Connect 10 pool controller - fully local control
Hello - I’ve recently been diving into HomeAssistant and hooked up the Connect 10 Internet Gateway on the back of the instructions here via connectmypool. However, as noted it’s painfully slow - I press the button and 5-15 seconds later the action will actually happen.
As a learning project (dusting off my old electrical skills) I’ve been working on an ESP32 project that can read the wire protocol for the Connect 10. It can currently read all the key properties such as temperature, channel state and publishes it to MQTT for smoother integration with Home assistant. It updates the states almost instantly which is nice. I’ve also recently got it working with writing so it can now turn on and off pool lights etc.
Sharing the progress on the protocol here for interest, and collaboration if people are interested. :point_down::point_down::point_down::point_down::point_down::point_down:
Connect 10 Pool Controller Protocol Documentation
This document describes the proprietary serial protocol used by the Astral Connect 10 pool controller and has been clean-room developed by sniffing the messages on the RS-232 like bus that is used for communications.
Message Structure
All messages follow this basic structure:
[START] [SRC_HI] [SRC_LO] [DST_HI] [DST_LO] [CTRL_HI] [CTRL_LO] [CMD] [SUBCMD] [DATA...] [CHECKSUM] [END]
Message Format
Offset Field Description
0 START Always 0x02
1-2 SOURCE Source device address (big endian)
3-4 DEST Destination device address (big endian)
5-6 CONTROL Control bytes (typically 0x80 0x00)
7+ COMMAND Command and subcommand bytes
10+ DATA Payload data (varies by message type)
N-2 CHECKSUM Sum of all data bytes (from index 10 to N-3) masked with 0xFF
N-1 END Always 0x03
Checksum Calculation
The checksum is calculated as the sum of all bytes from index 10 to (length - 3), masked to 8 bits:
uint32_t sum = 0;
for (int i = 10; i < len - 2; i++) {
    sum += data[i];
uint8_t checksum = sum & 0xFF;
Device Addresses
Address Device Description
0x0050 Touch Screen Touch screen interface.
0x0062 Temp Sensor Temperature sensor module
0x006F Controller Main pool controller (Connect 10)
0x0090 Chlorinator Chemistry/chlorinator module
0x00F0 Internet GW Internet gateway module
0xFFFF Broadcast Broadcast to all devices
Message Types
The messages that are fully decoded have a :white_check_mark: and the partially decoded ones have a :warning:
1. Mode Message (Spa/Pool) :white_check_mark:
Reports the current operating mode - pool or spa.
Pattern: 02 00 50 FF FF 80 00 14 0D F1
Example - Spa Mode:
02 00 50 FF FF 80 00 14 0D F1 00 00 03
                              Mode: 0x00 = Spa, 0x01 = Pool
Example - Pool Mode:
02 00 50 FF FF 80 00 14 0D F1 01 01 03
Data Fields:
  • Byte 10: Mode (0x00 = Spa, 0x01 = Pool)
2. Temperature Settings :white_check_mark:
Reports the temperature setpoints for both spa and pool.
Pattern: 02 00 50 FF FF 80 00 17 10 F7
Example:
02 00 50 FF FF 80 00 17 10 F7 25 1D 63 54 F9 03
                              ^^ Spa setpoint Celcius (37°C in this example)
                                 ^^ Pool setpoint Celcius (25°C in this example)
                                    ^^ Spa setpoint Fahrenheit (99°F in this example)
                                       ^^ Pool setpoint Fahrenheit (84°F in this example)
Data Fields:
  • Byte 10: Spa setpoint temperature Celcius
  • Byte 11: Pool setpoint temperature Celcius
  • Byte 12: Spa setpoint temperature Fahrenheit
  • Byte 13: Pool setpoint temperature Fahrenheit
Note: Temperature scale (Celsius/Fahrenheit) is set by configuration message.
3. Temperature Reading :warning:
Current water temperature from the sensor.
Pattern: 02 00 62 FF FF 80 00 16 0E 06
Example:
02 00 62 FF FF 80 00 16 0E 06 19 00 19 03
                              ^^ Current temperature (25°C)
                                 ^^ Unknown
Data Fields:
  • Byte 10: Current water temperature
  • Byte 11: Unknown - could be secondary temp sensor
4. Heater Status :warning:
Reports whether the heater is on or off.
