Modbus with Carlo Gavazzi EM24
Hello.
I am trying to configurate some sensors of my electricity meter.
My hardware is a Carlo Gavazzi EM24… which is connected to a Modbus/TCP converter.
I need the modbus register of the EM24.
Is here somebody who has already installed it?
Thank you a lot.
im also stuck with this… did you get it to work?
I got it work. Here you can find my yaml.
modbus:
  - name: zaehler
    type: tcp
    host: x.x.x.x
    port: 502
    sensors:
      - name: L1-N
        unit_of_measurement: V
        slave: 1
        address: 0
        input_type: input
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
        count: 2
        device_class: voltage
      - name: L2-N
        slave: 1
        address: 1
        data_type: int32
        scale: 0.1
        precision: 2
      - name: L3-N
        slave: 1
        address: 3
        data_type: int32
        scale: 0.1
        precision: 2
      - name: L12
        slave: 1
        address: 5
        data_type: int32
        scale: 0.1
        precision: 2
      - name: L23
        slave: 1
        address: 7
        data_type: int32
        scale: 0.1
        precision: 2
      - name: L31
        slave: 1
        address: 9
        data_type: int32
        scale: 0.1
        precision: 2
      - name: L1
        unit_of_measurement: A
        slave: 1
        address: 12
        input_type: input
        data_type: int32
        scale: 0.001
        precision: 2
        swap: word
        count: 2
        device_class: current
      - name: L2
        slave: 1
        address: 13
        data_type: int32
        scale: 0.001
        precision: 2
      - name: L3
        slave: 1
        address: 15
        data_type: int32
        scale: 0.001
        precision: 2
      - name: Gesamt
        unit_of_measurement: kWh
        slave: 1
        address: 61
        data_type: int32
        scale: 0.1
        precision: 2
        device_class: energy
        state_class: total
      - name: W L1
        unit_of_measurement: W
        slave: 1
        address: 17
        data_type: int32
        scale: 0.1
        precision: 2
        device_class: power
      - name: W L2
        slave: 1
        address: 19
        data_type: int32
        scale: 0.1
        precision: 2
        device_class: power
        input_type: input
      - name: W L3
        slave: 1
        address: 21
        data_type: int32
        scale: 0.1
        precision: 2
        device_class: power
        input_type: input
      - name: momentanE
        slave: 1
        address: 39
        data_type: int32
        scale: 0.1
        precision: 2
        count: 2
        device_class: power
For me the addresses looks all wrong. If L1-N and L2-N are both two registers long the addresses muste be have an offset of 2. I had strange values ​​at large consumption.
This is my working yaml file:
modbus:
  - name: zaehler
    type: tcp
    host: XXX.XXX.XXX.XXX
    port: 502
    sensors:
      - name: L1-N
        slave: 1
        address: 0
        input_type: input
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
        count: 2
      - name: L2-N
        slave: 1
        address: 2
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
      - name: L3-N
        slave: 1
        address: 4
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
      - name: L12
        slave: 1
        address: 6
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
      - name: L23
        slave: 1
        address: 8
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
      - name: L31
        slave: 1
        address: 10
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
      - name: L1
        slave: 1
        address: 12
        input_type: input
        data_type: int32
        scale: 0.001
        precision: 2
        swap: word
        count: 2
      - name: L2
        slave: 1
        address: 14
        data_type: int32
        scale: 0.001
        precision: 2
        swap: word
      - name: L3
        slave: 1
        address: 16
        data_type: int32
        scale: 0.001
        precision: 2
        swap: word
      - name: Bezug Netz
        slave: 1
        address: 52
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
        state_class: total
      - name: Einspeisung Netz
        slave: 1
        address: 78
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
        state_class: total
      - name: Leistung L1
        slave: 1
        address: 18
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
        device_class: power
      - name: Leistung L2
        slave: 1
        address: 20
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
        device_class: power
        input_type: input
      - name: Leistung L3
        slave: 1
        address: 22
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
        device_class: power
        input_type: input
      - name: Leistung Gesamt
        slave: 1
        address: 40
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
        count: 2
        device_class: power
You need check hex values in debug log
To see if you need swap or not, etc
It is interesting because my yaml file is also working.
Where should I check hex values in debug log? Can you explain it please?
Thank you
logger:
  logs:
    homeassistant.components.modbus: debug
    pymodbus.client: debug
configuration.yaml
Thanks. I have added it but under Configuration/Log I can`t find any entries?
Supervisor logs
Or in /config/
Hi Martin, all
here is a sample of my config which is working except for sometimes some neg. values when high power is consumed.
