Daikin P1P2 comms and adding Wifi + Voice control to a 20year old ducted Air Conditioner
I moved into a new house a couple of years ago, built around 20 years ago it was a stretch of the budget and I knew I would have to save for a while before I could start making big changes. It wasn’t long before (immediately after the first power bill) I realised the 20 year old air conditioner would also be a financial burden, and its temperature control was poor, it would barely keep us cool the first half of the night and by 3am we would get frostbite on our toes. The AC is a 6.5kw Daikin system, a heat pump outside and a unit in the roof with 3 zones, there is a controller upstairs and another in the kitchen area.
For a while we played with settings and found a happy medium of comfort vs cost to run, a setting of 26 degrees. I always wanted to be able to automate the system, so when the solar is producing power we can run the unit full tilt and get the house cool for the evening, and then start winding it down to save power as the night went on. But I couldn’t find anything for a 20 year old system, and all the new
systems are tied to the cloud and well above my limited budget (plus Dutch blood doesn’t help). Searching the controller part number + Wi-Fi I found some people adding a Wi-Fi relay to the power button, but that’s not enough, I wanted a professional integration. what I did notice was the labels P1/P2 inside the controller, that lead me to
I followed the project for a while, it wasn’t exactly what I was after, they were working on the Daikin Altherma heat pumps and there was no info about the type of VRV AC unit I had. I saw he had just developed a new device so I reached out to him about a month ago to see if I could get my hands on one. I managed to buy his last board and with a warning “this is a prototype and will require loads of reverse engineering” he send it to the opposite side of the world. It took 3 weeks to arrive, and in the meantime I read everything on his GitHub and setup an ESP32 with a couple of bme280 temp/humidity/pressure sensors so I could cross reference readings to reverse engineer the data. I searched every Daikin manual I could get my hands on for any tidbit of info
Within 10 minutes of the device arriving I had hooked it up and connected to my Wi-Fi, its powered directly off the P1P2 bus, so it was just a matter of jumping the 2 wires from the controller to the device - note how small it is! It creates the usual AP where you can connect to enter your Wi-Fi details. Once connected to the Wi-Fi the device has a telnet interface, it was just a matter of opening a command prompt and typing “telnet 192.168.0.151” and with a simple command “b 192.168.0.100 1833 mqttuser mqttpassword” it started throwing numbers at my mqtt server in home assistant.
Franticly I started pressing buttons on the controller, but couldn’t figure out how to read it as the data was changing so quickly. I turned to node-RED and set up a simple flow, using a “mqtt_in” node subscribing to the topic “P1P2/R/#” and connecting that to a “write to file” node. this gave me more insight, but I found it difficult to decode without knowing what I was doing at the time, so I put a simple
“function” node between to add a timestamp
var d = new Date();
var t = d.getTime();
var payload = {"time":t,"payload":msg.payload}
msg.payload = payload
return msg;
Armed with this I started with some simple tests, turn the power on, change modes, and change the temperature setpoint. here is quite literally less than 2 seconds of data from the bus, from the great
documentation on Arnold’s GitHub I quickly figured out that the first byte 00 was from the main controller, the second byte F0 was to the Aux controller and the third byte 38 is the type of message. in the second line its the other way, 40 means reply, F0 means from the Aux controller and 38 is still the type.
{"time":1661920109585,"payload":"R T  0.026:
00F038000060001C00110018005101002A00C0E6"}
{"time":1661920109632,"payload":"R T  0.026:
40F03800601C00110018005101000000C00019"}
{"time":1661920109669,"payload":"R T  0.026: 800018000000000000008A"}
{"time":1661920109816,"payload":"R T  0.121: 0000110000030F0011C80000004A"}
{"time":1661920109869,"payload":"R T  0.048: 4000110000000000157B005C"}
{"time":1661920109877,"payload":"R P
00000E00000F72007A120000000000000000000000000093"}
{"time":1661920109878,"payload":"R P
40000E00000C02000000000000000017700003000003E9A2"}
{"time":1661920109900,"payload":"R T  0.026: 0008200461"}
{"time":1661920110062,"payload":"R T  0.131:
{"time":1661920110113,"payload":"R T  0.026:
40F03801601C00110018005101000000C00099"}
{"time":1661920110283,"payload":"R T  0.028:
0000100160001C00110002000000000080400100000000F8"}
{"time":1661920110286,"payload":"R P
00000F1D03050B080000003209C400000300010003090097"}
{"time":1661920110287,"payload":"R P
40000F01015358007B0000010200000000002009F1000072"}
{"time":1661920110287,"payload":"R T  0.067:
400010010060001C0011003A000000000080000001000000"}
{"time":1661920110288,"payload":"R P
00000D0000000000000000000000000000000000000000C4"}
{"time":1661920110370,"payload":"R P
40000D0D0A950001191F000000000000000000000000002D"}
{"time":1661920110371,"payload":"R T  0.026:
00F038010060001C00110018005101002A00C03F"}
{"time":1661920110402,"payload":"R T  0.026:
8000100160001C001100020000000000800000000000005F"}
{"time":1661920110541,"payload":"R T  0.136: 0009200430"}
{"time":1661920110696,"payload":"R T  0.122:
{"time":1661920110735,"payload":"R T  0.026:
{"time":1661920110790,"payload":"R T  0.027:
{"time":1661920110884,"payload":"R T  0.066:
400010010060001C0011003A000000000005000001000057"}
{"time":1661920110900,"payload":"R P
{"time":1661920110901,"payload":"R P
40000D0D0A950001192C000000000000000000000000006C"}
{"time":1661920110932,"payload":"R T  0.026:
{"time":1661920110985,"payload":"R T  0.026:
{"time":1661920111007,"payload":"R T  0.026: 000A2004C3"}
{"time":1661920111168,"payload":"R T  0.119:
{"time":1661920111199,"payload":"R T  0.026:
{"time":1661920111254,"payload":"R T  0.027:
0000100160001C0011000200000000000540010000000030"}
{"time":1661920111347,"payload":"R T  0.065:
{"time":1661920111356,"payload":"R P
{"time":1661920111357,"payload":"R P
40000D0D0A9500011936000000000000000000000000007C"}
{"time":1661920111394,"payload":"R T  0.026:
{"time":1661920111443,"payload":"R T  0.026:
{"time":1661920111472,"payload":"R T  0.026: 00001F31"}
{"time":1661920111519,"payload":"R T  0.031: 4000FFE3"}
Using my phone to record a video while I pushed buttons meant I could accurately associate the time to the changes in the data it didn’t take long to come up with some tables, I didn’t manage to figure every byte, but I got the main things at least.
