Weishaupt WWP L9 ID - modbus

Inspired by the very pupular topic Weishaupt Heatpump integration via modbus - Share your Projects! - Home Assistant Community (home-assistant.io), I have decided to share my Weishaupt Heatpump (WWP L9 ID) setup as well.

Hardware

  • Weishaupt LWPM 410, ~150€
  • RS485 Konverter Bus Adapter Seriell USB, ~3€

Config

  • heatpump config

    • Menu → Config → Network: Select modbus, baudrate 9600 and slave address 1 (if only device)
    • Optional for Smart Grid: Menü + Enter → Config → Anlage → Flexeingang → N1/J5-ID1+2 digital: Smart Grid
  • modbus config

modbus:
  - name: weishaupt_wwp_l9
    type: serial
    baudrate: 9600
    bytesize: 8
    method: rtu
    parity: N
    port: /dev/ttyUSB0
    stopbits: 1
    #retry_on_empty: true
    timeout: 14
    climates:
    # Heizen
    - name: "WP Climate Heizen Temperatur"
      unique_id: wp_climate_heizentemperature
      address: 46 # 5 Vorlauf, scale 0.1
      slave: 1
      input_type: input
      data_type: int16
      max_temp: 38
      min_temp: 0
      offset: 0
      precision: 1
      scale: 1
      target_temp_register: 163 # Parallelverschiebung
      target_temp_write_registers: true
      temp_step: 1
      temperature_unit: C
    #  hvac_onoff_register: 103
    #  hvac_mode_register:
    #    address: 103
    #    values:
    #      state_off: 1
    #      state_heat: 2
    #      state_cool: 5
    - name: "WP Climate  Warmwasser Temperatur"
      unique_id: wp_climate_watertemperature
      address: 0 # 3, should be scale 0.1
      slave: 1
      input_type: input
      data_type: int16
      max_temp: 85
      min_temp: 10
      offset: 0
      precision: 1
      scale: 1
      target_temp_register: 174
      target_temp_write_registers: true
      temp_step: 1
      temperature_unit: C
      # leads to duplicate issue
      #hvac_onoff_register: 103
      #hvac_mode_register:
      #  address: 103
      #  values:
      #    state_off: 1
      #    state_heat: 4
    sensors:
    # Warmwasser
    - name: "WP Warmwasser Solltemperatur"
      unique_id: wp_warmwasser_solltemperatur
      slave: 1
      address: 58
      input_type: input
      unit_of_measurement: °C
      state_class: measurement
      scale: 0.1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Warmwasser Solltemperatur Maximal"
      unique_id: wp_warmwasser_solltemperatur_maximal
      slave: 1
      address: 175
      input_type: input
      unit_of_measurement: °C
      state_class: measurement
      scale: 1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Warmwasser Hysterese"
      unique_id: wp_warmwasser_hysterese
      slave: 1
      address: 172
      input_type: input
      unit_of_measurement: K
      state_class: measurement
      scale: 1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Warmwasser Temperatur"
      unique_id: wp_warmwasser_temperatur
      slave: 1
      address: 3
      input_type: input
      unit_of_measurement: °C
      state_class: measurement
      scale: 0.1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Warmwasser Thermische Desinfektion"
      unique_id: wp_warmwasser_thermische_desinfektion
      slave: 1
      address: 192
      input_type: input
      scale: 1
      offset: 0
      precision: 0
      data_type: int16
    # System
    - name: "WP Betriebsmodus ID"
      unique_id: wp_betriebsmodus_id
      slave: 1
      address: 142
      input_type: input
      scale: 1
      offset: 0
      precision: 0
      data_type: int16
    - name: "WP Display Status ID"
      unique_id: wp_display_status_id
      slave: 1
      address: 103
      input_type: input
      scale: 1
      offset: 0
      precision: 0
      data_type: int16
    - name: "WP Display Sperre ID"
      unique_id: wp_display_sperre_id
      slave: 1
      address: 104
      input_type: input
      scale: 1
      offset: 0
      precision: 0
      data_type: int16
    - name: "WP Display Störung ID"
      unique_id: wp_display_stoerung_id
      slave: 1
      address: 105
      input_type: input
      scale: 1
      offset: 0
      precision: 0
      data_type: int16
    - name: "WP Display Sensor ID"
      unique_id: wp_display_sensor_id
      slave: 1
      address: 106
      input_type: input
      scale: 1
      offset: 0
      precision: 0
      data_type: int16
    - name: "WP Außen Temperatur"
      unique_id: wp_aussen_temperatur
      slave: 1
      address: 1
      input_type: input
      unit_of_measurement: °C
