PZEM-004T Stale or unavailable sensor values
The PZEM sensors recently and often (every few days) stop updating values and remain constant or the sensor values report as unavailable. The ESP itself is still online but the PZEM sensor values are either stale (the same constant value) or report as unknown. I have a software reset button in the config and the sensors recover after a reset, however the consumption data and charts are off in the energy dashboard until I software reset the ESP.
This started recently, maybe in the past month and happens on three separate ESPs. Previously they worked for several months, if not a year before having an issue. Typical issues in the past were caused by removing high voltage input from the PZEM (unplugging monitored device from the wall).
Seems like something in ESPHome changed recently and is causing this. Appears there have been several modbus PRs recently.
Is anyone else having the same issue?
In case anyone else is having this issue, I’ve converted the code to use default ESPHome modbus functions to read from the PZEM-004T directly instead of using the pzemac component. So far it appears to work fine and is self healing, to an extent.
This has two advantages:
  1. The ESP does not need to be restarted if the PZEM is disconnected from high voltage. Meaning, if mains power is removed and returned, the ESP is able to obtain PZEM values without needing to be power cycled or restarted.
  2. This also allows for the ability to detect when the PZEM is not communicating properly by implementing a lambda filter which updates a watchdog. I’ve used this watchdog to automatically software reboot the ESP if the PZEM is offline for more than 30 minutes.
However, the main disadvantage is the yaml config is much larger and harder to follow.
substitutions:
  friendly_name: Matts ESP32
  comment: Power meter for Matts TV equipment, Matts HVAC and Matts Nightstand
  ip_address: 10.10.21.13
  pzem_1: HVAC
  pzem_2: TV_Equip
  pzem_3: Nightstand
  pzem_watchdog_timeout: '30' # PZEM watchdog timeout (in minutes)
  pzem_update: '10' # PZEM update interval in seconds
esphome:
  friendly_name: ${friendly_name}
  comment: ${comment}
esp32:
  board: wemos_d1_mini32
  # board: mhetesp32devkit # this is what's listed in Quin's sketch https://quinled.info/quinled-an-penta-diy-esphome-example-configuration/
  framework:
    type: esp-idf
time:
  - platform: sntp
    servers: !secret ntp_servers
    timezone: America/Los_Angeles
    on_time:
      # sync time
      - seconds: 0
        minutes: 59
        hours: 23
        then:
          - lambda: |-
              auto time = id(sntp_time).now();
              ESP_LOGD("time_sync", "Time before sync: %04d-%02d-%02d %02d:%02d:%02d", time.year, time.month, time.day_of_month, time.hour, time.minute, time.second);
          - lambda: "id(sntp_time).update();"
          - lambda: |-
              ESP_LOGD("time_sync", "Time after sync: %04d-%02d-%02d %02d:%02d:%02d", time.year, time.month, time.day_of_month, time.hour, time.minute, time.second);
      # reset energy at midnight
      - seconds: 50
        minutes: 59
        hours: 23
        then:
          # Send reset energy command to PZEM 1
          - uart.write:
              data: [0x02, 0x42, 0x80, 0xE1]
          - delay: 1s
          # Send reset energy command to PZEM 2
          - uart.write:
              data: [0x03, 0x42, 0x81, 0x71]
          - delay: 1s
          # Send reset energy command to PZEM 3
          - uart.write:
              data: [0x04, 0x42, 0x83, 0x41]
          - logger.log:
              format: "PZEMs energy reset"
              level: debug
preferences:
