Modbus configuration for NIBE S series heatpumps
Note that this was done for a NIBE S1155 PC, but would expect the majority to work for other heatpumps from the S series as well.
After combining information from the modbus documentation from NIBE themselves, the exported CSV from the heatpump and a lot of trail and error (with the assistance of myuplink), I would like to share the current yaml I have for at least the majority of sensors as included in the ‘info’ menu.
More than willing to receive any feedback and or comments, particularly as I would not consider myself experienced with this kind of stuff yet, hence any best practices are welcome.
Added comments where possible, including some deviations (mainly data type) between the modbus reference and what I ended up using, in the comments you’ll find what is included in the most recent version of the reference document.
- name: "NIBE S1155"
  type: tcp
  host: 192.168.2.11
  port: 502
  sensors:
      # 3.1.2 Overview
    - name: "Operating Prioritisation"
      unique_id: "operating_prioritisation"
      data_type: int16  # int8
      # 10: Off, 20: Hot Water, 30: Heat, 40: Pool, 50: Cooling
      address: 1028
      input_type: input  # R/W
      scale: 1
      precision: 0
      state_class: measurement
      slave: 1
    - name: "Power Usage"
      unique_id: "power_usage"
      unit_of_measurement: "W"
      data_type: int16
      device_class: power
      address: 2166
      input_type: input
      scale: 1
      precision: 0
      slave: 1
      # 3.1.3 Heating
    - name: "Degree Minutes (Heating)"
      unique_id: "degree_minutes_heating"
      unit_of_measurement: "DM"
      data_type: int16
      address: 18
      input_type: holding  # R/W
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Room Temperature"  # BT50
      unique_id: "room_temperature_bt50"
      unit_of_measurement: "°C"
      data_type: int16
      device_class: temperature
      address: 116  # 116 for RMU S40, 26 for BT50
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Calculated Supply (Heating)"
      unique_id: "calculated_supply_heating"
      data_type: int16
      address: 1017
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Supply Line Temperature"  # BT2
      unique_id: "supply_line_temperature_bt2"
      data_type: int16
      address: 5
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Return Line Temperature"  # BT3
      unique_id: "return_line_temperature_bt3"
      data_type: int16
      address: 7
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Outdoor Temperature"  # BT1
      unique_id: "outdoor_temperature_bt1"
      data_type: int16
      address: 1
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Average Outdoor Temperature"
      unique_id: "average_outdoor_temperature"
      data_type: int16
      address: 37
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Condenser Supply"  # BT12
      unique_id: "condenser_supply_bt12"
      data_type: int16
      address: 12
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Brine In"  # BT10
      unique_id: "brine_in_bt10"
      data_type: int16
      address: 10
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Brine Out"  # BT11
      unique_id: "brine_out_bt11"
      data_type: int16
      address: 11
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Underfloor Drying Function"
      unique_id: "underfloor_drying_function"
      data_type: int16
      address: 120
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
      # 3.1.4 Hot Water
    - name: "Hot Water Demand"  # aka "Comfort Mode"
      unique_id: "hot_water_demand"
      # 0: Small, 1: Medium, 2: Large, 3: Smart Control
      address: 56
      scale: 1
      precision: 0
      slave: 1
    - name: "Hot Water Charging"  # BT6
      unique_id: "hot_water_charging_bt6"
      data_type: int16
      address: 9
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Hot Water Top"  # BT7
      unique_id: "hot_water_top_bt7"
      data_type: int16
      address: 8
      scale: 0.1
      precision: 1
      slave: 1
      # 3.1.5 Cooling
    - name: "Calculated Supply (Cooling)"
      unique_id: "calculated_supply_cooling"
