Hello,
i have a pluggit ventilation plant. It supports modbus. But i dont understand, how i can integrate it in home assistant.
For basic testing i used a temperature value, but i dont get any data.
i create this configuration
modbus:
- name: "Pluggit"
type: tcp
host: 192.168.178.22
port: 502
sensors:
- name: PluggitTest
unit_of_measurement: °C
slave: 1
address: 40089
The manual says for temperature the following
What is wrong with my config? Thanks for your help.
StefanW
(StefanW)
January 28, 2022, 5:46pm
2
I found the log for modbus and saw, that there was an illegal address. So i changed the input type to input.
Now my config is
modbus:
- name: "Pluggit"
type: tcp
host: 192.168.178.22
port: 502
sensors:
- name: PluggitTest
unit_of_measurement: °C
slave: 1
address: 40089
input_type: input
data_type: float
But i have also no data availabe and the log says.
PluggitTest with float is not valid, trying to convert
But the docu says, it is a float. Any ideas?
nikito7
(nikito7)
January 28, 2022, 6:17pm
3
40089 maybe it is holding (4)0089
address: 89
count: 2
input_type: holding
data_type: float
swap: none
Maybe it is need to change swap
StefanW
(StefanW)
January 29, 2022, 7:16pm
4
Thanks nikito. It’s working. Please, can you explain why count should be 2? And why swap?
1 Like
nikito7
(nikito7)
January 30, 2022, 2:27am
5
Because float(4bytes) is two registers
2bytes + 2bytes
Sometimes it is need to swap it: reg1reg2 or reg2reg1