Vevor EM5500 solar modbus interface
I have a Vevor EM5500-48 inverter with battery and I would like to get the status of the battery and all available information via Modbus. A modbus connection via Waveshare modbus is realised but I don’t know how to obtain data. Probably via Solax inverter but I don’t know how to coninue. I have received the modbus documentation via Vevor. Can somebody help?
MeatimeI have build the mobus.yaml and also verified with a separate app that my device is communicating. I can define entities but they all are ‘unavalable’.
The main part of modbus .yaml looks like:
  - name: modbus_hub
    type: tcp
    host: 192.168.22.120
    port: 502
    sensors:
      - name: Mains voltage effective value
        slave: 1
        address: 202 # <- Register address
        input_type: input
        data_type: int16  # or maybe int16
        unit_of_measurement: "V"
        scale: 0.1
        scan_interval: 5
      - name: Mains frequency
        slave: 1
        address: 203 # <- Register address
        input_type: input
        unit_of_measurement: "Hz"
        scale: 0.01
        scan_interval: 5
Can somebody advicewhat to do? The logfile states ‘Pymodbus: modbus_hub: Error: device: 1 address: 202 → Modbus Error: [Input/Output] No response received after 3 retries, continue with next request’
Thanks in advance!
I figured it out. Seems that the registers are no input registers but holding registers!
Example:
  - name: modbus_hub
    type: tcp
    port: 502
    sensors:
      - name: "Mains voltage effective value"
        slave: 1
        input_type: holding
        scale: 0.1
        scan_interval: 5
      - name: "Mains frequency"
        slave: 1
        input_type: holding
        scale: 0.01
        scan_interval: 5
      - name: "Battery percentage"
        slave: 1 # <- Device address
        address: 229 # <- Register address
        input_type: holding
        unit_of_measurement: "%"
Hi bosmanrja,
I have the Vevor EM3500-24L model and have the wifi enabled but port 502 doesn’t seem to be open (using nmap from a Linux box on same IP net to test). I have also now tried the Waveshare USB TO RS485 (B) adapter and used a Rj45 cable to connect (pin 1 to B and 2 to A and swapped) to the RS-485 port, but no luck in connecting. I am testing using Galdalf Modbus Wizard to test whether I can get modbus via the USB Waveshare. Any hints?
Hi everyone,
I saw the existing thread regarding Modbus access for the Vevor EM5500/EM6200 hybrid inverters. I contacted Vevor directly and received what appears to be the Chinese communication protocol document (“1号通讯协议”).
Thats the Link Vevor send me: 1号通讯协议
Disclaimer:
The Modbus register map below is derived from an AI-generated translation of the Vevor inverter’s internal communication protocol (‘1号通讯协议’). Due to the nature of automated translation for technical documentation, the accuracy of register definitions, data formats, and error codes cannot be guaranteed. Always cross-reference this data before deploying it in a live system.
Communication Data Format :floppy_disk:
During communication, data is sent back in the form of words (WORD - 2 bytes). In each word sent back, the high byte comes first and the low byte comes last. If two words are sent back consecutively (e.g., long integer), the high word comes first and the low word comes last.
Data Type Number of Registers Byte Count Illustration
Character Type 1 1 Send back two characters at a time, padded with 0 if necessary.
Plastic Surgery 1 2 Send back in one go, with the high byte first and the low byte last.
Long plastic surgery 2 4 Send back in two words, with the higher word first and the lower word second.
Frame Format :envelope:
Register Content Lookup (Function Code 03H)
The start and end addresses of the query must be the start and end addresses of a complete data block; otherwise, the returned data will be incorrect. For example, if the starting address of the device serial number register is 186 and the length is 12, then the starting address during the query cannot be between 186 and 198, and similarly, the ending address (starting address + number of registers read) cannot fall within this range.
Frame Format Sent by the Host Computer
Byte Order Code Example Illustration
0 Device address 01H Device address (1~247)
1 03H 03H Function code
2 High byte of start register address 00H High 8 bits of register address
3 Start register address low byte 10H Lower 8 bits of register address
4 Number of registers (high byte) 00H High 8 bits of the register count
5 Number of registers (low byte) 02H The lower 8 bits of the register count
6 CRC16 checksum of high byte C0H CRC16 checksum high 8 bits
7 CRC16 checksum of low byte CBH CRC16 checksum low 8 bits
Frame Format Successfully Parsed and Sent Back by the Lower-Level Machine
Byte Order Code Illustration
0 Device address Device address (1~247)
1 03H Function code
2 Number of bytes of data sent back (N) N = number of requested registers * 2
3 The first register data high byte
4 The low byte of the first register data
N+2 The high byte of data in the Nth register
N+3 The low byte of data in the Nth register
N+4 CRC16 checksum of high byte All bytes preceding the CRC checksum must be included in the verification.
