Hello,
does everyone use the full requests of
Paradigma
→ SystaSmartC
or
→ Systa Comfort II ?
Maybe someone can help me with a yaml script so that I will not have to do it (create) again.
Best regards
Tim
Hello,
does everyone use the full requests of
Paradigma
→ SystaSmartC
or
→ Systa Comfort II ?
Maybe someone can help me with a yaml script so that I will not have to do it (create) again.
Best regards
Tim
Blunt reply: No.
Exactly what is your issue? What are you creating again?
Would using something like this help?
With the information i could find i made 2 templates for the protocol_wizard.
(below an example part)
You could runtime add all these registers in one go via the integration and presto have all the registers.
GitHub - partach/protocol_wizard: The Protocol Wizard helps you build your home assistant devices without need for any yaml!.
Will add the templates in the next release (can make today if requested)
[
{
"name": "Boiler Status",
"address": 0,
"data_type": "uint16",
"register_type": "holding",
"rw": "read",
"unit": "",
"scale": 1.0,
"offset": 0.0,
"byte_order": "big",
"word_order": "big",
"allow_bits": false,
"options": "{\"0\": \"Standby\", \"1\": \"Heating\", \"2\": \"Error\"}"
},
{
"name": "Current Boiler Temperature",
"address": 1,
"data_type": "float32",
"register_type": "holding",
"rw": "read",
"unit": "°C",
"scale": 0.1,
"offset": 0.0,
"byte_order": "big",
"word_order": "big",
"allow_bits": false
},
{
"name": "Set Boiler Temperature",
"address": 2,
"data_type": "float32",
"register_type": "holding",
"rw": "rw",
"unit": "°C",
"scale": 0.1,
"offset": 0.0,
"byte_order": "big",
"word_order": "big",
"allow_bits": false
},
{
"name": "Pump Status",
"address": 10,
"data_type": "uint16",
"register_type": "holding",
"rw": "read",
"unit": "",
"scale": 1.0,
"offset": 0.0,
"byte_order": "big",
"word_order": "big",
"allow_bits": false,
"options": "{\"0\": \"Off\", \"1\": \"On\"}"
},
{
"name": "Outdoor Temperature",
"address": 20,
"data_type": "float32",
"register_type": "holding",
"rw": "read",
"unit": "°C",
"scale": 0.1,
"offset": 0.0,
"byte_order": "big",
"word_order": "big",
"allow_bits": false
},
{
"name": "Total Operating Hours",
"address": 30,
"data_type": "uint32",
"register_type": "holding",
"rw": "read",
"unit": "h",
"scale": 1.0,
"offset": 0.0,
"byte_order": "big",
"word_order": "big",
"allow_bits": false
},
{
"name": "Fault Code",
"address": 40,
"data_type": "uint16",
"register_type": "holding",
"rw": "read",
"unit": "",
"scale": 1.0,
"offset": 0.0,
"byte_order": "big",
"word_order": "big",
"allow_bits": false
}
]```
Hello partach,
thanks for answering my request.
I need both blueprints because I have both heatings.