Pattern: 02 00 62 FF FF 80 00 12 0F 03
Example - Heater On:
02 00 62 FF FF 80 00 12 0F 03 00 01 08 09 03
                                 ^^ 0x01 = On, 0x00 = Off
                                    ^^ Unknown
Example - Heater Off:
02 00 62 FF FF 80 00 12 0F 03 00 00 08 08 03
                                    ^^ Unknown
Data Fields:
  • Byte 10: Padding/unused
  • Byte 11: Heater state (0x00 = Off, 0x01 = On)
  • Byte 12: Unknown (maybe bitmask or interlock?)
5. Configuration :warning:
System configuration including temperature scale.
Pattern: 02 00 50 FF FF 80 00 26 0E 04
Example - Celsius:
02 00 50 FF FF 80 00 26 0E 04 01 06 07 03
                              ^^ 0x01 - Celcius
                                 ^^ Unknown
Example - Fahrenheit:
02 00 50 FF FF 80 00 26 0E 04 11 06 17 03
                              ^^ 0x11 - Fahrenheit
                                 ^^ Unknown
Data Fields:
  • Byte 10: Temperature configuration - 01 Celcius, 11, Fahrenheit - possible bitmask as defined below.
    • Bit 7:
    • Bit 6:
    • Bit 5:
    • Bit 4: 0: celsius, 1:fahrenheit
    • Bit 3:
    • Bit 2:
    • Bit 1:
    • Bit 0: 1:heat 0: cool
  • Byte 11: Unknown
6. Active Channels Bitmask
Reports which channels are currently active.
Pattern: 02 00 50 00 6F 80 00 0D 0D 5B
Example:
02 00 50 00 6F 80 00 0D 0D 5B 10 10 03
                              Bitmask: 0x10 = Channel 5 active
Data Fields:
  • Byte 10: Channel bitmask
    • Bit 7: Channel 8
    • Bit 6: Channel 7
    • Bit 5: Channel 6
    • Bit 4: Channel 5
    • Bit 3: Channel 4
    • Bit 2: Channel 3
    • Bit 1: Channel 2
    • Bit 0: Channel 1
7. Channel Status :white_check_mark::warning:
Detailed status for all configured channels.
Pattern: 02 00 50 FF FF 80 00 0B 25 00
Example:
02 00 50 FF FF 80 00 0B 25 00 08 01 00 00 02 00 00 FE 00 00 FE 00 00 0B 02 01 09 00 00 FD 00 00 00 00 00 1B 03
                              ^^ Number of channels
                                 ^^  Channel 1: Type=1 (Filter)
                                    ^^ Channel 1: State (00 off, 01, Auto, 02 One)
                                       ^^ Channel 1:  currently active (either on or auto timer)
                                         ^^ Channel 2: Type=2 (Cleaner)
                                            etc
Data Fields:
  • Byte 10: Number of channels
  • Bytes 11+: For each channel (3 bytes):
    • Byte 0: Channel type
    • Byte 1: Channel state
    • Byte 2: Additional data
Channel Types:
  • 0x00: Unused
  • 0x01: Filter
  • 0x02: Cleaning
  • 0x03: Heater Pump
  • 0x04: Booster
  • 0x05: Waterfall
  • 0x06: Fountain
  • 0x07: Spa Pump
  • 0x08: Solar
  • 0x09: Blower
  • 0x0A: Swimjet
  • 0x0B: Jets
  • 0x0C: Spa Jets
  • 0x0D: Overflow
  • 0x0E: Spillway
  • 0x0F: Audio
  • 0x11: Hot Seat
  • 0x12: Heater Power
  • 0x13: Custom Name
  • 0xFE: Unused channel (disabled) (Light channel)
  • 0xFD: End marker (no more channels beyond this) (Controlled heater power)
Channel States:
  • 0x00: Off
  • 0x01: Auto
  • 0x02: On
8. Register Messages (Universal Register System) :warning:
The controller uses a unified register-based system for configuration and state. All register messages follow the same pattern with a register ID and slot (data type) to distinguish different aspects of the same register.
