I need help to create the code to interact with my LG ducted system.
I currently have a Bail Industrie system controlling my LG air conditioning (UUD3 U30) with its indoor unit UM36F N20. I would like to replace this system with an ESP32 to integrate it into Home Assistant for controlling the heating with other thermostats and automated management. This system uses an RS485 module (Intesis LG-RC-MBS-1) that is connected to the LG bus. There is LG PREMTB100 / RS3 too that display infos and set parameters for the LG outdoor unit.
I have an ESP32-S3-6CH-RELAY (https://www.waveshare.com/wiki/ESP32-S3-Relay-6CH ) which has relays (which will allow me to control my air vents) and also an RS485 interface on TX GPIO17 & RX GPIO18, allowing me to connect the Intesis module to it.
I am unable to figure out how to create this code in ESPHome, although I know it is possible. I have the register information for controlling and retrieving sensors from the module here: https://cdn.chipkin.com/assets/uploads/2018/feb/16-01-14-46_intesisbox_lg-rc-mbs-1_user_manual_en.pdf (pages 7, 8, 9).
Here is an idea of the code, but it doesn’t work :
esphome:
name: lg_intesis_complete
platform: esp32
board: esp32-s3-devkitc-1
# UART for RS485
uart:
tx_pin: GPIO17 # TX pin ESP32 board
rx_pin: GPIO18 # RX pin ESP32 board
baud_rate: 9600
parity: NONE
stop_bits: 1
# Modbus RTU
modbus:
id: modbus1
# On/Off Control
switch:
- platform: modbus_controller
modbus_id: modbus1
name: "HVAC Power"
address: 1
register_type: holding
register: 0 # Register for On/Off
command_on_value: 1
command_off_value: 0
# Mode selection (Auto, Heat, Cool, etc.)
select:
- platform: modbus_controller
modbus_id: modbus1
name: "HVAC Mode"
address: 1
register_type: holding
register: 1 # Register for the mode
options:
- "Auto"
- "Heat"
- "Cool"
- "Fan"
- "Dry"
# Fan speed selection with Lambda
- platform: modbus_controller
modbus_id: modbus1
name: "Fan Speed"
address: 1
register_type: holding
register: 2 # Register for fan speed
options:
- "Auto"
- "Low"
- "Medium"
- "High"
lambda: |-
if (x == 0) return "Auto";
if (x <= 2) return "Low"; // Positions 1 and 2
if (x <= 5) return "Medium"; // Positions 3, 4, 5
if (x <= 7) return "High"; // Positions 6 and 7
return "Unknown";
# Temperature setting
number:
- platform: modbus_controller
modbus_id: modbus1
name: "Set Temperature"
address: 1
register_type: holding
register: 4 # Register for target temperature
unit_of_measurement: "°C"
min_value: 16
max_value: 30
step: 0.5
# Sensors for monitoring
sensor:
# Room temperature
- platform: modbus_controller
modbus_id: modbus1
name: "Room Temperature"
address: 1
register_type: input
register: 5 # Register for room temperature
unit_of_measurement: "°C"
accuracy_decimals: 1
filters:
- multiply: 0.1 # Conversion from decicelsius -> celsius
# Current setpoint temperature
- platform: modbus_controller
modbus_id: modbus1
name: "Setpoint Temperature"
address: 1
register_type: input
register: 4 # Register for target temperature
unit_of_measurement: "°C"
accuracy_decimals: 1
filters:
- multiply: 0.1
# Compressor status
- platform: modbus_controller
modbus_id: modbus1
name: "Compressor Status"
address: 1
register_type: input
register: 53 # Register for compressor status
filters:
- lambda: |-
if (x == 0) return "Off";
if (x == 1) return "To Off";
if (x == 2) return "To On";
if (x == 3) return "On";
return "Unknown";
# Binary sensor for alarms
binary_sensor:
- platform: modbus_controller
modbus_id: modbus1
name: "HVAC Alarm"
address: 1
register_type: input
register: 10 # Register for alarms
filters:
- lambda: |-
return x == 1; # Activated if an alarm is present
Can someone help me? Thank you very much.
Anoxym1
(Anoxym)
December 28, 2024, 2:11pm
2
I want to use climate to get this in HA but don’t know how to integrate it with modbus code :
Karosm
(Karosm)
December 28, 2024, 5:28pm
3
Your code is missing modbus controller component.
