Hello,
thank you very much everyone for sharing your configuration.
I am having some troubles with the modbus connection to home assistant.
The first couple of days everything was working perfectly. However, then i started to notice some weird spikes in the dashboard:
This spike occurs every day for the last week or so. At some days it even reaches about 20kwh grid export at one hour in the morning, which does not make any sense. It also does not make sense, that the battery is charged at this time.
I looked into the home-assistant database values for further investigation. These is a cutout of the values i got for the e3dc_grid_export_power sensor this morning:
datetime(last_updated_ts, ‘unixepoch’, ‘localtime’) | state |
---|---|
2023-02-07 03:25:39 | 8 |
2023-02-07 03:25:41 | 4 |
2023-02-07 03:25:43 | 1 |
2023-02-07 03:25:45 | 8 |
2023-02-07 03:25:47 | 1 |
2023-02-07 03:25:49 | 13 |
2023-02-07 03:25:51 | 0 |
2023-02-07 03:25:57 | 5 |
2023-02-07 03:25:59 | 4 |
2023-02-07 03:26:01 | 0 |
2023-02-07 05:53:35 | 1968 |
2023-02-07 05:53:37 | 0 |
2023-02-07 05:53:47 | 5 |
2023-02-07 05:53:49 | 0 |
2023-02-07 05:53:51 | 46 |
2023-02-07 05:53:53 | 0 |
2023-02-07 05:53:55 | 11 |
2023-02-07 05:53:57 | 3 |
2023-02-07 05:53:59 | 0 |
2023-02-07 05:54:01 | 15 |
2023-02-07 05:54:03 | 78 |
2023-02-07 05:54:05 | 0 |
2023-02-07 05:54:13 | 2 |
2023-02-07 05:54:15 | 1 |
2023-02-07 05:54:17 | 0 |
2023-02-07 05:54:19 | 51 |
2023-02-07 05:54:21 | 0 |
2023-02-07 05:54:23 | 22 |
2023-02-07 05:54:25 | 20 |
2023-02-07 05:54:27 | 0 |
2023-02-07 05:54:29 | 17 |
2023-02-07 05:54:31 | 0 |
2023-02-07 05:54:35 | 16 |
2023-02-07 05:54:37 | 10 |
2023-02-07 05:54:39 | 2 |
2023-02-07 05:54:41 | 0 |
2023-02-07 05:54:47 | 40 |
2023-02-07 05:54:49 | 0 |
2023-02-07 05:54:51 | 13 |
2023-02-07 05:54:53 | 0 |
2023-02-07 05:54:55 | 3 |
2023-02-07 05:54:57 | 20 |
2023-02-07 05:54:59 | 13 |
2023-02-07 05:55:01 | 9 |
2023-02-07 05:55:03 | 0 |
2023-02-07 05:55:13 | 40 |
2023-02-07 05:55:15 | 16 |
2023-02-07 05:55:17 | 0 |
2023-02-07 05:55:19 | 9 |
2023-02-07 05:55:21 | 0 |
As you can see, there are no values for about 2 hours, and then an extreme spike.
However, i could not figure out, where this is coming from and how to solve this problem.
Is anyone else having this problem or knows a fix for this problem?
Thank you very much!
Here are my configuration files:
Modbus.yaml
- name: "E3DC"
type: tcp
host: 192.168.0.189
port: 502
retry_on_empty: true
sensors:
- name: E3DC Serial Number
unique_id: e3dc_serial_number
address: 40035
data_type: string
count: 8
scan_interval: 86400
- name: E3DC Model
unique_id: e3dc_model
address: 40019
data_type: string
count: 8
scan_interval: 86400
- name: E3DC Manufacturer
unique_id: e3dc_manufacturer
address: 40003
data_type: string
count: 8
scan_interval: 86400
- name: E3DC Firmware
unique_id: e3dc_firmware
address: 40051
data_type: string
count: 8
scan_interval: 86400
- name: E3DC Modbus Firmware
unique_id: e3dc_modbus_firmware
address: 40001
data_type: uint16
scan_interval: 86400
- name: E3DC Solar Power
unique_id: e3dc_solar_power
unit_of_measurement: W
data_type: int16
address: 40067
device_class: power
scan_interval: 2
- name: E3DC Wallbox Power
unit_of_measurement: W
data_type: int16
address: 40077
device_class: power
scan_interval: 2
- name: E3DC Battery Power
unique_id: e3dc_battery_power
unit_of_measurement: W
address: 40069
data_type: int16
device_class: power
scan_interval: 2
- name: E3DC Battery State of Charge
unique_id: e3dc_battery_state_of_charge
unit_of_measurement: '%'
address: 40082
data_type: uint16
device_class: battery
scan_interval: 30
- name: E3DC Power Consumption House
unique_id: e3dc_house_consumption_power
unit_of_measurement: W
data_type: int16
address: 40071
device_class: power
scan_interval: 2
- name: E3DC Grid Power
unique_id: e3dc_grid_power
unit_of_measurement: W
data_type: int16
address: 40073
device_class: power
scan_interval: 2
- name: E3DC Emergency Power State
unique_id: e3dc_emergency_power_state
data_type: int16
address: 40083
scan_interval: 10
- name: E3DC Autarky and Consumption
unique_id: e3dc_autarky_and_consumption