Message Structure
Base Pattern: 02 00 50 FF FF 80 00 38
Complete Structure:
02 00 50 FF FF 80 00 38 [CMD] [SUB] [REG_ID] [SLOT] [DATA...] [CHECKSUM] 03
                        CMD/SUB have a checksum relationship:
                        SUB = CMD + 8
Example:
02 00 50 FF FF 80 00 38 0F 17 C0 01 00 C1 03
                        ^^ CMD (0x0F)
                           ^^ SUB (0x17 = 0x0F + 8) ✓
                              ^^ Register ID (0xC0)
                                 ^^ Slot/Data Type (0x01)
                                    ^^ Data (Light state: 0=Off)
Key Fields:
  • Byte 8 (CMD): Command byte
  • Byte 9 (SUB): Subcommand byte - always equals CMD + 8
  • Byte 10 (REG_ID): Register identifier (which setting/channel/zone)
  • Byte 11 (SLOT): Data slot - defines data type and format
  • Byte 12+: Data payload (varies by register and slot)
Important: The CMD/SUB checksum relationship (SUB = CMD + 8) is a validation mechanism. Messages violating this are rejected.
Register Dispatch Table
The register ID and slot together determine the message meaning. The slot distinguishes different data aspects of the same register:
Register Range Slot Purpose Data Format
0x31-0x38 0x03 Favourite Labels Null-terminated ASCII string
0x6C-0x73 0x02 Channel Types 1-byte type code (see channel types)
0x7C-0x83 0x02 Channel Names Null-terminated ASCII string
0xC0-0xC7 0x01 Light Zone State 1-byte value (0=Off, 1=Auto, 2=On)
0xD0-0xD1 0x03 Valve Labels Null-terminated ASCII string
0xD0-0xD7 0x01 Light Zone Color 1-byte color code
0xE0-0xE7 0x01 Light Zone Active 1-byte binary (0x00=Inactive, 0x01=Active)
Note:
  • Register ranges can overlap (e.g., 0xD0-0xD7) but are distinguished by the slot value
  • The same slot value (e.g., 0x02) can represent different data formats depending on the register
  • Slot values appear to be context-dependent rather than globally defining a data type
Examples by Register Type
Channel Type Configuration (0x6C-0x73, Slot 0x02):
02 00 50 FF FF 80 00 38 0F 17 6C 02 01 6F 03
                              ^^ Channel 1 (0x6C)
                                 ^^ Slot 0x02 (Type)
                                    ^^ Type code: 0x01 = Filter
Channel Name (0x7C-0x83, Slot 0x02):
02 00 50 FF FF 80 00 38 17 1F 7C 02 46 69 6C 74 65 72 00 A6 03
                              ^^ Channel 1 (0x7C)
                                 ^^ Slot 0x02 (Name)
                                    F  i  l  t  e  r  \0
Light Zone State (0xC0-0xC7, Slot 0x01):
02 00 50 FF FF 80 00 38 0F 17 C0 01 02 C3 03
                              ^^ Light Zone 1 (0xC0)
                                 ^^ Slot 0x01 (State)
                                    ^^ Value: 0x02 = On
Light Zone Color (0xD0-0xD7, Slot 0x01):
02 00 50 FF FF 80 00 38 0F 17 D0 01 05 D6 03
                              ^^ Light Zone 1 (0xD0)
                                 ^^ Slot 0x01 (Color)
                                    ^^ Color code: 0x05 = Blue
Valve Label (0xD0-0xD1, Slot 0x03):
02 00 50 FF FF 80 00 38 16 1E D0 03 56 61 6C 76 65 20 31 00 21 03
                              ^^ Valve 1 (0xD0) - same register as Light Zone 1!
                                 ^^ Slot 0x03 (Label) - different slot
                                    V  a  l  v  e     1  \0
Note: Register 0xD0 serves dual purpose:
  • With slot 0x01: Light zone 1 color (numeric)
  • With slot 0x03: Valve 1 label (text)
Light Zone Active (0xE0-0xE7, Slot 0x01):
02 00 50 FF FF 80 00 38 0F 17 E0 01 01 E2 03
                              ^^ Light Zone 1 (0xE0)
                                 ^^ Slot 0x01 (Active flag)
                                    ^^ Value: 0x01 = Active
Register ID Mappings
Channels (0x6C-0x73):
  • 0x6C: Channel 1
  • 0x6D: Channel 2
  • 0x6E: Channel 3
  • 0x6F: Channel 4
  • 0x70: Channel 5
  • 0x71: Channel 6
  • 0x72: Channel 7
  • 0x73: Channel 8
Lighting Zones:
  • State (0xC0-0xC7): 0xC0 = Zone 1, 0xC1 = Zone 2, etc.