What I wanted to have is something like ths;
- name: "SystaComfort"
type: tcp
host: 192.XXX.XXX.XX
port: 5XX
sensors:
- name: "Außentemperatur_Heizungsregler-SystaComfort2"
unique_id: Außentemperatur_Heizungsregler-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 0
data_type: int16
- name: "Vorlauftemperatur Heizkreis 1_Heizungsregler-SystaComfort2"
unique_id: Vorlauftemperatur Heizkreis 1_Heizungsregler-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 1
data_type: int16
- name: "Rücklauftemperatur Heizkreis 1_Heizungsregler-SystaComfort2"
unique_id: Rücklauftemperatur Heizkreis 1_Heizungsregler-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 2
data_type: int16
- name: "Warmwassertemperatur oben_Heizungsregler-SystaComfort2"
unique_id: Warmwassertemperatur oben_Heizungsregler-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 3
data_type: int16
- name: "Puffertemperatur oben_Heizungsregler-SystaComfort2"
unique_id: Puffertemperatur oben_Heizungsregler-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 4
data_type: int16
- name: "Puffertemperatur unten_Heizungsregler-SystaComfort2"
unique_id: Puffertemperatur unten_Heizungsregler-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 5
data_type: int16
- name: "Temperatur Zirkulationsrücklauf_Heizungsregler-SystaComfort2"
unique_id: Temperatur Zirkulationsrücklauf_Heizungsregler-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 6
data_type: int16
- name: "Vorlauftemperatur Heizkreis 2_Heizungsregler-SystaComfort2"
unique_id: Vorlauftemperatur Heizkreis 2_Heizungsregler-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 7
data_type: int16
- name: "Rücklauftemperatur Heizkreis 2_Heizungsregler-SystaComfort2"
unique_id: Rücklauftemperatur Heizkreis 2_Heizungsregler-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 8
data_type: int16
- name: "Raumtemperatur Heizkreis 1_Heizungsregler-SystaComfort2"
unique_id: Raumtemperatur Heizkreis 1_Heizungsregler-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 9
data_type: int16
- name: "Raumtemperatur Heizkreis 2_Heizungsregler-SystaComfort2"
unique_id: Raumtemperatur Heizkreis 2_Heizungsregler-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 10
data_type: int16
- name: "_SystaSolar Aqua II-SystaComfort2"
unique_id: _SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 11
data_type: int16
- name: "Vorlauftemperatur Kessel_Kessel (OT/LAN)-SystaComfort2"
unique_id: Vorlauftemperatur Kessel_Kessel (OT/LAN)-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 12
data_type: int16
- name: "Rücklauftemperatur Kessel_Kessel (OT/LAN)-SystaComfort2"
unique_id: Rücklauftemperatur Kessel_Kessel (OT/LAN)-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 13
data_type: int16
- name: "Vorlauftemperatur Holzkessel_SystaComfort Wood-SystaComfort2"
unique_id: Vorlauftemperatur Holzkessel_SystaComfort Wood-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 14
data_type: int16
- name: "Rücklauftemperatur Holzkessel_SystaComfort Wood-SystaComfort2"
unique_id: Rücklauftemperatur Holzkessel_SystaComfort Wood-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 15
data_type: int16
- name: "Puffertemperatur oben Holzkessel_SystaComfort Wood-SystaComfort2"
unique_id: Puffertemperatur oben Holzkessel_SystaComfort Wood-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 16
data_type: int16
- name: "Vorlauftemperatur Heizkreis 3_SystaComfort Heat-SystaComfort2"
unique_id: Vorlauftemperatur Heizkreis 3_SystaComfort Heat-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 17
data_type: int16
- name: "Rücklauftemperatur Heizkreis 3 _SystaComfort Heat-SystaComfort2"
unique_id: Rücklauftemperatur Heizkreis 3 _SystaComfort Heat-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 18
data_type: int16
- name: "Schwimmbad-Temperatur_SystaComfort Pool-SystaComfort2"
unique_id: Schwimmbad-Temperatur_SystaComfort Pool-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 19
data_type: int16
- name: "Vorlauftemperatur Schwimmbad-_SystaComfort Pool-SystaComfort2"
unique_id: Vorlauftemperatur Schwimmbad-_SystaComfort Pool-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 20
data_type: int16
- name: "Rücklauftemperatur_SystaComfort Pool-SystaComfort2"