      state_class: measurement
      scale: 0.1
      offset: 0
      precision: 1
      data_type: int16
    # Heizkreis
    - name: "WP Rücklauf Solltemperatur"
      unique_id: wp_ruecklauf_solltemperatur
      slave: 1
      address: 53
      input_type: input
      unit_of_measurement: °C
      state_class: measurement
      scale: 0.1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Vorlauf Temperatur"
      unique_id: wp_vorlauf_temperatur
      slave: 1
      address: 5
      input_type: input
      unit_of_measurement: °C
      state_class: measurement
      scale: 0.1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Rücklauf Temperatur"
      unique_id: wp_ruecklauf_temperatur
      slave: 1
      address: 2
      input_type: input
      unit_of_measurement: °C
      state_class: measurement
      scale: 0.1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Parallelverschiebung"
      unique_id: wp_parallelverschiebung
      slave: 1
      address: 163
      input_type: holding
      state_class: measurement
      scale: 1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Heizen Hysterese"
      unique_id: wp_heizen_hysterese
      slave: 1
      address: 47
      input_type: input
      unit_of_measurement: K
      state_class: measurement
      scale: 0.1
      offset: 0
      precision: 1
      data_type: int16
    # WEZ
    - name: "WP Verdichter1 Stunden"
      unique_id: wp_verdichter1_stunden
      slave: 1
      address: 72
      input_type: input
      unit_of_measurement: h
      state_class: measurement
      scale: 1
      offset: 0
      precision: 0
      data_type: int16
    - name: "WP 2.Wärmeerzeuger Stunden"
      unique_id: wp_2waermeerzeuger_stunden
      slave: 1
      address: 75
      input_type: input
      unit_of_measurement: h
      state_class: measurement
      scale: 1
      offset: 0
      precision: 0
      data_type: int16
    # Energy
    - name: "WP Energy Heizen 1-4"
      unique_id: wp_energy_heizen_1_4
      slave: 1
      address: 223
      input_type: input
      unit_of_measurement: kWh
      device_class: energy
      state_class: total
      scale: 1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Energy Heizen 5-8"
      unique_id: wp_energy_heizen_5_8
      slave: 1
      address: 224
      input_type: input
      unit_of_measurement: kWh
      device_class: energy
      state_class: total
      scale: 1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Energy Heizen 9-12"
      unique_id: wp_energy_heizen_9_12
      slave: 1
      address: 225
      input_type: input
      unit_of_measurement: kWh
      device_class: energy
      state_class: total
      scale: 1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Energy Warmwasser 1-4"
      unique_id: wp_energy_warmwasser_1_4
      slave: 1
      address: 226
      input_type: input
      unit_of_measurement: kWh
      device_class: energy
      state_class: total
      scale: 1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Energy Warmwasser 5-8"
      unique_id: wp_energy_warmwasser_5_8
      slave: 1
      address: 227
      input_type: input
      unit_of_measurement: kWh
      device_class: energy
      state_class: total
      scale: 1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Energy Warmwasser 9-12"
      unique_id: wp_energy_warmwasser_9_12
      slave: 1
      address: 228
      input_type: input
      unit_of_measurement: kWh
      device_class: energy
      state_class: total
      scale: 1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Energy Umwelt 1-4"
      unique_id: wp_energy_umwelt_1_4
      slave: 1
      address: 254
      input_type: input
      unit_of_measurement: kWh
      device_class: energy
      state_class: total
      scale: 1
      offset: 0
      precision: 1
      data_type: int16
    - name: "WP Energy Umwelt 5-8"
      unique_id: wp_energy_umwelt_5_8
      slave: 1
      address: 255
      input_type: input
      unit_of_measurement: kWh
      device_class: energy
      state_class: total
      scale: 1
      offset: 0
      precision: 1
      data_type: int16
    #- name: "WP Energy Umwelt 9-12"
    #  unique_id: wp_energy_umwelt_9_12
    #  slave: 1
    #  address: 256
    #  input_type: input
    #  unit_of_measurement: kWh
    #  device_class: energy
    #  state_class: total
    #  scale: 1
    #  offset: 0
    #  precision: 1
    #  data_type: int16
    binary_sensors:
    # Smart Grid
    - name: "WP Smart Grid 1"