  • Color (0xD0-0xD7): 0xD0 = Zone 1, 0xD1 = Zone 2, etc.
  • Active (0xE0-0xE7): 0xE0 = Zone 1, 0xE1 = Zone 2, etc.
Implementation
The firmware uses a dispatch table to route register messages to appropriate handlers. See message_decoder.c for the complete implementation:
static const register_handler_t REGISTER_HANDLERS[] = {
    {0x6C, 0x73, 0x02, handle_channel_type,       "Channel Type"},
    {0x7C, 0x83, 0x02, handle_channel_name,       "Channel Name"},
    {0xC0, 0xC7, 0x01, handle_light_zone_state,   "Light Zone State"},
    {0xD0, 0xD7, 0x01, handle_light_zone_color,   "Light Zone Color"},
    {0xE0, 0xE7, 0x01, handle_light_zone_active,  "Light Zone Active"},
    {0xD0, 0xD1, 0x03, handle_valve_label,        "Valve Label"},
    {0x00, 0xFF, 0x03, handle_register_label_generic, "Register Label"},
The dispatcher:
  1. Validates CMD/SUB relationship (SUB = CMD + 8)
  2. Extracts register ID and slot
  3. Looks up matching handler in table
  4. Routes to appropriate handler function
9. Register Labels :white_check_mark:
Generic register label assignments.
Pattern: Channels? 02 00 50 FF FF 80 00 38 1A 22
Example:
02 00 50 FF FF 80 00 38 1A 22 7C 02 46 69 6C 74 65 72 20 50 75 6D 70 00 A6 03
                              ^^ Register ID (0x7C)
                                 ^^  Slot ID
                                    F  i  l  t  e  r     P  u  m  p  (null terminated)
Data Fields:
  • Byte 10: Register ID
  • Byte 11: Slot ID
  • Byte 12+: ASCII label string (null terminated)
Pattern Variant: Lighting/Valve Labels 02 00 50 FF FF 80 00 38 16 1E
Assigns custom names to lighting zones or valve registers (0xD0-0xD3 range).
Example - Valve 1:
02 00 50 FF FF 80 00 38 16 1E D0 02 56 61 6C 76 65 20 31 00 21 03
                              ^^ Register ID (0xD0 = Light Zone 1 Color/Valve 1)
                                 ^^ Slot ID
                                    V  a  l  v  e     1  \0  (null-terminated ASCII string)
Example - Valve 2:
02 00 50 FF FF 80 00 38 16 1E D1 02 56 61 6C 76 65 20 32 00 23 03
                              ^^ Register ID (0xD1 = Light Zone 2 Color/Valve 2)
                                 ^^ Slot ID
                                    V  a  l  v  e     2  \0  (null-terminated ASCII string)
Data Fields:
  • Byte 10: Register ID (0xD0-0xD3 for zones/valves 1-4)
  • Byte 11: Slot ID
  • Bytes 12+: Null-terminated ASCII string (custom label/name)
Notes:
  • These registers (0xD0-0xD3) appear to be multipurpose
  • Can represent either lighting zone colors or valve names depending on system configuration
  • The null-terminated string format allows for variable-length names
  • Maximum string length appears to be limited by message size constraints
10. Lighting Zone Configuration :warning:
Indicates which lighting zones are installed.
Pattern: 02 00 50 FF FF 80 00 06 0E E4
Example:
02 00 50 FF FF 80 00 06 0E E4 00 00 00 03
                              ^^ Zone index (0-3 for zones 1-4)
                                 ^^ Unknown
Data Fields:
  • Byte 10: Zone index (0x00 to 0x03 for zones 1-4)
  • Byte 11: Unknown
11. Chlorinator pH Setpoint :white_check_mark:
Target pH level for the chlorinator.