  # the default of 1min is far too short--flash chip is rated
  # for approx 100k writes.
  flash_write_interval: "1h"
ethernet:
  type: LAN8720
  mdc_pin: GPIO23
  mdio_pin: GPIO18
  clk_mode: GPIO17_OUT
  phy_addr: 0
  power_pin: GPIO5
  use_address: ${ip_address}
mdns:
  disabled: true
api:
  encryption:
    key: !secret encryption_key
  reboot_timeout: 0s
ota:
  password: !secret ota_password
  platform: esphome
logger:
  baud_rate: 0  # Disable UART logging
  # level: WARN  # normal level for logger
  level: DEBUG # only use this level when debugging an issue
  # level: VERBOSE
  # level: VERY_VERBOSE # only use this level if debug is not producing enough info to debug an issue
  # logs:
  #   hx711: ERROR
# web_server:
uart:
# PZEM UART Bus
  rx_pin: 15
  tx_pin: 13
  baud_rate: 9600
  stop_bits: 2 # not sure if this should be 1 or 2
modbus:
# PZEM Modbus
  uart_id: ubus
globals:
  # PZEM watchdog globals
  - id: pzem_1_failed_minutes
    type: int
    restore_value: no
    initial_value: '0'
  - id: pzem_1_last_success
    type: unsigned long
    restore_value: no
    initial_value: '0'
  - id: pzem_2_failed_minutes
    type: int
    restore_value: no
    initial_value: '0'
  - id: pzem_2_last_success
    type: unsigned long
    restore_value: no
    initial_value: '0'
  - id: pzem_3_failed_minutes
    type: int
    restore_value: no
    initial_value: '0'
  - id: pzem_3_last_success
    type: unsigned long
    restore_value: no
    initial_value: '0'
modbus_controller:
# Modbus controllers for direct PZEM communication
  - id: pzem_1_controller
    address: 2
    modbus_id: mbus
    update_interval: ${pzem_update}s
  - id: pzem_2_controller
    address: 3
    modbus_id: mbus
  - id: pzem_3_controller
    address: 4
    modbus_id: mbus
button:
  # Virtual Restart
  - platform: restart
# Manual Flash Write
    name: "Save Preferences to Flash"
    icon: "mdi:content-save"
    entity_category: config
    disabled_by_default: true
    on_press:
      - lambda: |-
          ESP_LOGI("preferences", "Manual flash write triggered");
          global_preferences->sync();
          ESP_LOGI("preferences", "Flash write completed");
# Reset Energy for pzem_1
    name: "${pzem_1} Energy Reset"
    on_press:
      - uart.write:
# Reset Energy for pzem_2
    name: "${pzem_2} Energy Reset"
    on_press:
      - uart.write:
    name: "${pzem_3} Energy Reset"
    on_press:
      - uart.write:
# Uptime Sensor
  - platform: uptime
# PZEM 1 Modbus Sensors
  # Power sensor - Read from registers 0x0003-0x0004 (32-bit)
  - platform: modbus_controller
    modbus_controller_id: pzem_1_controller
    address: 0x0003  # Power register
    register_type: read
    value_type: U_DWORD_R  # 32-bit unsigned, reversed byte order
    accuracy_decimals: 3
    unit_of_measurement: "kW"
    device_class: power
    state_class: measurement
    filters:
      - lambda: |-
          // Update timestamp BEFORE any filtering
          id(pzem_1_last_success) = millis();
          if (id(pzem_1_failed_minutes) > 0) {
            ESP_LOGI("pzem_watchdog", "${pzem_1} communication restored");
            id(pzem_1_failed_minutes) = 0;
          id(pzem_1_connected).publish_state(true);
          return x;
      - multiply: 0.0001  # PZEM reports power in 0.1W units, convert to kW
      - or:
        - throttle: 1min
        - delta: .01
    skip_updates: 0  # Never skip updates
  # Energy sensor - Read from registers 0x0005-0x0006 (32-bit)
    address: 0x0005  # Energy register
    register_type: read
    unit_of_measurement: "kWh"
    device_class: energy
    state_class: total_increasing
    filters:
      - multiply: 0.001  # PZEM reports energy in Wh, convert to kWh
      - or:
        - throttle: 1min
        - delta: .01
# PZEM 2 Modbus Sensors
    modbus_controller_id: pzem_2_controller
    register_type: read
    device_class: power
    filters:
      - lambda: |-
          id(pzem_2_last_success) = millis();
          if (id(pzem_2_failed_minutes) > 0) {
            ESP_LOGI("pzem_watchdog", "${pzem_2} communication restored");