      data_type: int16
      address: 1567
      scale: 0.1
      precision: 1
      slave: 1
      # 3.1.7 Compressor
    - name: "Compressor Frequency"
      unique_id: "compressor_frequency"
      unit_of_measurement: "Hz"
      data_type: int16  # uint16
      device_class: frequency
      address: 1046
      scale: 0.1
      precision: 0  # could be set to 1
      slave: 1
    - name: "Requested Compressor Frequency"
      unique_id: "requested_compressor_frequency"
      data_type: int16
      address: 140
      scale: 1
      precision: 0
      slave: 1
    - name: "Minimum Compressor Frequency"
      unique_id: "minimum_compressor_frequency"
      data_type: int16
      address: 1041
      scale: 1
      precision: 0
      slave: 1
    - name: "Compressor Status"
      unique_id: "compressor_status"
      data_type: int16  # uint8
      # 0: Off, 1: On (Operate)
      address: 1100
      scale: 1
      precision: 0
      slave: 1
    - name: "Discharge"  # BT14
      unique_id: "discharge_bt14"
      data_type: int16
      address: 13
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Liquid Line"  # BT15
      unique_id: "liquid_line_bt15"
      data_type: int16
      address: 14
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Suction Gas"  # BT17
      unique_id: "suction_gas_bt17"
      data_type: int16
      address: 16
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Inverter Temperature"
      unique_id: "inverter_temperature"
      data_type: int16
      address: 1047
      input_type: input
      scale: 0.1
      precision: 1
      slave: 1
      # 3.1.9 Additional Heating
    - name: "Status Additional Heating"
      unique_id: "status_additional_heating"
      data_type: int16
      address: 1029
      input_type: input
      scale: 1
      precision: 0
      slave: 1
    - name: "Power Usage Additional Heating"
      unique_id: "power_usage_additional_heating"
      unit_of_measurement: "kW"
      data_type: int16
      device_class: power
      address: 1027
      scale: 0.01
      precision: 1
      slave: 1
    - name: "Maximum Power Usage Additional Heating"
      unique_id: "maximum_power_usage_additional_heating"
      data_type: int16
      device_class: power
      address: 102
      scale: 0.01
      precision: 1
      slave: 1
    - name: "Fuse Size"
      unique_id: "fuze_size"
      unit_of_measurement: "A"
      data_type: int16
      device_class: current
      address: 103
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
    - name: "Current Phase 1"  # BE1
      unique_id: "current_be1"
      data_type: uint32
      address: 50
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Current Phase 2"  # BE2
      unique_id: "current_be2"
      data_type: uint32
      address: 48
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Current Phase 3"  # BE3
      unique_id: "current_be3"
      data_type: uint32
      address: 46
      scale: 0.1
      precision: 1
      slave: 1
      # 3.1.10 Circulation Pumps
    - name: "Operating Mode Heating Pump"
      unique_id: "operating_mode_heating_pump"
      data_type: int16
      # 0: Auto, 1: Manual
      address: 853
      scale: 1
      precision: 0
      slave: 1
    - name: "Heating Pump Speed"  # GP1
      unique_id: "heating_pump_speed"
      unit_of_measurement: "%"
      data_type: int16
      device_class: power_factor
      address: 1102
      scale: 1
      precision: 0.1
      slave: 1
    - name: "Heating Pump Speed (Manual)"
      unique_id: "heating_pump_speed_manual"
      data_type: int16
      address: 218
      scale: 1
      precision: 0.1
      slave: 1
    - name: "Brine Pump Speed"  # GP2
      unique_id: "brine_pump_speed"
      data_type: int16
      address: 1104
      scale: 1
      precision: 0.1
      slave: 1
    - name: "Brine Pump Speed (Manual)"
      unique_id: "brine_pump_speed_manual"
      data_type: int16
      address: 222
      scale: 1
      precision: 0.1
      slave: 1
      # 3.1.12 Statistics
    - name: "Number Of Starts (Compressor)"
      unique_id: "number_of_starts_compressor"
      data_type: int16
      address: 1534
      input_type: input