      unique_id: wp_smart_grid_1
      slave: 1
      address: 3
      input_type: coil
    - name: "WP Smart Grid 2"
      unique_id: wp_smart_grid_2
      slave: 1
      address: 4
      input_type: coil
  • template sensors
template:
  - sensor:
      # WP Energy
      - name: "WP Energy Heizen (Total)"
        unique_id: wp_energy_heizen_total
        unit_of_measurement: 'kWh'
        state_class: total_increasing
        device_class: energy
        state: >-
          {% if states('sensor.wp_energy_heizen_1_4') in ['unknown', 'unavailable']
             or states('sensor.wp_energy_heizen_5_8') in ['unknown', 'unavailable']
             or states('sensor.wp_energy_heizen_9_12') in ['unknown', 'unavailable']
          %}
             {{ states("sensor.wp_energy_heizen_total") }}
          {% else %}
             {{ states("sensor.wp_energy_heizen_9_12")|float(0) * 100000000
              + states("sensor.wp_energy_heizen_5_8")|float(0) * 10000
              + states("sensor.wp_energy_heizen_1_4")|float(0)
             }}
          {% endif %}
      - name: "WP Energy Warmwasser (Total)"
        unique_id: wp_energy_warmwasser_total
        unit_of_measurement: 'kWh'
        state_class: total_increasing
        device_class: energy
        state: >-
          {% if states('sensor.wp_energy_warmwasser_1_4') in ['unknown', 'unavailable']
             or states('sensor.wp_energy_warmwasser_5_8') in ['unknown', 'unavailable']
             or states('sensor.wp_energy_warmwasser_9_12') in ['unknown', 'unavailable']
          %}
             {{ states("sensor.wp_energy_warmwasser_total") }}
          {% else %}
             {{ states("sensor.wp_energy_warmwasser_9_12")|float(0) * 100000000
              + states("sensor.wp_energy_warmwasser_5_8")|float(0) * 10000
              + states("sensor.wp_energy_warmwasser_1_4")|float(0)
             }}
          {% endif %}
      - name: "WP Energy Umwelt (Total)"
        unique_id: wp_energy_umwelt_total
        unit_of_measurement: 'kWh'
        state_class: total_increasing
        device_class: energy
        state: >-
          {% if states('sensor.wp_energy_umwelt_1_4') in ['unknown', 'unavailable']
             or states('sensor.wp_energy_umwelt_5_8') in ['unknown', 'unavailable']
          %}
             {{ states("sensor.wp_energy_umwelt_total") }}
          {% else %}
             {{ states("sensor.wp_energy_umwelt_5_8")|float(0) * 10000
              + states("sensor.wp_energy_umwelt_1_4")|float(0)
             }}
          {% endif %}
      - name: "WP Energy Grid (Total)"
        unique_id: wp_energy_grid_total
        unit_of_measurement: 'kWh'
        state_class: total_increasing
        device_class: energy
        state: >-
             {{ states("sensor.wp_energy_heizen_total")|float(0)
              + states("sensor.wp_energy_warmwasser_total")|float(0)
              - states("sensor.wp_energy_umwelt_total")|float(0)
             }}
      # WP Modus
      - name: "WP Betriebsmodus"
        unique_id: wp_betriebsmodus
        state: >
          {% if is_state('sensor.wp_betriebsmodus_id', '0') %}
            Sommer
          {% elif is_state('sensor.wp_betriebsmodus_id', '1') %}
            Auto
          {% elif is_state('sensor.wp_betriebsmodus_id', '2') %}
            Urlaub
          {% elif is_state('sensor.wp_betriebsmodus_id', '3') %}
            Party
          {% elif is_state('sensor.wp_betriebsmodus_id', '4') %}
            2.Wärmeerzeuger
          {% else %}
            {{ states('sensor.wp_betriebsmodus') }}
          {% endif %}
      # WP Smart Grid
      - name: "WP Smart Grid"
        unique_id: wp_smart_grid
        state: >-
          {% if states('binary_sensor.wp_smart_grid_1') in ['unknown', 'unavailable']
             or states('binary_sensor.wp_smart_grid_2') in ['unknown', 'unavailable']
          %}
            {{ states('sensor.wp_smart_grid') }}
          {% else %}
            {% if is_state('binary_sensor.wp_smart_grid_1', 'off') and is_state('binary_sensor.wp_smart_grid_2', 'on') %}
              rot
            {% elif is_state('binary_sensor.wp_smart_grid_1', 'off') and is_state('binary_sensor.wp_smart_grid_2', 'off') %}
              gelb
            {% elif is_state('binary_sensor.wp_smart_grid_1', 'on') and is_state('binary_sensor.wp_smart_grid_2', 'off') %}
              grün
            {% elif is_state('binary_sensor.wp_smart_grid_1', 'on') and is_state('binary_sensor.wp_smart_grid_2', 'on') %}
