Sonoff ZBMINI Extreme - ZBMINIL2 - 2 Way Wiring

Thanks Frank :+1:t2:

Well, I can only assume it’s defective as I changed nothing other than the relay itself and then all worked as it should :thinking:

I have the same wiring. I am stuck with the line (in) at the bottom of the stairs with switch 1, the load (out) at the top of the stairs with switch 2 and the light in the ceiling at the top of the stairs with a 14-3 (b/w/r/g) cable between 1 and 2. I have no way of installing another conductor to get the line (in) to the top of the stairs. Would it work to convert the two 3-way switches into single-pole, “steal” the traveler (red) wire and make it hot to the top of the stairs, tie the red to Sonoff L in, and to the switch 2 line and connect load to Sonoff S2, use black wire at switch 1 as load to top of stairs into Sonoff S1, and then the black to the load (out) into Sonoff L out? Or does that create an overload problem with potential fire hazard?

Better convert it to retractive switch, and change the switch mode on the mini

Hello All,

What is the situation for SONOFF Orb-ZBW1L witch uses the same relays? S1 and S2 are alredy occupied by wall enclosure.

Any chase to get this working as master and slave (dump switch) with one live wire?

Follow-up on my earlier question, in case it helps someone else with the same issue.

Setup: two 3-way (staircase) rocker switches controlling one light, in separate junction boxes about 7 meters apart. ZBMINIL2 installed in the box next to the bulb.

What DIDN’T work:
Wiring each switch as a simple 2-terminal switch (common + one traveler-turned-signal-wire to S1 or S2 respectively), leaving the third terminal on each switch unconnected. Result: each switch toggled the light perfectly on its own, but combining them failed — e.g. turn the light ON with switch 1, and switch 2 couldn’t turn it OFF. Wiring was triple-checked with a multimeter and was correct; the issue was that with one terminal left floating, each switch only produced a defined electrical signal in ONE of its two rocker positions.

What DID work:
Keep the ORIGINAL 3-way wiring between the two switches completely intact — both switches keep all 3 terminals in use (common + the two traveler wires between them), exactly as in a traditional staircase circuit. Only the COMMON of switch 2 connects to S2 on the module. S1 is left unused entirely. The module’s L in gets a permanent live feed (in my case from a nearby socket circuit, clearly labeled since it’s a different breaker than the lighting circuit — worth avoiding if you can feed it from the lighting circuit instead).

This matches the wiring diagram shared earlier in this thread (switch loop → S2 only, L in fed separately).

Official confirmation:
I contacted SONOFF support directly and they confirmed: S1 is not used in 2-way (staircase) configurations. Only S2 is used, fed by the intact traveler loop between the two switches.

Hope this saves someone else the troubleshooting time!