unique_id: Rücklauftemperatur_SystaComfort Pool-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 21
data_type: int16
- name: "Einschaltfühler Schichtenspeicher_SystaComfort SI/KAS-SystaComfort2"
unique_id: Einschaltfühler Schichtenspeicher_SystaComfort SI/KAS-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 22
data_type: int16
- name: "Ausschaltfühler Schichtenspeicher_SystaComfort SI/KAS-SystaComfort2"
unique_id: Ausschaltfühler Schichtenspeicher_SystaComfort SI/KAS-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 23
data_type: int16
- name: "Einschichttemperatur Schichtenspeicher_SystaComfort SI/KAS-SystaComfort2"
unique_id: Einschichttemperatur Schichtenspeicher_SystaComfort SI/KAS-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 24
data_type: int16
- name: "Vorlauftemperatur Schichtenspeicher_SystaComfort SI/KAS-SystaComfort2"
unique_id: Vorlauftemperatur Schichtenspeicher_SystaComfort SI/KAS-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 25
data_type: int16
- name: "Temperatur Kaskade_SystaComfort SI/KAS-SystaComfort2"
unique_id: Temperatur Kaskade_SystaComfort SI/KAS-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 26
data_type: int16
- name: "Vorlauftemperatur Kessel 1 (Kaskade)_Kessel (OT/LAN)-SystaComfort2"
unique_id: Vorlauftemperatur Kessel 1 (Kaskade)_Kessel (OT/LAN)-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 27
data_type: int16
- name: "Vorlauftemperatur Kessel 2 (Kaskade)_Kessel (OT/LAN)-SystaComfort2"
unique_id: Vorlauftemperatur Kessel 2 (Kaskade)_Kessel (OT/LAN)-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 28
data_type: int16
- name: "Vorlauftemperatur Kessel 3 (Kaskade)_Kessel (OT/LAN)-SystaComfort2"
unique_id: Vorlauftemperatur Kessel 3 (Kaskade)_Kessel (OT/LAN)-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 29
data_type: int16
- name: "Vorlauftemperatur Kessel 4 (Kaskade)_Kessel (OT/LAN)-SystaComfort2"
unique_id: Vorlauftemperatur Kessel 4 (Kaskade)_Kessel (OT/LAN)-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 30
data_type: int16
- name: "Solare Eintrittstemperatur_SystaSolar Aqua II-SystaComfort2"
unique_id: Solare Eintrittstemperatur_SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 31
data_type: int16
- name: "Temperatur Speicher oben_SystaSolar Aqua II-SystaComfort2"
unique_id: Temperatur Speicher oben_SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 32
data_type: int16
- name: "Temperatur Solarverlauf_SystaSolar Aqua II-SystaComfort2"
unique_id: Temperatur Solarverlauf_SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 33
data_type: int16
- name: "Temperatur Speicher 2 oben_SystaSolar Aqua II-SystaComfort2"
unique_id: Temperatur Speicher 2 oben_SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 34
data_type: int16
- name: "Volumenstrom Solar_SystaSolar Aqua II-SystaComfort2"
unique_id: Volumenstrom Solar_SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: l/min
address: 35
data_type: int16
- name: "Außentemperatur am Kollektor 1_SystaSolar Aqua II-SystaComfort2"
unique_id: Außentemperatur am Kollektor 1_SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 36
data_type: int16
- name: "Außentemperatur am Kollektor 2_SystaSolar Aqua II-SystaComfort2"
unique_id: Außentemperatur am Kollektor 2_SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 37
data_type: int16
- name: "Kollektortemperatur 1_SystaSolar Aqua II-SystaComfort2"
unique_id: Kollektortemperatur 1_SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 38
data_type: int16
- name: "Kollektortemperatur 2_SystaSolar Aqua II-SystaComfort2"
unique_id: Kollektortemperatur 2_SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 39
data_type: int16
- name: "Eintrittstemperatur Speicher in die Frischwasserstation_SystaExpresso II-SystaComfort2"
unique_id: Eintrittstemperatur Speicher in die Frischwasserstation_SystaExpresso II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 40
data_type: int16
- name: "Austrittstemperatur Warmwasser Frischwasserstation_SystaExpresso II-SystaComfort2"
unique_id: Austrittstemperatur Warmwasser Frischwasserstation_SystaExpresso II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 41
data_type: int16
