Control Acond Heat Pump over ModBus
Hello, I spent already more than a week to get this working, but I still can not achieve the result I want. I have heat pump from Acond which support communication over ModBus. The problem is that when I set it up it jups between the auto mode and the ModBus mode. In the documentation there is mentioned that it will switch to auto mode when in time = MaxCommDataRefresh there was no value written or read over ModBus. I suspect that this MaxCommDataRefresh is 1s or lower, but Home Assistant only allows me to read in 1s intervals. That is the first problem.
Second problem is that when I setup “climates” it can write only one register, but based on the documentation I need to write multiple registers because some needs to be set to some values. Is there some solution how to write multiple registers when the target temperature is set?
Here are my current settings:
modbus:
  - name: Acond
    type: tcp
    host: 192.168.1.219
    port: 502
    climates:
      - name: "Tepelné čerpadlo - vzduch"
        address: 1
        input_type: input
        max_temp: 35
        min_temp: 10
        scan_interval: 1
        offset: 0
        precision: 1
        scale: 0.1
        target_temp_register: 0
        temp_step: 0.5
        temperature_unit: °C
Hi Jakub! I also have an Acond heat pump and I am just getting my bearings around its Modbus interface. Can you tell me where you obtained the documentation you mentioned?
Also, did you make any headway with the issue you described here? I am currently looking to use the heat pump as a sensor source only, and I want to be able to track its reported outside and inside air temperature, and the heating and hot water temperature. In other words, I am currently only interested in the read registers. Since your question was about writes, I suppose you already succeeded at reads before those?
here is my configuration.yaml which I use and it works.
You have to change the IP address.
And technicians from Acond must allow Modbus communication on the unit.
With Best Regards Thomas
Loads default set of integrations. Do not remove.
default_config:
Text to speech
tts:
  • platform: google_translate
script: !include scripts.yaml
scene: !include scenes.yaml
modbus:
  • name: Acond
    type: tcp
    host: 192.168.1.21
    port: 502
    close_comm_on_error: false
    delay: 1
    timeout: 1
    retry_on_empty: false
    message_wait_milliseconds: 1
    retries: 1
    climates:
    • name: ACOND_T_set_indoor_0
      slave: 1
      input_type: input
      address: 1
      data_type: int16
      scan_interval: 60
      scale: 0.1
      precision: 1
      max_temp: 25
      min_temp: 11
      temp_step: 0.1
      unique_id: 30000
    • name: ACOND_T_set_water_back
      slave: 1
      input_type: input
      address: 8
      target_temp_register: 7
      data_type: int16
      scan_interval: 10
      scale: 0.1
      precision: 1
      max_temp: 55
      min_temp: 11
      temp_step: 0.1
      unique_id: 30008
    • name: ACOND_typ_StandardON
      slave: 1
      input_type: input
      address: 14
      target_temp_register: 6
      data_type: int16
      scan_interval: 10
      scale: 1
      precision: 1
      max_temp: 2
      min_temp: 0
      temp_step: 1
      unique_id: 30007
      sensors:
    • name: ACOND_T_act_indoor1
      slave: 1
      address: 1
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
      unit_of_measurement: “°C”
      device_class: temperature
      unique_id: 50001
    • name: ACOND_T_act_water_back
      slave: 1
      address: 8
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
      unique_id: 50009
    • name: ACOND_T_act_air
      slave: 1
      address: 9
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
      unique_id: 50010
    • name: ACOND_typ_reg_pan
      slave: 1
      address: 14
      data_type: int16
      input_type: input
      unique_id: 50015
    • name: ACOND_T_act_water_outlet
      slave: 1
      address: 17
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
      unique_id: 50018
    • name: ACOND_capacity_actual_W
      slave: 1
      address: 23
      data_type: int16
      scale: 1
      input_type: input
      unique_id: 50024
      #logger:
logs:
homeassistant.components.modbus: debug
pymodbus.client: debug
though I haven’t made much headway yet, I just wanted to say thanks for the pointers thus far. :slight_smile:
I have put in this request with the contractor that installed my heat pump, and am still waiting to hear back from them.