N+5 CRC16 checksum of low byte
Lower-Level Machine Parsing Error Feedback Frame Format
1 03H Function code
3 The first zero A total of N zeros were sent back.
4 The second zero
N+2 The (N-1)th zero
N+3 The Nth zero
Register Read Example:
Read the effective value of the mains voltage (start register 202) to the average value of the mains power, where the mains voltage returns 230.0V, the mains frequency returns 50.0Hz, and the average mains power returns 1200W.
  • Host computer: 01 03 00 CA 00 03 25 F5
  • Lower-level machine: 01 03 06 08 FC 13 88 04 B0 F7 F3
Register Content Settings (Function Code 10H)
1 10H 10H Function code
2 High byte of start register address 01H High 8 bits of register address
4 Number of registers (high byte) 00H The number of registers is always equal to 0 in the high 8 bits.
6 Number of bytes to be written (N) N = number of registers * 2
7 The first register data high byte
8 The low byte of the first register data
N+6 The high byte of data in the Nth register
N+7 The low byte of data in the Nth register
N+8 CRC16 checksum of high byte CRC16 checksum high 8 bits
N+9 CRC16 checksum of low byte CRC16 checksum low 8 bits
6 CRC16 checksum of high byte 41H CRC16 checksum high 8 bits
7 CRC16 checksum of low byte F1H CRC16 checksum low 8 bits
1 90H Function code
2 Error code Error code
3 CRC16 checksum of high byte CRC16 checksum high 8 bits
4 CRC16 checksum of low byte CRC16 checksum low 8 bits
Error Code Description
Code Illustration
01H The read-only register was manipulated.
03H Writing data beyond the acceptable range
07H Registers that cannot be modified in the current operating mode
Register Write Example:
Set the output voltage (start register 320) to 220V.
  • Host computer: 01 10 01 40 00 01 02 08 98 BE 3A
  • Lower-level machine: 01 10 01 40 00 01 01 E1
Device Register Address :round_pushpin:
  • R: Indicates readability, meaning it supports the 03H command.
  • W: Indicates writeability, meaning it supports the 10H command.
  • Int: Integer; Long: Long integer; UInt: Unsigned integer; ULong: Unsigned long integer; ASC: ASCII code.
  • Max: Retrieves the maximum value; Min: Retrieves the minimum value.
  • All addresses in the table below are represented in decimal.
Data Name Unit Data Format Starting Address Number of Registers Reading and Writing Remark
Equipment Fault Codes Long 100 2 R The fault codes are 32 bits, with each bit corresponding to a specific fault code. See the fault code table for details. Fault code 1 corresponds to bit 1, fault code 2 corresponds to bit 2, and so on.
Reserved 102 2 Reserved address
Obtaining warning codes without masking 104 2 For details on 32-bit warning codes, please refer to the warning code description.
Reserved 106 2 Reserved address
Get the warning code after blocking Long 108 2 R/W For details on 32-bit warning codes, please refer to the warning code description.
Reserved 110 61 Reserved address
Equipment type UInt 171 1 R
Equipment Name ASC 172 12 R/W Device name, written or read in ASCII format
Invalid data UInt 184 1 R Protocol number, this protocol returns 1
Reserved 185 1 Reserved address
Device serial number ASC 186 12 R
Reserved 198 2 Reserved address
Invalid data UInt 200 1 Internal commands
Work mode UInt 201 1 R 0: Power-on mode; 1: Standby mode; 2: AC power mode; 3: Off-grid mode; 4: Bypass mode; 5: Charging mode; 6: Fault mode.
Effective value of mains voltage 0.1v Int 202 1 R
Mains frequency 0.01Hz Int 203 1 R
Average mains power 1w Int 204 1 R
Inverter voltage RMS value 0.1v Int 205 1 R
Inverter current RMS value 0.1A Int 206 1 R
Inverter frequency 0.01Hz Int 207 1 R
Average inverter power 1w Int 208 1 R Positive numbers represent inverter outputs, and negative numbers represent inverter inputs.
