Tim1
(Tim.)
January 24, 2020, 4:32am
1
I have been using a GoControl Z-Wave Plus thermostat (GC-TBZ48L) for some time now and am happy with it. The only downside has been that 2 climate entities are created (one for heat, one for cool). This has been normal and expected behavior.
With the release of Home Assistant 0.103 a fix was included for this (https://github.com/home-assistant/home-assistant/pull/27040 ) which should instead create a single entity as long as COMMAND_CLASS_THERMOSTAT_MODE is supported by the Z-Wave thermostat. I updated but still had 2 entities (I assumed this to be normal, as perhaps the Z-Wave device needed to be removed/added to be detected with the new update). I removed the thermostat via the Z-Wave control panel, verified it was gone, restarted Home Assistant, added the thermostat and then found that 2 entities were still created (one for heat and one for cool).
My thermostat seems to support the appropriate command class: https://products.z-wavealliance.org/products/2370/classes
Additionally when adding the thermostat I get the following line in the OZW Log:
Info, Node015, ZWave+ Info Received from Node 15
#and after other command classes listed
Info, Node015, COMMAND_CLASS_THERMOSTAT_MODE
So it seems OZW does see the command class Home Assistant needs based on this new update.
Anyone having any success with the new update combining their Z-Wave thermostat entities?
freshcoast
(Z-Wave AI Bot)
January 24, 2020, 4:50am
2
There wasn’t really any reason to remove the node and add it again. Instead, you should have a new climate entity, something like climate.blah_blah_thermostat_mode
Did you check the Devices page, or the States page and verify if there where any different entities? The home-assistant.log should also have a message about adding a new entity, if you are logging INFO.
If the new entity is really not there, you can post the contents of the zwcfg*.xml file related to the thermostat, it could help explain what’s going on. The existence of COMMAND_CLASS_THERMOSTAT is not the only thing that decides how the climate entities are created.
Tim1
(Tim.)
January 24, 2020, 5:50am
3
Yes I checked the States page and it still shows just 2 climate devices. (I also checked the States page after updating from 0.102 to 0.104 and there was still just the 2 climate devices)
I checked my zwcfg_*.xml, here is the section relevant to the thermostat (Node 15):
<Node id="15" name="" location="" basic="4" generic="8" specific="6" roletype="5" devicetype="4608" nodetype="0" type="General Thermostat V2" listening="true" frequentListening="false" beaming="true" routing="true" max_baud_rate="40000" version="4" query_stage="Complete">
<Manufacturer id="14f" name="Linear (Nortek Security Control LLC)">
<Product type="5442" id="5437" name="GC-TBZ48 Battery Powered Z-Wave Thermostat" />
</Manufacturer>
<CommandClasses>
<CommandClass id="32" name="COMMAND_CLASS_BASIC" version="1" request_flags="4" mapping="64">
<Instance index="1" />
</CommandClass>
<CommandClass id="43" name="COMMAND_CLASS_SCENE_ACTIVATION" version="1" request_flags="4" innif="true">
</CommandClass>
<CommandClass id="49" name="COMMAND_CLASS_SENSOR_MULTILEVEL" version="1" innif="true">
<Value type="decimal" genre="user" instance="1" index="1" label="Temperature" units="F" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="72" />
</CommandClass>
<CommandClass id="64" name="COMMAND_CLASS_THERMOSTAT_MODE" version="1" request_flags="4" innif="true">
<Value type="list" genre="user" instance="1" index="0" label="Mode" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="1" size="1">
<Item label="Off" value="0" />
<Item label="Heat" value="1" />
<Item label="Cool" value="2" />
<Item label="Auto" value="3" />
<Item label="Aux Heat" value="4" />
</Value>
<SupportedModes>
<Mode index="0" label="Off" />
<Mode index="1" label="Heat" />
<Mode index="2" label="Cool" />
<Mode index="3" label="Auto" />
<Mode index="4" label="Aux Heat" />
</SupportedModes>
</CommandClass>
<CommandClass id="66" name="COMMAND_CLASS_THERMOSTAT_OPERATING_STATE" version="1" request_flags="4" innif="true">
<Value type="string" genre="user" instance="1" index="0" label="Operating State" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="Idle" />
</CommandClass>
<CommandClass id="67" name="COMMAND_CLASS_THERMOSTAT_SETPOINT" version="1" request_flags="4" innif="true" base="0">
<Value type="decimal" genre="user" instance="1" index="1" label="Heating 1" units="F" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="63" />
<Value type="decimal" genre="user" instance="1" index="2" label="Cooling 1" units="F" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="85" />
</CommandClass>
<CommandClass id="68" name="COMMAND_CLASS_THERMOSTAT_FAN_MODE" version="1" request_flags="6" innif="true">
<SupportedModes />
</CommandClass>
<CommandClass id="69" name="COMMAND_CLASS_THERMOSTAT_FAN_STATE" version="1" request_flags="4" innif="true">
<Value type="string" genre="user" instance="1" index="0" label="Fan State" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="Idle" />
</CommandClass>
