Hi there,
I have some trouble with my KNX actuator and the home assistant climate device.
According to the documentation target_temperature_address is DPT 9.001 which means temperature in °C. But looking at the group monitor I see:
Telegramm 1540
20.01.2025, 17:02:36,030
Ausgehend
Quelle
1.1.15
Home Assistant
Ziel
11/7/0
Wohnzimmer
Nachricht
GroupValueWrite
DPT 9.002 temperature_difference_2byte
Daten
0x0c42
Wert
21.8 K
It says DPT 9.002 temperature_difference_2byte. That is wrong on two levels. First it should be DPT 9.001. Second if it is 9.002 it is not a temperature difference but a temperature in K.
My actuator does not like that and comes back with a different target_temperature_state_address value:
Telegramm 1541
20.01.2025, 17:02:36,210
Eingehend
Quelle
1.2.2
MDT technologies Heizungsaktor 8-fach, 230V, EG
Ziel
11/1/0
Wohnzimmer
Nachricht
GroupValueWrite
DPT 9.001 temperature
Daten
0x0c8d
Wert
23.3 °C
Am I doing something wrong here?