Inverter charging power 1w Int 209 1 R
Output voltage RMS value 0.1v Int 210 1 R
Output current RMS value 0.1A Int 211 1 R
Output frequency 0.01Hz Int 212 1 R
Output active power 1w Int 213 1 R
Output apparent power 1VA Int 214 1 R
Average battery voltage 0.1v Int 215 1 R
Average battery current 0.1A Int 216 1 R
Average battery power 1w Int 217 1 R
Invalid data 218 1 Internal commands
PV voltage average 0.1v Int 219 1 R
Average PV current 0.1A Int 220 1 R
Reserved 221 2 Reserved address
Average PV power 1w Int 223 1 R
Average PV charging power 1w Int 224 1 R
load percentage 1% Int 225 1 R
DCDC temperature 1℃ Int 226 1 R
Inverter temperature 1℃ Int 227 1 R
Reserved 228 1 Reserved address
Battery percentage 1% UInt 229 1 R
Invalid data 230 1 Internal commands
Electricity flow status UInt 231 1 R See the description of the current flag for details.
Battery current filtered average value 0.1A Int 232 1 R Positive numbers indicate charging, and negative numbers indicate discharging.
Average inverter charging current 0.1A Int 233 1 R
Average PV charging current 0.1A Int 234 1 R
Invalid data 235 1 Internal commands
Invalid data 236 1 Internal commands
Reserved 237 63 Reserved address
Output mode Uint 300 1 R/W 0: Single unit; 1: Parallel unit; 2: Three-phase combination - P1; 3: Three-phase combination - P2; 4: Three-phase combination - P3
Output priority Uint 301 1 R/W 0: Mains - PV - Battery (UTI); 1: PV - Mains - Battery (SOL) [Inverter preferred]; 2: PV - Battery - Mains (SBU); 3: PV - Mains - Battery (SUB) [Mains preferred]
Input voltage range Uint 302 1 R/W 0: APL; 1: UPS;
Buzzer mode Uint 303 1 R/W 0: Mute in all situations; 1: Sounds when the input source changes, or when there is a specific warning or malfunction; 2: Sounds when there is a specific warning or malfunction; 3: Sounds when there is a malfunction;
Reserved 304 1 R/W Reserved address
LCD backlight Uint 305 1 R/W 0: Timed shutdown; 1: Always on;
The LCD automatically returns to the homepage. Uint 306 1 R/W 0: Do not return automatically; 1: Return automatically after 1 minute;
Energy Saving Mode Switch Uint 307 1 R/W 0: Energy saving mode off; 1: Energy saving mode on;
Overload automatic restart Uint 308 1 R/W 0: No restart for overload fault; 1: Automatic restart for overload fault;
Automatic restart when overheating Uint 309 1 R/W 0: No restart for over-temperature fault; 1: Automatic restart for over-temperature fault;
Overload bypass enable Uint 310 1 R/W 0: Disable; 1: Enable;
Reserved 311 2 Reserved address
Battery Eq mode enabled Uint 313 1 R/W 0: Disable; 1: Enable;
Warning mask [I] Long 314 2 R/W Warnings with a value of 1 are displayed normally, while warnings with a value of 0 are blocked.
dry contact Uint 316 1 R/W 0: Normal mode; 1: Grounding box mode;
Reserved 317 3 Reserved address
Output voltage 0.1v Uint 320 1 R/W 2200: 220V output; 2300: 230V output; 2400: 240V output;
Output frequency 0.01Hz Uint 321 1 R/W 5000: 50Hz output; 6000: 60Hz output;
Battery Type Uint 322 1 R/W 0: AGM; 1: FLD; 2: USER; 3: Li1; 4: Li2; 5: Li3; 6: Li4
Battery overvoltage protection point [A] 0.1v Uint 323 1 R/W Range: ( B + 1v * J ) ~ 16.5v * J
Maximum charging voltage [B] 0.1v Uint 324 1 R/W Range: C ~ ( A - 1v)
Float charging voltage [C] 0.1v Uint 325 1 R/W Range: (12v * J ) ~ B
Battery discharge recovery point in AC power mode [D] 0.1v Uint 326 1 R/W Range: ( B - 0.5V * J ) ~ Max(12V * J , E ) Setting it to 0 indicates full recovery.
