Hello All,
I have a working setup with a SDM630 meter.
I can read KWH, voltage, current, all working fine.
But i like to read a couple of values more than the example gives:
https://esphome.io/components/sensor/sdm_meter.html
- platform: sdm_meter
phase_a:
current:
voltage:
active_power:
power_factor:
name: "SDM220M Power Factor"
apparent_power:
name: "SDM220M Apparent Power"
reactive_power:
name: "SDM220M Reactive Power"
phase_angle:
name: "SDM220M Phase Angle"
frequency:
name: "SDM220M Frequency"
import_active_energy:
name: "SDM220M Import Active Energy"
export_active_energy:
name: "SDM220M Export Active Energy"
import_reactive_energy:
name: "SDM220M Import Reactive Energy"
export_reactive_energy:
name: "SDM220M Export Reactive Energy"
update_interval: 60s
This above working fine:
But in source code for SDM there are more options:
https://github.com/esphome/esphome/blob/073828235f67318df933fbe7350a3e0dc17bb773/esphome/components/sdm_meter/sdm_meter_registers.h
/* PHASE STATUS REGISTERS */
static const uint16_t SDM_PHASE_1_VOLTAGE = 0x0000;
static const uint16_t SDM_PHASE_2_VOLTAGE = 0x0002;
static const uint16_t SDM_PHASE_3_VOLTAGE = 0x0004;
static const uint16_t SDM_PHASE_1_CURRENT = 0x0006;
static const uint16_t SDM_PHASE_2_CURRENT = 0x0008;
static const uint16_t SDM_PHASE_3_CURRENT = 0x000A;
static const uint16_t SDM_PHASE_1_ACTIVE_POWER = 0x000C;
static const uint16_t SDM_PHASE_2_ACTIVE_POWER = 0x000E;
static const uint16_t SDM_PHASE_3_ACTIVE_POWER = 0x0010;
static const uint16_t SDM_PHASE_1_APPARENT_POWER = 0x0012;
static const uint16_t SDM_PHASE_2_APPARENT_POWER = 0x0014;
static const uint16_t SDM_PHASE_3_APPARENT_POWER = 0x0016;
static const uint16_t SDM_PHASE_1_REACTIVE_POWER = 0x0018;
static const uint16_t SDM_PHASE_2_REACTIVE_POWER = 0x001A;
static const uint16_t SDM_PHASE_3_REACTIVE_POWER = 0x001C;
static const uint16_t SDM_PHASE_1_POWER_FACTOR = 0x001E;
static const uint16_t SDM_PHASE_2_POWER_FACTOR = 0x0020;
static const uint16_t SDM_PHASE_3_POWER_FACTOR = 0x0022;
static const uint16_t SDM_PHASE_1_ANGLE = 0x0024;
static const uint16_t SDM_PHASE_2_ANGLE = 0x0026;
static const uint16_t SDM_PHASE_3_ANGLE = 0x0028;
static const uint16_t SDM_AVERAGE_L_TO_N_VOLTS = 0x002A;
static const uint16_t SDM_AVERAGE_LINE_CURRENT = 0x002E;
static const uint16_t SDM_SUM_LINE_CURRENT = 0x0030;
static const uint16_t SDM_TOTAL_SYSTEM_POWER = 0x0034;
static const uint16_t SDM_TOTAL_SYSTEM_APPARENT_POWER = 0x0038;
static const uint16_t SDM_TOTAL_SYSTEM_REACTIVE_POWER = 0x003C;
static const uint16_t SDM_TOTAL_SYSTEM_POWER_FACTOR = 0x003E;
static const uint16_t SDM_TOTAL_SYSTEM_PHASE_ANGLE = 0x0042;
How can i read for example: SDM_TOTAL_SYSTEM_POWER
If i add this key(or similar) to esphome it does not recognize it.
How can i read these values?
does anybody know this?
How to read more items from the eastron meters?
i have the exact same question for my SDM72M-V2.
Any solution yet?
Thanks!
No have not found a solution yet
I added a fork (not yet a pullrequest since it is untested).
