I’m a beginner and after multiple tries, I was able to read Modbus registry from an energy meter.
How I can read a “double registry” ?
The yaml extras is:
uart:
rx_pin: GPIO3
tx_pin: GPIO1
baud_rate: 115200
stop_bits: 1
data_bits: 8
parity: EVEN
modbus:
flow_control_pin: GPIO16
id: modbus1
modbus_controller:
id: sbc
address: 0x1
modbus_id: modbus1
setup_priority: -10
sensor:
platform: modbus_controller
modbus_controller_id: sbc
name: “Energy_Total”
id: sbc_meter_et
register_type: holding
address: 28
unit_of_measurement: “kWh”
value_type: S_DWORD_R
filters:
- multiply: 0.1
nikito7
(nikito7)
October 10, 2022, 12:36pm
2
- platform: modbus_controller
name: "${dev} Active Power Import"
address: 0x0079
register_type: read
value_type: U_DWORD
register_count: 2
response_size: 4
accuracy_decimals: 0
device_class: power
unit_of_measurement: "W"
Thanks, but still a I get an error. See below.
In the meter spec is mentionet: address 28-29. For double registers (4 – 5, 16 – 17, 28 – 29, 30 – 31) the high register is sent first (big_Endian).
For the rest of the registry, I need to have in yaml file the adress -1, seems that is starting the counting from 1. To read the voltage o phase_1 (reg:36) I have specified in yaml file 35
nikito7
(nikito7)
October 10, 2022, 2:43pm
4
28 decimal or hex?
Input or holding?
S_DWORD_R ?
S_DWORD ?
Signed or unSingned?
You need to adapt my example above
01 04 xx is input/read
01 03 xx is holding
Show me a working example
this is working, is reading the Phase 1 voltage
I have changed to holding. Something is reading / returning values now.
Thank you for the support / help