Anoxym1
(Anoxym)
December 28, 2024, 6:15pm
4
Ok thanks I have added :
modbus_controller:
- id: modbus_device
address: 0x1 ## address of the Modbus slave device on the bus
modbus_id: modbus1
setup_priority: -10
But I don’t know which value to set for setup_priority ?
Now I have errors here :
# On/Off Control
switch:
- platform: modbus_controller
modbus_controller_id: modbus1
name: "HVAC Power"
address: 1
register_type: holding
register: 0 # Register for On/Off
command_on_value: 1
command_off_value: 0
[register] is an invalid option for [switch.modbus_controller]. Did you mean [register_type]?
[command_on_value] is an invalid option for [switch.modbus_controller]. Did you mean [command_topic], [command_retain]?
Karosm
(Karosm)
December 28, 2024, 6:27pm
5
Register 0 in decimal doesn’t exist.
May I suggest to remove all the number/select/switch from your yaml until you have successful communication with your devices input registers.
Anoxym1
(Anoxym)
December 29, 2024, 1:40pm
6
Is this good ? :
esphome:
name: lg_intesis_complete
platform: esp32
board: esp32-s3-devkitc-1
# Enable logging
logger:
level: INFO
# level: DEBUG
# UART for RS485
uart:
tx_pin: GPIO17 # TX pin ESP32 board
rx_pin: GPIO18 # RX pin ESP32 board
baud_rate: 9600
parity: NONE
stop_bits: 1
# Modbus RTU
modbus:
id: modbus1
modbus_controller:
- id: modbus_device
address: 0x1 ## address of the Modbus slave device on the bus
modbus_id: modbus1
setup_priority: -10
# Switch for On/Off control
switch:
- platform: modbus_controller
modbus_controller_id: modbus_device
name: "HVAC On/Off"
id: hvac_on_off
address: 0 # Protocol register address for On/Off
register_type: holding
write_lambda: |-
if (state) {
return 1; // ON value
} else {
return 0; // OFF value
}
Karosm
(Karosm)
December 29, 2024, 1:54pm
7
It’s opposite to my suggestion, so what can I answer?
Just leave few input registers like these:
Karosm
(Karosm)
December 29, 2024, 2:12pm
8
Ignore previous post.
The protocol sheet you linked describes holding registers, not input!
Also there are several errors on you code…
Edit: it also describes 8N2 communication (8 data bits, no parity and 2 stop bit)
Try with this:
uart:
id: uartx
tx_pin: GPIO17 # TX pin ESP32 board
rx_pin: GPIO18 # RX pin ESP32 board
baud_rate: 9600
parity: NONE
stop_bits: 2
modbus:
id: modbus1
uart_id: uartx
modbus_controller:
- id: modbus_device
address: 0x1 ## address of the Modbus slave device on the bus
modbus_id: modbus1
update_interval: 10s
sensor:
- platform: modbus_controller
modbus_controller_id: modbus_device
name: "Fan Speed"
id: fan_speed
register_type: holding
address: 0x0002
value_type: U_WORD
Anoxym1
(Anoxym)
December 29, 2024, 5:20pm
9
I got :
[18:16:30][D][modbus_controller:040]: Modbus command to device=1 register=0x02 no response received - removed from send queue
But when my current system is connected to the Intesis module I received info :
[18:48:42][D][modbus_controller:040]: Modbus command to device=1 register=0x02 no response received - removed from send queue
[18:48:51][V][modbus_controller:232]: Updating modbus component
[18:48:51][V][modbus_controller:199]: Range : 2 Size: 1 (3) skip: 0
[18:48:51][V][modbus_controller:044]: Sending next modbus command to device 1 register 0x02 count 1
[18:48:51][V][modbus:223]: Modbus write: 01.03.00.02.00.01.25.CA (8)
[18:48:51][V][modbus_controller:569]: Command sent 3 0x2 1 send_count: 1
[18:48:51][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[18:48:51][V][modbus:042]: Stop waiting for response from 1
[18:48:51][V][modbus_controller:044]: Sending next modbus command to device 1 register 0x02 count 1