Mains power mode battery low voltage protection point [E] 0.1v Uint 327 1 R/W Range: Min(14.3v * J , D ) ~ Max(11v * J , F )
Reserved 328 1 Reserved address
Off-grid mode battery low voltage protection point [F] 0.1v Uint 329 1 R/W Range: (10V * J ) ~ Min(13.5V * J , E )
Waiting time for constant voltage to float charging min Uint 330 1 R/W Range: 1~900min. Setting it to 0 will default to 10min.
Battery charging priority Uint 331 1 R/W 0: Mains power priority; 1: PV priority; 2: PV and mains power are of equal priority; 3: Only PV charging is allowed.
Maximum charging current [G] 0.1A Uint 332 1 R/W Range: Max(10A, H ) ~ 80A
Maximum AC charging current [H] 0.1A Uint 333 1 R/W Range: 2A ~ G
Eq charging voltage 0.1v Uint 334 1 R/W Range: C ~ ( A - 0.5v * J )
bat_eq_time min Uint 335 1 R/W Range: 0 ~ 900
Eq timed out and exited min Uint 336 1 R/W Range: 0 ~ 900
Interval between two Eq charges day Uint 337 1 R/W Range: 1 ~ 90
Automatic mains output enable Uint 338 1 R/W 0: No AC power output without pressing the power button; 1: AC power output will automatically occur even without pressing the power button.
Reserved 339 2 Reserved address
Mains power mode battery discharge SOC protection value [K] 1% Uint 341 1 R/W Range: 5%~96%
Mains power mode battery discharge SOC recovery value 1% Uint 342 1 R/W Range: 10%~100%
Off-grid mode battery discharge SOC protection value 1% Uint 343 1 R/W Range: 0%~Min( K , 95%)
Reserved 344 7
Maximum discharge current protection 1A Uint 351 1 R/W Maximum discharge current protection value in single-machine mode
Reserved 352 3
Mains power identification times Uint 355 1 R/W The time required for the machine to detect mains power and then determine that mains power is available. Range: 5 ~ 300
Lithium battery activation times Uint 356 1 R/W Range: 6 ~ 300
Lithium battery stops charging SOC 1% Uint 357 1 R/W After successful communication with the lithium battery, the SOC value is obtained. Charging stops when the set SOC is reached. Range: 20 ~ 100
BMS Follow Mode Uint 358 1 R/W 0: Charging voltage and current do not follow BMS values. 1: CV and Float voltage follow BMS and cannot be set; charging current does not follow BMS. 2: CV, Float voltage, and maximum charging current follow BMS and cannot be set. 3: Charging stops based on the set SOC, not the voltage; charging current does not follow BMS. 4: Charging stops based on the set SOC, not the voltage; maximum charging current follows BMS and cannot be set.
EEPROM maximum charging voltage 0.1v Uint 359 1 R
EEPROM float charge voltage 0.1v Uint 360 1 R
EEPROM maximum charging current 0.1A Uint 361 1 R
Reserved 362 38
Power-on method Uint 406 1 R/W 0: Can be powered on locally or remotely; 1: Can only be powered on locally; 2: Can only be powered on remotely.
Reserved 407 13 Reserved address
Remote switch Uint 420 1 R/W 0: Remote shutdown; 1: Remote power on
Invalid data 421 1 Internal commands
Reserved 422 3 Reserved address
Forced Eq charging Uint 425 1 IN 1: Manually force EQ to charge once.
Exit fault lockout state Uint 426 1 IN 1: Exit fault lockout state (this will only take effect if the machine enters fault mode)
Invalid data 427 1 Internal commands
Reserved 428 22 Reserved address
Invalid data 450 7 Internal commands
Reserved 457 3 Reserved address
Clear records 460 1 IN 0xAA: Clear operation and fault records (effective in non-offline mode)
Reset user parameters 461 1 IN 0xAA: Restores user parameters to default values ​​(works in non-offline mode)
Invalid data 462 6 Internal commands
Reserved 468 32 Reserved address
Invalid data 500 34 Internal commands
Reserved 534 66 Reserved address
Invalid data 600 34 Internal commands
Program version ASC 626 8 R
Reserved 634 7 Reserved address
Rated power In UInt 643 1 R
Rated number of battery cells [J] PCS UInt 644 1 R
Reserved 645 55 Reserved address
Fault log storage information [K] Long 700 2 R High 16 bits: Position of the latest record; Low 16 bits: Total number of existing fault messages.
