Question for those who have a Heat Recovery Ventilation Unit (HRU):
What kind of efficiency are you seeing with your HRU systems, based on temperature measurements? I’d appreciate it if you could share your own values so we can compare.
I have an Alnor HRU Slim Air 500 CF unit, and the example below was measured at an airflow of 250 m³/h:
-
Indoor temperature (air extracted from the house): 22.86°C
-
Supply air temperature (fresh air entering the house after HRU): 20.16°C
-
Outdoor temperature (fresh air entering the HRU): 14.67°C
-
Exhaust air temperature (air leaving the HRU to the outside): 15.65°C
Using the standard efficiency formula:
(Supply - Outdoor) / (Indoor - Outdoor)
I get an efficiency of approximately 67%.
The manufacturer suggested I use Supply / Indoor, which gives about 88%, but to me that seems misleading — it completely ignores the outdoor air temperature.
If you can share your measurements (ideally at a known airflow), that would be really helpful to understand what’s normal and whether I should investigate further.
Thanks in advance!