Pattern: 02 00 90 FF FF 80 00 1D 0F 3C (followed by register)
Example:
02 00 90 FF FF 80 00 1D 0F 3C 01 4E 00 4F 03
                              ^^ PH Setpoint
                                 ^^ ^^ pH value (little endian)
                                          78 = 7.8 pH (value / 10)
Data Fields:
  • Byte 10: pH setpoint register (0x01)
  • Bytes 11-12: pH value in tenths (little endian, divide by 10 for actual pH)
12. Chlorinator pH Reading :white_check_mark:
Current pH reading from the sensor.
Pattern: 02 00 90 FF FF 80 00 1F 0F 3E (followed by register)
Example:
02 00 90 FF FF 80 00 1F 0F 3E 01 55 00 56 03
                              ^^ pH reading
                                          85 = 8.5 pH
Data Fields:
13. Chlorinator ORP Setpoint :white_check_mark:
Target ORP (oxidation-reduction potential) level.
Example:
02 00 90 FF FF 80 00 1D 0F 3C 02 8A 02 8E 03
                              ^^ ORP setpoint register
                                 ^^ ^^ ORP value in mV (little endian)
                                       650 mV (0x028A)
Data Fields:
  • Byte 10: ORP setpoint register (0x02)
  • Bytes 11-12: ORP value in millivolts (little endian)
14. Chlorinator ORP Reading :white_check_mark:
Current ORP reading from the sensor.
Pattern: 02 00 90 FF FF 80 00 (followed by subcommand)
Example:
02 00 90 FF FF 80 00 1F 0F 3E 02 0A 02 0E 03
                              ^^ ORP reading register
                                          522 mV (0x020A)
Data Fields:
  • Byte 10: ORP reading register
15. Internet Gateway Serial Number :warning:
Serial number of the internet gateway module.
Pattern: 02 00 F0 FF FF 80 00 37 11
Example:
02 00 F0 FF FF 80 00 37 11 B8 04 A3 15 21 00 DD 03
                              ^^ Unknown
                                 ^^ ^^ ^^ ^^ Serial number (little endian)
                                               0x002115A3 = 2168227
Data Fields:
  • Byte 10 (Maybe a type 04)
  • Bytes 11-14: Serial number (32-bit little endian)
16. Internet Gateway Network Config :warning:
IP address and signal strength of the gateway.
Pattern: 02 00 F0 FF FF 80 00 37 15 BC
Example:
On Startup (no connection)
02 00 F0 FF FF 80 00 37 15 BC 01 01 01 03 00 00 00 00 00 06 03
With IP address (wifi connected)
02 00 F0 FF FF 80 00 37 15 BC 01 01 01 07 C0 A8 00 17 2B B4 03
                              ^^ Unknown
                                 ^^ Unknown
                                    ^^ Unknown
                                       ^^ Unknown
                                          ^^ ^^ ^^ ^^ IP address (192.168.1.23)
                                                      ^^ Signal level (43)
Data Fields:
  • Byte 10: Unknown
  • Byte 11: Unknown
  • Byte 12: Unknown
  • Byte 13: Unknown
  • Bytes 14-17: IP address (4 bytes, standard order)
  • Byte 18: WiFi signal level (0-100)
17. Internet Gateway Communications Status :warning:
Status of the gateway’s internet connection.
Pattern: 02 00 F0 FF FF 80 00 37 0F B6
Example - Communicating with server:
02 00 F0 FF FF 80 00 37 0F B6 02 01 80 83 03
                              ^^ Unknown
                                 ^^ ^^ Status code (little endian)
                                          0x8001 = 32769: Communicating with server
Data Fields:
  • Byte 10: Unknown (observed as always 0x02)
  • Bytes 11-12: Communications status code (little endian)
Status Codes:
  • 0x0000:0 Idle
  • 0x0100:256 No suitable interfaces ready
  • 0x0201:513 DNS resolve error
  • 0x0301:769 Internal error creating local socket
  • 0x0400:1024 Connecting to server
  • 0x0401:1025 Failed to connect
  • 0x8000:32768 Connection open
  • 0x8001:32769 Communicating with server
  • 0xF000:61440 Connection closed
  • 0xF001:61441 Communication error with server
  • 0xF002:61442 Communication error with server
  • 0xF003:61443 Communication error with server
  • 0xF004:61444 Communication error with server
18. Register Read Request/Response
The Internet Gateway periodically polls controller registers to sync state with the cloud service. This uses a request-response pattern.
