Heatpump (KEBA) select functioning mode via input selector
and happy to join the HA community with my first post :slight_smile: . I am trying to integrate my M-TEC heatpump (it uses KEBA KeEnergy software) to HA using the yaml config files. (infos found here: Keba KeEnergy Heizungssteuerung (M-TEC WP) in Smarthome)
So I succesfully integrated the Heatpump via modbus, but I am struggeling with two points:
  1. I created an input selector Heatpump Mode to select the functioning mode of my heatpump. I am then passing the selected mode to the heatpump using the automation and this works perfectly set_heatpump_mode.
    However, the second part get_heatpump_mode, that updates the input selector when the mode on the heatpump was changed manually, is resisting my beginner skills.
    I keep getting an error message: Invalid config for [automation]: must contain at least one of below, above.. Got OrderedDict. I searched for hours, tried changing the automations.yml without success …
  2. My heatpump, uses a user defined offset (Heatpump_offsetRoomTemp) that ranges from -2.5 to 2.5 that helps to fine tune the temperature. This offset is added to the Heatpump_normalSetTempTest or the Heatpump_reducedSetTemp – depending on the selected mode (Day/Night) – to achieve the final temperature Heatpump_SetpointTemperature.
    My issue is that i tried to integrated it as a HVAC as for the two other but it does not let me input a negative value? Any idea on how to achieve this?
Below my configuration:
input_select:
  heatpump_mode:
    options:
      - "Standby"
      - "Timer"
      - "Day"
      - "Night"
      - "Vacation"
      - "Party"
    icon: mdi:home-thermometer
modbus:
  - name: Heatpump
    type: tcp
    host: 192.168.1.30
    port: 502
    sensors:
      - name: Heatpump_selectedSetTemp
        data_type: uint16
        slave: 1
        address: 2
        scale: 0.1
        precision: 1
        unit_of_measurement: °C
      - name: Heatpump_SetpointTemperature
        data_type: uint16
        slave: 1
        address: 3
        scale: 0.1
        precision: 1
      - name: Heatpump_offsetRoomTemp
        data_type: uint16
        slave: 1
        address: 6
        scale: 0.1
        precision: 1
      - name: Heatpump_HotWater_Temperature
        data_type: uint16
        slave: 1
        address: 401
        scale: 0.1
        precision: 1
      - name: Heatpump_HotWater_SetpointTemperature
        data_type: uint16
        slave: 1
        address: 402
        scale: 0.1
        precision: 1
      - name: Heatpump_TotalAccumulatedHeatingEnergy
        data_type: uint16
        slave: 1
        address: 701
        scale: 1
        precision: 1
        unit_of_measurement: kWh
      - name: Heatpump_State
        data_type: uint16
        slave: 1
        address: 703
      - name: Heatpump_ActualFlowTemperature
        data_type: uint16
        slave: 1
        address: 705
        scale: 0.1
        precision: 1
      - name: Heatpump_HeatPower
        data_type: uint16
        slave: 1
        address: 706
        scale: 0.001
        precision: 2
      - name: Heatpump_RefluxTemperature
        data_type: uint16
        slave: 1
        address: 710
        scale: 0.1
        precision: 1
      - name: Heatpump_CirculationPump
        data_type: uint16
        slave: 1
        address: 712
        scale: 0.01
        precision: 2
      - name: Heatpump_OutdoorTempValues
        data_type: uint16
        slave: 1
        address: 1502
        scale: 0.1
        precision: 1
      - name: Heatpump_operatingMode
        data_type: uint16
        slave: 1
        address: 7
    climates:
      - name: Heatpump_normalSetTempTest
        data_type: uint16
        slave: 1
        address: 4
        input_type: holding
        count: 1
        max_temp: 30
        min_temp: 10
        offset: 0
        precision: 1
        scale: 0.1
        target_temp_register: 4
        temp_step: 1
        temperature_unit: C
      - name: Heatpump_reducedSetTemp
        data_type: uint16
        slave: 1
        address: 5
        input_type: holding
        count: 1
        max_temp: 30
        min_temp: 10
        offset: 0
        precision: 1
        scale: 0.1
        target_temp_register: 5
        temp_step: 1
        temperature_unit: C
And my automation
- id: '1670278639728'
  alias: set_heatpump_mode
  description: ''
  - platform: state
    entity_id:
    - input_select.heatpump_mode
  condition: []
  - service: modbus.write_register
      address: 7
      hub: Heatpump
      value: >
        {% if is_state('input_select.heatpump_mode', 'Standby') %}
           0
        {% elif is_state('input_select.heatpump_mode', 'Timer') %}
           1