Fault Information Query Index [L] Uint 702 1 R/W Set the index for the fault information to be queried, ranging from 0 to the total number of existing fault information entries.
Fault Log [M] 703 26 R See the fault log format for details.
Run log 729 16 R See the running log for details.
Reserved 745 5 Reserved address
Fault Code Table :stop_sign:
Fault Codes Illustration
1 Inverter overheating
2 DCDC overheating
3 Battery overvoltage
4 PV overheating
5 Output short circuit
6 Inverter overvoltage
7 Output overload
8 Busbar overvoltage
9 Busbar soft start timeout
10 PV overcurrent
11 PV overvoltage
12 Battery overcurrent
13 Inverter overcurrent
14 Busbar Low Voltage
15 Reserve
16 Inverter DC component too high
17 Reserve
18 Output current zero bias is too large
19 Inverter current zero bias too large
20 Excessive battery current zero bias
21 PV current zero bias is too large
22 Inverter low voltage
23 Inverter negative power protection
24 Parallel system main unit lost
25 Synchronization signal abnormality in parallel system
26 Battery type incompatible
27 Parallel version incompatible
Warning Code Explanation :warning:
System warnings are 32-bit unsigned long integers, with each bit corresponding to a warning. Each bit can also be masked using a warning mask I. If a warning is masked, it will not be read on the LCD or through commands.
Warning Code Table
Bit Illustration
bit 0 Mains power zero crossing loss
bit 1 Abnormal mains waveform
bit 2 Mains overvoltage
bit 3 Undervoltage of mains power
bit 4 Overfrequency mains power
bit 5 Mains power frequency
bit 6 PV undervoltage
bit 7 Overheating
bit 8 Low battery voltage
bit 9 Battery not connected
bit 10 Overload
bit 11 Battery Eq charging
bit 12 The battery is discharging at a low voltage and has not yet been charged back to its recovery point.
bit 13 Output power derating
bit 14 Fan stall
bit 15 PV energy is too low to use
bit 16 Parallel communication interrupted
bit 17 Inconsistent single and parallel output modes
bit 18 Excessive voltage difference between parallel batteries
bit 19 Lithium battery communication anomaly
bit 20 Battery discharge current exceeds set value
bit 21~31 Reserve
Current Symbol Explanation :battery:
Electric current is represented by a 16-bit unsigned integer, and the meaning of each bit is shown in the table below:
Power Flow Table
Bit Illustration
bit 0~1 0: PV not connected to the system; 1: PV connected to the system
bit 2~3 0: Mains power not connected to the system; 1: Mains power connected to the system.
bit 4~5 0: Battery neither charging nor discharging; 1: Battery charging; 2: Battery discharging.
bit 6~7 0: System does not output load; 1: System outputs load.
bit 8 0: Not charging via AC power; 1: Charging via AC power
bit 9 0: PV not charging; 1: PV charging
bit 10 0: Battery icon lit; 1: Battery icon off.
bit 11 0: PV icon lit; 1: PV icon off.
bit 12 0: Power icon lit; 1: Power icon off
bit 13 0: Load icon is on; 1: Load icon is off.