Request Pattern: 02 00 F0 FF FF 80 00 39 0E B7
Response Pattern: 02 00 50 FF FF 80 00 38 0F 17
Example - Request for register 0x88:
02 00 F0 FF FF 80 00 39 0E B7 88 02 8A 03
                              ^^ Register ID (0x88)
                                 ^^ Slot ID
Example - Response with register 0x88 value:
02 00 50 FF FF 80 00 38 0F 17 88 02 00 8A 03
                                 ^^ Slot ID
                                    ^^ Register value (0x00)
Request Data Fields (from Gateway):
  • Byte 10: Register ID to read
  • Byte 11: Slot ID
Response Data Fields (from Controller):
  • Byte 10: Register ID (echoed from request)
  • Byte 11: Slot ID
  • Byte 12: Register value
Observed Behavior:
  • Gateway sends sequential requests (e.g., 0x88, 0x89, 0x8A, 0x8B)
  • Controller responds ~120ms after each request
  • Next request sent ~780ms after previous response
  • Used for periodic status polling and cloud synchronization
Notes:
  • The response command pattern 38 0F 17 is similar to MSG_TYPE_REGISTER_STATUS (38 0F 17)
  • Both request and response are broadcast (destination 0xFFFF)
  • The gateway appears to scan ranges of registers systematically
19. Controller Day/Time/Clock
Current time from the controller’s internal clock. Broadcast periodically for synchronization.
Pattern: 02 00 50 FF FF 80 00 FD 0F DC
Example:
02 00 50 FF FF 80 00 FD 0F DC 39 08 05 46 03
                              ^^ Minutes (57)
                                 ^^ Hours (8)
                                    ^^ Day of Week (5)
                                       → 08:57 on Saturday
Example - Minute rollover:
02 00 50 FF FF 80 00 FD 0F DC 3B 08 05 48 03  → 05:08:59
02 00 50 FF FF 80 00 FD 0F DC 00 09 05 0E 03  → 05:09:00
Data Fields:
  • Byte 10: Minutes (0-59)
  • Byte 11: Hours (0-23, 24-hour format)
  • Byte 12: Day of Week (0-6, 0: Monday → 6: Sunday)
Notes:
  • This message is broadcast by the controller for device time synchronization
  • Used by connected devices (touchscreen, internet gateway) to maintain consistent time
  • Appears to be sent every minute.
20. Touchscreen Firmware Version
Touchscreen firmware version announcement. Broadcast periodically by the controller.
Pattern: 02 00 50 FF FF 80 00 0A 0E E8
Example:
02 00 50 FF FF 80 00 0A 0E E8 02 08 0A 03
                              ^^ Major version (2)
                                 ^^ Minor version (8)
                                    → Version 2.8
Data Fields:
  • Byte 10: Major version number
  • Byte 11: Minor version number
Notes:
  • This message is broadcast by the controller as part of the regular system status sequence
  • Appears alongside other system announcements (firmware version, system status, time)
  • The version reflects the touchscreen/display interface firmware version
  • Value remains constant unless the touchscreen firmware is updated
21. Touchscreen Unknown 1 - 5 little pigs?
This is broadcast consistently after the version number message 0A 0E E8 and currently
appears to always have the data value 05 00
Pattern: 02 00 50 FF FF 80 00 12 0E F0 05 00 05 03
Example:
                              ^^ Unknown (always 0x05)
                                 ^^ Unknown (always 0x00)
Data Fields:
  • Byte 10: Unknown
  • Byte 11: Unknown
Notes:
22. Touchscreen Unknown 2 - ??
This is broadcast consistently after the version number message 27 0D 04 and currently
appears to always have the data value 00 00
Pattern: 02 00 50 FF FF 80 00 27 0D 04 00 00 03
Example:
Data Fields:
  • Byte 10: Unknown
  • Byte 11: Unknown
Notes:
Control Commands (Gateway to Controller)
The following commands can be sent from the Internet Gateway (or emulated gateway) to control pool equipment.