              dunkelgrün
            {% endif %}
          {% endif %}
      # WP Betrieb
      - name: "WP Display Status"
        unique_id: wp_display_status
        state: >
          {% if is_state('sensor.wp_display_status_id', '0') %}
            Aus
          {% elif is_state('sensor.wp_display_status_id', '1') %}
            Aus
          {% elif is_state('sensor.wp_display_status_id', '2') %}
            Heizen
          {% elif is_state('sensor.wp_display_status_id', '4') %}
            Warmwasser
          {% elif is_state('sensor.wp_display_status_id', '11') %}
            Durchflussüberwachung
          {% elif is_state('sensor.wp_display_status_id', '30') %}
            Sperre
          {% else %}
            {{ states('sensor.wp_display_status') }}
          {% endif %}
      # WP Display Sperre
      - name: "WP Display Sperre"
        unique_id: wp_display_sperre
        state: >
          {% if is_state('sensor.wp_display_sperre_id', '0') %}
            keine
          {% elif is_state('sensor.wp_display_sperre_id', '2') %}
            Volumenstrom
          {% elif is_state('sensor.wp_display_sperre_id', '5') %}
            Funktionskontrolle
          {% elif is_state('sensor.wp_display_sperre_id', '6') %}
            Einsatzgrenze HT
          {% elif is_state('sensor.wp_display_sperre_id', '7') %}
            Systemkontrolle
          {% elif is_state('sensor.wp_display_sperre_id', '9') %}
            Pumpenvorlauf
          {% elif is_state('sensor.wp_display_sperre_id', '10') %}
            Mindeststandzeit
          {% elif is_state('sensor.wp_display_sperre_id', '11') %}
            Netzbelastung
          {% elif is_state('sensor.wp_display_sperre_id', '12') %}
            Schaltspielsperre
          {% elif is_state('sensor.wp_display_sperre_id', '13') %}
            Warmwasser Nacherwärmung
          {% elif is_state('sensor.wp_display_sperre_id', '14') %}
            Regenerativ
          {% elif is_state('sensor.wp_display_sperre_id', '15') %}
            EVU-Sperre
          {% elif is_state('sensor.wp_display_sperre_id', '16') %}
            Sanftanlasser
          {% elif is_state('sensor.wp_display_sperre_id', '17') %}
            Durchfluss
          {% elif is_state('sensor.wp_display_sperre_id', '18') %}
            Einsatzgrenze Wärmepumpe
          {% elif is_state('sensor.wp_display_sperre_id', '19') %}
            Hochdruck
          {% elif is_state('sensor.wp_display_sperre_id', '20') %}
            Niederdruck
          {% elif is_state('sensor.wp_display_sperre_id', '21') %}
            Einsatzgrenze Wärmequelle
          {% elif is_state('sensor.wp_display_sperre_id', '23') %}
            System Grenze
          {% elif is_state('sensor.wp_display_sperre_id', '24') %}
            Last Primärkreis
          {% elif is_state('sensor.wp_display_sperre_id', '25') %}
            Sperre Extern
          {% elif is_state('sensor.wp_display_sperre_id', '31') %}
            Aufwärmen
          {% elif is_state('sensor.wp_display_sperre_id', '33') %}
            EvD Initialisierung
          {% elif is_state('sensor.wp_display_sperre_id', '34') %}
            2.Wärmeerzeuger freigegeben
          {% elif is_state('sensor.wp_display_sperre_id', '35') %}
            Störung
          {% elif is_state('sensor.wp_display_sperre_id', '38') %}
            Kommunikation Wärmepumpe (Master)
          {% elif is_state('sensor.wp_display_sperre_id', '39') %}
            Störung Wärmepumpe (Master)
          {% else %}
            {{ states('sensor.wp_display_sperre') }}
          {% endif %}
      # WP Display Störung
      - name: "WP Display Störung"
        unique_id: wp_display_stoerung
        state: >
          {% if is_state('sensor.wp_display_stoerung_id', '0') %}
            keine
          {% elif is_state('sensor.wp_display_stoerung_id', '1') %}
            Fehler N17.1
          {% elif is_state('sensor.wp_display_stoerung_id', '2') %}
            Fehler N17.2
          {% elif is_state('sensor.wp_display_stoerung_id', '3') %}
            Fehler N17.3
          {% elif is_state('sensor.wp_display_stoerung_id', '4') %}
            Fehler N17.4
          {% elif is_state('sensor.wp_display_stoerung_id', '6') %}
            Elektronisches Ex.Ventil
          {% elif is_state('sensor.wp_display_stoerung_id', '10') %}
            WPIO
          {% elif is_state('sensor.wp_display_stoerung_id', '12') %}
            Inverter
          {% elif is_state('sensor.wp_display_stoerung_id', '13') %}