<CommandClass id="90" name="COMMAND_CLASS_DEVICE_RESET_LOCALLY" version="1" request_flags="4" innif="true">
</CommandClass>
<CommandClass id="94" name="COMMAND_CLASS_ZWAVEPLUS_INFO" version="1" request_flags="4" innif="true">
<Value type="byte" genre="system" instance="1" index="0" label="ZWave+ Version" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="255" value="1" />
<Value type="short" genre="system" instance="1" index="1" label="InstallerIcon" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="-32768" max="32767" value="4608" />
<Value type="short" genre="system" instance="1" index="2" label="UserIcon" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="-32768" max="32767" value="4608" />
</CommandClass>
<CommandClass id="112" name="COMMAND_CLASS_CONFIGURATION" version="1" request_flags="4" innif="true">
<Value type="list" genre="config" instance="1" index="1" label="System Type" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="1" vindex="0" size="1">
<Help>0 = Standard, 1 = Heat Pump</Help>
<Item label="Standard" value="0" />
<Item label="Heat Pump" value="1" />
</Value>
<Value type="list" genre="config" instance="1" index="2" label="Fan Type" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="1" vindex="0" size="1">
<Help>0 = Gas (no fan w/Heat), 1 = Electric (Fan w/Heat)</Help>
<Item label="Gas" value="0" />
<Item label="Electric" value="1" />
</Value>
<Value type="list" genre="config" instance="1" index="3" label="Change Over Type" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="1" vindex="0" size="1">
<Help>0 = w/Cool, 1 = w/Heat</Help>
<Item label="w/Cool" value="0" />
<Item label="w/Heat" value="1" />
</Value>
<Value type="list" genre="config" instance="1" index="4" label="2nd Stage Heat Enable" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="1" vindex="0" size="1">
<Help>0 = no 2nd stage heat, 1 = 2nd stage heat</Help>
</Value>
<Value type="list" genre="config" instance="1" index="5" label="Aux Heat Enable" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="1" vindex="0" size="1">
<Help>0 = no aux heat, 1 = aux heat enabled</Help>
<Item label="Disabled" value="0" />
<Item label="Enabled" value="1" />
</Value>
<Value type="list" genre="config" instance="1" index="6" label="2nd Stage Cool Enable" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="1" vindex="0" size="1">
<Help>0 = no 2nd stage cool, 1 = 2nd stage cool</Help>
</Value>
<Value type="list" genre="config" instance="1" index="7" label="Temperature Unit" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="1" vindex="1" size="1">
<Help>0 = Celsius, 1 = Fahrenheit</Help>
<Item label="Celsius" value="0" />
<Item label="Fahrenheit" value="1" />
</Value>
<Value type="byte" genre="config" instance="1" index="8" label="Minimum Off Time" units="minutes" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="5" max="9" value="5">
<Help>Sets the Minimum Off Time (MOT) delay before another heating/cooling cycle can begin</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="9" label="Minimum Run Time" units="minutes" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="3" max="9" value="3">
<Help>Sets the Minimum Run Time (MRT) delay before a heating/cooling cycle can turn of</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="10" label="Setpoint H/C Delta" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="3" max="15" value="3">
<Help>Sets the minimum separation between heating and cooling setpoints</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="11" label="H Delta Stage 1 ON" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="1" max="6" value="1">
<Help>Sets the delta from setpoint that stage 1 heating starts</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="12" label="H Delta Stage 1 OFF" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="5" value="0">
<Help>Sets the delta from setpoint that stage 1 heating stops</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="13" label="H Delta Stage 2 ON" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="2" max="7" value="2">
<Help>Sets the delta from setpoint that stage 2 heating starts</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="14" label="H Delta Stage 2 OFF" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="6" value="0">
<Help>Sets the delay from setpoint that stage 2 heating stops</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="15" label="H Delta Aux ON" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="3" max="8" value="3">
<Help>Sets the delta from setpoint that stage 3 heating starts</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="16" label="H Delta Stage 2 OFF" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="7" value="0">
<Help>Sets the delta from setpoint that stage 3 heating stops</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="17" label="C Delta Stage 1 ON" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="1" max="6" value="1">
<Help>Sets the delta from setpoint that stage 1 cooling starts</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="18" label="C Delta Stage 1 OFF" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="5" value="0">