        {% elif is_state('input_select.heatpump_mode', 'Day') %}
           2
        {% elif is_state('input_select.heatpump_mode', 'Night') %}
           3
        {% elif is_state('input_select.heatpump_mode', 'Vacation') %}
           4
        {% elif is_state('input_select.heatpump_mode', 'Party') %}
           5
        {% endif %}
  mode: single
- id: '1670426700029'
  alias: get_heatpump_mode
  description: ''
  - platform: numeric_state
    entity_id:
    - sensor.heatpump_operatingmode
  condition: []
  - service: input_select.select_option
      entity_id: input_select.heatpump_mode
      option: >
        {% if is_state('sensor.heatpump_operatingmode', 0) %}
           'Standby'
        {% elif is_state('sensor.heatpump_operatingmode', 1) %}
           'Timer'
        {% elif is_state('sensor.heatpump_operatingmode', 2) %}
           'Day'
        {% elif is_state('sensor.heatpump_operatingmode', 3) %}
           'Night'
        {% elif is_state('sensor.heatpump_operatingmode', 4) %}
           'Vacation'
        {% elif is_state('sensor.heatpump_operatingmode', 5) %}
           'Party'
        {% endif %}
  mode: single
Thanks !
In case someone is searching, I did a beginner mistake in the automation by adding unnecessary quotes, I also cast the value of the sensor to an int.
Automation get_heatpump_mode should be written as this:
- id: '1670504791806'
  description: ''
  - platform: state
    entity_id:
  condition: []
      option: "{% set mode = states('sensor.heatpump_operatingmode') | int(0) %}  {%
        if mode == 0 %}\n   Standby\n{% elif mode == 1 %}\n   Timer  \n{% elif mode
        == 2 %}\n   Day\n{% elif mode == 3 %}\n   Night\n{% elif mode == 4 %}\n   Vacation\n{%
        elif mode == 5 %}\n   Part\n{% endif %}\n"
  mode: single
I am still missing the second part and the negative offset although
I finally solved my issue. I tried to create the manual temperature offset using a climate entity, but this was not possible. Although, it is maybe possible to create a new climate entity in Python to handle this specific use case…
So the easiest solution was for me just to create a new input_number helper called Normal Temp. I then used it again in an automation and write the input state to the modbus register.
So here my M-TEC (KEBA) heatpump dashboard with on top the mode selector and below the manual offset:
And here my configurstion file:
# Helper for the Heatpump automation
input_select:
  heatpump_mode:
    options:
      - "Standby"
      - "Timer"
      - "Day"
      - "Night"
      - "Vacation"
      - "Party"
# KEBA Heatpump
modbus:
  - name: Heatpump
    type: tcp
    host: 192.168.1.30
    port: 502
    sensors:
        data_type: uint16
        slave: 1
        address: 2
        scale: 0.1
        precision: 1
        data_type: uint16
        slave: 1
        address: 3
        scale: 0.1
        precision: 1
        data_type: uint16
        slave: 1
        address: 6
        scale: 0.1
        precision: 1
        data_type: uint16
        slave: 1
        address: 401
        scale: 0.1
        precision: 1
        data_type: uint16
        slave: 1
        address: 402
        scale: 0.1
        precision: 1
        data_type: uint16
        slave: 1
        address: 701
        scale: 1
        precision: 1
        data_type: uint16
        slave: 1
        address: 703
        data_type: uint16
        slave: 1
        address: 705
        scale: 0.1
        precision: 1
        data_type: uint16
        slave: 1
        address: 706
        scale: 0.001
        precision: 2
        data_type: uint16
        slave: 1
        address: 710
        scale: 0.1
        precision: 1
        data_type: uint16
        slave: 1
        address: 712
        scale: 0.01
        precision: 2
        data_type: uint16
        slave: 1
        address: 1502
        scale: 0.1
        precision: 1
        data_type: uint16
        slave: 1
        address: 7
    climates:
        data_type: uint16
        slave: 1
        address: 4
        input_type: holding
        count: 1
        max_temp: 30
        min_temp: 10
        offset: 0
        precision: 0.1
        scale: 0.1
        temp_step: 0.5
        temperature_unit: C
        data_type: uint16
        slave: 1
        address: 5
        input_type: holding
        count: 1
        max_temp: 30
        min_temp: 10
        offset: 0
        precision: 0.1
        scale: 0.1
        temp_step: 0.5
        temperature_unit: C
And the automation file:
- id: "1670278639728"
  description: Set the mode of the heatpump
  - platform: state
    entity_id:
  condition: []
  mode: single
- id: '1670963163660'
  alias: set_temp_offset