I added Import and Export Power to the readout.
try:
external_components:
- source:
type: git
url: https://github.com/guineapirates/esphome
ref: dev
components: [ sdm_meter ]
total_power:
import_power:
export_power:
guineapirates:
SDM72M
What did you change for this? does this change also apply to the sdm630?
And are you going to make a PR for this change and add this to ESPhome?
@ frank8the9tank guineapirates
I’m using custom component for SDM630 in ESPHome:
esphome:
platform: ESP8266
board: nodemcuv2
includes:
- custom_components/sdm/SDM_Config_User.h
- custom_components/sdm/SDM.h
- custom_components/sdm/sdm_esphome.h
wifi:
ssid: "Secret"
password: !secret wifi_pass
ap:
ssid: "${friendly_name} Hotspot"
password: "As9HOTthln7T"
captive_portal:
substitutions:
# Device Names
device_name: "powermetersdm630"
friendly_name: "SDM630"
# Icon
# https://materialdesignicons.com/
# https://www.esphome.app/docs/icons
main_icon: "mdi:gauge"
logger:
#level: DEBUG
level: VERBOSE
#level: INFO
baud_rate: 0 #disable uart log
esp8266_store_log_strings_in_flash: false
# Enable Home Assistant API
api:
password: !secret api
ota:
password: !secret ota
uart:
rx_pin: GPIO3
tx_pin: GPIO1
baud_rate: 9600
stop_bits: 1
binary_sensor:
# https://esphome.io/components/binary_sensor/status.html
- platform: status
time:
# https://esphome.io/components/time.html
- platform: homeassistant
timezone: Europe/Warsaw
- platform: wifi_signal
- platform: uptime
- platform: custom
lambda: |-
auto sdm_sensors = new SDMComponent();
App.register_component(sdm_sensors);
return {sdm_sensors->voltage1_sensor, sdm_sensors->voltage2_sensor, sdm_sensors->voltage3_sensor, sdm_sensors->current1_sensor, sdm_sensors->current2_sensor, sdm_sensors->current3_sensor, sdm_sensors->current_sum_sensor,
sdm_sensors->power1_sensor, sdm_sensors->power2_sensor, sdm_sensors->power3_sensor, sdm_sensors->power_total_sensor, sdm_sensors->reactive1_sensor, sdm_sensors->reactive2_sensor, sdm_sensors->reactive3_sensor,
sdm_sensors->power_factor_total_sensor, sdm_sensors->frequency_sensor, sdm_sensors->import_active_energy_sensor,
sdm_sensors->export_active_energy_sensor, sdm_sensors->import_reactive_energy_sensor, sdm_sensors->export_reactive_energy_sensor, sdm_sensors->import1_sensor,
sdm_sensors->import2_sensor, sdm_sensors->import3_sensor, sdm_sensors->export1_sensor, sdm_sensors->export2_sensor, sdm_sensors->export3_sensor, sdm_sensors->total_energy1_sensor,
sdm_sensors->total_energy2_sensor, sdm_sensors->total_energy3_sensor, sdm_sensors->total_energy_sensor};
sensors:
- name: "${friendly_name} Napięcie L1"
unit_of_measurement: V
accuracy_decimals: 1
#icon: "mdi:alpha-v-circle-outline"
device_class: "voltage"
state_class: "measurement"
- name: "${friendly_name} Napięcie L2"
- name: "${friendly_name} Napięcie L3"
- name: "${friendly_name} Prąd L1"
unit_of_measurement: A
accuracy_decimals: 3
#icon: "mdi:alpha-a-circle-outline"
device_class: "current"
- name: "${friendly_name} Prąd L2"
#unit_of_measurement: A
- name: "${friendly_name} Prąd L3"
- name: "${friendly_name} Prąd całkowiy"
- name: "${friendly_name} Moc czynna L1"
unit_of_measurement: W
#icon: "mdi:gauge"
device_class: "power"
- name: "${friendly_name} Moc czynna L2"
#icon: "mdi:gauge"
- name: "${friendly_name} Moc czynna L3"
#icon: "mdi:gauge"
- name: "${friendly_name} Moc czynna całkowita"
#accuracy_decimals: 1
icon: "mdi:gauge"
- name: "${friendly_name} Moc bierna L1"
