So at the top of page 10 in both the inverter manuals they mention that we need to query the inverter for the correct Slave ID.
It says to do this we need to read register 42019 with a slave ID as 1. Then once we have the slave ID we can use that to poll the rest of the registers.
We can use the TCP view software.
Open the software and go to configure in the menu at the top.
Select “master”
And the mode as TCP, then put in the IP address of the inverter.
then back on the main page set the following
Variable Type: Holding Registers Start Register: 2019 (you dont need the 4 because the software already knows you are trying to read a holding register so the 4 is implied) Length: 4 (going by the manual, it seems to imply we want 4 registers returned) Display as: unsigned ints
and finally make sure they address on the right is set to 1!
You should then be able to hit read and hopefully the poll will succeed and in register +3 we will have the slave ID of the unit.
Once you have the correct slave ID you can use this software to poll any available registers and its very quick to use and test. Once you know you can successfully read registers then you can set up your home assistant config to match.
Thanks very much for the extra effort you put in for me Techs. Sorry I took so long to come back. Had some other problems to deal with. Anyway, it did get me to a point where I managed to Read OK, but have issues with the results now. All values returned 65535. Does that mean anything to you?
Omg I just realised I misread the register number. The address we need to poll is 42109 not 42019. Lol sorry about that. Try the correct address and hopefully the data should make sense!
Hmm I don’t understand why all data is like that. We are successfully polling the registers of the inverter and I can’t see anything we have missed in the manual. Are you getting those same results on both inverters?
The other inverter just doesn’t respond. I get an error “Poll 0 Time Out occurred”. Not sure if the modbus is exposed on that one as I noticed the other day my other monitoring service also doesn’t read from it.
Hi Cheesewine
there are few different modbus function if you would like to read 40037 that means you are working with holding register type. In the sensor declaration, no need to write the entire number but only 37 because the “group” 40000 is already defined by the argument: register_type
for more information related modbus have a look on this site: Data Communication Solutions | Simply Modbus Software
Anyway try the following code:
sensor:
- platform: modbus
scan_interval: 10 #scan every 10 secs
registers:
- name: SI6ModelID
hub: SI6
slave: 1 #with TCP should be optional
register: 37 # if not working try 36 some modbus map starting from 0 instead of 1
register_type: holding
count: 1
- name: SB5ModelID
hub: SB5000
slave: 1
register: 37
register_type: holding
count: 1
Thanks All. I tried all the various variations but still have no success. Although I do have a different error message now. Considering the errors and the tips @techs gave then I’m getting the feeling the problem is in properly connecting to modbus in the first place rather than reading the registers. Does this error mean anything to anyone?
Error while setting up platform modbus
Traceback (most recent call last):
File "/usr/src/homeassistant/homeassistant/helpers/entity_platform.py", line 126, in _async_setup_platform
SLOW_SETUP_MAX_WAIT)
File "/usr/local/lib/python3.7/asyncio/tasks.py", line 416, in wait_for
return fut.result()
File "/usr/local/lib/python3.7/concurrent/futures/thread.py", line 57, in run
result = self.fn(*self.args, **self.kwargs)
File "/usr/src/homeassistant/homeassistant/components/modbus/sensor.py", line 92, in setup_platform
hub = hass.data[MODBUS_DOMAIN][hub_name]
KeyError: 'default'
have u done any changes exept enable modbus udp and tcp at the inverter via sunny explorer ?
I try to connect to my stp 10000tl-20 with no luck so far .The Ip Adresses are choosen automaticaly so i try to get to the modbus via my sunny homemanager 2.0.
To enable this I only activated modbus tcp on the inverter. You must use the IP address from the inverter however.
I also have a home manager 2.0 setup. and I was not able to get any modbus communication with home Manager via tcp going so far. But I realized that the HomeManager 2.0 sends udp multicast messages every second with data from the built in energy meter.
So my approach is twofold.
I use a Node Red Flow to intercept the udp muticast messages from Home Manager 2.0 to get Energy in and out (current values and meters). see here: SMA Energy Meter in Home Assistant
I use the HA modbus integration to read the inverter.
So to get this to work you need to use the IP address from your inverter in the host section.
@chris_ka thankyou. I just tried slave 3 and it finally started returning some sort of data. Although the data ins’t totally meaningful. I’m getting -1 as the result. For some other registers I’m getting some sort of number other than -1 but none are correct. Is it the “count” or something else I should be looking at?
You have the password to log in as installer/plumber to change settings
Get the IP address of the inverter in your local Network. At daytime when the Inverter is sending data you can check your router to find the ip address. (note it down)
Start Sunny Explorer and connect to your Inverter. Go to Settings and open External Communication: You should find something similar to this
Note down the UnitID and TCP-Server port. Ensure that TCP-Server is active. If not change it!