CRC Check Algorithm :locked:
Parametric model: CRC-16/MODBUS $X^{16} + X^{15} + X^2 + 1$
C code
`Cconst char auchCRCHi = {
0x00, 0xC1, 0x81, 0x40, 0x01, 0xC0, 0x80, 0x41, 0x01, 0xC0,
0x80, 0x41, 0x00, 0xC1, 0x81, 0x40, 0x01, 0xC0, 0x80, 0x41,
0x00, 0xC1, 0x81, 0x40, 0x00, 0xC1, 0x81, 0x40, 0x01, 0xC0,
0x80, 0x41, 0x01, 0xC0, 0x80, 0x41, 0x00, 0xC1, 0x81, 0x40,
0x00, 0xC1, 0x81, 0x40, 0x01, 0xC0, 0x80, 0x41, 0x00, 0xC1,
0x81, 0x40, 0x01, 0xC0, 0x80, 0x41, 0x01, 0xC0, 0x80, 0x41,
0x81, 0x40, 0x00, 0xC1, 0x81, 0x40, 0x01, 0xC0, 0x80, 0x41,
0x80, 0x41, 0x00, 0xC1, 0x81, 0x40, 0x00, 0xC1, 0x81, 0x40,
0x01, 0xC0, 0x80, 0x41, 0x01, 0xC0, 0x80, 0x41, 0x00, 0xC1,
0x81, 0x40, 0x01, 0xC0, 0x80, 0x41, 0x00, 0xC1, 0x81, 0x40,
0x01, 0xC0, 0x80, 0x41, 0x00, 0xC1, 0x81, 0x40, 0x01, 0xC0,
const char auchCRCLo = {
0x00, 0xC0, 0xC1, 0x01, 0xC3, 0x03, 0x02, 0xC2, 0xC6, 0x06,
0x07, 0xC7, 0x05, 0xC5, 0xC4, 0x04, 0xCC, 0x0C, 0x0D, 0xCD,
0x0F, 0xCF, 0xCE, 0x0E, 0x0A, 0xCA, 0xCB, 0x0B, 0xC9, 0x09,
0x08, 0xC8, 0xD8, 0x18, 0x19, 0xD9, 0x1B, 0xDB, 0xDA, 0x1A,
0x1E, 0xDE, 0xDF, 0x1F, 0xDD, 0x1D, 0x1C, 0xDC, 0x14, 0xD4,
0xD5, 0x15, 0xD7, 0x17, 0x16, 0xD6, 0xD2, 0x12, 0x13, 0xD3,
0x11, 0xD1, 0xD0, 0x10, 0xF0, 0x30, 0x31, 0xF1, 0x33, 0xF3,
0xF2, 0x32, 0x36, 0xF6, 0xF7, 0x37, 0xF5, 0x35, 0x34, 0xF4,
0x3C, 0xFC, 0xFD, 0x3D, 0xFF, 0x3F, 0x3E, 0xFE, 0xFA, 0x3A,
0x3B, 0xFB, 0x39, 0xF9, 0xF8, 0x38, 0x28, 0xE8, 0xE9, 0x29,
0xEB, 0x2B, 0x2A, 0xEA, 0xEE, 0x2E, 0x2F, 0xEF, 0x2D, 0xED,
0xEC, 0x2C, 0xE4, 0x24, 0x25, 0xE5, 0x27, 0xE7, 0xE6, 0x26,
0x22, 0xE2, 0xE3, 0x23, 0xE1, 0x21, 0x20, 0xE0, 0xA0, 0x60,
0x61, 0xA1, 0x63, 0xA3, 0xA2, 0x62, 0x66, 0xA6, 0xA7, 0x67,
0xA5, 0x65, 0x64, 0xA4, 0x6C, 0xAC, 0xAD, 0x6D, 0xAF, 0x6F,
0x6E, 0xAE, 0xAA, 0x6A, 0x6B, 0xAB, 0x69, 0xA9, 0xA8, 0x68,
0x78, 0xB8, 0xB9, 0x79, 0xBB, 0x7B, 0x7A, 0xBA, 0xBE, 0x7E,
0x7F, 0xBF, 0x7D, 0xBD, 0xBC, 0x7C, 0xB4, 0x74, 0x75, 0xB5,
0x77, 0xB7, 0xB6, 0x76, 0x72, 0xB2, 0xB3, 0x73, 0xB1, 0x71,
0x70, 0xB0, 0x50, 0x90, 0x91, 0x51, 0x93, 0x53, 0x52, 0x92,
0x96, 0x56, 0x57, 0x97, 0x55, 0x95, 0x94, 0x54, 0x9C, 0x5C,
0x5D, 0x9D, 0x5F, 0x9F, 0x9E, 0x5E, 0x5A, 0x9A, 0x9B, 0x5B,
0x99, 0x59, 0x58, 0x98, 0x88, 0x48, 0x49, 0x89, 0x4B, 0x8B,
0x8A, 0x4A, 0x4E, 0x8E, 0x8F, 0x4F, 0x8D, 0x4D, 0x4C, 0x8C,
0x44, 0x84, 0x85, 0x45, 0x87, 0x47, 0x46, 0x86, 0x82, 0x42,
0x43, 0x83, 0x41, 0x81, 0x80, 0x40
unsigned short sModbusCrc16(INT8U *chMsg, INT16U dataLen)
unsigned char ubCRCHi = 0xFF;
unsigned char ubCRCLo = 0xFF;
unsigned char duwIndex;
while ( dataLen – )
duwIndex = 0xff&(ubCRCHi ^ *chMsg++);
ubCRCHi = 0xff&(ubCRCLo ^ auchCRCHi[duwIndex]);
ubCRCLo = auchCRCLo[duwIndex];
return (ubCRCHi << 8 | ubCRCLo);
I have used Waveshare RS485 to POE Eth.