unit_of_measurement: VAr
icon: "mdi:gauge"
#device_class: "power"
#state_class: "measurement"
- name: "${friendly_name} Moc bierna L2"
icon: "mdi:gauge"
- name: "${friendly_name} Moc bierna L3"
icon: "mdi:gauge"
- name: "${friendly_name} Współczynnik mocy"
accuracy_decimals: 2
icon: "mdi:alpha-f-circle-outline"
#device_class: "power_factor"
- name: "${friendly_name} Częstotliwość"
unit_of_measurement: Hz
icon: "mdi:current-ac"
- name: "${friendly_name} Energia czynna pobrana"
unit_of_measurement: kWh
#icon: "mdi:gauge"
device_class: "energy"
- name: "${friendly_name} Energia czynna oddana"
#icon: "mdi:gauge"
- name: "${friendly_name} Energia bierna pobrana"
unit_of_measurement: kVARh
icon: "mdi:gauge"
- name: "${friendly_name} Energia bierna oddana"
icon: "mdi:gauge"
- name: "${friendly_name} Energia pobrana L1"
#icon: "mdi:gauge"
- name: "${friendly_name} Energia pobrana L2"
#icon: "mdi:gauge"
- name: "${friendly_name} Energia pobrana L3"
#icon: "mdi:gauge"
- name: "${friendly_name} Energia oddana L1"
#icon: "mdi:gauge"
- name: "${friendly_name} Energia oddana L2"
#icon: "mdi:gauge"
- name: "${friendly_name} Energia oddana L3"
#icon: "mdi:gauge"
- name: "${friendly_name} Energia całkowita L1"
#icon: "mdi:counter"
- name: "${friendly_name} Energia całkowita L2"
- name: "${friendly_name} Energia całkowita L3"
- name: "${friendly_name} Energia całkowita"
# https://esphome.io/components/sensor/total_daily_energy.html
- platform: total_daily_energy
name: "${friendly_name} Dzienne zużycie energii"
icon: "mdi:counter"
power_id: power
filters:
# Multiplication factor from W to kW is 0.001
- multiply: 0.001
text_sensor:
lambda: |-
int seconds = (id(uptime_sec).state);
int days = seconds / (24 * 3600);
seconds = seconds % (24 * 3600);
int hours = seconds / 3600;
seconds = seconds % 3600;
int minutes = seconds / 60;
seconds = seconds % 60;
return { (String(days) +"d " + String(hours) +"h " + String(minutes) +"m "+ String(seconds) +"s").c_str() };
icon: mdi:clock-start
update_interval: 120s
Files
While trying to complile your example I have plenty of errors as:
/config/esphome/sdm-new.yaml: In lambda function:
/config/esphome/sdm-new.yaml:74:28: error: 'class SDMComponent' has no member named 'voltage1_sensor'; did you mean 'voltage_sensorL1'?
74 | return {sdm_sensors->voltage1_sensor, sdm_sensors->voltage2_sensor, sdm_sensors->voltage3_sensor, sdm_sensors->current1_sensor, sdm_sensors->current2_sensor, sdm_sensors->current3_sensor, sdm_sensors->current_sum_sensor,
| voltage_sensorL1
What am I doing wrong?
It is not enough to put the import_active_energy sensor:
name: SDM220M Import Active Energy to the home assistant in the energy panel? then it will do what you need.
dirksenrdh
(Rob Dirksen)
October 10, 2022, 7:10pm
10
maybe a stupid question, but what kind of SDM630 do you have. is it the Wifi version which you have to read out via the HomeWizzard integration or is it the modbus version which you can read out with the modbus integration.
I use the modbus version. you can readout every parameter in the SDM630 by adressing the correct register.
you can also find the SDM630 documentation which describes all the parameters that you can read and set via the modbus interface.
Its the version with modbus, and i use ESPhome for a 485/modbus connection to the meter.
Can you give me a example of your configuration?
dirksenrdh
(Rob Dirksen)
October 14, 2022, 1:44pm
12
sure.
