I use Modbus to get electrical data from 3 devices. the setup is HA connect to a TCP <=> Modbus converter. the 3 devices are connected via a RS485 bus to the converter.
In the configuration.yaml file the 3 devices are addressed via the Slave parameter and I use the Sensor platform to read the data.
so fa so good, this works fine, HA receives all the required information.
but
one of the devices is my Goodwe PV inverter. and for some obscure reason the inverter does not like being interrogated during bootup.
every morning when there is enough power from the PV panels the inverter boots. when HA sends a request to the inverter during this moment, the inverter resets all of its internal counters. Goodwe is not willing to seriously investigate the problem.
So what I want is to stop interrogating this slave from sunset to sunrise.
the 2 other slaves should continue to operate, so I can’t stop the whole modbus thing. I want only to stop the secified slave.
Any suggestions how to achieve this?
You’ll need to disable polling on the modbus integration and create an automation to do the polling. The automation in turn will make the decision of what to poll / not poll.
To disable polling go into the integration system options and turn polling off, then use this method call to poll when needed.
- service: homeassistant.update_entity
data: {}
entity_id: sensor.r_generator_state
Actually for modbus you’ll want to set the scan_interval to zero
scan_interval integer (optional, default: 15)
Update interval in seconds. scan_interval = 0 for no polling. Entities are read shortly after startup and then according to scan_interval. Remark, when restarting HA the last known value is restored.
thanks. this works like a charm.
Hi, I have the same problem. I have a Modbus TCP gateway that queries two Modbus 485 devices identified as slave 1 and slave 2. If both devices are on, there’s no issue, but if slave 1 is off, slave 2 stops working. This problem occurs only with Home Assistant; if I query them using a Modbus simulator, everything works fine.
How did you manage to modify the scan interval dynamically?
Thanks!
I have the same problem, were you able to solve it?
Hello, I don’t remember my solution, so I’m pasting my configuration as an example. When only Slave 2 is online, the system operates, but it’s not very speedy. However, when all slaves are online, the system runs at full speed without any delays.
We attempted to create a dynamic scan interval, but it isn’t a functional solution
type: tcp
host: 192.168.2.58
port: 502
delay: 5
timeout: 2sensors:
name: “RPM Attuali Pompa”
slave: 2
address: 3140 # 0x0C44 in decimale
input_type: holding # CORRETTO: Usa Holding Register (funzione 03)
scan_interval: 10
data_type: uint16
unit_of_measurement: “RPM” -
name: “Consumo Pompa Piscina”
slave: 2
address: 3141 # 0x0C45 in decimale
scan_interval: 10
data_type: uint16
unit_of_measurement: “W” -
name: “PWP Speed Percentage”
slave: 1
address: 0
input_type: input
scan_interval: 0 #15
data_type: uint16
unit_of_measurement: “%” -
name: “Voltage of PFC”
slave: 1
address: 2
input_type: input
data_type: uint16
unit_of_measurement: “V” -
name: “PWP Inlet Water Temperature”
slave: 1
address: 3
input_type: input
data_type: uint16
unit_of_measurement: “°C”
scale: 0.5
offset: -30
precision: 1 -
name: “PWP Outlet Water Temperature”
slave: 1
address: 4
input_type: input
data_type: uint16
scale: 0.5
offset: -30
precision: 1 -
name: “PWP Ambient Air Temperature”
slave: 1
address: 5
input_type: input
data_type: uint16
scale: 0.5
offset: -30
precision: 1 -
name: “PWP Compressor Current”
slave: 1
address: 11
input_type: input
data_type: uint16
unit_of_measurement: “A”
scale: 0.1 -
name: “PWP Compressor Running Frequency”
slave: 1
address: 10
input_type: input
data_type: uint16
unit_of_measurement: “Hz” -
name: “PWP Cooling Plate Temperature”
slave: 1
address: 12
input_type: input
data_type: uint16
scale: 0.5
offset: -30
precision: 1 -
name: “PWP DC Fan Speed”
slave: 1
address: 14
input_type: input
data_type: uint16
name: “Voltage of Power Supply”
slave: 1
address: 30
input_type: input
data_type: uint16
switches:
- name: “PWP Power Switch”
slave: 1
address: 0
write_type: coil
binary_sensors:
name: “PWP Error E0”
slave: 1
address: 48
input_type: discrete_input
device_class: problem -
name: “PWP Error E1 - High Pressure Protection”
slave: 1
address: 49
name: “PWP Error E2 Low Pressure Protection”
slave: 1
address: 50
name: “PWP Warning E3 No Water Protection”
slave: 1
address: 51
name: “PWP Error E4 3 Phase Sequence Protection”
slave: 1
address: 52
name: “PWP Warning E5 Power Supply Out of Range”
slave: 1
address: 53