In Homeassistant I added Modbus interface, line in configuration.yaml:
modbus: !include modbus.yaml
Contents Modbus.yaml:
  - name: modbus_hub
    type: tcp
    port: 502
    sensors:
      - name: "Equipment fault code"
        slave: 1
        address: 100
        input_type: holding
        data_type: int32
      - name: "Obtain the warning code after shield processing"
        slave: 1
        address: 108
        input_type: holding
        data_type: int32
      - name: "Device type"
        slave: 1
        address: 171
        input_type: holding
        data_type: int16
      - name: "Device name"
        slave: 1
        address: 172
        input_type: holding
        data_type: string
        count: 12
      - name: "Device serial number"
        slave: 1
        address: 186
        input_type: holding
        data_type: string
        count: 12
        slave: 1
        address: 202
        input_type: holding
        data_type: int16
        scale:  0.1
        slave: 1
        address: 203
        input_type: holding
        data_type: int16
        scale:  0.01
      - name: "Average mains power"
        slave: 1
        address: 204
        input_type: holding
        data_type: int16
        unit_of_measurement: "W"
        scale:  1
      - name: "Effective value of inverter voltage"
        slave: 1
        address: 205
        input_type: holding
        data_type: int16
        scale:  0.1
      - name: "Effective value of inverter current"
        slave: 1
        address: 206
        input_type: holding
        data_type: int16
        unit_of_measurement: "A"
        scale: 0.1
      - name: "Inverter frequency"
        slave: 1
        address: 207
        input_type: holding
        data_type: int16
        scale: 0.01
      - name: "Inverter power average"
        slave: 1
        address: 208
        input_type: holding
        data_type: int16
        scale: 1
      - name: "Inverter charging power"
        slave: 1
        address: 209
        input_type: holding
        data_type: int16
        scale: 1
      - name: "Effective value of output voltage"
        slave: 1
        address: 210
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Effective value of output current"
        slave: 1
        address: 211
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Output frequency"
        slave: 1
        address: 212
        input_type: holding
        data_type: int16
        scale: 0.01
      - name: "Average battery voltage"
        slave: 1
        address: 215
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Average battery current"
        slave: 1
        address: 216
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Average battery power"
        slave: 1
        address: 217
        input_type: holding
        data_type: int16
        scale: 1
      - name: "Average PV voltage"
        slave: 1
        address: 219
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Average PV current"
        slave: 1
        address: 220
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Average PV power"
        slave: 1
        address: 223
        input_type: holding
        data_type: int16
        scale: 1
      - name: "Average PV Charging power"
        slave: 1
        address: 224
        input_type: holding
        data_type: int16
        scale: 1
      - name: "Percent of load"
        slave: 1
        address: 225
        input_type: holding
        data_type: int16
        scale: 1
      - name: "DCDC temperature"
        slave: 1
        address: 226
        input_type: holding
        data_type: int16
        unit_of_measurement: "⁰C"
        scale: 1
      - name: "Inverter temperature"
        slave: 1
        address: 227
        input_type: holding
        data_type: int16
        scale: 1
        slave: 1
        address: 229
        input_type: holding
        data_type: int16
        scale: 1
      - name: "Power flow status"
        slave: 1
        address: 231
        input_type: holding
        data_type: int16
      - name: "Battery current filter average"
        slave: 1
        address: 232
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Average value of inverter charging current"
        slave: 1
        address: 233
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Average PV charging current"
        slave: 1
        address: 234
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Output mode"
        slave: 1
        address: 300
        input_type: holding
        data_type: int16
      - name: "Output priority"
        slave: 1
        address: 301
        input_type: holding
        data_type: int16
      - name: "Input voltage range"
        slave: 1
        address: 302
        input_type: holding
        data_type: int16
      - name: "Buzzer mode"
        slave: 1
        address: 303
        input_type: holding
        data_type: int16
      - name: "LCD Backlight"
        slave: 1
        address: 305
        input_type: holding
        data_type: int16
      - name: "LCD automatically returns to the homepage"
        slave: 1
        address: 306
        input_type: holding
        data_type: int16
      - name: "Energy saving mode switch"
        slave: 1
        address: 307
        input_type: holding