I have found this video though; it contains some information about Modbus from about the 14-minute mark:
Unfortunately I don’t speak Czech, and Youtube’s auto-caption/auto-translate feature doesn’t appear to work for this video. So I can’t make out a whole lot. One question that I do have is this, though: do the Modbus registers expose the system’s current power consumption? Is that the ACOND_capacity_actual_W sensor you define, @tnovicky?
Ahoj Jakube,
I see your modbus with ACOND is working. I have ACOND as well, I have paper protocol from ACOND, and I think I made it all exactly according this protocol, but answer is ILLEGAL DATA ADDRESS. Can you send me a couple of packets from communication recorded by wireshark or can you check where should be problem on my side please? I have info from ACOND that it should works, but not in my case. Thank you Vasek.
Continuing the discussion from Control Acond Heat Pump over ModBus:
below is my configuration.yaml. I think I copied it correctly from you, but I can’t get the correct result.
After restarting HA it gives me an error:
Logger: homeassistant.setup
Source: setup.py:190
First occurred: 11:41:39 (2 occurrences)
Last logged: 11:41:40
Setup failed for sensors: Integration not found.
Setup failed for climates: Integration not found.
Could you please help me with what I am doing wrong.
I’m sorry, but I’m a beginner with HA, so please be patient and forgiving.
thank you very much
default_config:
Load frontend themes from the themes folder
frontend:
themes: !include_dir_merge_named themes
Text to speech
tts:
http:
use_x_forwarded_for: true
trusted_proxies:
- 172.30.33.0/24
modbus:
  • name: Acond
    type: tcp
    host: 10.254.251.199
    port: 502
    delay: 1
    timeout: 1
    retries: 1
    climates:
    slave: 1
    input_type: input
    address: 1
    data_type: int16
    scan_interval: 60
    scale: 0.1
    precision: 1
    max_temp: 25
    min_temp: 11
    temp_step: 0.1
    unique_id: 30000
    slave: 1
    input_type: input
    address: 8
    data_type: int16
    scan_interval: 10
    scale: 0.1
    precision: 1
    max_temp: 55
    min_temp: 11
    temp_step: 0.1
    unique_id: 30008
    slave: 1
    input_type: input
    address: 14
    data_type: int16
    scan_interval: 10
    scale: 1
    precision: 1
    max_temp: 2
    min_temp: 0
    temp_step: 1
    unique_id: 30007
    sensors:
    slave: 1
    address: 1
    data_type: int16
    scale: 0.1
    precision: 1
    input_type: input
    unique_id: 50001
    slave: 1
    address: 8
    data_type: int16
    scale: 0.1
    precision: 1
    input_type: input
    unique_id: 50009
    slave: 1
    address: 9
    data_type: int16
    scale: 0.1
    precision: 1
    input_type: input
    unique_id: 50010
    slave: 1
    address: 14
    data_type: int16
    input_type: input
    unique_id: 50015
    slave: 1
    address: 17
    data_type: int16
    scale: 0.1
    precision: 1
    input_type: input
    unique_id: 50018
    slave: 1
    address: 23
    data_type: int16
    scale: 1
    input_type: input
    unique_id: 50024
Hello, did You solve the problem? If not I will try to help, but prefer email conversation. So send Your question to [email protected].
Returning to this thread with additional information, just in case someone finds it useful.
I’ve finally added my Acond PRO-R to my Home Assistant configuration via Modbus, using the documentation available from loxone-library as a reference (this appears to be a translation of https://acond.cz/wp-content/uploads/Acond_ModbusTCP-v2.34.pdf though the version IDs don’t match up, and also I’m not sure if the translation comes directly from Acond or from a third party).
