Smart Oil Guage
It makes me happy to know that other people are getting use out of my code and random poking around.
I am curious enough about how they built the Duo sensor, that have ordered one to play with.
As for the sensor reading unavailable when deep sleeping, this turned out to be a race condition while the controller was going to sleep. ESP Home Entity not available in Deep Sleep after update to 2025.6.0+ · Issue #7145 · esphome/issues · GitHub
I have since had to increase the delay I am using to 50ms:
  on_shutdown:
    - priority: 800
      then:
      - if:
          condition:
            - switch.is_on: deep_sleep_trig
          then:
            - lambda: 'delay(50);'
            - switch.turn_on: Done
I have also changed to using a Calibrate Linear Filter to go from inches to gallons of oil in the tank instead of calculating it geometrically. The linear filter is giving me a slightly more consistent gallons-per-hour burn rate calculation as the oil is being consumed.
Thank you so much for sharing! This is easily one of the most useful ESP devices I am running and helped me save money greatly by scheduling oil deliveries when prices were cheapest during the coldest parts of this winter. It’s also significantly more reliable than the float gauge on the tank which is off by at least 15-20%
Is this code is intended to replace:
  on_shutdown:
    then:
      - switch.turn_off: ultrasonic_en
      - output.turn_off: LED_pwm
      - if:
          condition:
          then:
            - switch.turn_on: sleep_1hr
If so, I will test when I get home next week. Would be great if a cloned sensor wasn’t needed any longer. If this works, I will submit a PR to update the device documentation.
Would you mind sharing the other code for the calibrate linear filter? I can test that as well.
What method are you using to calculate burn rate (I’m using a derivative sensor helper based on the cloned sensor currently)?
This is my full code as I am currently running it.
substitutions:
  device_name: "hacked-oil"
  friendly_name: "Hacked_Oil"
  Samples_Before_Sleep: '3'
  Auto_Sleep_On_dc: '2.5%'
  Auto_Sleep_Off_dc: '87%'
  ultrasonic_interval: '250ms'
  tank_size: "330" # 275, 330, 500, 550, or 1000
  tank_orientation: '1'  # 1 = Vertical,  2 = Horizontal
esphome:
  friendly_name: ${friendly_name}
  on_boot:
    - priority: 800
      then:
        - switch.turn_off: deep_sleep_trig
        - switch.turn_off: VarCheck
        - switch.turn_off: ultrasonic_pwr
        - switch.turn_off: Auto_Sleep_Disable
    - priority: -100
      then:
        - script.execute: set_tank_dimensions
        - output.turn_on: LED_pwm
        - output.set_level:
            level: ${Auto_Sleep_On_dc}
        - switch.turn_on: TempSens_EN
  on_shutdown:
    #- priority: -100
    #  then:
    #    - switch.turn_off: ultrasonic_en
    #    - output.turn_off: LED_pwm
    - priority: 800
      then:
        #- switch.turn_off: ultrasonic_en
        #- output.turn_off: LED_pwm
        - if:
            condition:
            then:
esp8266:
  board: esp_wroom_02
### PIN Identification ###
# 1 - 3V3
# 2 - EN, Pulled High
# 3 - GPIO14, Pulled Low, Output, Ultrasonic Sensor PWR EN
# 4 - GPIO12, Pulled High, Input, Control Button
# 5 - GPIO13, Pulled Low, Output, Timer TPL5111 - Done
# 6 - GPIO15, Pulled Low, Output, ADC SPDT Select Switch
# 7 - GPIO2, Pulled High, Output, Board LED
# 8 - GPIO0, Pulled High, Input, Front Surface Pad Second From Antenna
# 9 - GND
# 10 - GND
# 11 - GPIO16, Pulled High, Connected to RST
# 12 - TOUT, A0, Input, ADC, SPDT Common
# 13 - RST, Pulled High, Connected to GPIO16
# 14 - GPIO5, Pulled High, Input, Ultrasonic Echo
# 15 - GND, Surface Pad near Ant (Both Sides)
# 16 - TXD, Back Surface Pad Closest to Edge
# 17 - RXD, Back Surface Pad Second from Edge
# 18 - GPIO4, Pulled High, Output, Ultrasonic Trigger
# SPDT - Select Low -> Pin3 - 10MOhm to Batt and 1MOhm to GND
# SPDT - Select High -> Pin1 - Temperature - smdcode: AFT3 - MCP9700AT-E/TT  https://ww1.microchip.com/downloads/aemDocuments/documents/MSLD/ProductDocuments/DataSheets/MCP970X-Family-Data-Sheet-DS20001942.pdf
# UltraSonic is JSN-SR04T set to behave like HC-SR04   https://components101.com/sites/default/files/component_datasheet/JSN-SR04-Datasheet.pdf