      scale: 1
      precision: 0
      state_class: total_increasing
      slave: 1
    - name: "Operating Time (Total)"
      unique_id: "operating_time_total"
      data_type: int16
      address: 1536
      input_type: input
      scale: 1
      precision: 0
      slave: 1
    - name: "Operating Time (Hot Water)"
      unique_id: "operating_time_hot_water"
      data_type: int16
      address: 1538
      input_type: input
      scale: 1
      precision: 0
      slave: 1
    - name: "Flow Hot Water (Compressor)"
      unique_id: "flow_hot_water_compressor"
      unit_of_measurement: "kWh"
      data_type: int16
      device_class: energy
      address: 1583
      input_type: input
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Flow Hot Water (Total)"
      unique_id: "flow_hot_water_total"
      data_type: int16
      address: 1575
      input_type: input
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Flow Heating (Compressor)"
      unique_id: "flow_heating_compressor"
      data_type: int16  # No idea what this should be
      address: 1585
      input_type: input
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Flow Heating (Total)"
      unique_id: "flow_heating_total"
      address: 1577
      input_type: input
      scale: 0.1
      precision: 1
      slave: 1
      # To bo categorised
    - name: "Active Alarm"
      unique_id: "active_alarm"
      address: 2195
      input_type: input
      scale: 1
      precision: 0
      slave: 1
    - name: "Alarm Number"
      unique_id: "alarm_number"
      address: 1975
      input_type: input
      scale: 1
      precision: 0
      slave: 1
    - name: "Start Compressor"
      unique_id: "start_compressor"
      data_type: int16
      address: 159
      input_type: holding
      scale: 1
      precision: 1
      slave: 1
    - name: "Start Additional Heat"
      unique_id: "start_additional_heat"
      data_type: int16
      address: 97
      input_type: holding
      scale: 1
      precision: 1
      slave: 1
    - name: "Degree Minutes Cooling"
      unique_id: "degree_minutes_cooling"
      data_type: int16
      address: 20
      input_type: holding
      scale: 1
      precision: 1
      slave: 1
    - name: "Reset Alarm"
      unique_id: "reset_alarm"
      address: 22
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
    - name: "Heating Curve"  # 1.30.1
      unique_id: "heating_curve"
      address: 26
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
    - name: "Heating Curve Offset"  # 1.30.1
      unique_id: "heating_curve_offset"
      address: 30
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
    - name: "Supply Temperature Min"  # 1.30.4
      unique_id: "supply_temperature_min"
      address: 34
      input_type: holding
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Supply Temperature Max"  # 1.30.6
      unique_id: "supply_temperature_max"
      address: 38
      input_type: holding
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Own Curve"  # 1.30.7
      unique_id: "own_curve"
      address: 39  # 39-45
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
    - name: "Flow Sensor (BF1)"
      unique_id: "flow_sensor_bf1"
      unit_of_measurement: "l/min"
      data_type: int16
      address: 40
      input_type: input
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Start Temperature Hot Water"
      unique_id: "start_temperature_hot_water"
      address: 59
      input_type: holding
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Stop Temperature Hot Water"
      unique_id: "stop_temperature_hot_water"
      address: 63
      input_type: holding
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Period Time Heating"  # unclear unit, hours per day?
      unique_id: "period_time_heating"
      unit_of_measurement: "h"
      address: 92
      input_type: holding
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Period Time Hot Water"  # unclear unit, hours per day?
      unique_id: "period_time_hot_water"
      address: 93
      input_type: holding
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Period Time Cooling"  # unclear unit, hours per day?