data_type: uint16
address: 40081
scan_interval: 60
- name: E3DC String 1 Power
unique_id: e3dc_string_1_power
data_type: uint16
address: 40101
device_class: power
unit_of_measurement: W
scan_interval: 10
- name: E3DC String 2 Power
unique_id: e3dc_string_2_power
data_type: uint16
address: 40102
device_class: power
unit_of_measurement: W
scan_interval: 10
- name: E3DC String 1 Voltage
unique_id: e3dc_string_1_voltage
data_type: uint16
address: 40095
device_class: voltage
unit_of_measurement: V
scan_interval: 10
- name: E3DC String 2 Voltage
unique_id: e3dc_string_2_voltage
data_type: uint16
address: 40096
device_class: voltage
unit_of_measurement: V
scan_interval: 10
- name: E3DC String 1 Current
unique_id: e3dc_string_1_current
data_type: uint16
address: 40098
device_class: current
unit_of_measurement: A
scale: 0.01
precision: 2
scan_interval: 10
- name: E3DC String 2 Current
unique_id: e3dc_string_2_current
data_type: uint16
address: 40099
device_class: current
unit_of_measurement: A
scale: 0.01
precision: 2
scan_interval: 10
- name: E3DC Powermeter 1 L1-L3
unique_id: e3dc_powermeter_1
data_type: int16
address: 40105
device_class: power
unit_of_measurement: W
scan_interval: 10
- name: E3DC Powermeter 1 L1
unique_id: e3dc_powermeter_1_L1
data_type: int16
address: 40106
device_class: power
unit_of_measurement: W
scan_interval: 10
- name: E3DC Powermeter 1 L2
unique_id: e3dc_powermeter_1_L2
data_type: int16
address: 40107
device_class: power
unit_of_measurement: W
scan_interval: 10
- name: E3DC Powermeter 1 L3
unique_id: e3dc_powermeter_1_L3
data_type: int16
address: 40108
device_class: power
unit_of_measurement: W
scan_interval: 10
sensors.yaml
- platform: integration
source: sensor.e3dc_grid_import_power
name: E3DC Grid Import Energy
unit_prefix: k
round: 2
- platform: integration
source: sensor.e3dc_grid_export_power
name: E3DC Grid Export Energy
unit_prefix: k
round: 2
- platform: integration
source: sensor.e3dc_solar_power
name: E3DC Solar Energy
unit_prefix: k
round: 2
- platform: integration
source: sensor.e3dc_wallbox_power
name: E3DC Wallbox energy
unit_prefix: k
round: 2
- platform: integration
source: sensor.e3dc_battery_power
name: E3DC Builtin Battery Energy
unit_prefix: k
round: 2
- platform: integration
source: sensor.e3dc_battery_charge_power
name: E3DC Battery Charge Energy
unit_prefix: k
round: 2
- platform: integration
source: sensor.e3dc_battery_discharge_power
name: E3DC Battery Discharge Energy
unit_prefix: k
round: 2
- platform: template
sensors:
e3dc_grid_export_power:
unique_id: e3dc_grid_export_power
friendly_name: E3DC Grid Export Power
unit_of_measurement: W
device_class: power
value_template: >
{% if states('sensor.e3dc_grid_power') | int > 0 %}
0
{% else -%}
{{ (states('sensor.e3dc_grid_power') | int) | abs }}
{% endif %}
e3dc_grid_import_power:
unique_id: e3dc_grid_import_power
friendly_name: E3DC Grid Import Power
unit_of_measurement: W
device_class: power
value_template: >
{% if states('sensor.e3dc_grid_power') | int > 0 %}
{{ states('sensor.e3dc_grid_power') }}
{% else -%}
0
{% endif %}
e3dc_battery_charge_power:
unique_id: e3dc_battery_charge_power
friendly_name: E3DC Battery Charging Power
unit_of_measurement: W
device_class: power
value_template: >
{% if states('sensor.e3dc_battery_power') | int >= 0 %}
{{ states('sensor.e3dc_battery_power') }}
{% endif %}
e3dc_battery_discharge_power:
unique_id: e3dc_battery_discharge_power
friendly_name: E3DC Battery Discharging Power
unit_of_measurement: W
device_class: power
value_template: >
{% if states('sensor.e3dc_battery_power') | int <= 0 %}
{{ (states('sensor.e3dc_battery_power') | int) | abs }}
{% endif %}
e3dc_autarky:
friendly_name: 'E3DC Autarky'
unique_id: e3dc_autarky
unit_of_measurement: '%'
value_template: "{{ (states('sensor.e3dc_autarky_and_consumption')|int / 256)|round(0,'floor') }}"
e3dc_own_consumption:
friendly_name: 'E3DC Own Consumption ratio'
unique_id: e3dc_own_consumption_ratio
unit_of_measurement: '%'
value_template: "{{ ((states('sensor.e3dc_autarky_and_consumption')|int / 256 - states('sensor.e3dc_autarky')|int) * 256)|round(0,'floor') }}"