Now get this document: http://files.sma.de/dl/2585/WEBBOX-MODBUS-TB-en-19.pdf
and have a look on page 28 Section 5.4.1 common Addresses of all SMA Devices. here you find the values for all relevant registers (ADR), the count (CNT) and their description.
configure modbus integration in Home Manager configuration
modbus:
name: sma
type: tcp
host: 192.168.178.101 # use the ip address for your inverter as mentioned in the text
port: 502 # use the port you saw in sunny explorer
configure modbus sensors in HA
sensors:
- platform: modbus
scan_interval: 30
registers:
- name: Gesamtertrag
hub: sma
unit_of_measurement: kWh # see register description in section 5.4.1 of the document
slave: 3 # use the UnitID you found in Sunny Explorer
register: 30531 # use a register from section 5.4.1 of the document
register_type: input # all registers starting with 3 need to have the type input
count: 2 # use the correct count for the register see section 5.4.1 of the document
Ah turns out getting the slave number, register and count right as per the SMA specs right can lead to point 7.
All seems to be working well except for a couple of registers such as model ID. Maybe my model is actually -1. in any case, it’ unimportant as the other values are working as expected.
Just noting that I fount there are 2 different sets of Sunny Island (SI) register specifications. The Excel one that is found on the SMA website seems to be only partially correct which this one http://files.sma.de/dl/2585/WEBBOX-MODBUS-TB-en-19.pdf has registers that mostly work.
I use the following. This gets data out of the SMA Tripower 8.0. Not all registers seem to have the right variables I think. And if the power generated by the solar panels is to low or none, the most of the registers will go to the maximum value in the variable or so. Few still make sense like SMA total.
Does anyone else has the same experience?
configuration.yaml:
modbus:
type: tcp
host: 192.168.15.35
port: 502
sensor.yaml
- platform: modbus
scan_interval: 10
registers:
- name: SMA Power L1
unit_of_measurement: kW
slave: 3
register: 30777
count: 2
data_type: uint
scale: 0.001
precision: 2
- name: SMA Power L2
unit_of_measurement: kW
slave: 3
register: 30779
count: 2
data_type: uint
scale: 0.001
precision: 2
- name: SMA Power L3
unit_of_measurement: kW
slave: 3
register: 30781
count: 2
data_type: uint
scale: 0.001
precision: 2
- name: SMA Stroom L1
unit_of_measurement: A
slave: 3
register: 30977
count: 2
data_type: uint
scale: 0.001
precision: 2
- name: SMA Stroom L2
unit_of_measurement: A
slave: 3
register: 30979
count: 2
data_type: uint
scale: 0.001
precision: 2
- name: SMA Stroom L3
unit_of_measurement: A
slave: 3
register: 30981
count: 2
data_type: uint
scale: 0.001
precision: 2
- name: SMA Spanning L1
unit_of_measurement: V
slave: 3
register: 30783
count: 2
data_type: uint
scale: 0.01
precision: 1
- name: SMA Spanning L2
unit_of_measurement: V
slave: 3
register: 30785
count: 2
data_type: uint
scale: 0.01
precision: 1
- name: SMA Spanning L3
unit_of_measurement: V
slave: 3
register: 30787
count: 2
data_type: uint
scale: 0.01
precision: 1
- name: SMA Netfrequentie
unit_of_measurement: Hz
slave: 3
register: 30803
count: 2
data_type: uint
scale: 0.01
precision: 2
- name: SMA power
unit_of_measurement: k
slave: 3
register: 30775
count: 2
data_type: int
scale: 0.001
precision: 2
- name: SMA Total
unit_of_measurement: kW
slave: 3
register: 30529
count: 2
data_type: uint
scale: 0.001
precision: 2
- name: SMA Today
unit_of_measurement: kWh
slave: 3
register: 30535
count: 2
data_type: uint
scale: 0.001
precision: 2
- name: SMA device type 9347 = 8.0
slave: 3
register: 30053
count: 2
data_type: int
- name: SMA grid relay 51=Closed 311= Open
slave: 3
register: 30217
count: 2
data_type: int
And would colde like the code in the bottom of this message be a good catch to go to ‘0’ in stead of high values?
# SMA over modbus
modbus:
type: tcp
host: 192.168.178.171
port: 502
and this in sensors
- platform: modbus
scan_interval: 30
registers:
- name: Gesamtertrag
hub: sma
unit_of_measurement: kWh # see register description in section 5.4.1 of the document
slave: 3 # use the UnitID you found in Sunny Explorer
register: 30531 # use a register from section 5.4.1 of the document
register_type: input # all registers starting with 3 need to have the type input
count: 2 # use the correct count for the register see section 5.4.1 of the document
and get this error in my log
Traceback (most recent call last):
File "/usr/src/homeassistant/homeassistant/helpers/entity_platform.py", line 179, in _async_setup_platform
await asyncio.wait_for(asyncio.shield(task), SLOW_SETUP_MAX_WAIT)
File "/usr/local/lib/python3.7/asyncio/tasks.py", line 442, in wait_for
return fut.result()
File "/usr/local/lib/python3.7/concurrent/futures/thread.py", line 57, in run
result = self.fn(*self.args, **self.kwargs)
File "/usr/src/homeassistant/homeassistant/components/modbus/sensor.py", line 129, in setup_platform
hub = hass.data[MODBUS_DOMAIN][hub_name]
KeyError: 'sma'
I can login to the webinterface just fine. I came here bc the standard SMA integration was not working, but am having issues with this as well. Anyone care to shed some light on this?