- name: "Eintrittstemperatur Kaltwasser Frischwasserstation_SystaExpresso II-SystaComfort2"
unique_id: Eintrittstemperatur Kaltwasser Frischwasserstation_SystaExpresso II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 42
data_type: int16
- name: "Volumenstrom Kaltwasser_SystaExpresso II-SystaComfort2"
unique_id: Volumenstrom Kaltwasser_SystaExpresso II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: l/min
address: 43
data_type: int16
- name: "Volumenstrom Speicherseite_SystaExpresso II-SystaComfort2"
unique_id: Volumenstrom Speicherseite_SystaExpresso II-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: l/min
address: 44
data_type: int16
- name: "Test-Register,_ -SystaComfort2"
unique_id: Test-Register,_ -SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 1
precision: 1
unit_of_measurement: 1
address: 9995
data_type: int16
- name: "Test-Register,_ -SystaComfort2"
unique_id: Test-Register,_ -SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 1
precision: 1
unit_of_measurement: 1
address: 9996
data_type: int16
- name: "Test-Register, Wert -7,2°C_ -SystaComfort2"
unique_id: Test-Register, Wert -7,2°C_ -SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 9997
data_type: int16
- name: "Test-Register, Wert +54,3°C_-SystaComfort2"
unique_id: Test-Register, Wert +54,3°C_-SystaComfort2
scan_interval: 100
slave: 1
input_type: input
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 9998
data_type: int16
- name: "Störcode des Leitsystems_Leitsystem-SystaComfort2"
unique_id: Störcode des Leitsystems_Leitsystem-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
precision: 1
unit_of_measurement: " "
address: 1
data_type: uint16
- name: "Sollwert Vorlauftemperatur Heizkreis 1_SystaComfort II-SystaComfort2"
unique_id: Sollwert Vorlauftemperatur Heizkreis 1_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 2
data_type: int16
- name: "Sollwert Vorlauftemperatur Heizkreis 2_SystaComfort II-SystaComfort2"
unique_id: Sollwert Vorlauftemperatur Heizkreis 2_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 3
data_type: int16
- name: "Sollwert Vorlauftemperatur Heizkreis 3_SystaComfort II-SystaComfort2"
unique_id: Sollwert Vorlauftemperatur Heizkreis 3_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 4
data_type: int16
- name: "Sollwert Leistung Heizkreis 1_SystaComfort II-SystaComfort2"
unique_id: Sollwert Leistung Heizkreis 1_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
precision: 1
unit_of_measurement: "%"
address: 5
data_type: uint16
- name: "Sollwert Leistung Heizkreis 2_SystaComfort II-SystaComfort2"
unique_id: Sollwert Leistung Heizkreis 2_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
precision: 1
unit_of_measurement: "%"
address: 6
data_type: uint16
- name: "Sollwert Leistung Heizkreis 3_SystaComfort Heat-SystaComfort2"
unique_id: Sollwert Leistung Heizkreis 3_SystaComfort Heat-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
precision: 1
unit_of_measurement: "%"
address: 7
data_type: uint16
- name: "Trinkwassertemperatur_SystaComfort II / SystaExpresso II-SystaComfort2"
unique_id: Trinkwassertemperatur_SystaComfort II / SystaExpresso II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 8
data_type: int16
- name: "maximale Vorlauftemperatur Heizkreis 1_SystaComfort II-SystaComfort2"
unique_id: maximale Vorlauftemperatur Heizkreis 1_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 9
data_type: int16
- name: "maximale Vorlauftemperatur Heizkreis 2_SystaComfort II-SystaComfort2"
unique_id: maximale Vorlauftemperatur Heizkreis 2_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 10
data_type: int16
- name: "maximale Vorlauftemperatur Heizkreis 3_SystaComfort Heat-SystaComfort2"
unique_id: maximale Vorlauftemperatur Heizkreis 3_SystaComfort Heat-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 11
data_type: int16
- name: "Störcode Heizungsregler 0 = keine Störung_SystaComfort II-SystaComfort2"
unique_id: Störcode Heizungsregler 0 = keine Störung_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 12
data_type: uint16
- name: "Störcode Solarregler 0 = keine Störung_SystaSolar Aqua II-SystaComfort2"
unique_id: Störcode Solarregler 0 = keine Störung_SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 13