      unique_id: "period_time_cooling"
      address: 94
      input_type: holding
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Start Temperature Cooling"
      unique_id: "start_temperature_cooling"
      address: 183
      input_type: holding
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Stop Temperature Heating"
      unique_id: "stop_temperature_heating"
      address: 184
      input_type: holding
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Stop Temperature Additional Heating"
      unique_id: "stop_temperature_additional_heating"
      address: 185
      input_type: holding
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Lower Room Temperature Alarm"
      unique_id: "lower_room_temperature_alarm"
      address: 196
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
    - name: "Lower Hot Water Temperature Alarm"
      unique_id: "lower_hot_water_temperature_alarm"
      address: 197
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
    - name: "Operating Mode"  # 4.1
      # 0: auto, 1: manual, 2: additional heating only
      unique_id: "operating_mode"
      address: 237
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
    - name: "Allow Additional Heating (Manual)"  # 4.1
      unique_id: "allow_additional_heating_manual"
      address: 180
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
    - name: "Allow Heating (Manual)"  # 4.1
      unique_id: "allow_heating_manual"
      address: 181
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
    - name: "Allow Cooling (Manual)"  # 4.1
      unique_id: "allow_cooling_manual"
      address: 182
      input_type: holding
      scale: 1
      precision: 0
      slave: 1
    - name: "Total Run Time Additional Heat"  # Value does not align with UpLink?
      unique_id: "total_run_time_additional_heat"
      data_type: int32
      address: 1025
      input_type: input
      scale: 0.1
      precision: 1
      slave: 1
    - name: "Compressor Statistics (EP14)"
      unique_id: "compressor_statistics_ep14"
      data_type: int32
      address: 1087
      input_type: input
      scale: 1
      precision: 0
      slave: 1
Hey this great! By far very extensive. I too have a similar heat pump. However I didn’t use all the registers as some are not necessary for my purposes.
Have you been able to write to the Pump?
I have some different values for some of the registers, maybe because I have the S1255?
  - name: "Heatpump - Priority"
    # 10: Off, 20: Hot Water, 30: Heat, 40: Pool, 60: Cooling
    address: 1028
    scale: 1
    precision: 0
    slave: 1
You have 50 for Cooling.
  - name: "Heatpump - Hot Water Demand"
    data_type: int16
    # 0: Small, 1: Medium, 2: Large, 4: Smart Control
    address: 56
    scale: 1
    precision: 0
    slave: 1
I get 4 for Smart Control.
Check this list of Modbus registers. At least some from the common registers should work for you. https://partner.nibe.eu/nibedocuments/29795/M12676EN.pdf
I’ve been able to get a good amount of data from my Nibe S2125 now into home assistant; purely using modbus and the NIBE SMO S40 control unit.
You can enable modbus in menu 7.5.9 - set setting to “on” and your control unit will communicate modbus via the LAN. check the ip via DHCP (this can be found in menu 5.2.2).
Below the general registry list I could pull from the unit:
Titel	Type register	Register	Deel­factor	Eenheid	Grootte van varia­bele	Min. waarde	Max. waarde	Stan­daard­waarde
Huidige buiten­tempe­ratuur (BT1)	MODBUS_INPUT_REGISTER	**1**	10	°C	2	0	0	0
Graad­minuten	MODBUS_HOLDING_REGISTER	**11**	10	GRD MIN	3	-30000	30000	0
Roomsensor 1-1	MODBUS_INPUT_REGISTER	**26**	10	°C	2	0	0	0
Gemid­delde tempera­tuur (BT1)	MODBUS_INPUT_REGISTER	**37**	10	°C	2	0	0	0
Externe aanvoer­leiding (BT25)	MODBUS_INPUT_REGISTER	**39**	10	°C	2	0	0	0
Retour­leiding (BT71)	MODBUS_INPUT_REGISTER	**88**	10	°C	2	0	0	0
Be­rekende toevoer klimaat­systeem 1	MODBUS_INPUT_REGISTER	**1017**	10	°C	2	0	0	0
Be­drijfs­stand interne bijver­warming	MODBUS_INPUT_REGISTER	**1029**	1		4	0	0	0