Here’s what I’ve added to my modbus configuration thus far:
- name: Acond PRO-R
  type: tcp
  host: acond.lan  # This is a DNS entry in my local network; using an IP address is fine too
  port: 502
  delay: 1
  timeout: 1
  retries: 1
  climates:
    - name: ACOND_T_set_indoor1  # Indoor temperature, sensor #1 (I only have one at this time)
      slave: 1
      address: 1
      input_type: input
      data_type: int16
      scan_interval: 60
      scale: 0.1
      precision: 1
      max_temp: 28
      min_temp: 10
      temp_step: 0.1
    - name: ACOND_T_set_TUV  # Domestic hot water temperature
      slave: 1
      address: 5
      target_temp_register: 4
      input_type: input
      data_type: int16
      scan_interval: 60
      scale: 0.1
      precision: 1
      max_temp: 55
      min_temp: 10
      temp_step: 0.1
  sensors:
    - name: ACOND_T_act_indoor1  # Current indoor temperature at sensor #1
      slave: 1
      address: 1
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
      unit_of_measurement: "°C"
    - name: ACOND_T_act_TUV  # Current domestic hot water temperature
      slave: 1
      address: 5
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
    - name: ACOND_T_act_water_back  # Current return water temperature in heating circuit
      slave: 1
      address: 8
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
    - name: ACOND_T_act_air  # Current outside air temperature
      slave: 1
      address: 9
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
    - name: ACOND_err_number  # General error number, should always be 0 in normal operation
      slave: 1
      address: 20
      data_type: int16
      input_type: input
    - name: ACOND_err_number_SECMono  # SECMono error number, should always be 0 in normal operation
      slave: 1
      address: 21
      data_type: int16
      input_type: input
    - name: ACOND_err_number_driver  # Driver error number, should always be 0 in normal operation
      slave: 1
      address: 22
      data_type: int16
      input_type: input
    - name: ACOND_capacity_actual_W  # Current heat production
      slave: 1
      address: 23
      data_type: int16
      input_type: input
      device_class: power
      unit_of_measurement: "W"
If you’d like to be able to reconfigure these in the Home Assistant GUI, be sure to add unique_id variables to those entities.
Thanks for the update!
For the ACOND Grandis R/P the configuration is different.
For instance the power settings
I have made some automations to let the heat pump work with TADO.
The house I own is build in 1895. And has over 240 square meters flooring, of which most is ground level.
To make sure the rooms will get the correct temperature, I let TADO decide what the room temperature should be.
config.yaml
# Modbus configuration for Acond Grandis R
modbus: !include modbus.yaml
# Logger for modbud
logger: !include logger.yaml
# Template for the modbus implementation
template: !include template.yaml
# Include scripts configuration
scripts: !include scripts.yaml
# Include the automations
modbus.yaml
- name: acond_grandis_r
  type: tcp
  host: _host_ip_address_# Change to the IP address of the control unit
  port: 502
  delay: 1
  timeout: 1
  climates:
      slave: 1
      address: 0
      input_type: input
      data_type: int16
      scan_interval: 60
      scale: 0.1
      precision: 1
      max_temp: 28
      min_temp: 10
      temp_step: 0.1
      unique_id: acond_grandis_r_0001
      slave: 1
      address: 4
      input_type: input
      data_type: int16
      scan_interval: 60
      scale: 0.1
      precision: 1
      max_temp: 65
      min_temp: 10
      temp_step: 0.1
      unique_id: acond_grandis_r_0002
  sensors:
      slave: 1
      address: 1
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
      unit_of_measurement: 'ÂşC'
      unique_id: acond_grandis_r_0003
      slave: 1
      address: 5
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
      unique_id: acond_grandis_r_0004
      slave: 1
      address: 8
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
      unique_id: acond_grandis_r_0005
      slave: 1
      address: 9
      data_type: int16
      scale: 0.1
      precision: 1
      input_type: input
      unique_id: acond_grandis_r_0006
      slave: 1
      address: 20
      data_type: int16
      input_type: input
      unique_id: acond_grandis_r_0007
      slave: 1
      address: 21
      data_type: int16
      input_type: input