data_type: uint16
- name: "Störung Wärmeerzeuger 1 _Kessel (OT/LAN)-SystaComfort2"
unique_id: Störung Wärmeerzeuger 1 _Kessel (OT/LAN)-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 14
data_type: uint16
- name: "Störung Wärmeerzeuger 1 _Kessel (OT/LAN)-SystaComfort2"
unique_id: Störung Wärmeerzeuger 1 _Kessel (OT/LAN)-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 15
data_type: uint16
- name: "Status Heizkreis 1_SystaComfort II-SystaComfort2"
unique_id: Status Heizkreis 1_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 36
data_type: uint16
- name: "Status Heizkreis 2_SystaComfort II-SystaComfort2"
unique_id: Status Heizkreis 2_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 37
data_type: uint16
- name: "Status Heizkreis 3_SystaComfort Heat-SystaComfort2"
unique_id: Status Heizkreis 3_SystaComfort Heat-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 38
data_type: uint16
- name: "Status Solar_SystaSolar Aqua II-SystaComfort2"
unique_id: Status Solar_SystaSolar Aqua II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 39
data_type: uint16
- name: "Status Schwimmbad_SystaComfort Pool-SystaComfort2"
unique_id: Status Schwimmbad_SystaComfort Pool-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 40
data_type: uint16
- name: "Status Heizkessel_SystaComfort II-SystaComfort2"
unique_id: Status Heizkessel_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 41
data_type: uint16
- name: "Status Wodtke Pelletsofen_SystaComfort Stove-SystaComfort2"
unique_id: Status Wodtke Pelletsofen_SystaComfort Stove-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 42
data_type: uint16
- name: "Status Holzkessel_SystaComfort Stove-SystaComfort2"
unique_id: Status Holzkessel_SystaComfort Stove-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 43
data_type: uint16
- name: "Solltemperatur Puffer oben _SystaComfort II-SystaComfort2"
unique_id: Solltemperatur Puffer oben _SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 44
data_type: int16
- name: "Kesselsolltemperatur _SystaComfort II-SystaComfort2"
unique_id: Kesselsolltemperatur _SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 45
data_type: int16
- name: "Solltemperatur Schwimmbad bei Erwärmung durch Heizkessel_SystaComfort Pool-SystaComfort2"
unique_id: Solltemperatur Schwimmbad bei Erwärmung durch Heizkessel_SystaComfort Pool-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 46
data_type: int16
- name: "Solltemperatur Schwimmbad beim Heizen mit solarer Überschusswärme_SystaComfort Pool-SystaComfort2"
unique_id: Solltemperatur Schwimmbad beim Heizen mit solarer Überschusswärme_SystaComfort Pool-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 47
data_type: int16
- name: "Betriebsart Heizkreis 1_SystaComfort II-SystaComfort2"
unique_id: Betriebsart Heizkreis 1_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 48
data_type: uint16
- name: "Betriebsart Heizkreis 2_SystaComfort II-SystaComfort2"
unique_id: Betriebsart Heizkreis 2_SystaComfort II-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 49
data_type: uint16
- name: "Betriebsart Heizkreis 3_SystaComfort Heat-SystaComfort2"
unique_id: Betriebsart Heizkreis 3_SystaComfort Heat-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
unit_of_measurement: 1
address: 50
data_type: uint16
- name: "Test-Register +47,2@C_ -SystaComfort2"
unique_id: Test-Register +47,2@C_ -SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 9992
data_type: int16
- name: "Test-Register, Wert 81327,5 kWh_ -SystaComfort2"
unique_id: Test-Register, Wert 81327,5 kWh_ -SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: kWh
address: 9993
data_type: uint32
- name: "Test-Register, Wert 0x7FFF = +32767_ -SystaComfort2"
unique_id: Test-Register, Wert 0x7FFF = +32767_ -SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
precision: 1
unit_of_measurement: 1
address: 9995
data_type: int16
- name: "Test-Register, Wert 0x8000 = -32768_ -SystaComfort2"
unique_id: Test-Register, Wert 0x8000 = -32768_ -SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 1
precision: 1
unit_of_measurement: 1
address: 9996
data_type: int16
- name: "Test-Register, Wert -7,2°C_ -SystaComfort2"