        data_type: int16
      - name: "Overload automatic restart"
        slave: 1
        address: 308
        input_type: holding
        data_type: int16
      - name: "Overtemperature automatic restart"
        slave: 1
        address: 309
        input_type: holding
        data_type: int16
      - name: "Overload bypass enable"
        slave: 1
        address: 310
        input_type: holding
        data_type: int16
      - name: "Battery Eq mode enable"
        slave: 1
        address: 313
        input_type: holding
        data_type: int16
      - name: "Warning mask (I)"
        slave: 1
        address: 314
        input_type: holding
        data_type: int32
      - name: "Dry contact"
        slave: 1
        address: 316
        input_type: holding
        data_type: int16
      - name: "Output voltage"
        slave: 1
        address: 320
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Output frequency set"
        slave: 1
        address: 321
        input_type: holding
        data_type: int16
        scale: 0.01
      - name: "Battery type"
        slave: 1
        address: 322
        input_type: holding
        data_type: int16
      - name: "Battery overvoltage protection point [A]"
        slave: 1
        address: 323
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Maximum charge voltage [B]"
        slave: 1
        address: 324
        input_type: holding
        data_type: int16
      - name: "Maximum charge voltage [C]"
        slave: 1
        address: 325
        input_type: holding
        data_type: int16
      - name: "Mains mode battery discharge recovery point [D]"
        slave: 1
        address: 326
        input_type: holding
        data_type: int16
      - name: "Battery low voltage protection point inmains mode [E]"
        slave: 1
        address: 327
        input_type: holding
        data_type: int16
      - name: "Off-grid mode battery low voltage protection point [F]"
        slave: 1
        address: 329
        input_type: holding
        data_type: int16
      - name: "Waiting time from constant voltage to floating charge"
        slave: 1
        address: 330
        input_type: holding
        data_type: int16
      - name: "Battery charging priority"
        slave: 1
        address: 331
        input_type: holding
        data_type: int16
      - name: "Maximum charge current [G]"
        slave: 1
        address: 332
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "Maximum mains charging current [H]"
        slave: 1
        address: 333
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "The charging voltage of Eq"
        slave: 1
        address: 334
        input_type: holding
        data_type: int16
        scale: 0.1
      - name: "bat_eq_time"
        slave: 1
        address: 335
        input_type: holding
        data_type: int16
        unit_of_measurement: "min"
        scale: 1
      - name: "EQ timed out"
        slave: 1
        address: 336
        input_type: holding
        data_type: int16
        scale: 1
      - name: "Two-time EQ charge interval"
        slave: 1
        address: 337
        input_type: holding
        data_type: int16
        unit_of_measurement: "day"
        scale: 1
      - name: "Automatic mains output enable"
        slave: 1
        address: 338
        input_type: holding
        data_type: int16
      - name: "Mains mode battery discharge SOC protectionvalue [K]"
        slave: 1
        address: 341
        input_type: holding
        data_type: int16
        scale: 1
      - name: "Mains mode battery discharge SOC recovery value"
        slave: 1
        address: 342
        input_type: holding
        data_type: int16
        scale: 1
      - name: "Battery discharge SOC protection in off-grid mode"
        slave: 1
        address: 343
        input_type: holding
        data_type: int16
        scale: 1
      - name: "Maximum discharge current protection"
        slave: 1
        address: 351
        input_type: holding
        data_type: int16
        scale: 1
      - name: "remote switch"
        slave: 1
        address: 420
        input_type: holding
        data_type: int16
      - name: "Forcing the charge of Eq"
        slave: 1
        address: 425
        input_type: holding
        data_type: int16
      - name: "Exits the fail-locked state"
        slave: 1
        address: 426
        input_type: holding
        data_type: int16
      - name: "Program version"
        slave: 1
        address: 626
        input_type: holding
        data_type: string
        count: 8
      - name: "Rated power"
        slave: 1
        address: 643
        input_type: holding
        data_type: int16
        scale: 1
      - name: "Number of cells [J]"
        slave: 1
        address: 644
        input_type: holding
        data_type: int16
        unit_of_measurement: "PCS"
        scale: 1
      - name: "Fault record storage information [K]"
        slave: 1
        address: 700
        input_type: holding
        data_type: int32
      - name: "Fault information Query  Index"
        slave: 1
        address: 702
        input_type: holding
        data_type: int16
I’m reviving this thread, but I’d be interested to know if you managed to connect the Vevor to HA.
cordialy