# Timer Chip - smdcode: ZFVX - TPL5111
# Timer will cut 3.3V when Done goes High, will wake after 1hr. Expect to cause ESP8266 reset every hour.
# https://www.ti.com/lit/ds/symlink/tpl5111.pdf?ts=1739630376626&ref_url=https%253A%252F%252Fwww.google.com%252F
# Unstable operation when Battery Voltage is down to around 6.33V
# Enable logging
logger:
  level: DEBUG
# Enable Home Assistant API
api:
  encryption:
    key: !secret api_encryption_key_oil_gauge
ota:
  - platform: esphome
    password: !secret ota_password_oil_gauge
wifi:
  ssid: !secret wifi_ssid
  min_auth_mode: WPA2
  ap:
    ssid: ${device_name}
    password: !secret fallback_password_oil_gauge
captive_portal:
deep_sleep:
  sleep_duration: 30s
globals:
  - id: Tank_Width
    type: float
    initial_value: '0'
  - id: Tank_Radius
    type: float
    initial_value: '0'
  - id: Tank_Height
    type: float
    initial_value: '0'
  - id: Tank_Length
    type: float
    initial_value: '0'
#  - id: Oil_Height
#    type: double
#    initial_value: '0'
  - id: Rectangle_Height
    type: double
    initial_value: '0'
  - id: Arc_Height
    type: double
    initial_value: '0'
  - id: Rectangle_Area
    type: double
    initial_value: '0'
  - id: Arc_Area
    type: double
    initial_value: '0'
  - id: Total_Area
    type: double
    initial_value: '0'
#  - id: Oil_In_Tank
#    type: double
  - id: Max_Fill
    type: double
    initial_value: '0'
  - id: Tank_Orientation
    type: float
    initial_value: ${tank_orientation}
  - id: Tank_Size
    type: float
    initial_value: ${tank_size}
  - id: Measure_Count
    type: int
    initial_value: '0'
  - id: Samples_Before_Sleep
    type: int
    initial_value: ${Samples_Before_Sleep}
switch:
  - platform: restart
    entity_category: "config"
    disabled_by_default: true
    optimistic: true
    on_turn_on:
      then:
        - script.execute: ultrasonic_loop
    on_turn_off:
      then:
    name: "Deep Sleep Trigger"
    optimistic: True
    on_turn_on:
      then:
        - script.stop: ultrasonic_loop
        #- delay: 5s
        - deep_sleep.enter:
    name: "Auto Sleep Disable"
    optimistic: True
    on_turn_on:
      - output.set_level:
          level: ${Auto_Sleep_Off_dc}
    on_turn_off:
      - output.set_level:
    optimistic: True
  - platform: gpio
    pin: GPIO15
  - platform: gpio
    pin: GPIO14
    disabled_by_default: false
    on_turn_on:
      then:
        - delay: 3s
        - switch.turn_on: ultrasonic_en
  - platform: gpio
    pin: GPIO13 # Done Signal to TPL5111
    id: Done # Use Deep_Sleep_EN
output:
  - platform: slow_pwm
    period: 1s
    pin: GPIO2
    inverted: True
binary_sensor:
  - platform: gpio
    pin:
      number: GPIO12
      inverted: true
    on_multi_click:
      - timing:
          - ON for at most 1s
          - OFF for at most 1s
          - ON for at most 1s
          - OFF for at least 0.2s
        then:
          - switch.toggle: Auto_Sleep_Disable
      - timing:
          - ON for at most 1s
          - OFF for at least 0.5s
        then:
          - switch.turn_on: deep_sleep_trig
    name: 'Oil In Tank'
    device_class: volume_storage
    state_class: measurement
    unit_of_measurement: 'gal'
    accuracy_decimals: 4
    state_class: total
  - platform: adc
    pin: A0
    accuracy_decimals: 3
    update_interval: 5s
    entity_category: "diagnostic"
    filters:
      - lambda: |-
          // Battery Voltage Divider R Values
          int R1 = 10;  // MOhm
          int R2 = 1;   // MOhm
          float offset = -2.2; // Temperature correction offset (degC)