            id(pzem_2_failed_minutes) = 0;
          id(pzem_2_connected).publish_state(true);
          return x;
      - or:
        - throttle: 1min
        - delta: .01
    register_type: read
    filters:
      - or:
        - throttle: 1min
        - delta: .01
# PZEM 3 Modbus Sensors
    modbus_controller_id: pzem_3_controller
    register_type: read
    device_class: power
    filters:
      - lambda: |-
          id(pzem_3_last_success) = millis();
          if (id(pzem_3_failed_minutes) > 0) {
            ESP_LOGI("pzem_watchdog", "${pzem_3} communication restored");
            id(pzem_3_failed_minutes) = 0;
          id(pzem_3_connected).publish_state(true);
          return x;
      - or:
        - throttle: 1min
        - delta: .01
    register_type: read
    filters:
      - or:
        - throttle: 1min
        - delta: .01
# PZEM Watchdog sensors
    name: "${pzem_1} Failed Minutes"
    lambda: |-
      return id(pzem_1_failed_minutes);
    update_interval: 60s
    entity_category: diagnostic
    unit_of_measurement: "min"
    name: "${pzem_2} Failed Minutes"
    lambda: |-
      return id(pzem_2_failed_minutes);
    name: "${pzem_3} Failed Minutes"
    lambda: |-
      return id(pzem_3_failed_minutes);
# Binary sensors for PZEM communication status
binary_sensor:
    name: "${pzem_1} Connected"
    device_class: connectivity
    lambda: |-
      // Check if we've had a successful read in the last interval
      // Convert seconds to milliseconds for comparison
      unsigned long disconnect_time_ms = ${pzem_update} * 3 * 1000;  // 30 seconds in milliseconds
      if (id(pzem_1_last_success) == 0) return false;  // Never connected
      unsigned long time_since = millis() - id(pzem_1_last_success);
      return time_since < disconnect_time_ms;
    filters:
      - delayed_on_off: 2s  # Add small delay to prevent flapping
    name: "${pzem_2} Connected"
    lambda: |-
      if (id(pzem_2_last_success) == 0) return false;  // Never connected
      unsigned long time_since = millis() - id(pzem_2_last_success);
    filters:
    name: "${pzem_3} Connected"
    lambda: |-
      if (id(pzem_3_last_success) == 0) return false;  // Never connected
      unsigned long time_since = millis() - id(pzem_3_last_success);
    filters:
# Combined problem sensor
    name: "PZEM Problem Detected"
    device_class: problem
    lambda: |-
      // Problem exists if either PZEM is disconnected
      return !id(pzem_1_connected).state || !id(pzem_2_connected).state || !id(pzem_3_connected).state;
    filters:
      - delayed_on: 5s  # Only show problem after 5 seconds of disconnection
# Interval to check PZEM health every minute
interval:
  - interval: 1min
    then:
      - lambda: |-
          unsigned long current_time = millis();
          // Check PZEM 1
          if (id(pzem_1_last_success) == 0 || (current_time - id(pzem_1_last_success)) > 60000) {
            id(pzem_1_failed_minutes)++;
            ESP_LOGW("pzem_watchdog", "${pzem_1} no response for %d minutes", id(pzem_1_failed_minutes));
          // Check PZEM 2
          if (id(pzem_2_last_success) == 0 || (current_time - id(pzem_2_last_success)) > 60000) {
            id(pzem_2_failed_minutes)++;
            ESP_LOGW("pzem_watchdog", "${pzem_2} no response for %d minutes", id(pzem_2_failed_minutes));
          // Check PZEM 3
          if (id(pzem_3_last_success) == 0 || (current_time - id(pzem_3_last_success)) > 60000) {
            id(pzem_3_failed_minutes)++;
            ESP_LOGW("pzem_watchdog", "${pzem_3} no response for %d minutes", id(pzem_3_failed_minutes));
          // Check if either PZEM has exceeded the timeout
          if (id(pzem_1_failed_minutes) >= ${pzem_watchdog_timeout} || id(pzem_2_failed_minutes) >= ${pzem_watchdog_timeout}) {
            ESP_LOGE("pzem_watchdog", "PZEM communication timeout exceeded! Restarting ESP...");
            // Reset counters before restart
            // Trigger restart
            id(restart_button).press();
  # Check connection status more frequently
  - interval: 5s
    then:
      - lambda: |-
          // Update PZEM 1 connected status