I use a HF2211 as 485 to ethernet converter. I talk ModbusTCP to the converter which converts it into Modbus RTU to the devices.
modbus:
- name: Hub1
type: tcp
host: 172.x.y.65
port: 8899
sensors:
- name: recharge_Vac1
#hub: Hub1
slave: 1
input_type: input
address: 0
count: 2
data_type: float32
precision: 1
scan_interval: 5
device_class: voltage
- name: recharge_Vac2
slave: 1
input_type: input
address: 2
count: 2
data_type: float32
precision: 1
scan_interval: 5
- name: recharge_Vac3
slave: 1
input_type: input
address: 4
count: 2
data_type: float32
precision: 1
scan_interval: 5
- name: recharge_Iac1
slave: 1
input_type: input
address: 6
count: 2
data_type: float32
precision: 3
scan_interval: 5
device_class: current
- name: recharge_Iac2
slave: 1
input_type: input
address: 8
count: 2
data_type: float32
precision: 1
scan_interval: 5
- name: recharge_Iac3
slave: 1
input_type: input
address: 10
count: 2
data_type: float32
precision: 1
scan_interval: 5
- name: recharge_Pac1
slave: 1
input_type: input
address: 12
count: 2
data_type: float32
precision: 2
scan_interval: 5
Mine looks like this - works flawlessly now.
esphome:
name: stromzaehler # need to adjust to your setup
platform: ESP8266 # need to adjust to your setup
board: nodemcuv2 # need to adjust to your setup
wifi:
ssid: "xxx" # need to adjust to your setup
password: "xxx" # need to adjust to your setup
ap:
ssid: "Stromzaehler Fallback Hotspot" # need to adjust to your setup
captive_portal:
# Enable logging
logger:
level: DEBUG
baud_rate: 0 #needs 0, because info & data goes thru one line.
web_server:
port: 80
api:
ota:
time:
uart:
rx_pin: D5 # need to adjust to your setup
tx_pin: D0 # need to adjust to your setup
baud_rate: 9600
stop_bits: 1
modbus:
uart_id: mod_bus
modbus_controller:
- id: sdm
address: 0x0001 # need to adjust to your setup, standard SDM is 1
modbus_id: modbus1
update_interval: 10s
##### SDM Meter via Modbus
- platform: modbus_controller
modbus_controller_id: sdm
name: "HT NT Import Leistung"
register_type: read
address: 0x0500
value_type: FP32
accuracy_decimals: 0
unit_of_measurement: "W"
state_class: measurement
device_class: power
filters:
- multiply: 1.0
name: "HT NT Export Leistung"
register_type: read
address: 0x0502
value_type: FP32
device_class: power
filters:
- multiply: 1.0
###SDM Meter can be used for the rest
phase_a:
current:
name: "HT NT L1 Strom"
voltage:
name: "HT NT L1 Spannung"
active_power:
name: "HT NT L1 Leistung"
power_factor:
name: "HT NT L1 Leistungsfaktor"
apparent_power:
name: "HT NT L1 Scheinleistung"
reactive_power:
name: "HT NT L1 Blindleistung"
phase_b:
current:
name: "HT NT L2 Strom"
voltage:
name: "HT NT L2 Spannung"
active_power:
name: "HT NT L2 Leistung"
power_factor:
name: "HT NT L2 Leistungsfaktor"
apparent_power:
name: "HT NT L2 Scheinleistung"
reactive_power:
name: "HT NT L2 Blindleistung"
phase_c:
current:
name: "HT NT L3 Strom"
voltage:
name: "HT NT L3 Spannung"
active_power:
name: "HT NT L3 Leistung"
power_factor:
name: "HT NT L3 Leistungsfaktor"
apparent_power:
name: "HT NT L3 Scheinleistung"
reactive_power:
name: "HT NT L3 Blindleistung"
frequency:
name: "HT NT Netzfrequenz"
total_power:
name: "HT NT Summe Leistung"
name: "HT NT Import Energie"
name: "HT NT Export Energie"
name: "HT NT Import Blindenergie"
name: "HT NT Export Blindenergie"
@blackscreener can you put the files somewhere else? The link has expired. Thank you !
Phil23
December 8, 2022, 9:12pm
15
Thanks for this Integration.
Tried it yesterday with a spare SDM220 I had on hand.
Had little trouble getting it up in short order & now it’s reading just Volts & Freq as no load is present.
Now I need to get it reading on the Identical meters I have in service.
