Well I tried to use 1 as slave but didn’t help, but your comment made me realize that maybe I am missing some configuration in the VSR300 itself? meaning do I have to setup something in the air recuperation, like activate that modbus or something like this, I had no chance to do something like this since I didn’t receive yet the VSR300 remote with the LCD (it looks like there are lack of them and still the company which install it for didn’t have in stock so I could not check the menu) I have just basic one on/off and fan speed I think…

Here it wat i had to do with good help from the creator
1: took the vsr300.json file in vstudio and mass edited each node to use my modbus/tcp ip adress
2: After some trial and error we saw that the json file nodes also was hard coded to use 1 as slave adress and that does not change by setting it in node red itself, therfore setting the adress to 1 was imperitive if you do not want to mass edit the json to use another adress.
Also after importing the file check modbus settings that ip/port is correct.



I also use a none standard port in HF2211 because of a bug in the firmware



actually since it is modbus over tcpip the baudrate here does not matter

i sat my baudrate at the highest possible baud in vsr300 and took som polling nodes down from 30 & 10 seconds to 2 % 3 seconds since i thougt commands was a bit slow. After i got everyting working

Hi thanks for your help, just I am a bit lost, not sure where did you get those json files, I am afraid that maybe you have a different modbus-ethernet interface right? as I said I have like newer model from the one used here: https://www-hjemmeautomasjon-no.translate.goog/forside/guider/homeseer/mini-guide-hvordan-bruke-modbus-med-homeseer-r49/?_x_tr_sl=auto&_x_tr_tl=en&_x_tr_hl=en&_x_tr_pto=wapp

but not sure why it’s communicating properly, like it seems that it is receiving some messages but no transmitting anything… it is just weird… I also checked the firewall just in case but it seems to be ok… and I would see anyways some packages transmitted from the interface…

I tried with the debugging but there is not much there…

2022-10-12 10:34:42.999 DEBUG (SyncWorker_1) [pymodbus.client.sync] Connection to Modbus server established. Socket ('10.0.0.3', 47805)
2022-10-12 10:34:53.609 DEBUG (SyncWorker_1) [pymodbus.client.sync] Connection to Modbus server established. Socket ('10.0.0.3', 48215)
2022-10-12 10:35:04.823 DEBUG (SyncWorker_1) [pymodbus.client.sync] Connection to Modbus server established. Socket ('10.0.0.3', 59619)
2022-10-12 10:35:14.830 ERROR (SyncWorker_1) [homeassistant.components.modbus.modbus] Pymodbus: VTR300: Modbus Error: [Input/Output] Modbus Error: [Invalid Message] No response received, expected at least 8 bytes (0 received)
2022-10-12 10:35:15.586 DEBUG (SyncWorker_6) [pymodbus.client.sync] Connection to Modbus server established. Socket ('10.0.0.3', 55019)
2022-10-12 10:35:15.587 DEBUG (SyncWorker_6) [pymodbus.client.sync] New Transaction state 'SENDING'
2022-10-12 10:35:52.724 DEBUG (SyncWorker_6) [homeassistant.components.modbus.modbus] Pymodbus: VTR300: Modbus Error: [Input/Output] No Response received from the remote unit/Unable to decode response
2022-10-12 10:35:53.478 DEBUG (SyncWorker_3) [pymodbus.client.sync] Connection to Modbus server established. Socket ('10.0.0.3', 38081)
2022-10-12 10:35:53.479 DEBUG (SyncWorker_3) [pymodbus.client.sync] New Transaction state 'SENDING'
2022-10-12 10:36:30.615 DEBUG (SyncWorker_3) [homeassistant.components.modbus.modbus] Pymodbus: VTR300: Modbus Error: [Input/Output] No Response received from the remote unit/Unable to decode response
2022-10-12 10:36:31.368 DEBUG (SyncWorker_7) [pymodbus.client.sync] Connection to Modbus server established. Socket ('10.0.0.3', 57071)

Also I realised that maybe some option has to be activate in the VSR300… so on Monday it seems that I will have access to the other remove and I will be able to set it up… I will try and post the results here :slight_smile:

EDIT: As I was expecting was the configuration of the VSR300 so finally I am getting finally data from it, still I will need to have a look to the modbus guide, but it looks much better now :slight_smile:

2 Likes

I know this is completely offtopic but can someone explain in plain words

  1. What is the humidity transfer? I notice that at this point the rotary unit slows down to…
  2. Following the first Actual season for Demand Control 0: Summer 1: Winter (register 1039)

Hi! I have the same problem as you describe with the same RS485 to Ethernet device from USR IOT. I have the VSR500, but I guess it might be the same config as yours. Can you please explain what configuration you need to set on the VSR to get data from it? Best regards from Oystein.

Hi, so actually it was quite simple, I have just needed to match the config from the VSR to the RS485 to Ethernet device so:

And that was it…

1 Like

Well about the humidity transfer I realized it is happening whenever in the room where the machine is, there is higher humidity than the one set in Set Point in the section Moisture transfer control, so I guess it’s just trying to compensate the humidity somehow…

For the second question I have no idea, I am also trying to understand how this works :slight_smile:

Ah, nice. I only have a «light display» type where it is only possible to change the power. And in my region they can’t deliver the save touch panel. Thanks anyhow for the answer!

Ohh I feel you, I waited 1.5 months for it! but in the meantime maybe you can ask the installers to activate this option for you, and you won’t need at all the other remote controller :slight_smile:

1 Like

Why not just match the USR IOT settings.

Have the same except for baudrate. But as i remember it was trial and error.

modbus:
type: serial
method: rtu
port: /dev/ttymodbus
baudrate: 9600
stopbits: 1
bytesize: 8
parity: N

oh in my case were completely different, the baudrate was nearly the minimum and a few other things… I really needed to change it …

Any ideas what is the difference between modbus registers?

12103 -400 800 Supply Air Temperature sensor (standard)
and
12108 -400 800 Over Heat Temperature sensor (Electrical
Heater)

Which one is the temp of the supplied air temp?

Did anybody find a way to get modbus to work with usb from factory settings? With only having the “Light screen” ?

I got some info from systemair today.
Modbus should be active from factory, with this settings:
image

Hi,
I’m trying to communicate with the VSR 300 by modbus/RTU, but with your configuration i am not getting the response.
Slave address 0 is reserved to broadcast (only write without response).
Are you getting a response with this setting?

I had to try different USB adresses.

This is what I use now
modbus:

  • name: hub1
    type: serial
    method: rtu
    port: /dev/ttyUSB1
    baudrate: 1200
    stopbits: 1
    bytesize: 8
    parity: N
    sensors:

I have also used USB0 (dont know why it changed to 1)

My guess is that the overheat sensor is ON or very near the heater element.
So if the heater is on, then this temp will be higher then the supplied air.
If its off, it should be the same temp.