-16) [pymodbus.transaction] Changing transaction state from ‘WAITING FOR REPLY’ to ‘PROCESSING REPLY’
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-16) [pymodbus.transaction] RECV:
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-16) [pymodbus.framer.rtu_framer] Frame - [b’’] not ready
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-16) [pymodbus.transaction] Getting transaction 17
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-16) [pymodbus.transaction] Changing transaction state from ‘PROCESSING REPLY’ to ‘TRANSACTION_COMPLETE’
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 ERROR (Thread-16) [homeassistant.components.modbus.switch] No response from hub hub1, slave 1, coil 2
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-10) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-10) [pymodbus.transaction] Running transaction 18
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-10) [pymodbus.transaction] SEND: 0x1 0x1 0x0 0x1 0x0 0x1 0xac 0xa
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-10) [pymodbus.framer.rtu_framer] Changing state to IDLE - Last Frame End - 1556633653.040219, Current Time stamp - 1556633653.067706
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-10) [pymodbus.client.sync] New Transaction state ‘SENDING’
Apr 30 22:14:13 raspberrypi hass[30580]: 2019-04-30 22:14:13 DEBUG (Thread-10) [pymodbus.transaction] Changing transaction state from ‘SENDING’ to ‘WAITING FOR REPLY’
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.transaction] Incomplete message received, Expected 6 bytes Recieved 0 bytes !!!
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.transaction] Changing transaction state from ‘WAITING FOR REPLY’ to ‘PROCESSING REPLY’
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.transaction] RECV:
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.framer.rtu_framer] Frame - [b’’] not ready
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.transaction] Getting transaction 18
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.transaction] Changing transaction state from ‘PROCESSING REPLY’ to ‘TRANSACTION_COMPLETE’
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 ERROR (Thread-10) [homeassistant.components.modbus.switch] No response from hub hub1, slave 1, coil 1
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.transaction] Current transaction state - TRANSCATION_COMPLETE
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.transaction] Running transaction 19
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.transaction] SEND: 0x1 0x1 0x0 0x0 0x0 0x1 0xfd 0xca
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.framer.rtu_framer] Changing state to IDLE - Last Frame End - 1556633656.071715, Current Time stamp - 1556633656.089956
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.client.sync] New Transaction state ‘SENDING’
Apr 30 22:14:16 raspberrypi hass[30580]: 2019-04-30 22:14:16 DEBUG (Thread-10) [pymodbus.transaction] Changing transaction state from ‘SENDING’ to ‘WAITING FOR REPLY’
Apr 30 22:14:19 raspberrypi hass[30580]: 2019-04-30 22:14:19 DEBUG (Thread-10) [pymodbus.transaction] Incomplete message received, Expected 6 bytes Recieved 0 bytes !!!
Apr 30 22:14:19 raspberrypi hass[30580]: 2019-04-30 22:14:19 DEBUG (Thread-10) [pymodbus.transaction] Changing transaction state from ‘WAITING FOR REPLY’ to ‘PROCESSING REPLY’
Apr 30 22:14:19 raspberrypi hass[30580]: 2019-04-30 22:14:19 DEBUG (Thread-10) [pymodbus.transaction] RECV:
Apr 30 22:14:19 raspberrypi hass[30580]: 2019-04-30 22:14:19 DEBUG (Thread-10) [pymodbus.framer.rtu_framer] Frame - [b’’] not ready
Apr 30 22:14:19 raspberrypi hass[30580]: 2019-04-30 22:14:19 DEBUG (Thread-10) [pymodbus.transaction] Getting transaction 19
Apr 30 22:14:19 raspberrypi hass[30580]: 2019-04-30 22:14:19 DEBUG (Thread-10) [pymodbus.transaction] Changing transaction state from ‘PROCESSING REPLY’ to ‘TRANSACTION_COMPLETE’
Apr 30 22:14:19 raspberrypi hass[30580]: 2019-04-30 22:14:19 ERROR (Thread-10) [homeassistant.components.modbus.switch] No response from hub hub1, slave 1, coil 0
I appreciate your help.
I am playing with that a couple of day and always:
“No response from hub huawei, slave 1, register 32081
17:47 components/modbus/sensor.py (ERROR)”
I put your logger code into configuration.yaml, but else?
Pls let me know some other instructions, how to solve it…
Thank you.
Peter
I follow this post…
Is any way to fix it?
I have a lot of errors like this:
No response from hub default, slave 5, register 6
18:39 components/modbus/sensor.py (ERROR) - message first occured at 3 октября 2019 г., 21:57 and shows up 967 times
No response from hub default, slave 1, register 7
18:39 components/modbus/sensor.py (ERROR) - message first occured at 3 октября 2019 г., 21:58 and shows up 917 times
Cleanup recv buffer before send: 0xfe
18:39 components/modbus/init.py (WARNING) - message first occured at 3 октября 2019 г., 21:57 and shows up 628 times
No response from hub default, slave 1, register 6
18:39 components/modbus/sensor.py (ERROR) - message first occured at 3 октября 2019 г., 21:56 and shows up 857 times
No response from hub default, slave 3, register 10
18:39 components/modbus/sensor.py (ERROR) - message first occured at 3 октября 2019 г., 21:57 and shows up 901 times
Cleanup recv buffer before send: 0x0
18:39 components/modbus/init.py (WARNING) - message first occured at 3 октября 2019 г., 22:12 and shows up 119 times
No response from hub default, slave 4, register 10
18:39 components/modbus/sensor.py (ERROR) - message first occured at 3 октября 2019 г., 21:58 and shows up 901 times