First issue I can’t find a real solution to is how I address the 3 meters I have daisy chained on the same Bus. Addresses are 1, 2 & 3.
First one is on the Mains Supply arriving at the Meter Box.
2nd one is on Power feed into my Hybrid Inverter, &
3rd on the output that feeds a Sub-Board.
Currently I’m just reading them with a PIC32MX170 running basic & code I have written.
It just polls the 3 addresses & reports data on a TFT & the serial console.
Would be great to have all 3 available within Home Assistant.
I see no mention in the config of a Modbus Address, but assume it using Add01, as that’s what the spare I am testing with is on.
Using this device between an ESP32 & the SDM220, and also on my working PIC connection.
Any assistance greatly appreciated, as I’m on the edge of my Skill Set.
Cheers
For anybody that comes looking:
I have a couple of these eastron meters connected to a m5stack atom,
With the esp eastron integration it gave me alot of trouble to get is stable.
Changed over to just modbus reads and that works fine and stable for weeks now.
my code:
uart:
rx_pin: 22
tx_pin: 19
baud_rate: 9600
stop_bits: 1
parity: NONE
modbus:
#flow_control_pin: 5
modbus_controller:
- id: modbus002
# Nibe F2120
address: 0x2
modbus_id: modbus1
setup_priority: -10
update_interval: 30s
- id: modbus010
# Car charger
address: 10
modbus_id: modbus1
setup_priority: -10
- id: modbus030
# Daikin airco
address: 30
modbus_id: modbus1
setup_priority: -10
- id: modbus040
# Zehnder q450
address: 40
modbus_id: modbus1
setup_priority: -10
#Nibe F2120
modbus_controller_id: modbus002
name: "Nibe heatpump f2120 kwh"
register_type: read
address: 0x004A
unit_of_measurement: "kWh"
value_type: FP32
state_class: "total_increasing"
name: "Nibe heatpump f2120 power"
register_type: read
address: 0x0034
unit_of_measurement: "kW"
value_type: FP32
filters:
- multiply: -0.001
#Car charger
modbus_controller_id: modbus010
name: "Car charger kwh"
register_type: read
address: 0x0048
value_type: FP32
name: "Car charger power"
register_type: read
address: 0x000C
value_type: FP32
filters:
- multiply: 0.001
#Daikin
modbus_controller_id: modbus030
name: "Daikin airco stairs kwh"
register_type: read
address: 0x0048
value_type: FP32
name: "Daikin airco stairs power"
register_type: read
address: 0x000C
value_type: FP32
filters:
- multiply: 0.001
#Zenhder
modbus_controller_id: modbus040
name: "Zehnder q450 kwh"
register_type: read
address: 0x0048
value_type: FP32
name: "Zehnder q450 power"
register_type: read
address: 0x000C
value_type: FP32
filters:
- multiply: 0.001
text_sensor:
name: "Car charger state"
lambda: !lambda |-
if (id(car_charger_power).state > 0.25) {
return std::string("Charging");
} else {
return std::string("Idle");
The only thing is now that the statistics don’t work now in home assistant.
Trying to read one register without success. Can some please guide me in the right direction?
esphome:
friendly_name: tac2100
esp32:
board: esp32dev
framework:
type: esp-idf
# Enable logging
logger:
level: VERBOSE
baud_rate: 0
api:
encryption:
key: "4glSwI9DIHBUsxa7E1PYwDuXosZaP9EpRaauXvEbhUU="
ota:
password: "5c0e9168cbb9223eb6f9bf9ce5737bc9"
wifi:
ssid: !secret wifi_ssid
ap:
ssid: "Tac2100 Fallback Hotspot"
password: "s6utAx2k0ZMM"
captive_portal:
uart:
rx_pin: GPIO17
tx_pin: GPIO16
baud_rate: 9600
stop_bits: 1
modbus:
uart_id: mod_bus
send_wait_time: 500ms
modbus_controller:
- id: sdm
address: 1 # need to adjust to your setup, standard SDM is 1
modbus_id: modbus1
update_interval: 5s
register_type: read
address: 0
value_type: FP32
unit_of_measurement: "V"
filters:
- multiply: 1.0