Mike
EM24-E1
modbus:
  • name: EM24eth
    type: tcp
    host: 192.168.X.XX
    port: 502
    timeout: 5
    delay: 3
    sensors:
    • name: PG-L1-N
      address: 0x0000
      count: 1
      slave: 30
      precision: 2
      scale: 0.1
    • name: PG-L2-N
      address: 0x0002
      count: 1
      slave: 30
      precision: 2
      scale: 0.1
    • name: PG-W-L1
      address: 0x0012
      count: 1
      slave: 30
      precision: 2
      scale: 0.1
      scan_interval: 5
      device_class: power
    • name: PG-Import-Total
      address: 0x0112
      count: 1
      slave: 30
      precision: 2
      scale: 0.1
    • name: PG-Export-Total
      address: 0x0116
      count: 1
      slave: 30
      precision: 2
      scale: 0.1
Hi there.
At first, thank you for sharing your code!
Its running without any problem on my own network.
One additional question:
I have to add the frequency data.
But its not working.
Tested with swap none, byte, word.
So i have used the followed code snipped.
- name: EM24_Frequency
        unit_of_measurement: Hz
        slave: 1
        address: 55
        input_type: input
        data_type: int16
        scale: 0.1
        precision: 2
        swap: none
        device_class: frequency
Maybe somebody can give me a hint what i’m doing wrong…
Two further power data are working great.
Maybe somebody have to add these, too:
- name: EM24_P Scheinl Aktuell
        unit_of_measurement: VA
        slave: 1
        address: 42
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
        count: 2
        device_class: power
      - name: EM24_P Blindl Aktuell
        unit_of_measurement: VAr
        slave: 1
        address: 44
        data_type: int32
        scale: 0.1
        precision: 2
        swap: word
        count: 2
        device_class: power
Hi all,
this is my Frequency Implementation:
BR
Mike
# PG - Frequency
    - name: PG-Frequency
      address: 0x0033
      count: 1
      slave: 30
      precision: 2
      scale: 0.1
Hi all,
totally new to modbus, and need a hint on interfacing.
My setup will be Wallbox Copper SB <–> Carlo Gavazzi EM340.
How do the modbus-serial or modbus-ethernet interface? The wallbox will probably be Master and the EM340 will be at address 1. What is the interface then? Address 2? Or address-less promiscous listener?
Marek
Did you get this to work? I’m looking for a way to copy the data from my Garlo Gavazzi EM330 connected to Wallbox Pulsar MAX
It’s not working with a EM24-E1-AV5 X
i would expect at least some data for L1-N
modbus:
  • name: Carlo Gavazzi EM24
    type: tcp
    host: 192.168.023.050
    port: 502
    sensors:
    • name: L1-N
      slave: 1
      address: 0
      input_type: input
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
    • name: L2-N
      slave: 1
      address: 2
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
    • name: L3-N
      slave: 1
      address: 4
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
    • name: L12
      slave: 1
      address: 6
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
    • name: L23
      slave: 1
      address: 8
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
    • name: L31
      slave: 1
      address: 10
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
    • name: L1
      slave: 1
      address: 12
      input_type: input
      data_type: int32
      scale: 0.001
      precision: 2
      swap: word
    • name: L2
      slave: 1
      address: 14
      data_type: int32
      scale: 0.001
      precision: 2
      swap: word
    • name: L3
      slave: 1
      address: 16
      data_type: int32
      scale: 0.001
      precision: 2
      swap: word
    • name: Reference network
      slave: 1
      address: 52
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
      state_class: total
    • name: Feeding into the network
      slave: 1
      address: 78
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
      state_class: total
    • name: Power L1
      slave: 1
      address: 18
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
      device_class: power
    • name: Power L2
      slave: 1
      address: 20
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
      device_class: power
      input_type: input
    • name: Power L3
      slave: 1
      address: 22
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
      device_class: power
      input_type: input
    • name: Total power
      slave: 1
      address: 40
      data_type: int32
      scale: 0.1
      precision: 2
      swap: word
      device_class: power
What am I doing wrong here? I removed some of the count variables “count: 2” to get it working. Please help.