            WQIF
          {% elif is_state('sensor.wp_display_stoerung_id', '15') %}
            Sensorik
          {% elif is_state('sensor.wp_display_stoerung_id', '16') %}
            Niederdruck Sole
          {% elif is_state('sensor.wp_display_stoerung_id', '19') %}
            Primärkreis
          {% elif is_state('sensor.wp_display_stoerung_id', '20') %}
            Abtauen
          {% elif is_state('sensor.wp_display_stoerung_id', '21') %}
            Niederdruck Sole
          {% elif is_state('sensor.wp_display_stoerung_id', '22') %}
            Warmwasser
          {% elif is_state('sensor.wp_display_stoerung_id', '23') %}
            Last Verdichter
          {% elif is_state('sensor.wp_display_stoerung_id', '24') %}
            Codierung
          {% elif is_state('sensor.wp_display_stoerung_id', '25') %}
            Niederdruck
          {% elif is_state('sensor.wp_display_stoerung_id', '26') %}
            Frostschutz
          {% elif is_state('sensor.wp_display_stoerung_id', '28') %}
            Hochdruck
          {% elif is_state('sensor.wp_display_stoerung_id', '29') %}
            Temperatur Differenz
          {% elif is_state('sensor.wp_display_stoerung_id', '30') %}
            Heißgasthermostat
          {% elif is_state('sensor.wp_display_stoerung_id', '31') %}
            Durchfluss
          {% else %}
            {{ states('sensor.wp_display_stoerung') }}
          {% endif %}
      # WP Display Sensor
      - name: "WP Display Sensor"
        unique_id: wp_display_sensor
        state: >
          {% if is_state('sensor.wp_display_sensor_id', '0') %}
            kein
          {% elif is_state('sensor.wp_display_sensor_id', '1') %}
            Außenfühler (R1)
          {% elif is_state('sensor.wp_display_sensor_id', '2') %}
            Rücklauffühler (R2)
          {% elif is_state('sensor.wp_display_sensor_id', '3') %}
            Warmwasserfühler (R3)
          {% elif is_state('sensor.wp_display_sensor_id', '4') %}
            Codierung (R7)
          {% elif is_state('sensor.wp_display_sensor_id', '5') %}
            Vorlauffühler (R9)
          {% elif is_state('sensor.wp_display_sensor_id', '6') %}
            2.Heizkreisfühler (R5)
          {% elif is_state('sensor.wp_display_sensor_id', '7') %}
            3.Heizkreisfühler (R13)
          {% elif is_state('sensor.wp_display_sensor_id', '8') %}
            Regenerativfühler (R13)
          {% elif is_state('sensor.wp_display_sensor_id', '9') %}
            Raumfühler 1
          {% elif is_state('sensor.wp_display_sensor_id', '10') %}
            Raumfühler 2
          {% elif is_state('sensor.wp_display_sensor_id', '11') %}
            Fühler Wärmequellenaustritt (R6)
          {% elif is_state('sensor.wp_display_sensor_id', '12') %}
            Fühler Wärmequelleneintritt (R24)
          {% elif is_state('sensor.wp_display_sensor_id', '14') %}
            Kollektorfühler (R23)
          {% elif is_state('sensor.wp_display_sensor_id', '15') %}
            Niederdrucksensor (R25)
          {% elif is_state('sensor.wp_display_sensor_id', '16') %}
            Hochdrucksensor (R26)
          {% elif is_state('sensor.wp_display_sensor_id', '17') %}
            Raumfeuchte 1
          {% elif is_state('sensor.wp_display_sensor_id', '18') %}
            Raumfeuchte 2
          {% elif is_state('sensor.wp_display_sensor_id', '19') %}
            Fühler Frostschutz-Kälte
          {% elif is_state('sensor.wp_display_sensor_id', '20') %}
            Heisgas
          {% elif is_state('sensor.wp_display_sensor_id', '21') %}
            Rücklauffühler (R2.1)
          {% elif is_state('sensor.wp_display_sensor_id', '22') %}
            Schwimmbadfühler (R20)
          {% elif is_state('sensor.wp_display_sensor_id', '23') %}
            Vorlauffühler Kühlen Passiv (R11)
          {% elif is_state('sensor.wp_display_sensor_id', '24') %}
            Rücklauffühler Kühlen Passiv (R4)
          {% elif is_state('sensor.wp_display_sensor_id', '26') %}
            Fühler Solarspeicher (R22)
          {% elif is_state('sensor.wp_display_sensor_id', '28') %}
            Anforderungsfühler Heizen (R2.2)
          {% elif is_state('sensor.wp_display_sensor_id', '29') %}
            RTM Econ
          {% elif is_state('sensor.wp_display_sensor_id', '30') %}
            Anforderungsfühler Kühlen (R39)
          {% else %}
            {{ states('sensor.wp_display_sensor') }}
          {% endif %}