[18:48:51][V][modbus:223]: Modbus write: 01.03.00.02.00.01.25.CA (8)
[18:48:51][V][modbus_controller:569]: Command sent 3 0x2 1 send_count: 2
[18:48:51][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[18:48:51][V][modbus:042]: Stop waiting for response from 1
[18:48:51][V][modbus_controller:044]: Sending next modbus command to device 1 register 0x02 count 1
[18:48:51][V][modbus:223]: Modbus write: 01.03.00.02.00.01.25.CA (8)
[18:48:51][V][modbus_controller:569]: Command sent 3 0x2 1 send_count: 3
[18:48:51][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[18:48:51][V][modbus:042]: Stop waiting for response from 1
[18:48:51][V][modbus_controller:044]: Sending next modbus command to device 1 register 0x02 count 1
[18:48:51][V][modbus:223]: Modbus write: 01.03.00.02.00.01.25.CA (8)
[18:48:51][V][modbus_controller:569]: Command sent 3 0x2 1 send_count: 4
[18:48:52][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[18:48:52][V][modbus:042]: Stop waiting for response from 1
[18:48:52][V][modbus_controller:044]: Sending next modbus command to device 1 register 0x02 count 1
[18:48:52][V][modbus:223]: Modbus write: 01.03.00.02.00.01.25.CA (8)
[18:48:52][V][modbus_controller:569]: Command sent 3 0x2 1 send_count: 5
[18:48:52][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[18:48:52][V][modbus:042]: Stop waiting for response from 1
[18:48:52][D][modbus_controller:040]: Modbus command to device=1 register=0x02 no response received - removed from send queue
[18:48:54][W][modbus:125]: Modbus CRC Check failed! 9255!=100
[18:48:54][V][modbus:026]: Clearing buffer of 8 bytes - parse failed
[18:48:54][W][modbus:125]: Modbus CRC Check failed! 3071!=00
[18:48:54][V][modbus:026]: Clearing buffer of 5 bytes - parse failed
[18:48:54][V][modbus:035]: Clearing buffer of 9 bytes - timeout
[18:48:54][W][modbus:125]: Modbus CRC Check failed! CDB1!=1003
[18:48:54][V][modbus:026]: Clearing buffer of 5 bytes - parse failed
[18:48:55][V][modbus:035]: Clearing buffer of 18 bytes - timeout
[18:48:55][W][modbus:125]: Modbus CRC Check failed! E291!=603
[18:48:55][V][modbus:026]: Clearing buffer of 5 bytes - parse failed
[18:48:55][V][modbus:035]: Clearing buffer of 8 bytes - timeout
[18:48:55][W][modbus:125]: Modbus CRC Check failed! DED8!=801
[18:48:55][V][modbus:026]: Clearing buffer of 8 bytes - parse failed
[18:48:55][V][modbus:035]: Clearing buffer of 2 bytes - timeout
[18:48:56][W][modbus:125]: Modbus CRC Check failed! 9255!=100
[18:48:56][V][modbus:026]: Clearing buffer of 8 bytes - parse failed
[18:48:56][W][modbus:125]: Modbus CRC Check failed! 3071!=00
[18:48:56][V][modbus:026]: Clearing buffer of 5 bytes - parse failed
[18:48:56][V][modbus:035]: Clearing buffer of 9 bytes - timeout
[18:48:56][W][modbus:125]: Modbus CRC Check failed! CDB1!=1003
[18:48:56][V][modbus:026]: Clearing buffer of 5 bytes - parse failed
[18:48:56][V][modbus:035]: Clearing buffer of 18 bytes - timeout
[18:48:57][W][modbus:125]: Modbus CRC Check failed! E291!=603
[18:48:57][V][modbus:026]: Clearing buffer of 5 bytes - parse failed
[18:48:57][V][modbus:035]: Clearing buffer of 8 bytes - timeout
[18:48:57][W][modbus:125]: Modbus CRC Check failed! DED8!=801
[18:48:57][V][modbus:026]: Clearing buffer of 8 bytes - parse failed
[18:48:57][V][modbus:035]: Clearing buffer of 2 bytes - timeout
[18:48:58][W][modbus:155]: Got Modbus frame from unknown address 0x20!
[18:48:58][V][modbus:159]: Clearing buffer of 7 bytes - parse succeeded
[18:48:58][V][modbus:035]: Clearing buffer of 9 bytes - timeout
[18:48:58][W][modbus:155]: Got Modbus frame from unknown address 0x20!