<Help>Sets the delta from setpoint that stage 1 cooling stops</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="19" label="C Delta Stage 2 ON" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="2" max="7" value="2">
<Help>Sets the delta from setpoint that stage 2 cooling starts</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="20" label="C Delta Stage 2 OFF" units="fahrenheit" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="6" value="0">
<Help>Sets the delta from setpoint that stage 2 cooling stops</Help>
</Value>
<Value type="list" genre="config" instance="1" index="24" label="Display Lock" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="1" max="1" vindex="0" size="1">
<Help>Display Lock</Help>
<Item label="Unlocked" value="0" />
<Item label="Locked" value="1" />
</Value>
<Value type="byte" genre="config" instance="1" index="26" label="Backlight Timer" units="seconds" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="10" max="30" value="20">
<Help>Sets the time from last button press that the backlight will turn OFF</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="33" label="Max Heat Setpoint" units="degrees" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="30" max="109" value="90">
<Help>Sets the maximum heating setpoint value</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="34" label="Min Cool Setpoint" units="degrees" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="33" max="112" value="61">
<Help>Sets the minimum cooling setpoint value</Help>
</Value>
<Value type="list" genre="config" instance="1" index="38" label="Schedule Enable" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="1" vindex="0" size="1">
<Help>Enable or disable thermostat's local scheduler</Help>
</Value>
<Value type="list" genre="config" instance="1" index="39" label="Run/Hold Mode" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="1" vindex="0" size="1">
<Help>0 = Hold, 1 = Run</Help>
<Item label="Hold" value="0" />
<Item label="Run" value="1" />
</Value>
<Value type="list" genre="config" instance="1" index="40" label="Setback Mode" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="2" vindex="0" size="1">
<Help>0 = No setback, 2 = Un-occupied mode</Help>
<Item label="No Setback" value="0" />
<Item label="Unoccupied Mode" value="2" />
</Value>
<Value type="byte" genre="config" instance="1" index="41" label="Un-Occupied HSP" units="degrees" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="30" max="109" value="62">
<Help>Heat Setpoint for Unoccupied mode</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="42" label="Un-Occupied CSP" units="degrees" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="33" max="112" value="80">
<Help>Cool Setpoint for Unoccupied mode</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="43" label="Remote Sensor 1 Node Number" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="252" value="87">
<Help>Node number for Remote Sensor 1</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="46" label="Remote Sensor 1 Temperature" units="degrees" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="112" value="110">
<Help>Temperature of Remote Sensor 1</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="48" label="Internal Sensor Temp Offset" units="degrees" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="-7" max="7" value="0">
<Help>Internal Sensor Temperature Offset</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="49" label="R1 Sensor Temp Offset" units="degrees" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="-7" max="7" value="0">
<Help>R1 Sensor Temperature Offset</Help>
</Value>
<Value type="short" genre="config" instance="1" index="52" label="Filter Timer" units="hours" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="4000" value="4000">
<Help>Timer to let know when to change or clean the filter</Help>
</Value>
<Value type="short" genre="config" instance="1" index="53" label="Max Filter Timer" units="hours" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="4000" value="44">
<Help>Maximum allowed value for filter timer</Help>
</Value>
<Value type="short" genre="config" instance="1" index="54" label="Heat Timer" units="hours" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="4000" value="0">
<Help>Heat Timer in hours</Help>
</Value>
<Value type="short" genre="config" instance="1" index="55" label="Cool Timer" units="hours" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="4000" value="0">
<Help>Cool Timer in hours</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="61" label="Fan Purge Heat" units="seconds" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="90" value="0">
<Help>Fan purge period for Heat mode</Help>
</Value>
<Value type="byte" genre="config" instance="1" index="62" label="Fan Purge Cool" units="hours" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="90" value="0">
<Help>Fan purge period for Cool mode</Help>
</Value>
</CommandClass>
<CommandClass id="114" name="COMMAND_CLASS_MANUFACTURER_SPECIFIC" version="1" request_flags="4" innif="true">
</CommandClass>