Based on this I can do pretty much everything :slight_smile: My main use cases are:

  • Smart Grid based on Solar energy produced / forecast (incl. thermal desinfection)
  • Change operation mode
  • Monitor energy consumption of heatpump
  • Calc JAZ
  • Monitor temperatures around the heatpump (watertemp, room temp, …)

Further Links

3 Likes

Hi, ich habe eine Dimplex WP hier stehen und lese ebenfalls die Werte via Modbus aus. Bei den Energiewerten bekomme ich aber nur Werte bei Warmwasser 1-4 und Wärmemenge 1-4. Die Werte 5-8 und 9-12 stehen seit einem Jahr auf 0,00 kWh.

Ist das bei dir auch so?

Hey, bei mir haben mittlerweile alle 5-8er Werte. Hängt von deinem Verbrauch ab … die 5-8er Werte haben ja den Faktor 10000 und zählen erst wenn 1-4 “voll” ist

1 Like

Hi.
I bought the Hardware but nothing is working.
Can anybody help me with the configuration?

If you only bought it it will not do anything. You need to plug it into your heatpump :wink:

Ja das ist mir klar.
Habe natürlich die Karte in die Wärmepumpe eingebaut und diese mit dem Stick verbunden.
HA läuft auf Proxmox.
Sobald ich den Code in die Config.yaml einfüge bekomme ich Fehlermeldungen.
Weiß nicht ob ich evtl falsch geklemmt oder den USB Stick falsch in Proxmox durchgeschleift habe.
Stehe da gerade auf dem Schlauch.