[quote=“Tueftler, post:11, topic:353336”]
  - name: Carlo_Gavazzi_EM24
    type: tcp
    host: 10.10.10.215
    port: 502
    sensors:
      - name: L1-N
        slave: 1
        address: 0
        state_class: measurement
        scale: 0.1
        offset: 0
        precision: 2
        data_type: int32
        unique_id: L1-N
        swap: word
      - name: L2-N
        slave: 1
        address: 2
        scale: 0.1
        offset: 0
        precision: 2
        data_type: int32
        unique_id: L2-N
        swap: word
      - name: L3-N
        slave: 1
        address: 4
        scale: 0.1
        offset: 0
        precision: 2
        data_type: int32
        unique_id: L3-N
        swap: word
      - name: L1-L2
        slave: 1
        address: 6
        data_type: int32
        scale: 0.1
        precision: 2
        unique_id: L1-L2
        swap: word
      - name: L2-L3
        slave: 1
        address: 8
        data_type: int32
        scale: 0.1
        precision: 2
        unique_id: L2-L3
        swap: word
      - name: L3-L1
        slave: 1
        address: 10
        data_type: int32
        scale: 0.1
        precision: 2
        unique_id: L3-L1
        swap: word
      - name: L1
        slave: 1
        address: 12
        data_type: int32
        scale: 0.001
        precision: 2
        unique_id: L1
        swap: word
      - name: L2
        slave: 1
        address: 14
        data_type: int32
        scale: 0.001
        precision: 2
        unique_id: L2
        swap: word
      - name: L3
        slave: 1
        address: 16
        data_type: int32
        scale: 0.001
        precision: 2
        unique_id: L3
        swap: word
      - name: Reference network
        slave: 1
        address: 52
        data_type: int32
        scale: 0.1
        precision: 2
        state_class: total
        unique_id: Reference_network
        swap: word
      - name: Feeding into the network
        slave: 1
        address: 78
        data_type: int32
        scale: 0.1
        precision: 2
        state_class: total
        unique_id: Feeding_into_the_network
        swap: word
      - name: Power L1
        slave: 1
        address: 24
        data_type: int32
        scale: 0.1
        precision: 2
        device_class: power
        unique_id: Power_L1
        swap: word
      - name: Power L2
        slave: 1
        address: 26
        data_type: int32
        scale: 0.1
        precision: 2
        device_class: power
        input_type: input
        unique_id: Power_L2
        swap: word
      - name: Power L3
        slave: 1
        address: 28
        data_type: int32
        scale: 0.1
        precision: 2
        device_class: power
        input_type: input
        unique_id: Power_L3
        swap: word
      - name: Total power
        slave: 1
        address: 42
        data_type: int32
        scale: 0.1
        precision: 2
        device_class: power
        unique_id: Total_Power
        swap: word
      - name: Frequency
        slave: 1
        address: 51
        input_type: input
        data_type: int16
        scale: 0.1
        precision: 2
        unique_id: Frequency
        swap: word
You’re welcome :slight_smile:
Hi, i was trying to get my EM24-E1 working in homeassistant via modbus earlier.
I found some of the sensor values here in the thread were not really helpful to my application, hence i will share my implementation below.
some key points to consider:
  • for int32 values you need to use swap: word, because of the different word order in the EM24
  • added scan_interval to values needing quick reaction times for responsive use steering
  • for the actual addresses refer to the following document from Carlo G: EM24-E1-Communication-Protocol
  • can also use 0x to add the hex addresses directly without converting to decimal if you want (havent done it myself below).
- name: EM24-E1
  type: tcp
  host: x.x.x.x
  port: 502
  sensors:
    - name: W L1
      slave: 1
      address: 18
      swap: word
      data_type: int32
      scale: 0.1
      precision: 2
      device_class: power
      input_type: input
      scan_interval: 1
    - name: W L2
      slave: 1
      address: 20
      swap: word
      data_type: int32
      scale: 0.1
      precision: 2
      device_class: power
      input_type: input
      scan_interval: 1
    - name: W L3
      slave: 1
      address: 22
      swap: word
      data_type: int32
      scale: 0.1
      precision: 2
      device_class: power
      input_type: input
      scan_interval: 1
    - name: W L1L2L3
      slave: 1
      address: 40
      swap: word
      data_type: int32
      scale: 0.1
      precision: 2
      device_class: power
      input_type: input
      scan_interval: 1
    - name: to Grid
      unit_of_measurement: KWh
      slave: 1
      address: 78
      swap: word
      data_type: int32
      scale: 0.1
      precision: 2
      device_class: power
      unique_id: to_grid
      input_type: input
      scan_interval: 60
    - name: from Grid
      slave: 1
      address: 52
      swap: word
      data_type: int32
      scale: 0.1
      precision: 2
      device_class: power
      unique_id: from_grid
      input_type: input
      scan_interval: 60
    - name: Frequency
      slave: 1
      address: 51
      input_type: input
      data_type: uint16
      scale: 0.1
      precision: 2
      scan_interval: 1