<CommandClass id="115" name="COMMAND_CLASS_POWERLEVEL" version="1" request_flags="4" innif="true">
<Value type="list" genre="system" instance="1" index="0" label="Powerlevel" units="dB" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Item label="Normal" value="0" />
<Item label="-1dB" value="1" />
<Item label="-2dB" value="2" />
<Item label="-3dB" value="3" />
<Item label="-4dB" value="4" />
<Item label="-5dB" value="5" />
<Item label="-6dB" value="6" />
<Item label="-7dB" value="7" />
<Item label="-8dB" value="8" />
<Item label="-9dB" value="9" />
</Value>
<Value type="byte" genre="system" instance="1" index="1" label="Timeout" units="seconds" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="255" value="0" />
<Value type="button" genre="system" instance="1" index="2" label="Set Powerlevel" units="" read_only="false" write_only="true" verify_changes="false" poll_intensity="0" min="0" max="0" />
<Value type="byte" genre="system" instance="1" index="3" label="Test Node" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="255" value="0" />
<Value type="list" genre="system" instance="1" index="4" label="Test Powerlevel" units="dB" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
</Value>
<Value type="short" genre="system" instance="1" index="5" label="Frame Count" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="-32768" max="32767" value="0" />
<Value type="button" genre="system" instance="1" index="6" label="Test" units="" read_only="false" write_only="true" verify_changes="false" poll_intensity="0" min="0" max="0" />
<Value type="button" genre="system" instance="1" index="7" label="Report" units="" read_only="false" write_only="true" verify_changes="false" poll_intensity="0" min="0" max="0" />
<Value type="list" genre="system" instance="1" index="8" label="Test Status" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Item label="Failed" value="0" />
<Item label="Success" value="1" />
<Item label="In Progress" value="2" />
</Value>
<Value type="short" genre="system" instance="1" index="9" label="Acked Frames" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="-32768" max="32767" value="0" />
</CommandClass>
<CommandClass id="128" name="COMMAND_CLASS_BATTERY" version="1" request_flags="4" innif="true">
<Value type="byte" genre="user" instance="1" index="0" label="Battery Level" units="%" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="255" value="100" />
</CommandClass>
<CommandClass id="129" name="COMMAND_CLASS_CLOCK" version="1" request_flags="4" innif="true">
<Value type="list" genre="user" instance="1" index="0" label="Day" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="2" size="1">
<Item label="Monday" value="1" />
<Item label="Tuesday" value="2" />
<Item label="Wednesday" value="3" />
<Item label="Thursday" value="4" />
<Item label="Friday" value="5" />
<Item label="Saturday" value="6" />
<Item label="Sunday" value="7" />
</Value>
<Value type="byte" genre="user" instance="1" index="1" label="Hour" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="255" value="5" />
<Value type="byte" genre="user" instance="1" index="2" label="Minute" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="255" value="16" />
</CommandClass>
<CommandClass id="133" name="COMMAND_CLASS_ASSOCIATION" version="1" request_flags="4" innif="true">
<Associations num_groups="3">
<Group index="1" max_associations="5" label="Group 1" auto="true">
<Node id="1" />
</Group>
<Group index="2" max_associations="5" label="Group 2" auto="false" />
<Group index="3" max_associations="5" label="Group 3" auto="false" />
</Associations>
</CommandClass>
<CommandClass id="134" name="COMMAND_CLASS_VERSION" version="1" request_flags="4" innif="true">
<Value type="string" genre="system" instance="1" index="0" label="Library Version" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="6" />
<Value type="string" genre="system" instance="1" index="1" label="Protocol Version" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="4.05" />
<Value type="string" genre="system" instance="1" index="2" label="Application Version" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="1.00" />
</CommandClass>
<CommandClass id="143" name="COMMAND_CLASS_MULTI_CMD" version="1" request_flags="4" innif="true">
</CommandClass>
</CommandClasses>
</Node>
freshcoast
(Z-Wave AI Bot)
January 24, 2020, 6:05am
4
Hmm… XML file looks OK to me. On the first line, it has generic="8" specific="6"
. Those values plus the existence of COMMAND_CLASS_THERMOSTAT_MODE
is what is supposed to create the thermostat mode based climate entity.
Any chance you installed a zwave custom component in the past, that is pre-0.103, and is still installed? Did you double check the Info page and it shows v0.104, not still v0.102?
Otherwise, I’m not seeing anything wrong the XML file. Only other suggestion I have might be to enable debug logging for the zwave compoments, and post a copy of that to a pastebin (past the z-wave relevant portions, or remove anything that might be private before doing so).
logger:
default: info
logs:
homeassistant.components.zwave: debug
openzwave: debug
libopenzwave: debug