Welche Fehlermeldung denn?

Habe eben nochmal in der Config nachgeschaut.
Anscheinend muss ich die einzelnen Zeilen noch verschieden einrücken.
Könnte dass das Problem sein?
Hatte deine Config kopiert und eingefügt.
Das könnte das Problem evtl sein.
Bei dem Anschließen von den 3 Drähten kann man ja nicht viel falsch machen.

  • auf +, - auf - und GND auf GND

ja, das ist ein Problem. Keine Ahnung warum es oben verloren gegangen ist. Hier noch ein Versuch (habe oben aktualisiert)

1 Like

Die aktualisierte Version ließ sich jetzt ohne Fehler rein kopieren.
Allerdings wird jetzt beim rein kopieren von den Templates einiges rot.
Keine Ahnung was ich falsch mache.

Wie kann ich denn diese Werte korrekt zusammenfassen und plausibel darstellen in einer Kachel? Es bringt mir ja nichts wenn ich die originalen Werte sehe und selbst den Multiplikator anwenden muss.

Indem du aus meinem ersten Post die Template Sensoren dazu verwendest.

1 Like

Ok, das probiere ich aus. Sieht so aus als hätte deine WP die selben Adressen. Hast du die von Weishaupt oder von dimplex? Verwendest du die Werte von Modbus RTU oder TCP?
Ich vermisse nämlich Werte wie zb. “aktueller Energieverbrauch” oder “Schaltzeiten des Verdichters”. Auch JAZ zahlen vermisse ich oder tägliche/wöchentliche/monatliche Wärmemengen.

Sorry für vielleicht noch kommende Anfängerfragen, bin erst seit 5 Tagen in der HA-Welt.

Ok, scheinbar gibt es bei mir noch grundlegendes Knowhow, dass ich mir aneignen muss. Irgendwie scheitere ich schon beim Einfügen der Yaml über den Studio Code Server. Ich bekomme beim Testen der Datei diese Meldungen. Die darin enthaltenen Einträge sind aber gar nicht drin in der Yaml. Ich kann leider nur 1 Bild hochladen.

Habe deinen Code nur angepasst auf TCP.

modbus:
  - name: weishaupt_wwp_18
    type: tcp
    host: 192.168.178.57
    port: 502
    #retry_on_empty: true
    timeout: 14
    climates:
      # Heizen
      - name: "WP Climate Heizen Temperatur"
        unique_id: wp_climate_heizentemperature
        address: 46 # 5 Vorlauf, scale 0.1
        slave: 1
        input_type: input
        data_type: int16
        max_temp: 38
        min_temp: 0
        offset: 0
        precision: 1

Und in der Configdatei das hinzugefügt.

# Loads default set of integrations. Do not remove.

default_config:

# Load frontend themes from the themes folder

frontend:

themes: !include_dir_merge_named themes

automation: !include automations.yaml

script: !include scripts.yaml

scene: !include scenes.yaml

modbus: !include modbus.yaml

Ich nutze RTU wie oben beschrieben.
Meine Wärmepumpe steht auch da: Weishaupt WWP L9 ID

Die Attribute die dir “fehlen” (JAZ etc.) gibt es nicht. Siehe auch verlinkte Doku oben. JAZ kannste selber berechnen…

Ok, habe es hinbekommen. Einzig die Parallelverschiebung will nicht so richtig klappen. Hast du das korrekt abbilden können? Die Werte bei dir, zb. 163 temp register, wo hast du die her? Ich finde die in der RTU Doku nicht.

Parallelverschiebung nutze ich nicht

Die Heizfunktion funktioniert über die Parallelverschiebung, zumindest bei mir. Bei deinem Code steht ja auch der Hinweis zum Register dazu.

Egal, Habs selbst gelöst.

yo richtig. ich nutze fürs Heizen die Temperatur und lasse die Heizkurven wie sie sind. Zieltemperatur kommt in 163.

“Climate” funktioniert bei mir nicht, habs über Slider gelöst.

1 Like