      unique_id: acond_grandis_r_0008
      slave: 1
      address: 22
      data_type: int16
      input_type: input
      unique_id: acond_grandis_r_0009
    - name: ACOND_comp_rpm_actual  # Current compressor speed
      slave: 1
      address: 23
      data_type: int16
      input_type: input
      unit_of_measurement: "rpm"
      unique_id: acond_grandis_r_0010
    - name: ACOND_comp_rpm_max  # Maximum compressor speed
      slave: 1
      address: 19
      data_type: int16
      input_type: input
      unique_id: acond_grandis_r_0011
    - name: ACOND_type_reg_pan  # Current type regulation
      slave: 1
      address: 14
      data_type: int16
      input_type: input
      scan_interval: 60
      unique_id: acond_grandis_r_0012
    - name: ACOND_type_rezim_pan  # Heatpump mode
      slave: 1
      address: 13
      data_type: int16
      input_type: input
      scan_interval: 60
      unique_id: acond_grandis_r_0013
    - name: ACOND_TC_status # Current status of the heatpump
      slave: 1
      address: 6
      scan_interval: 60
      data_type: int16
      input_type: input
      unique_id: acond_grandis_r_0014
    - name: ACOND_TC_set # Set the state of the heatpump using the holding register
      slave: 1
      address: 5
      input_type: holding
      data_type: int16
      unique_id: acond_grandis_r_0015
    - name: ACOND_T_set_indoor1_holding # Set the indoor temperature of the heatpump using the holding register
      slave: 1
      address: 0
      input_type: holding
      data_type: int16
      unique_id: acond_grandis_r_0016
Template.yaml
- sensor:
  # Debugging the bitwise word value of sensor acond_tc_status
  - name: "Get_ACOND_TC_status"
    state: "{{ states('sensor.acond_tc_status') }}"
    attributes:
      hp_on: "{% if states('sensor.acond_tc_status') | int | bitwise_and(1) %}on{% else %}off{% endif %}"
      hp_operation: "{% if states('sensor.acond_tc_status') | int | bitwise_and(2) %}on{% else %}off{% endif %}"
      hp_failure: "{% if states('sensor.acond_tc_status') | int | bitwise_and(4) %}on{% else %}off{% endif %}"
      dhw_heating_progress: "{% if states('sensor.acond_tc_status') | int | bitwise_and(8) %}on{% else %}off{% endif %}"
      circulation_heating_circuit_1: "{% if states('sensor.acond_tc_status') | int | bitwise_and(16) %}on{% else %}off{% endif %}"
      circulation_heating_circuit_2: "{% if states('sensor.acond_tc_status') | int | bitwise_and(32) %}on{% else %}off{% endif %}"
      solar_circulation: "{% if states('sensor.acond_tc_status') | int | bitwise_and(64) %}on{% else %}off{% endif %}"
      pool_circulation: "{% if states('sensor.acond_tc_status') | int | bitwise_and(128) %}on{% else %}off{% endif %}"
      defrosting: "{% if states('sensor.acond_tc_status') | int | bitwise_and(256) %}on{% else %}off{% endif %}"
      auxiliary_heating: "{% if states('sensor.acond_tc_status') | int | bitwise_and(512) %}on{% else %}off{% endif %}"
      summer_operation: "{% if states('sensor.acond_tc_status') | int | bitwise_and(1024) %}on{% else %}off{% endif %}"
      brine_circulation: "{% if states('sensor.acond_tc_status') | int | bitwise_and(2048) %}on{% else %}off{% endif %}"
      cooling_operation: "{% if states('sensor.acond_tc_status') | int | bitwise_and(4096) %}on{% else %}off{% endif %}"
    unique_id: acond_grandis_r_0014_0
  # Debugging the sensor acond_type_reg_pan
  - name: "GET_ACOND_type_reg_pan"
    state: "{{ states('sensor.acond_type_reg_pan') }}"
    attributes:
      acondtherm: "{% if int(states('sensor.acond_type_reg_pan')) == 0 %}on{% else %}off{% endif %}"
      equiterm: "{% if int(states('sensor.acond_type_reg_pan')) == 1 %}on{% else %}off{% endif %}"
      manually: "{% if int(states('sensor.acond_type_reg_pan')) == 3 %}on{% else %}off{% endif %}"
    unique_id: acond_grandis_r_0012_0
  # Debugging the sensor acond_type_rezim_pan
  - name: "GET_ACOND_type_rezim_pan"
    state: "{{ states('sensor.acond_type_rezim_pan') }}"
    attributes:
      automatically: "{% if int(states('sensor.acond_type_rezim_pan')) == 0 %}on{% else %}off{% endif %}"
      only_heatpump: "{% if int(states('sensor.acond_type_rezim_pan')) == 1 %}on{% else %}off{% endif %}"
      only_auxiliary: "{% if int(states('sensor.acond_type_rezim_pan')) == 3 %}on{% else %}off{% endif %}"
      off: "{% if int(states('sensor.acond_type_rezim_pan')) == 4 %}on{% else %}off{% endif %}"
      manually: "{% if int(states('sensor.acond_type_rezim_pan')) == 5 %}on{% else %}off{% endif %}"