          if (id(TempSens_EN).state){
            return (((x*1000)-500)/10) + offset; // Temperature Sensor (degC)
          } else {
            return (x * (R1+R2))/R2; // Battery Voltage
    on_value:
      then:
        - if:
            condition:
              - switch.is_on: TempSens_EN
            then:
              - sensor.template.publish:
                  state: !lambda 'return id(ADC_Input).state;'
              - component.update: VP_Oil
              - switch.turn_off: TempSens_EN
              - delay: 1s
              - switch.turn_on: ultrasonic_pwr
            else:
    device_class: temperature
    unit_of_measurement: '°C'
    device_class: voltage
    unit_of_measurement: 'V'
    name: 'Vapor Pressure Oil'
    update_interval: never
    device_class: pressure
    unit_of_measurement: kPa
    accuracy_decimals: 8
    lambda: |-
      return id(TempC).state;
    filters:
      - calibrate_linear:
          method: exact
          datapoints:
            # https://www.eng-tips.com/threads/typical-diesel-info.109718/post-424028
            # Map 0.0 (from sensor) to 1.0 (true value)
            # degC to Oil Vapor Pressure kPa
            - 4.444444444 -> 0.021373756
            - 10.0 -> 0.03102642
            - 15.55555556 -> 0.051021224
            - 21.11111111	-> 0.06205284
            - 26.66666667	-> 0.08273712
            - 32.22222222	-> 0.11031616
            - 37.77777778	-> 0.15168472
  - platform: ultrasonic
    trigger_pin:
        number: GPIO4
        inverted: true
    echo_pin: GPIO5
    accuracy_decimals: 25
    update_interval: never # 4s
    internal: True
    filters:
      - median:
          window_size: 5
          send_every: 5
          send_first_at: 5
      - sliding_window_moving_average:
          window_size: 16
          send_every: 16
          send_first_at: 16
      - lambda: |-
          // Calc Molecular Weight of Vapor above Oil
          double MW_Oil = 167.31102; // g_Oil/mol_Oil  (C12H23)
          double MW_Air = 28.9639475; // g_Air/mol_Air
          double P_Total = 101.325; // kPa (Could use a measured pressure here)
          double P_Oil = id(VP_Oil).state; // Partial Pressure of Oil kPa
          double P_Air = P_Total - P_Oil; // Partial Pressure Of Air kPa
          double nOil_per_nTotal = P_Oil / P_Total; // mol_Oil/mol_Total
          double nAir_per_nTotal = P_Air / P_Total; // mol_Air/mol_Total
          double g_Oil_per_nTotal = nOil_per_nTotal * MW_Oil; // g_Oil/mol_Total
          double g_Air_per_nTotal = nAir_per_nTotal * MW_Air; // g_Air/mol_Total
          double MW_Total = g_Oil_per_nTotal + g_Air_per_nTotal; // g_Total/mol_Total
          MW_Total = MW_Total / 1000; // kg_Totla/mol_Total
          // Back Calc Time of Flight
          double ESP_speed_sound_m_per_s = 343.0;
          double total_dist = x * 2.0;
          double time_s = total_dist / ESP_speed_sound_m_per_s;
          // Calc Speed of Sound in Vapor above Oil
          // https://en.wikipedia.org/wiki/Speed_of_sound
          double gamma = 1.4; // Oil is small enough fraction that large change in gamma is not expected
          double R = 8.31446261815324;
          double Sc = sqrt(gamma * R * 273.15 / MW_Total);
          double speed_sound_m_per_s = Sc * sqrt(1+(id(TempC).state/273.15)); // ideal diatomic gas
          // Calc Distance to Oil Surface
          total_dist = time_s * speed_sound_m_per_s;
          return id(Tank_Height) - (total_dist/2.0) * 1000 / 25.4;
      - calibrate_linear: # inches to Gallons