Externe cv-pomp­ (GP10) status	MODBUS_INPUT_REGISTER	**1066**	1		4	0	0	0
Retour­leiding (EB101-BT3)	MODBUS_INPUT_REGISTER	**1475**	10	°C	2	0	0	0
Aanvoer­leiding (EB101-BT12)	MODBUS_INPUT_REGISTER	**1478**	10	°C	2	0	0	0
Buiten­temp. (EB101-BT28)	MODBUS_INPUT_REGISTER	**1621**	10	°C	2	0	0	0
Verdam­per (EB101-BT16)	MODBUS_INPUT_REGISTER	**1622**	10	°C	2	0	0	0
Snel­heid circu­latie­pomp verwarmings­systeem (GP1)	MODBUS_INPUT_REGISTER	**1636**	1	%	4	0	0	0
Lage druk (EB101-BP8)	MODBUS_INPUT_REGISTER	**1802**	10	bar	2	0	0	0
Huidige compres­sorfre­quentie (EB101)	MODBUS_INPUT_REGISTER	**1803**	10	Hz	2	0	0	0
Beveiligingsmodus (EB101)	MODBUS_INPUT_REGISTER	**1804**	1		5	0	0	0
Gewen­ste compres­sorfre­quentie (EB101)	MODBUS_INPUT_REGISTER	**1854**	1	Hz	4	0	0	0
Alarm­nummer	MODBUS_INPUT_REGISTER	**1975**	1		2	0	0	0
Below the configuration.yaml for it. (power consumption does not seem to work on the s2125)
modbus:
   - name: "Nibe2125"
     type: tcp
     host: xxx.xxx.xxx.xxx
     port: 502
     sensors:
          # 3.1.2 Overview
        - name: "wp Operating Prioritisation"
          unique_id: "wp_operating_prioritisation"
          address: 1028
          scale: 1
          precision: 0
          slave: 1
        - name: "wp Power Usage"
          unique_id: "wp_power_usage"
          data_type: int16
          device_class: power
          address: 2166
          input_type: input
          scale: 1
          precision: 0
          slave: 1
        - name: "wp Outdoortemperatur (BT1)"
          unique_id: "wp_outdoor_temp_bt1"
          data_type: int16
          address: 1
          count: 1
          slave: 1
          precision: 1
          input_type: input
          scale: 0.1
          scan_interval: 60
        - name: "wp AVG Outdoortemperatur (BT1)"
          unique_id: "wp_avg_outdoor_temp_bt1"
          data_type: int16
          address: 37
          count: 1
          slave: 1
          precision: 1
          input_type: input
          scale: 0.1
          scan_interval: 60
        - name: "wp Room temperature 1 (BT50)"
          unique_id: "wp_room_temp_bt50"
          data_type: int16
          address: 26
          count: 1
          slave: 1
          precision: 1
          input_type: input
          scale: 0.1
          scan_interval: 60
          # To be categorised
        - name: "wp Externe cv-pomp status"
          unique_id: "wp_Externe_cv-pomp_status"
          address: 1066
          input_type: input
          scale: 1
          precision: 0
          slave: 1
        - name: "wp Active Alarm"
          unique_id: "wp_active_alarm"
          address: 2195
          input_type: input
          scale: 1
          precision: 0
          slave: 1
        - name: "wp Alarm Number"
          unique_id: "wp_alarm_number"
          address: 1975
          input_type: input
          scale: 1
          precision: 0
          slave: 1
        - name: "wp Hot water Top (BT7)"
          unique_id: "wp_hot_water_top_bt7"
          data_type: int16
          address: 8
          count: 1
          slave: 1
          precision: 1
          input_type: input
          scale: 0.1
          scan_interval: 60
        - name: "wp Hot water charging (BT6)"
          unique_id: "wp_hot_water_charging_bt6"
          data_type: int16
          address: 9
          count: 1
          slave: 1
          precision: 1
          input_type: input
          scale: 0.1
          scan_interval: 60
        - name: "wp External supply line (BT25)"
          unique_id: "wp_external_supply_line_bt25"
          data_type: int16
          address: 39
          count: 1
          slave: 1
          precision: 1
          input_type: input
          scale: 0.1
          scan_interval: 60
        - name: "wp Return temperature (BT71)"
          unique_id: "wp_return_temp_bt71"
          data_type: int16
          address: 88
          count: 1
          slave: 1
          precision: 1
          input_type: input
          scale: 0.1
          scan_interval: 60
        - name: "wp Flow sensor (BF1)"
          unique_id: "wp_flowsensor_bf1"