[18:48:58][V][modbus:159]: Clearing buffer of 7 bytes - parse succeeded
[18:48:59][V][modbus:035]: Clearing buffer of 9 bytes - timeout
[18:48:59][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[18:49:00][V][modbus:035]: Clearing buffer of 4 bytes - timeout
[18:49:00][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[18:49:01][V][modbus:035]: Clearing buffer of 1 bytes - timeout
It means that the Intesis module does not send data to ESP32?
Karosm
(Karosm)
December 29, 2024, 5:49pm
10
What is “current system”??
Anoxym1
(Anoxym)
December 29, 2024, 5:53pm
11
The bail industrie at the left of the first picture
Karosm
(Karosm)
December 29, 2024, 6:02pm
12
I’m not able to follow your description about your setup that seems to change between posts.
Your yaml on your OP had about 100 errors.
If you run the code I wrote, with your Esp device connected to IntensisBox A+ to A+ and B- to B-, what you get in your esphome log??
Anoxym1
(Anoxym)
December 29, 2024, 6:11pm
13
With your code and the ESP connected to the Intesis module I have :
[18:16:30][D][modbus_controller:040]: Modbus command to device=1 register=0x02 no response received - removed from send queue
Karosm
(Karosm)
December 29, 2024, 6:25pm
14
Then you probably have bad wiring or wrong slave address/baud rate. Check the dip switches for address and baud and your wiring.
Anoxym1
(Anoxym)
December 29, 2024, 6:34pm
15
According to dip switches the address is 32 so 0x20. I have now :
[19:32:01][V][modbus_controller:232]: Updating modbus component
[19:32:01][V][modbus_controller:199]: Range : 2 Size: 1 (3) skip: 0
[19:32:01][V][modbus_controller:044]: Sending next modbus command to device 32 register 0x02 count 1
[19:32:01][V][modbus:223]: Modbus write: 20.03.00.02.00.01.23.7B (8)
[19:32:01][V][modbus_controller:569]: Command sent 3 0x2 1 send_count: 1
[19:32:01][V][modbus_controller:081]: Modbus response queued
[19:32:01][V][modbus:159]: Clearing buffer of 6 bytes - parse succeeded
[19:32:01][V][modbus_controller:089]: Process modbus response for address 0x2 size: 2
[19:32:01][V][modbus_controller:170]: data for register address : 0x2 :
[19:32:01][D][modbus_controller.sensor:025]: Sensor new state: 3.00
[19:32:01][V][sensor:043]: 'Fan Speed': Received new state 3.000000
[19:32:01][D][sensor:094]: 'Fan Speed': Sending state 3.00000 with 0 decimals of accuracy
[19:32:01][V][modbus:035]: Clearing buffer of 4 bytes - timeout
[19:32:01][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[19:32:02][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[19:32:02][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[19:32:03][V][modbus:035]: Clearing buffer of 4 bytes - timeout
[19:32:03][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[19:32:04][V][modbus:035]: Clearing buffer of 1 bytes - timeout
[19:32:04][W][modbus:125]: Modbus CRC Check failed! 9255!=100
[19:32:04][V][modbus:026]: Clearing buffer of 8 bytes - parse failed
So 3 for the fan speed, guess that communication works now. Given that my initial code is incorrect, how can I fix it to control the system using the register values provided in the documentation? Thanks for the help
Karosm
(Karosm)
December 29, 2024, 6:39pm
16
Repeat the sensor code for other addresses you have on your protocol sheet.
but what is this?
Anoxym1
(Anoxym)
December 29, 2024, 6:41pm
17
I don’t know, maybe it’s the other system (bail industrie) that sent data?
Karosm
(Karosm)
December 29, 2024, 6:42pm
18
Ahh, you have that connected… Modbus RTU can have only one master, so you need to disconnect it…
Anoxym1
(Anoxym)
December 29, 2024, 6:52pm
19
Yeah I will remove it
So in example, to power on/off the AC, is this code good ? :
switch:
- platform: modbus_controller
modbus_controller_id: modbus_device
name: "Turn AC On/Off"
id: turn_ac_on_off
register_type: holding
address: 0x0000
lambda: |-
if (x) {
return 1; // Turn ON
} else {
return 0; // Turn OFF
}
Karosm
(Karosm)
December 29, 2024, 7:06pm
20
Try.
I haven’t tried switch with holding registers. Might work even without that lamda, or might need some tuning.