23. Light Zone Control Command :white_check_mark:
Command to set light zone state (On/Off/Auto).
Pattern: 02 00 F0 FF FF 80 00 3A 0F B9
Example - Turn ON spa light (Zone 2):
02 00 F0 FF FF 80 00 3A 0F B9 C1 01 02 C4 03
                              ^^ Register ID (0xC1 = Zone 2)
                                 ^^ Slot ID (0x01 = State)
                                    ^^ State value (0x02 = On)
                                       ^^ Checksum (0xC1 + 0x01 + 0x02 = 0xC4)
Example - Turn OFF spa light (Zone 2):
02 00 F0 FF FF 80 00 3A 0F B9 C1 01 00 C2 03
                                    ^^ State value (0x00 = Off)
                                       ^^ Checksum (0xC1 + 0x01 + 0x00 = 0xC2)
Message Structure:
  • Bytes 0-1: 02 00 - Start
  • Bytes 2: 00 F0 - Source (Internet Gateway = 0x00F0)
  • Bytes 3-4: FF FF - Destination (Broadcast)
  • Bytes 5-6: 80 00 - Control bytes
  • Bytes 7-9: 3A 0F B9 - Command pattern for register control
  • Byte 10: Register ID (0xC0-0xC7 for zones 1-8)
  • Byte 11: Slot ID (0x01 = State)
  • Byte 12: State value (0x00 = Off, 0x01 = Auto, 0x02 = On)
  • Byte 13: Checksum (sum of bytes 10-12)
  • Byte 14: 03 - End byte
Register IDs:
  • 0xC0: Light Zone 1
  • 0xC1: Light Zone 2 (Spa)
  • 0xC2: Light Zone 3
  • 0xC3: Light Zone 4
  • 0xC4: Light Zone 5
  • 0xC5: Light Zone 6
  • 0xC6: Light Zone 7
  • 0xC7: Light Zone 8
State Values:
  • 0x00: Off
  • 0x01: Auto
  • 0x02: On
Notes:
  • This command requires the sender to impersonate the Internet Gateway (source address 0x00F0)
  • The controller will process the command and update the light zone state accordingly
  • The command pattern 3A 0F B9 distinguishes gateway control commands from status broadcasts (38 0F 17)
24. Mode Control Command (Pool/Spa) :white_check_mark:
Command to switch between Pool and Spa operating modes.
Pattern: 02 00 F0 00 50 80 00 2A 0D F9
Example - Switch to Spa mode:
02 00 F0 00 50 80 00 2A 0D F9 01 01 03
                              ^^ Mode value (0x01 = Switch to Spa)
                                 ^^ Checksum (0x01)
Example - Switch to Pool mode:
02 00 F0 00 50 80 00 2A 0D F9 00 00 03
                              ^^ Mode value (0x00 = Switch to Pool)
                                 ^^ Checksum (0x00)
Message Structure:
  • Bytes 0: 02 00 - Start
  • Bytes 1-2: 00 F0 - Source (Internet Gateway = 0x00F0)
  • Bytes 3-4: 00 50 - Destination (Touch Screen = 0x0050) - Not broadcast!
  • Bytes 7-9: 2A 0D F9 - Command pattern for mode control
  • Byte 10: Mode value (0x00 = Pool, 0x01 = Spa)
  • Byte 11: Checksum (byte 10)
  • Byte 12: 03 - End byte
Mode Values:
  • 0x00: Switch to Pool mode
  • 0x01: Switch to Spa mode
Important Notes:
  • Destination is Touch Screen (0x0050), not broadcast - Unlike light commands, this is addressed specifically to the touch screen controller
  • Command values are inverted from status values - In status messages (Message Type 1), Spa=0x00 and Pool=0x01, but in control commands, Spa=0x01 and Pool=0x00
  • The controller will switch modes and broadcast the new mode status to all devices
Implementation Notes
Message Validation
All messages should be validated before processing:
  1. Start byte: Must be 0x02
  2. End byte: Must be 0x03
  3. Minimum length: At least 13 bytes for checksum verification
  4. Checksum: Calculate and compare with received checksum byte
Thread Safety
When implementing a decoder:
  • Protect shared state with mutexes/semaphores
  • Use snapshots for publishing to avoid holding locks during I/O
  • Validate all array indices before access
UART Configuration
The Astral bus uses:
  • Baud rate: 9600
  • Data bits: 8
  • Parity: None
  • Stop bits: 1
  • TX inversion: May be required depending on interface hardware
Example: Complete Message Decode
^^ Start byte
   ^^^^^  Source: 0x0050 (Controller)
         ^^^^^  Destination: 0xFFFF (Broadcast)
               ^^^^^  Control: 0x8000
                     ^^^^^^^^  Command: Mode message pattern
                              ^^ Data: 0x01 = Pool mode
                                 ^^ Checksum: 0x01 (sum of byte 10)
                                    ^^ End byte
Decoded: Controller broadcasts Pool mode to all devices.
