Hello together,
I’m trying to connect the SDM72D with my Home Assistant, unfortunately without success.
I’m think the configuration is by the Protoss OK, because I can see in Protoss that the bytes are sending to my wallbox.
In my configuration.yaml I have:
# modbus communication
modbus:
- name: "hauptzahler"
close_comm_on_error: false
retry_on_empty: true
retries: 10
delay: 10
message_wait_milliseconds: 1000
timeout: 10
type: tcp
host: 192.168.178.XX
port: 8899
sensors:
- name: hauptzahler_phase_1_line_to_neutral_volts
slave: 1
address: 1
input_type: input
count: 2
precision: 2
data_type: float32
unit_of_measurement: V
device_class: voltage
scan_interval: 30
- name: hauptzahler_phase_1_current
slave: 1
address: 6
input_type: input
count: 2
precision: 2
data_type: float32
unit_of_measurement: A
device_class: current
scan_interval: 30
- name: hauptzahler_phase_1_power
slave: 1
address: 12
input_type: input
count: 2
precision: 3
data_type: float32
unit_of_measurement: kW
device_class: power
- name: hauptzahler_phase_1_va
slave: 1
address: 18
input_type: input
count: 2
precision: 2
data_type: float32
unit_of_measurement: VA
device_class: power
- name: hauptzahler_phase_1_va_reactive
slave: 1
address: 24
input_type: input
count: 2
precision: 2
data_type: float32
unit_of_measurement: VAr
device_class: power
- name: hauptzahler_sum_of_line_currents
slave: 1
address: 48
input_type: input
count: 2
precision: 3
data_type: float32
- name: hauptzahler_total_system_power
slave: 1
address: 52
input_type: input
count: 2
precision: 3
scale: 0.001
data_type: float32
device_class: power
- name: hauptzahler_total_system_va
slave: 1
address: 56
input_type: input
count: 2
precision: 2
data_type: float32
device_class: power
- name: hauptzahler_total_system_var
slave: 1
address: 60
input_type: input
count: 2
precision: 2
data_type: float32
device_class: power
- name: hauptzahler_frequency_of_supply_voltages
slave: 1
address: 70
input_type: input
count: 2
precision: 2
data_type: float32
unit_of_measurement: Hz
- name: hauptzahler_import_wh_since_last_reset
slave: 1
address: 73
input_type: input
count: 2
precision: 2
data_type: float32
unit_of_measurement: kWh
device_class: energy
- name: hauptzahler_export_wh_since_last_reset
slave: 1
address: 74
input_type: input
count: 2
precision: 2
data_type: float32
- name: hauptzahler_total_system_power_demand
slave: 1
address: 84
input_type: input
count: 2
precision: 2
data_type: float32
unit_of_measurement: W
device_class: power
- name: hauptzahler_maximum_total_system_power
slave: 1
address: 86
input_type: input
count: 2
precision: 2
data_type: float32
device_class: power
- name: hauptzahler_total_system_va_demand
slave: 1
address: 100
input_type: input
count: 2
precision: 2
data_type: float32
device_class: power
- name: hauptzahler_maximum_total_system_va_demand
slave: 1
address: 102
input_type: input
count: 2
precision: 2
data_type: float32
device_class: power
- name: hauptzahler_line_1_to_line_2_volts
slave: 1
address: 200
input_type: input
count: 2
precision: 2
data_type: float32
- name: hauptzahler_line_2_to_line_3_volts
slave: 1
address: 202
input_type: input
count: 2
precision: 2
data_type: float32
- name: hauptzahler_line_3_to_line_1_volts
slave: 1
address: 204
input_type: input
count: 2
precision: 2
data_type: float32
# Example configuration.yaml entry
utility_meter:
daily_energy:
source: sensor.hauptzahler_total_system_power
cycle: daily
monthly_energy:
cycle: monthly
The IP and port are correct and the addresses should be correct too. Nevertheless I get this error by HA:
Logger: homeassistant.components.modbus.modbus
Source: components/modbus/modbus.py:385
Integration: Modbus (documentation, issues)
First occurred: 18:23:14 (1 occurrences)
Last logged: 18:23:14Pymodbus: hauptzahler: Modbus Error: [Input/Output] Modbus Error: [Invalid Message] No response received, expected at least 8 bytes (0 received)
Can You help me?
EDIT: I have checked now once again and some bytes are sending via “Netp” to my synology where HA is installed (see attachment).