      cooling: "{% if int(states('sensor.acond_type_rezim_pan')) == 6 %}on{% else %}off{% endif %}"
    unique_id: acond_grandis_r_0013_0
# Defining all the binary sensors
- binary_sensor:
   - name: Heatpump On
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(1) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_1
- binary_sensor:
   - name: Heatpump Operation
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(2) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_2
- binary_sensor:
   - name: Heatpump Failure
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(4) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_3
- binary_sensor:
   - name: Domestic Hot Water heating in progress
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(8) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_13
- binary_sensor:
   - name: Circulation Heating Circuit 1
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(16) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_4
- binary_sensor:
   - name: Circulation Heating Circuit 2
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(32) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_5
- binary_sensor:
   - name: Solar Circulation
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(64) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_6
- binary_sensor:
   - name: Pool Circulation
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(128) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_7
- binary_sensor:
   - name: Defrosting
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(256) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_8
- binary_sensor:
   - name: Auxiliary Heating
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(512) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_9
- binary_sensor:
   - name: Summer Operation
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(1024) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_10
- binary_sensor:
   - name: Brine Circulation
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(2048) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_11
- binary_sensor:
   - name: Cooling Operation
     state: "{% if states('sensor.acond_tc_status') | int | bitwise_and(4096) %}on{% else %}off{% endif %}"
     unique_id: acond_grandis_r_0014_12
- sensor:
   - name: "Heatpump mode"
     icon: mdi:state-machine
     unique_id: acond_grandis_r_0013_1
     state: >-
             "Automatic"
         {% elif int(states('sensor.acond_type_rezim_pan')) == 1 %}
             "Only Heatpump"
         {% elif int(states('sensor.acond_type_rezim_pan')) == 3  %}
             "Only Auxiliary" }}
         {% elif int(states('sensor.acond_type_rezim_pan')) == 4  %}
             "Off"
         {% elif int(states('sensor.acond_type_rezim_pan')) == 5  %}
             "Manually"
         {% elif int(states('sensor.acond_type_rezim_pan')) == 6  %}
             "Cooling"
         {% else %}
             "Unknown"
         {% endif %}
- sensor:
   - name: "Heatpump temperature regulation"
     unique_id: acond_grandis_r_0012_1
     state: >-
             "Acondtherm"
         {% elif int(states('sensor.acond_type_reg_pan')) == 1 %}
             "Equitherm"
         {% elif int(states('sensor.acond_type_reg_pan')) == 3 %}
             "Manually"
         {% else %}
             "Unknown"
         {% endif %}
scripts.yaml
# Generic code to turn on a bit in a bitwise holding register
write_register_turn_on_bit:
  sequence:
    - service: modbus.write_register
        hub: "{{ hub }}"
        slave: "{{ slave_id }}"
        address: "{{ address }}"
        value: "{{ states(sensor_value) | int(default=0) | bitwise_or(2 ** (bit | int - 1)) }}"
    - service: homeassistant.update_entity
        entity_id: "{{ sensor_value }}"
# Generic code to turn off a bit in a bitwise holding register
write_register_turn_off_bit:
  sequence:
        hub: "{{ hub }}"
        value: "{{ states(sensor_value) | int(default=0) | bitwise_and(65535 - (2 ** (bit | int - 1))) }}"
# Increase the indoor temperature by an int value of the Acond Grandis R
increase_acond_temperature_value:
  sequence:
        hub: "{{ hub }}"
        value: "{{ int(states(sensor_value)) + (int(temperature_value) * 10) }}"
        entity_id:
          - "{{ sensor_value }}"
          - "{{ update_sensor }}"
# Decrease the indoor temperature by an int value of the Acond Grandis R
decrease_acond_temperature_value:
  sequence:
        hub: "{{ hub }}"