I am in awe. I’ll have a better read of this on the weekend, but great work!
Hi @zagnuts - not sure it will be too interesting of a read :-). However, I’ve now got more of it decoded and can fully control my system with a small home made PCB and ESP32. See attached images for how it looks in Home Assistant - and it’s generally instant which makes me happy.
I’m interested to get some more info on other configurations people may have - to help with finishing decoding the unknown bits I have. If you are willing to share help I’ll send you on a spreadsheet link to capture config.
@timd.au @RebelMagpie - you may be interested in this too - and if keen to help would be interested.
@timd.au have you got your connect 10? Is it a new one? I’m curious if they are still selling them.
FWIW It looks like they do still sell them, but are generally pushing the new Halo Connect kit for new pools. As an aside, it seems that Astral might have got a few feral messages from some Home Assistant users that has soured the relationship and possible future native support, which is a shame.
That’s a shame that people ended up souring the relationship - the people I’ve spoken to at Astral/Fluidra have been very helpful and friendly.
Hi Would be keen to try, as of today the connectmypool cloud seems to be off line and over the delays. do you have any hardware and connection details you can provide
Hi @antiqueyak, yes send me the spreadsheet. Happy to provide what I can. Very keen to see what can be done.
Interesting … I’ve just had a connect 10 installed and using the cloud connection using smck83/ha-connectmypool with success (apart from when the domain went down). Interested to see hardware details and yaml as this evolves. Great work!
@timd.au @RebelMagpie @abtec I’ve just today received a few of the boards I had built - needs a test before I know it’s good, but will get that done next week :crossed_fingers:
The code is pretty solid now - and needs a bit more testing with various configs to flush out the last of the important settings. GitHub - marklynch/pool-controller-code: ESP32 Code for pool controller for Connect 10 · GitHub
If you can use provide info extracted via the API using this: https://connectmypool.com.au/downloads/APITester.zip
Remember to remove your key as per example here:
Have posted info into the sheet (as a new subsheet)
Cool, that looks similar to my system so I think everything should be supported.
System Confg added to tab
Nicely done @antiqueyak - I’ll put this in my list of projects. I’m using the cloud version for some years from @smck83, PS saw there is a new version with Claude’s help - will check it out. Thanks both!
Sorry for the late reply; I’ve been travelling. I have added a tab with the details of my pool setup too. I hope it’s useful
Finally got the boards back, and unfortunately found 2 issues, one resolvable and one is not. So need to get them redone :man_facepalming:
Software is in a solid place now, with a few gaps that need testing on other systems to fill these.
Fixed the issues now and back to waiting - but do have a nice case and lid built for it while I wait for the PCB’s to arrive.
This is amazing - fantastic work antiqueyak! I literally this morning ordered a logic analyser so I could try and reverse engineer this protocol - I should have searched harder! I would be super interested in building this device. I looked at your github but couldn’t find a circuit diagram or BOM. I’m more than happy to help test - with the caveat that my Connect 10 touchscreen is broken (just the screen, the timers etc are still functioning), hence my desire to build a controller. Maybe even one with a touchscreen!
Hi @mike.l the pcb repo is linked above, be also here for simplicity
Circuit and PCB
ESP32 code including PROTOCOL.md file
3d printer case for pcb.
I have some PCB’s on order already so happy to share when they arrive.
Appreciate any feedback or ideas, or PRs :+1:
Cheers