unique_id: Test-Register, Wert -7,2°C_ -SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 9997
data_type: int16
- name: "Test-Register, Wert +54,3°C_-SystaComfort2"
unique_id: Test-Register, Wert +54,3°C_-SystaComfort2
scan_interval: 100
slave: 1
input_type: holding
scale: 0.1
precision: 1
unit_of_measurement: °C
address: 9998
data_type: int16
binary_sensors:
- name: Leitsystem aktiv_systacomfort2
address: 0
input_type: coil
scan_interval: 60
slave: 1
unique_id: Leitsystem aktiv_systacomfort2
- name: Heizkreis 1 vorhanden_systacomfort2
unique_id: Heizkreis 1 vorhanden_systacomfort2
slave: 1
address: 1
scan_interval: 60
input_type: coil
- name: Heizkreis 2 vorhanden_systacomfort2
unique_id: Heizkreis 2 vorhanden_systacomfort2
slave: 1
address: 2
scan_interval: 60
input_type: coil
- name: Heizkreis 3 vorhanden_systacomfort2
unique_id: Heizkreis 3 vorhanden_systacomfort2
slave: 1
address: 3
scan_interval: 60
input_type: coil
- name: Schwimmbadheizkreis_vorhanden_systacomfort2
unique_id: Heizkreis 3 vorhanden_systacomfort2
slave: 1
address: 8
input_type: coil
- name: Testbit_nicht_schreibbar_Wert_0_systacomfort2
unique_id: Testbit_nicht_schreibbar_Wert_0_systacomfort2
slave: 1
address: 9995
input_type: coil
- name: Testbit_nicht_schreibbar_Wert_1_systacomfort2
unique_id: Testbit_nicht_schreibbar_Wert_1_systacomfort2
slave: 1
address: 9996
input_type: coil
switches:
- name: Trinkwassererwaermung_freigeben_systacomfort2
unique_id: Trinkwassererwaermung_freigeben_systacomfort2
slave: 1
address: 4
write_type: coil
command_on: 1
command_off: 0
scan_interval: 60
- name: Trinkwassererwaermung_sperren_systacomfort2
unique_id: Trinkwassererwaermung_sperren_systacomfort2
slave: 1
address: 5
write_type: coil
command_on: 1
command_off: 0
scan_interval: 60
- name: Trinkwasserzirkulation_freigeben_systacomfort2
unique_id: Trinkwasserzirkulation_freigeben_systacomfort2
slave: 1
address: 6
write_type: coil
command_on: 1
command_off: 0
scan_interval: 60
- name: Trinkwasserzirkulation_sperren_systacomfort2
unique_id: Trinkwasserzirkulation_sperren_systacomfort2
slave: 1
address: 7
write_type: coil
command_on: 1
command_off: 0
scan_interval: 60
- name: Testbit_schreibbar_Wert_0_systacomfort2
unique_id: Testbit_schreibbar_Wert_0_systacomfort2
slave: 1
address: 9997
write_type: coil
command_on: 1
command_off: 0
scan_interval: 60
- name: Testbit_schreibbar_Wert_1_systacomfort2
unique_id: Testbit_schreibbar_Wert_1_systacomfort2
slave: 1
address: 9998
write_type: coil
command_on: 1
command_off: 0
scan_interval: 60
It is done for alle values. I think the most users will not need all values.
https://forum.iobroker.net/assets/uploads/files/1674034323539-th-3000_v1.1_0321_systacomfort_ii_compactc_modbus_informationen_b_fhw.pdf
For SystaComfort2 I have done it the last days. It will work but it take some time tp programm.
Next I have to do the automation, so that I can put in values the into holdings. The switches are working. I can put my files into the post if someone is interessted in.
I think it could be very helpfull when you can put in the settings to ModbusWizard. It take a lot of time to do it from scratch. Thats why I asked in the chat for help, I am sure a lot of people are using Paradigma.
Now I will do the next files for SystaSmartC.
Best regards
Tim
Hey make sure to take a look at my new Integration, it may help you. I’m also in contat with the engineers from Ritter to make an update as soon as the new Modbus Update ist published.
nice work, @nussfuellung !
are you aware of this modbus documentation from paradigma?
It’s from 2023 but from what i’ve tried in regards of my marin-series heatpump it seems to be accurate.
https://dam.ritter-energie.de/pinaccess/pinaccess.do?pinCode=KJx68pzqFP39
if you need someone to test the heat pump integration, just let me know
Got it installed but still cannot connect to unit. I think its related to my systacomfort beeing hardware version 1. Software 1.34 (latest) with the old 2 row LCD.
just noticed, that you have already implemeted everything that is being shared via modbus in their v1.1 doc and you are just waiting for the update on their modbus implementation.
Any ideas, by when the will publish the update?
Q2 - 2026 thats the information i got from ritter