        value: "{{ int(states(sensor_value)) - (int(temperature_value) * 10) }}"
        entity_id:
# Set the indoor temperature by an int value of the Acond Grandis R
set_acond_temperature_value:
  sequence:
        hub: "{{ hub }}"
        value: "(int(temperature_value) * 10)"
        entity_id:
logger.yaml
  default: warning
  logs:
    # Uncomment below to troubleshoot modbus implementation
    # homeassistant.components.modbus: debug
    # pymodbus: debug
And for the completion:
automations.yaml
- id: '1718984438123'
  alias: Tado Keuken naar verwarmen
  description: Tado keuken vraag om verwarming
  - platform: state
    entity_id:
    - climate.keuken
    enabled: true
    attribute: hvac_action
  - choose:
    - conditions:
      - condition: state
        entity_id: climate.keuken
        state: heating
      - condition: state
        entity_id: climate.acond_t_set_indoor1
        attribute: temperature
        state: <= 19.0
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: state
            entity_id: sensor.keuken_verwarmen
            attribute: unit_of_measurement
            state: < 50
          then:
          - service: script.increase_temperature_value
              temperature_value: 2
              hub: acond_grandis_r
              slave_id: 1
              address: 0
              sensor_value: sensor.acond_t_set_indoor1_holding
              update_sensor: climates.acond_t_set_indoor1
          else:
              temperature_value: 5
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: idle
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              entity_id: climate.achterdeur_en_schuur
              state: idle
            - condition: state
              enabled: true
              entity_id: climate.badkamer
              state: idle
            - condition: state
              enabled: true
              entity_id: climate.huiskamer
              state: idle
            - condition: state
              enabled: true
              entity_id: climate.logeerkamer
              state: idle
            - condition: state
              enabled: true
              entity_id: climate.slaapkamer_amy
              state: idle
          then:
          - service: script.set_acond_temperature_value
              temperature_value: 19
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: 'off'
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
          then:
              slave_id: 1
              address: 0
  mode: single
- id: '1719065491089'
  alias: Zet Warmtepomp 19 graden
  description: Wanneer Tado geen warmtevraag heeft. Zet de warmtepomp terug naar standaard
    19 graden
  trigger: []
  condition:
  - condition: and
    conditions:
    - condition: state
      enabled: true
      state: idle
    - condition: state
      enabled: true
      state: idle
    - condition: state
      enabled: true
      state: idle
    - condition: state
      enabled: true
      state: idle
    - condition: state
      enabled: true
      state: idle
    - condition: state
      enabled: true
      state: idle
    - condition: not
      conditions:
      - condition: state
        enabled: true
        state: '19'
      slave_id: 1
      address: 0
      update_sensor: climate.acond_t_set_indoor1
  mode: single
- id: '1719161658222'
  alias: Tado Slaapkamer Amy naar verwarmen
  description: Tado Slaapkamer Amy vraag om verwarming
  - platform: state
    entity_id:
    - climate.slaapkamer_amy
    enabled: true
  - choose:
    - conditions:
      - condition: state
        state: heating
      - condition: state
        state: <= 19.0
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: state
            entity_id: sensor.slaapkamer_amy_verwarmen
            state: < 50
          then:
              slave_id: 1
              address: 0
          else:
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: idle
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
          then:
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: 'off'
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
          then:
              slave_id: 1
              address: 0
  mode: single
- id: '1719161765917'
  alias: Tado Huiskamer naar verwarmen
  description: Tado Huiskamer vraag om verwarming
  - platform: state
    entity_id:
    - climate.keuken
    enabled: true
  - choose:
    - conditions:
      - condition: state
        state: heating
      - condition: state
        state: <= 19.0
