August 8, 2023, 6:13am
1
Hello,
i want to write a Modbus Register using the Modbus Integration. The datatype is 32int. I can read the register with the following sensor settings:
input_type: holding
count: 2
data_type: int32
The value i want to change is in the second register as far as i assume.
There is no Problem in writing to Registers with 2 bytes. How do i have to write the value?
Thx
1 Like
tom_l
August 8, 2023, 7:09am
2
You use the write register service, see: Modbus - Home Assistant
00Snider
(Benni)
August 8, 2023, 7:32am
3
Thanks. I know how to use that service. I already used it to write a single register (2byte, datatype int16), which works perfectly. But it doesn’t work when i am trying to write a 4 byte register with datatype int32.
Adress, variable, read or write, Data format, Data model.
1 Like
Adze
(Jeroen Louwes)
January 5, 2024, 10:54am
5
This is how iset the local time on my inverter using modbus. It’s a uint32 value:
alias: Sync klok Inverter1
trigger:
- platform: time
at: "14:00:00"
action:
- service: modbus.write_register
data:
hub: modbusdevice
unit: 2
address: 40000
data_template:
value:
- >-
{{ ((as_timestamp(now()) + 7200) | round(0) | float / 65536) |
round(0, "floor") | int }}
- >-
{{ ((as_timestamp(now()) + 7200) | round(0) - ((as_timestamp(now()) +
7200) | round(0) | float / 65536) | round(0, "floor") * 65536) | int
}}
mode: single