          if (id(pzem_1_last_success) > 0) {
            unsigned long time_since = current_time - id(pzem_1_last_success);
            bool should_be_connected = time_since < ${pzem_update} * 3 * 1000;
            if (id(pzem_1_connected).state != should_be_connected) {
              id(pzem_1_connected).publish_state(should_be_connected);
          // Update PZEM 2 connected status
          if (id(pzem_2_last_success) > 0) {
            unsigned long time_since = current_time - id(pzem_2_last_success);
            if (id(pzem_2_connected).state != should_be_connected) {
              id(pzem_2_connected).publish_state(should_be_connected);
          // Update PZEM 3 connected status
          if (id(pzem_3_last_success) > 0) {
            unsigned long time_since = current_time - id(pzem_3_last_success);
            if (id(pzem_3_connected).state != should_be_connected) {
              id(pzem_3_connected).publish_state(should_be_connected);
Same issue here after updating esphome… I will later try your approach and add the other sensors to the yaml file, that way I won’t break my automations
I’ve noticed this issue off and on for almost 2 years. The pzrm will report that it is seeing X watts and keep incrementing the energy usage as well (sometimes to hundreds of millions of kWh)
Super stoked that you figured this out, I was gearing up to take a look at SRC to see if I could find where the race condition is (I assume it’s a race condition).
Thanks!
FYI, I opened an issue and pointed it towards this post: Aaaaaaaa · Issue #7197 · esphome/issues · GitHub
Well, I did my version here based on the one you shared @mwolter, it seems to be working so far. I will monitor it meanwhile to see how it behaves.
If anyone wants to use as a baseline (improvements can be done for sure) my cfg/yaml file for two phases/pzems with addresses 1 and 2 is:
substitutions:
  ### System variables ###
  board_type: esp32-s3-devkitc-1
  hostname: "hass-power-meter" # Device hostname .local
  prefix: "Power Meter -"
  wifi_network: !secret wifi_ssid
  wifi_pswd: !secret wifi_password
  wifi_pswd_fallback: !secret wifi_password
  endpoint:  "<your_hostname.local.changeme>"
  wifi_hidden: 'False'
  wifi_fast_connect: 'False'
  ota_pswd: !secret ota_password # OTA update password
  pzem1_addr: "1" # PZEM phase 1 address
  pzem2_addr: "2" # PZEM phase 2 address
  phase_no: "2" # Amount of phases to be monitored
  update_s: "2" # Time between measurements
esphome:
  comment: PZEM-004T Energy Meter - Up to Two Phases
  friendly_name: ${hostname}
  platformio_options:
    build_flags: -D HAVE_HWSERIAL0
############################# Address Changing Routine #############################
  # on_boot:
  #   ## configure controller settings at setup
  #   ## make sure priority is lower than setup priority of modbus_controller
  #   priority: -100
  #   then:
  #     - lambda: |-
  #         auto new_address = 0x02;
  #         if(new_address < 0x01 || new_address > 0xF7) // sanity check
  #           ESP_LOGE("ModbusLambda", "Address needs to be between 0x01 and 0xF7");
  #           return;
  #         esphome::modbus_controller::ModbusController *controller = id(pzem);
  #         auto set_addr_cmd = esphome::modbus_controller::ModbusCommandItem::create_write_single_command(
  #           controller, 0x0002, new_address);
  #         delay(200) ;
  #         controller->queue_command(set_addr_cmd);
  #         ESP_LOGI("ModbusLambda", "PZEM Addr set");
esp32:
  board: ${board_type}
# Enable logging
logger:
# Enable Home Assistant API
api:
  encryption:
    key: "<change.me>"
# Enable OTA updates
ota:
  - platform: esphome
    password: ${ota_pswd}
wifi:
  networks:
    ssid: ${wifi_network}
    password: ${wifi_pswd}
    hidden: ${wifi_hidden}
  fast_connect: ${wifi_fast_connect}
  use_address: ${endpoint}
  ap:
    ssid: "power-meter-fallback"
    password: ${wifi_pswd_fallback}
# Enable webpage if connection to configured wifi is lost
captive_portal:
uart:
  rx_pin: GPIO02
  tx_pin: GPIO01
  baud_rate: 9600
  stop_bits: 1
modbus:
  uart_id: ubus
# modbus:
#   send_wait_time: 200ms
#   id: mod_bus_pzem
# modbus_controller:
#   - id: pzem
#     # The current device address.
#     address: 0xF8
#     # The special address 0xF8 is a broadcast address accepted by any pzem device,
#     # so if you use this address, make sure there is only one pzem device connected
#     # to the uart bus.
#     # address: 0xF8
#     modbus_id: mod_bus_pzem
#     command_throttle: 0ms
#     setup_priority: -10
#     update_interval: 30s
text_sensor:
  # Wifi network info
  - platform: wifi_info
    ip_address:
      name: ${prefix} IP Address
      icon: mdi:ip-network
    ssid:
      name: ${prefix} WiFi SSID
      icon: mdi:wifi
  # Compilation info
  - platform: version
    icon: mdi:information
binary_sensor:
  # Status (connected or disconnected)
  - platform: status
    name: "{prefix} Phase 1 - Connected"
    lambda: |-
      unsigned long disconnect_time_ms = ${update_s} * 3 * 1000;  // 30 seconds in milliseconds
    filters:
    name: "{prefix} Phase 2 - Connected"
    lambda: |-
    filters:
    lambda: |-
      return !id(pzem_1_connected).state || !id(pzem_2_connected).state;
    filters:
button:
    # Button to reset the ESP remotelly
  - platform: restart
    name: ${prefix} Software Reset
    icon: mdi:restart
    name: "${prefix} Phase 1 - Energy Reset"
    on_press:
      - uart.write:
          # base_addr, 0x42, CRC HSB, CRC LSB
          data: [0x01, 0x42, 0x80, 0x11] # use https://www.lammertbies.nl/comm/info/crc-calculation CRC-16 (Modbus)
    name: "${prefix} Phase 2 - Energy Reset"
    on_press:
      - uart.write:
### Device Specific Config ###
# Enable time component to reset energy at midnight
time:
  - platform: homeassistant
globals:
    type: int
    restore_value: no
    initial_value: '0'
    type: unsigned long
    restore_value: no
    initial_value: '0'
    type: int
    restore_value: no
    initial_value: '0'
    type: unsigned long
    restore_value: no
    initial_value: '0'
modbus_controller:
    address: ${pzem1_addr}
    modbus_id: mbus
    update_interval: ${update_s}s
    address: ${pzem2_addr}
    modbus_id: mbus
  # Wifi signal strength
  - platform: wifi_signal
    name: ${prefix} Wifi Strength
    icon: mdi:signal
    update_interval: 10s
  # Uptime Sensor
  - platform: uptime
  ############################# PZEM #1 #############################
  # Voltage value - Read from register 0x0000 (16-bit)
    icon: mdi:sine-wave
    name: "${prefix} Phase 1 - Voltage"
    address: 0x0000  # Voltage register
    register_type: read
    value_type: U_WORD  # 16-bit unsigned
    accuracy_decimals: 1
    unit_of_measurement: "V"
    device_class: voltage
    filters:
      - lambda: |-
            ESP_LOGI("pzem_watchdog", "Phase 1 communication restored");
          return x;
      - multiply: 0.1  # PZEM reports power in 0.1V units, convert to V
  # Current sensor - Read from registers 0x0001-0x0002 (32-bit)
    icon: mdi:current-ac
    name: "${prefix} Phase 1 - Current"
    address: 0x0001  # Current register
    register_type: read
    accuracy_decimals: 2
    unit_of_measurement: "A"
    device_class: current
    filters:
      - multiply: 0.001  # PZEM reports power in 0.001A units, convert to A
    icon: mdi:flash
    name: "${prefix} Phase 1 - Power"
    register_type: read
    unit_of_measurement: "W"
    device_class: power
    filters:
      - multiply: 0.1  # PZEM reports power in 0.1W units, convert to W
    icon: mdi:counter
    name: "${prefix} Phase 1 - Total Energy"
    register_type: read
    filters:
  # Frequency value - Read from register 0x0007 (16-bit)
    icon: mdi:sine-wave
    name: "${prefix} Phase 1 - Frequency"