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: state
            entity_id: sensor.huiskamer_verwarmen
            state: < 50
          then:
              slave_id: 1
              address: 0
          else:
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: idle
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
          then:
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: 'off'
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
          then:
              slave_id: 1
              address: 0
  mode: single
- id: '1719161864421'
  alias: Tado Achterdeur en Schuur naar verwarmen
  description: Tado Achterdeur en Schuur vraag om verwarming
  - platform: state
    entity_id:
    - climate.achterdeur_en_schuur
    enabled: true
  - choose:
    - conditions:
      - condition: state
        state: heating
      - condition: state
        state: <= 19.0
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: state
            entity_id: sensor.achterdeur_en_schuur_verwarmen
            state: < 50
          then:
              slave_id: 1
              address: 0
          else:
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: idle
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
          then:
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: 'off'
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
          then:
              slave_id: 1
              address: 0
  mode: single
- id: '1719162004956'
  alias: Tado Badkamer naar verwarmen
  description: Tado Badkamer vraag om verwarming
  - platform: state
    entity_id:
    - climate.badkamer
    enabled: true
  - choose:
    - conditions:
      - condition: state
        state: heating
      - condition: state
        state: <= 19.0
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: state
            entity_id: sensor.badkamer_verwarmen
            state: < 50
          then:
              slave_id: 1
              address: 0
          else:
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: idle
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
          then:
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: 'off'
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
          then:
              slave_id: 1
              address: 0
  mode: single
- id: '1719162150918'
  alias: Tado Logeerkamer naar verwarmen
  description: Tado Logeerkamer vraag om verwarming
  - platform: state
    entity_id:
    - climate.logeerkamer
    enabled: true
  - choose:
    - conditions:
      - condition: state
        state: heating
      - condition: state
        state: <= 19.0
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: state
            entity_id: sensor.logeerkamer_verwarmen
            state: < 50
          then:
              slave_id: 1
              address: 0
          else:
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: idle
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
          then:
              slave_id: 1
              address: 0
    - conditions:
      - condition: state
        state: 'off'
      - condition: state
        state: '>= 19.1'
      sequence:
      - sequence:
        - delay:
            hours: 0
            minutes: 2
            seconds: 0
            milliseconds: 0
        - if:
          - condition: and
            conditions:
            - condition: state
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
            - condition: state
              enabled: true
              state: idle
          then:
              slave_id: 1
              address: 0
  mode: single
Thanks everyone for keeping track of what you have done!
I am currently looking into this myself. However, as enabling Modbus is directly connected with a loss of warranty, I was wondering if anyone checked out how the local web server behaves? I was just briefly looking at it and it seems the client is just sending HTTP requests, such as a POST request for logging in:
POST /SYSWWW/LOGIN.XML HTTP/1.1
Host: 192.168.0.10
Content-Type: application/x-www-form-urlencoded
Priority: u=0, i
User-Agent: Mozilla/5.0 (Windows NT 10.0; rv:130.0) Gecko/20100101 Firefox/130.0
Referer: http://192.168.0.10/SYSWWW/LOGIN.XML
Content-Length: 56
USER=acond&PASS=03a9ca25acba8c63ef7d9ec14d4ffb2edc3a66ef
EDIT: Oh, and can someone explain to me, in more detail, what the purpose of the different modes (AcondTherm, EquiTherm, and Manual) is? I have no Acond control unit / sensor installed and am relying on the room thermostats.