  description: Set the temperature offset of the heatpump
  - platform: state
    entity_id:
    - input_number.normal_temp
  condition: []
      address: 6
      hub: Heatpump
      value: '{{states(''input_number.normal_temp'') | float()  * 10}}'
  mode: single
- id: '1670965913633'
  alias: get_temp_offset
  description: Get the temperature offset of the heatpump
  - platform: state
    entity_id:
    - sensor.heatpump_offsetroomtemp
  condition: []
  - service: input_number.set_value
      value: "{{states('sensor.heatpump_offsetroomtemp') | float()}}"
      entity_id: input_number.normal_temp
  mode: single
I am closing my topic :boom: ! I have still the boiler to do, but should be pretty straight forward.
Hi, thanks for you code,
I have one issue, I can change the value of sensor.heatpump_operatingmode but the change is not send to M-TEC (KEBA) heatpump dashboard . Do you know have I can fix this
Oops, I see that I am missing the first lines of the code on the automation.
I am editing it right now, and you can then just copy and paste it again.
Let me know if it is still not working. BTW please note that there is a small delay between sending the command and the update (usually a few seconds).
Hi @carmanber
I want to thank you very much for the configuration here! I also got a M-TEC heatpump and I’m new to HA.
I’ve added the configuration and automation. Could you also share the dashboard you created?
Thanks, Jo
Hi @jgrumboe ,
andd welcome to HA, hope you will have fun developping your Smart Home :slight_smile:
Here the yaml of the dashboard (you may have to adapt it to your system).
  - icon: mdi:home-thermometer
    title: Heat Pump
    subview: true
    badges: []
    cards:
      - type: custom:mushroom-chips-card
        chips:
          - type: back
          - type: action
            icon: mdi:information-outline
          - type: conditional
            conditions:
              - entity: input_select.heatpump_mode
                state_not: Standby
            chip:
              type: action
              icon: mdi:power
              hold_action:
                action: call-service
                  option: Standby
          - type: conditional
            conditions:
                state_not: Timer
            chip:
              type: action
              icon: mdi:clock-time-four-outline
              hold_action:
                  option: Timer
          - type: conditional
            conditions:
                state_not: Day
            chip:
              type: action
              icon: mdi:white-balance-sunny
              tap_action:
                action: none
              hold_action:
                  option: Day
          - type: conditional
            conditions:
                state_not: Night
            chip:
              type: action
              icon: mdi:moon-waning-crescent
              hold_action:
                  option: Night
      - type: vertical-stack
        cards:
          - type: custom:mushroom-title-card
            title: Temperature
          - type: entities
            entities:
                secondary_info: none
          - square: false
            columns: 3
            type: grid
            cards:
              - show_name: false
                show_icon: true
                type: button
                tap_action:
                  service: input_number.decrement
                  data: {}
                icon: mdi:arrow-down-bold
                icon_height: 57px
                title: '{{ states(''sensor.heatpump_setpointtemperature'') }} °C'
                alignment: center
              - show_name: false
                show_icon: true
                type: button
                tap_action:
                  service: input_number.increment
                  data: {}
                icon: mdi:arrow-up-bold
                icon_height: 58px
          - type: custom:mushroom-climate-card
            entity: climate.heatpump_normalsettemptest
            show_temperature_control: true
            collapsible_controls: true
            icon: mdi:thermometer-chevron-up
            layout: horizontal
            entity: climate.heatpump_reducedsettemp
            icon: mdi:thermometer-chevron-down
            fill_container: false
            layout: horizontal
        cards:
            title: Hot Water
            entity: climate.heatpump_hotwater_setpointtemperature
            layout: horizontal
          - type: custom:mushroom-entity-card
            entity: sensor.heatpump_hotwater_temperature
        cards:
            title: Heatpump
          - type: iframe
            url: http://chaudiere
            aspect_ratio: 50%
Hope it helps, let me know if there is any issue.