          data_type: int16
          address: 40
          count: 1
          slave: 1
          precision: 1
          input_type: input
          scale: 0.1
          scan_interval: 60
        - name: "wp Compressor Status"
          unique_id: "wp_compressor_status"
          address: 1100
          scale: 1
          precision: 0
          slave: 1
        - name: "wp Snelheid circulatiepomp verwarmingssysteem (GP1)"
          unique_id: "wp_Snelheid_circulatiepomp_verwarmingssysteem_(GP1)"
          data_type: int16
          address: 1636
          count: 1
          slave: 1
          precision: 1
          input_type: input
          scale: 1
          scan_interval: 60
        - name: "wp Degree minutes"
          unique_id: "wp_degree_minutes"
          data_type: int16
          address: 11
          scale: 0.1
          precision: 1
          slave: 1
        - name: "wp Limit Degree minutes"
          unique_id: "wp_limit_degree_minutes"
          data_type: int16
          address: 18
          scale: 0.1
          precision: 1
          slave: 1
Hey Victor, have you been able to “write” to the pump or just get values?
What seems to be the power consumption issue?
I created a “Riemann sum integral” integration and it shows up in my energy tab.
The S2125 icw the SMO40 does not seem to have it available; I do not see it in my exported registry, and the ‘common registry’ list address in the pdf does not provide any value.
I also do not see it in the display interface on the SMO40.
I’d love to have it.
Do you have a power consumption display in the SMO40?
My system is different and doesn’t have an SMO40
Seems on my setup the power measurement points were not enabled. But there seems to be a menu under 3.3
@RemonG Thanks. copied/pasted your yaml for my SMO S40 + S2125 and it mostly worked.
However, some show as unavailable. Two if the more interesting ones amoung them.
PS: I just activated the NIBE today. Spent all evenings last week hooking it up.
I would not mind having someone experienced to PM some torrent of questions on settings.
I never got the power working, doesn’t seem part of the default internals.
The Compressor state you can use this:
- name: “wp Compressor Status”
unique_id: “wp_compressor_status”
address: 1484
scale: 1
precision: 0
slave: 1
Tip start all your unique id’s with ‘wp’.
Thanks. That new address also gives unavailable.
How do you get those RAW modbus details dumped like you have on your first post in this thread?
Edit: the 1484 did work, but copy/pasting it from the text above give left-right (open/close) high double quotes instead of the programmes straight quotes.
Pity of the power use. I do also see in the manual you can get the AUX to generate a energy pulses. Both for electric energy and for heat energy, so you can calculate COP. I may build a ESP Home device for that later.
I wonder though, maybe if I already activate the AUX, it will show up in MODBUS. Again, how do you get those RAW modbus details dumped like you have on your first post in this thread?
Stick in an USB stick in the port (hidden behind the S40 plastic label), or remove the cover of the smo.
Insert a USB-stick in your SMO S40 display and go to meny 7.5.9 MODBUS TCP/IP.
Now you can export a list of all available Modbus addresses for your installation.
OK, strange. I have double quotes " in all my setup. That works fine.
Have you guys seen this???
https://www.home-assistant.io/integrations/nibe_heatpump
This is a new integration with the latest core update.
Supported devices:
  • F1145
  • F1155
  • F1245
  • F1255
  • F1345
  • F1355
  • F370
  • F470
  • F730
  • F750
  • SMO20
  • SMO40
  • VVM225
  • VVM310
  • VVM320
  • VVM325
  • VVM500
Sadly no S series!!! :cry:
That’s sad, ask the devs?
But you have the SMO40?
Why don’t you try it and post results. Maybe even the code and we can see what can be done.
I just upgraded to ha 2022. 10.1, now modbus is having issues connecting to the nibe IP (fixed address) .
Anyone else?
Mine is working fine. Post the yaml part for your heat pump configuration.