          method: exact
          datapoints:
            # https://allamericanenviro.com/determine-residential-heating-oil-tank-size-home-oil-tank-size-chart/
            # inches to gallons
            - 0	-> 0
            - 1	-> 3
            - 2	-> 6
            - 3	-> 11
            - 4	-> 17
            - 5	-> 23
            - 6	-> 30
            - 7	-> 37
            - 8	-> 44
            - 9	-> 52
            - 10	-> 60
            - 11	-> 68
            - 12	-> 77
            - 13	-> 85
            - 14	-> 93
            - 15	-> 102
            - 16	-> 110
            - 17	-> 119
            - 18	-> 127
            - 19	-> 136
            - 20	-> 144
            - 21	-> 152
            - 22	-> 161
            - 23	-> 169
            - 24	-> 178
            - 25	-> 186
            - 26	-> 194
            - 27	-> 203
            - 28	-> 211
            - 29	-> 220
            - 30	-> 228
            - 31	-> 237
            - 32	-> 245
            - 33	-> 253
            - 34	-> 262
            - 35	-> 270
            - 36	-> 278
            - 37	-> 285
            - 38	-> 292
            - 39	-> 299
            - 40	-> 306
            - 41	-> 311
            - 42	-> 317
            - 43	-> 320
            - 44	-> 325
    on_value:
      then:
        - script.execute: Calc_Oil
script:
#  - id: Calc_Oil_Height
#    then:
#      - if:
#          condition:
#            - lambda: |-
#                return id(Tank_Orientation) == 1; // Vertical
#          then:
#            - lambda: |-
#                id(Oil_Height) = id(Tank_Height) - (id(Oil_Distance).state * 1000 / 25.4);
#            - script.execute: Check_Oil_Height_V
#      - if:
#          condition:
#            - lambda: |-
#                return id(Tank_Orientation) == 2; // Horizontal
#          then:
#            - lambda: |-
#                id(Oil_Height) = id(Tank_Width) - (id(Oil_Distance).state * 1000 / 25.4);
#            - script.execute: Check_Oil_Height_H
  - id: Calc_Area
    then:
      - lambda: |-
          double d;
          double r;
          double arc;
          d = id(Arc_Height);
          r = id(Tank_Radius);
          arc = 2 * (acos((r-d)/r));
          id(Arc_Area) = ((r*r) * (arc - sin(arc))) / 2;
      - lambda: |-
          if (id(Tank_Orientation) == 1){ // Vertical
            id(Rectangle_Area) = id(Rectangle_Height) * id(Tank_Width);
          } else { // Horizontal
            id(Rectangle_Area) = id(Rectangle_Height) * (id(Tank_Height) - id(Tank_Width));
      - lambda: |-
          id(Total_Area) = id(Rectangle_Area) + id(Arc_Area);
#      - script.execute: Calc_Oil_Volume
  - id: Calc_Oil
    then:
          state: !lambda 'return id(Oil_In_Tank).state;'
          state: !lambda 'return id(Max_Fill) - id(Oil_In_Tank).state;'
      - if:
          condition:
            - switch.is_on: Auto_Sleep_Disable
          then:
            - globals.set:
                value: '0'
          else:
            - globals.set:
                value: !lambda 'return id(Measure_Count) += 1;'
            - if:
                condition:
                  - lambda: 'return id(Measure_Count) >= id(Samples_Before_Sleep);'
                then:
      - lambda: 'ESP_LOGD("MeasureCount", "%i", id(Measure_Count));'
      - if:
          condition:
            - switch.is_on: VarCheck
          then:
            - script.execute: Log_Values
  - id: Log_Values
    mode: queued
    then:
#      - lambda: |-
#          ESP_LOGD("VarCheck", "Tank_Orientation %.15g", id(Tank_Orientation));
#          ESP_LOGD("VarCheck", "Tank_Size %.15g", id(Tank_Size));
#          ESP_LOGD("VarCheck", "Oil_Distance %.15g", id(Oil_Distance).state);
#          ESP_LOGD("VarCheck", "Tank_Width %.15g", id(Tank_Width));
#          ESP_LOGD("VarCheck", "Tank_Height %.15g", id(Tank_Height));
#          ESP_LOGD("VarCheck", "Tank_Length %.15g", id(Tank_Length));
#          ESP_LOGD("VarCheck", "Tank_Radius %.15g", id(Tank_Radius));
#          ESP_LOGD("VarCheck", "Oil_Height %.15g", id(Oil_Height));
#          ESP_LOGD("VarCheck", "Arc_Height %.15g", id(Arc_Height));
#          ESP_LOGD("VarCheck", "Rectangle_Height %.15g", id(Rectangle_Height));
#          ESP_LOGD("VarCheck", "Arc_Area %.15g", id(Arc_Area));
#          ESP_LOGD("VarCheck", "Rectangle_Area %.15g", id(Rectangle_Area));
#          ESP_LOGD("VarCheck", "Total_Area%.15g", id(Total_Area));
#          ESP_LOGD("VarCheck", "Oil_In_Tank%.15g", id(Oil_In_Tank));
  - id: ultrasonic_loop
    mode: restart
    then:
      - delay: ${ultrasonic_interval}
      - while:
          condition:
            switch.is_on: ultrasonic_en
          then:
            - component.update: Oil_In_Tank
 # Tank Dimensions:
 # https://www.fuelsnap.com/heating_oil_tank_charts.php
  - id: set_tank_dimensions
    then:
      - lambda: |-
          if (id(Tank_Size) == 275){
              id(Max_Fill) = 250;
              id(Tank_Width) = 27.8;
              id(Tank_Height) = 44;
              id(Tank_Length) = 60;
          if (id(Tank_Size) == 330){
              id(Max_Fill) = 300;
              id(Tank_Length) = 72;
          if (id(Tank_Size) == 500){
              id(Max_Fill) = 450;
              id(Tank_Width) = 48;
              id(Tank_Height) = 48;
              id(Tank_Length) = 63.8;
          if (id(Tank_Size) == 550){
              id(Max_Fill) = 500;
              id(Tank_Length) = 70.25;
          if (id(Tank_Size) == 1000){
              id(Max_Fill) = 900;
              id(Tank_Length) = 127.6;
          id(Tank_Radius) = id(Tank_Width)/2;
To get the oil burn rate, I have an iotawatt meter on the electric circuit supplying the boiler along with a Shelly PM 1 in the boiler’s zone control that lets me figure out when the boiler’s blower and fuel pump are running. The tank sensor gives me the gallons consumed, the power meters gives me the runtime in hours. I expect a boiler’s gallons per hour burn rate to be fairly constant and not really dependant on the amount of oil in the tank. Using the calibrate linear filter gave me a slightly more constant burn rate calculation than calculating the volume of oil geometricly. When the oil does gets low enough to need a refill, I have seen that either method has given me fairly accurate measurements of how much oil would be needed to refill the tank.
Thanks for this, I will push this update to mine shortly when I get home next week.
Be sure and change the calibration table, the one I have in there is for a 330 gallon vertical tank.
Thanks so much for this. Can confirm the on_shutdown code update and additional Done sensor fixed the race condition for deep sleep. I’m going to submit a PR to update the documentation on github shortly.
Changing to the calibrate linear function adjusted the volume upwards by about 7 gallons. Will need to run for longer to assess the accuracy but this could be a future PR for the documentation although we’d need to setup substitutions for the calibration tables like there are already for tank dimensions and orientation.
They are still using an esp8266 for the duo.
I’ll do some poking of it to see how it does what it does.