Aso, you will see that the interface is a bit slow (the way the automation/modbus works). I am thinking whether to develop smtg specific, I will keep you posted if so.
Hi folks,
can someone help me to use my heat pump in Homeassistant? How do I integrate it? I would like to read out the sensors.
Greetings Barete
Hi Barete,
it might be difficult to help you without further information. It really depends on your model and manufacturer. You might connect it via Ethernet or WiF, Modbus or maybe even propetary protocol. You should check your instruction manual.
What information do you need?
It is an M-Tec heat pump, it has a KEBA platinum/software.
In that case you just need to connect your heatpump via ethernet (of wifi if you bought the module), use the code above in your configuration.yml. Just be careful about your device IP Adress.
Let me know if there is any issue, but it should be pretty straight forward. If you do not know about configuration yaml , you can find all the info in the official documentation: https://www.home-assistant.io/docs/configuration/
Do you mean the code from the first page?
Do I have to activate Modbus first?
I used the code from the first post. However, this does not lead to success, the following errors are listed:
Invalid config for ‘modbus’ at configuration.yaml, line 143: Heatpump_normalSetTempTest: count illegal with data_type: uint16 ‘modbus->0->climates->0’, got {‘name’: ‘Heatpump_normalSetTempTest’, ‘data_type’: ‘uint16’, ‘slave’: 1, ‘address’: 4, ‘input_type’: ‘holding’, ‘count’: 1, ‘max_temp’: 30, ‘min_temp’: 10, ‘offset’: 0, ‘precision’: 1, ‘scale’: 0.1, ‘target_temp_register’: 4, ‘temp_step’: 1, ‘temperature_unit’: ‘C’}
Invalid config for ‘modbus’ at configuration.yaml, line 157: Heatpump_reducedSetTemp: count illegal with data_type: uint16 ‘modbus->0->climates->1’, got {‘name’: ‘Heatpump_reducedSetTemp’, ‘data_type’: ‘uint16’, ‘slave’: 1, ‘address’: 5, ‘input_type’: ‘holding’, ‘count’: 1, ‘max_temp’: 30, ‘min_temp’: 10, ‘offset’: 0, ‘precision’: 1, ‘scale’: 0.1, ‘target_temp_register’: 5, ‘temp_step’: 1, ‘temperature_unit’: ‘C’}
Can you reach your Heatpump at its IP Address ?
I’m having a similar issue with the configuration.
I copied the code you provided but for an issue that Modbus was unable to start. Also tried with the code from Nicolaj
and in this configuration, I get the Modbus to run but the data is not received.
I would appreciate it if you have any feedback.
I’m not a programmer so I’ve been fighting with this for the past year with no success. :frowning:
I tried targeting different addresses for the Total accumulated heating energy [kWh]
  - name: Heatpump0_TotalAccumulatedHeatingEnergy
    data_type: uint16
    slave: 1
    address: 701
    scale: 1
    precision: 1
  - name: Heatpump1_TotalAccumulatedHeatingEnergy
    data_type: uint16
    slave: 1
    address: 726
    scale: 1
    precision: 1
  - name: Heatpump2_TotalAccumulatedHeatingEnergy
    data_type: uint16
    slave: 1
    address: 751
    scale: 1
    precision: 1
  - name: Heatpump3_TotalAccumulatedHeatingEnergy
    data_type: uint16
    slave: 1
    address: 776
    scale: 1
    precision: 1
Without success.
Thanks in advance sir. I need your assistance. I have just used your code exactly with adding my IP which is 192.168.255.xxx. It’s is giving unavailable error in all the entities.
Hi you IP address is kinda of strange 255 is normally a restricted IP used for broadcasting. How did you setup the IP address of your heat pump ? Try changing it via DHCP or diretly in your Heatpump menu. You might need to review your global network setting depending on your subnet mask.
Are the IP/address and the port correctly set ? I am not 100% sure but I think you need also to allow modbus from the heatpump menu.
Refer to the doc I linked above for the exact address mapping.
Hello everone,
I wrote a custom integration for my heat pump from M-TEC (Keba KeEnergy): [HACS] Custom Integration Keba KeEnergy for e.g. Heatpumps from M-TEC