Hi Bob, heel erg bedankt voor het delen van jou code bestanden. Ik ben helemaal nieuw met HA en totaal onervaren met code/programmeren maar kom langzaam wegwijs in de werking van de codering en heb jou code (met wat kleine aanpassingen) werkend gekregen op mijn acond PRO. Ik heb nu de modbus.yaml en template.yaml helemaal werkend en ben toegekomen aan het automatiserings gedeelte.
Hier had ik een vraag over, als ik het goed begrijp dan stuur jij de acond opdracht wanneer 1 van de verschillende kamers onder de gewenste temperatuur komt, om de acond thermostaat 2 of 5 graden te verhogen. Dit blijft verhoogd tot
dat alle kamers in idle staan en dan gaat de acond thermostaat weer terug naar 19 graden. Wanneer kies je ervoor om 2 of 5 graden te verhogen, wat houdt die meting <50 in?
Hoor het graag, en nogmaals bedankt!
gr Ben
Thank you Florian Haas to share this piece of code. I have my ACOND PRO-N working with this code you shared.
I know the Acond PRO-N records it’s Electrical Energy per day and Electrical Energy as a sum. I have been trying to add the sensor for the Electrical Energy per day with the following additional code for the sensors:
      - name: ACOND_EED # Electrical energy per day
        slave: 1
        address: 40
        data_type: int16
        input_type: input
        device_class: power
        unit_of_measurement: "kW"
However I have not succeeded in receiving a correct value. After reboot of HA it is still showing “unavailable”. Do you maybe have any suggestions?
In the meantime I have been able to add the sensors for HeartBeat (address 30017) and Actual PWM (address 30025). It seems to me that the addresses in red in the referred documentation are not implemented in my ACOND PRO-N. The document is dated 17.10.2024 and my PRO-N is installed 06-12-2022. I am not sure how ACOND is dealing with Software Updates on older systems, but I get the impression they do not update them.
Maybe anyone has some more insight or information regarding this.
My experience with Acond is that they only update the software if they know of a bug or a major improvement. So twice the first year and then not at all.
You need to write to the service in the summer and ask for an update, ideally with the description you provide here.
They are very helpful in the summer. In the winter they wrote to me that they updated the software, but only because of a new circulation pump that did not work well with PWM control. When I found out that the update also included a MODbus extension (in the previous version I only had up to address 30026), I also wanted a PDF for it. They sent me that (but stil only address up to 30026), but with the understanding that they are asking me to leave such requests for the summer because now they have to deal with repairs at the beginning of the heating season.
I have contact with the Dutch company importing the ACOND heatpump into the Netherlands and distributing it over the installers. On my question regarding firmware version on my heatpump and the update they reacted very quickly, and within half a day I had an update.
I have up to address 30049 visible in the webpage at the moment right now. But my documentation only describes up to address 30044. So I requested the MODBUS documentation describing up to 30049, but still waiting for an answer (send the request only two days ago).
When you are interested in the documentation up to 30044, I can send it you via a private message. Since it is not freely available from ACOND, I do not want to share it here publicly.
I am still relatively new to this forum, so I do not know yet how private messages work.
Dear all, who own a heat pump from acond:
I recently installed a Grandis R on my own, since technical background and some job background on that area.
Now the inicial operation should take place, but the reseller is not willing to provide the password to start coupling inner and outer unit. Instead the inicial operation should cost additional almost 2k€. This was not mentioned when selling the heat pump…
If someone can help, I would appreciate it. My Family also, to get warm water and house… thx.