I’m using ESP8266 with MAX485 to control GREE Versaty II. Everything is working fine with sensors, except Modbus Switch, Changing Modes (heat, cool, heat+hot water, cool+hot water, hot water only - which is Switch component as well).
Im stuck some now with Modbus Switch Integration. I’m trying to Power on and off the unit, and I can see all the sensors, and can turn it ON with Modbus when I set bitmask: 0xAA (which is command for turning On, as pdf document says from Gree), but for turning OFF I need other bitmask which is 0x55. Is there a way to achieve that?

Here is my configuration as well, and part of PDF which is describing commands:
ESPHome Config:

ap:
    ssid: "Modbus-Gree Fallback Hotspot"
    password: "sQeTy2wInuSJ"

captive_portal:
web_server:
  port: 80

uart:
  id: mod_bus
  tx_pin: 12
  rx_pin: 14
  baud_rate: 9600
  stop_bits: 1

modbus:
  flow_control_pin: 13
  send_wait_time: 200ms
  id: modbus_versati2
  
modbus_controller:
  - id: versati2
    ## the Modbus device addr
    address: 0x1
    modbus_id: modbus_versati2
    setup_priority: -10

sensor:
  - platform: modbus_controller
    modbus_controller_id: versati2
    id: outside_temp
    name: "Outside Temp"
    address: 0x002D
    unit_of_measurement: "°C" 
    register_type: holding
    value_type: U_WORD
    accuracy_decimals: 2
    filters:
    - multiply: 0.1

  - platform: modbus_controller
    modbus_controller_id: versati2
    id: heating_temp
    name: "Outgoing Water Temp"
    address: 0x0032
    unit_of_measurement: "°C" 
    register_type: holding
    value_type: U_WORD
    accuracy_decimals: 2
    filters:
    - multiply: 0.1

  - platform: modbus_controller
    modbus_controller_id: versati2
    id: boiler_temp
    name: "Water Tank Temp"
    address: 0x0035
    unit_of_measurement: "°C" 
    register_type: holding
    value_type: U_WORD
    accuracy_decimals: 2
    filters:
    - multiply: 0.1

  - platform: modbus_controller
    modbus_controller_id: versati2
    id: power_state
    name: "State"
    address: 0x01
    register_type: holding
    value_type: U_WORD
    
  - platform: modbus_controller
    modbus_controller_id: versati2
    id: mode_hvac
    name: "Mode"
    address: 0x02
    register_type: holding
    value_type: U_WORD
    
  - platform: modbus_controller
    modbus_controller_id: versati2
    id: boiler_setpoint
    name: "Boiler Setpoint Temp"
    address: 0x000D
    unit_of_measurement: "°C" 
    register_type: holding
    value_type: U_WORD
    accuracy_decimals: 2
    filters:
    - multiply: 0.1
  
  - platform: modbus_controller
    modbus_controller_id: versati2
    id: heting_setpoint
    name: "Heating Setpoint Temp"
    address: 0x000A
    unit_of_measurement: "°C" 
    register_type: holding
    value_type: U_WORD
    accuracy_decimals: 2
    filters:
    - multiply: 0.1

switch:
  - platform: modbus_controller
    modbus_controller_id: versati2
    id: turn_on_off
    name: "On Off"
    register_type: holding
    address: 0x001
    bitmask: 0xAA #"With bitmask: 0xAA Switch is working with correct possition, but it cannot turn off thermo pump for turning off 0x85 is needed"

This is a part of PDF document which Is describing commands:

Thank you in advance

If you do not format the code correctly it is undoable to read it:
image

Use two switches

Hi, I have the same heatpump can you please help me with the cable connection of the device side?
What kind of connector is needed?
Thanks

Hello,

I have a problem with esphome.
Does anyone know what I have wrong?

mcu: ESP32

esphome code:

uart:
  id: mod_bus
  tx_pin: GPIO16
  rx_pin: GPIO17
  baud_rate: 9600
  stop_bits: 1

modbus:
  send_wait_time: 200ms
  id: modbus_versati3

modbus_controller:
  - id: modbus_cotnroller
    address: 0x01
    modbus_id: modbus_versati3
    setup_priority: -10

sensor:
  - platform: modbus_controller
    modbus_controller_id: modbus_cotnroller
    id: nasi_komora_modbus_testsensor
    name: "nasi_komora_modbus_testsensor"
    address: 0x76
    register_type: holding
    value_type: U_WORD
    offset: 0

Error in log:
[13:55:28][D][modbus_controller:032]: Modbus command to device=1 register=0x76 countdown=0 no response received - removed from send queue

it’s finally working for me, I’ve created a tutorial here:

1 Like

@kristof.kalotay Sorry for long delay answer - yes I’ll Help you - I’ll send everything I have.
@Pecator Good Job dude - I’ll send you to you as well some other codes which will be usable to investigate problems with pump :wink:

2 Likes

the only thing I couldn’t figure out is how to write a sensor or switch for such registers…

Anyone have any ideas?

Hi everyone. I have recently implemented this integration and it has been working really well. With the change to winter now, I have run into a small issue. Every time the outdoor temp is below zero I get an outdoor tempo value of 6553. With the decimal of 3-8 depending on how cold it is.

any advice on why the Modbus is returning this value?

yes, need convert to negative float.

1 Like

  - platform: modbus_controller
    modbus_controller_id: versati3
    name: "versati_118_outdoor_temp"
    address: 118
    unit_of_measurement: "°C" 
    register_type: holding
    value_type: U_WORD
    accuracy_decimals: 1
    filters:
    - lambda: |-
        if (x > 32767) {
          x -= 65536;
        }
        return x * 0.1;
1 Like

Thank you very much.