    address: 0x0007  # Frequency register
    register_type: read
    accuracy_decimals: 0
    unit_of_measurement: "Hz"
    device_class: frequency
    filters:
      - multiply: 0.1  # PZEM reports power in 0.1Hz units, convert to Hz
  # Power Factor value - Read from register 0x0008 (16-bit)
    icon: mdi:angle-acute
    name: "${prefix} Phase 1 - Power Factor"
    address: 0x0008  # Frequency register
    register_type: read
    unit_of_measurement: "%"
    device_class: power_factor
    name: "${prefix} Phase 1 - Apparent Power"
    icon: mdi:alpha-s
    lambda: |-
        return id(pzem_1_current).state * id(pzem_1_voltage).state;
    unit_of_measurement: "VA"
    device_class: apparent_power
############################# PZEM #2 #############################
    icon: mdi:sine-wave
    name: "${prefix} Phase 2 - Voltage"
    register_type: read
    filters:
      - lambda: |-
            ESP_LOGI("pzem_watchdog", "Phase 2 communication restored");
          return x;
    name: "${prefix} Phase 2 - Current"
    register_type: read
    filters:
    icon: mdi:flash
    name: "${prefix} Phase 2 - Power"
    register_type: read
    device_class: power
    filters:
    icon: mdi:counter
    name: "${prefix} Phase 2 - Total Energy"
    register_type: read
    filters:
    icon: mdi:sine-wave
    name: "${prefix} Phase 2 - Frequency"
    register_type: read
    filters:
    name: "${prefix} Phase 2 - Power Factor"
    register_type: read
    name: "${prefix} Phase 2 - Apparent Power"
    icon: mdi:alpha-s
    lambda: |-
        return id(pzem_2_current).state * id(pzem_2_voltage).state;
  # ALL phases total aggregation
    name: "${prefix} Total Active Power"
    icon: mdi:flash
    lambda: |-
        if (${phase_no}==1) {
          return id(pzem_1_power).state;
        if (${phase_no}==2) {
          return id(pzem_1_power).state + id(pzem_2_power).state;
    device_class: power
    name: "${prefix} Total Apparent Power"
    icon: mdi:alpha-s
    lambda: |-
          return id(pzem_1_apparent_power).state;
          return id(pzem_1_apparent_power).state + id(pzem_2_apparent_power).state;
    name: "${prefix} Total Power Factor"
    lambda: |-
        return id(pzem_total_active_power).state / id(pzem_total_apparent_power).state;
    filters:
      - multiply: 100
    name: "${prefix} Total Energy"
    icon: 'mdi:counter'
    lambda: |-
          return (id(pzem_1_energy).state);
            return (id(pzem_1_energy).state + id(pzem_2_energy).state);
I noticed this issue as well.
I’m going to try the mwolter solution asap.
I can confim that it works, running here without interruption so far
Doesn’t sound like the esphome maintainer is too keen on fixing it (like usual, IME). They asked me to go to the discord to debug and then ignored me, not sure what the deal is there.
Going to implement these fixes in my code since they are working for everyone else. Just glad there is some sort of fix for this. Thanks, @mwolter
Hi @vinicius_trev , can you please tell or teach me how to get the CRC HSB and LSB value?
Because when I use yours or @mwolter, the energy not being reset.
Thank you
Here are my notes for calculating the checksum
To calculate a new checksum, use the site https://crccalc.com
  • enter the address and command in the box at the top, IE 0142
  • Select HEX input
  • Select CRC-16
  • Then look for the CRC-16/MODBUS result below. IE 0x1180
  • Convert this to two bytes. IE 0x80, 0x11
After several months of testing I isolated my issue (regarding 3 PZEM and an esp8266).
In my case was a commit applied to the esphome’s web_server component from release 2025.6.2 to 2025.6.3
I opened an issue here #14373