Ok, let’s try to avoid electrical shocks…
First : my boiler has an important difference from yours, the control circuit is 24V, not 220. And I don’t have the same model of thermostat, but a specific version for gas/fuel boilers.
@anon43302295 : could you post a picture of your model ? Right now, I’ll assume you have the same as cooljimi84 ?
So, first thing, power your thermostat. This is easy, live on 4, neutral on 3. (or the opposite, that’s not much of a problem)
Now, your boiler OUTPUTS 230V on its terminal 1. And it RECEIVES 230V on terminal 2.
The thermostat OUTPUTS 230V on terminals 1 and 2 : it’s live and neutral. Nothing can come from your boiler on those !!
If you plug in and out from the boiler to these terminals, you’ll most likely blow the thermostat, maybe some fuse in your installation but probably nothing on your boiler (that’s the only good news here !). Just because you’re gonna SEND 230V to your thermostat output…
What could work, is @cooljimy84 connections. Use the controled live terminal (1 on the thermostat) to send 220V to the control input of your boiler (terminal 2).
In fact, you have a thermostat for an electrical heater, terminals 1 and 2 are designed for a load.
The boiler needs a simple switch between terminals 1 and 2, because it provides the load (230V live).
When plugging only the live output (term 1 of thermostat) to the loop input of the boiler (term 2), you just provide the 230V it waits for to start heating. And forget about the 230V it outputs on terminal 1.
I may not work if :
- the boiler checks output vs input to prevent electrical shocks on the thermostat : if 230V comes in with no load on the output, it could enter a security mode
- the thermostat has a security on the controled output, if it sees power going out of the live terminal and none returning on the neutral one.
The other way of doing it, is to plug the live and neutral controlled output from the thermostat (term 1 & 2) to the main live and neutral input of the boiler; let the link between 1 & 2 on the boiler. When the thermostat turns on, it will power the boiler that should start ?