00 F0 38 message from master to slave
byte 3 00=off, 01=on, 03=turn on, 02=turn off
byte 4 00
byte 5 60=fan, 67=dry, 63 auto, 62=cool, 61=heat
byte 6 00=fan only, 01=heat, 02=cool
byte 7 19 current master set temp cooling in hex 25c (16-32c range- 10
to 20 hex)
byte 8 00 when slave equal, 80 when changed
byte 9 11=fan low, 51, fan high, D1=change to high, 91=change to
low  (cooling and fan mode)
byte 10 00
byte 11 20 current master set temp heating in hex 25c
byte 12 00 when slave equal, 80 when changed
byte 13 11=fan low, 51, fan high, D1=change to high, 91=change to
low (heat mode)
byte 14 01
byte 15 00
byte 16 2A
byte 17 00 goes to 01 next message after reply with 01 in byte 11,
sent out twice
byte 18 C0
40 F0 38 reply slave to master
byte 4 60=fan, 67=dry, 63 auto, 62=cool, 61=heat
byte 5 19 current master set temp cooling in hex 25c
byte 6 00
byte 7 11=fan low, 51, fan high (cooling and fan mode)
byte 8 00
byte 9 20 current set temp heating in hex
byte 10 00
byte 11 11=fan low, 51, fan high (heat mode)
byte 12 01
byte 13 00
byte 14 00 clear error codes. Goes to 01 for 1 message
byte 15 00
byte 16 c0
byte 17 00
I quickly realised I was missing temperature values, so I borrowed the wife’s hairdryer and started warming things up. it didn’t take long to figure out the temperatures, Arnold and others had figured out the Daikin method of encoding so I knew what to look for and how to convert it.
00 00 11 Master to heatpump status
byte 3 00
byte 4 00
byte 5 03
byte 6 0F
byte 7 00
byte 8 14 F8.8 temperature master
byte 9 C6 F8.8 temperature master
byte 10 00
byte 11 00
byte 12 00
40 00 11 Reply heatpump status
byte 3 00
byte 4 00
byte 5 00
byte 6 00
byte 7 00
byte 8 17 F8.8 temperature inside air intake
byte 9 F1 F8.8 temperature inside air intake
byte 10 00
byte 11 00
byte 12 00
I fed all this information back to Arnold, expecting him to take a while to figure out how to control it, within a day he had sent me a new firmware image with the code required to try controlling the AC.
Initially it worked great, I could power on and change modes but I ran into issues with fan speed and temperature control, looking into the code I realised a simple bug with the way the main controller flags to the aux controller and the way the aux should respond. Another few hours later I had a new build firmware ready to load. over the next few days we logged data and noted a few read errors which as a safety feature of the device inhibit controlling the AC. Arnold has been working hard changing the “scope mode” of the device which measures the timing of the falling edge and validates the read
data and the data written to the bus. these have now been resolved and the latest firmware seems to be rock solid. There was also some other little bug fixes, rate limiting some of the MQTT data, right down to the nitty gritty, like changing the degree symbol to the standard one home assistant uses so temperatures from the device can be graphed against others.
The device itself transmits via MQTT, and has auto discovery setup for home assistant. here are some of the relevant data points…
During the analysis of the data and the temperatures being passed around I noticed that the Aux controller temperature is never used, only the master controller… this was unexpected! and explains why the temperature control was so poor in the first place, at night to save energy we would set the zones to just the bedrooms, not the kitchen and living areas - so they would remain warm while we froze at 3am!. Just knowing this 1 piece of information will save us a load of energy, while we cant change the temperature reported by the master controller, we can adjust the setpoint knowing the temperature of the master, and the temperature of the bedrooms.
Here is some graphed data, the AC Intake and Output temperatures are from the ESP32 I set up with BME280’s in the intake/output ducts, all the other data is from the P1P2 device. also note the compressor status changing as it cycles on and off.
The next step was getting a user interface to control the AC, telnet was OK for me but ranks very low on the wife acceptance factor! Arnold is busy putting together some new firmware called P1P2MQTT which will simplify the process dramatically in setting this up, but I’m impatient, so I went and made a couple of automations to control the unit now. At the moment the device is setup for HA MQTT discovery, however the data needed a bit of work to make it nicely work with the MQTT-HVAC integration. I’ve setup 2 automations, one for feeding states into the HVAC integration, and another to control the device. setting up the MQTT HVAC also means that I can expose it to Google home and voice control the AC from anywhere in the world, and create automations and reminders based on other inputs, like Solar production
alias: ac mqtt state middleman
description: ""
  - platform: mqtt
    topic: P1P2/P/125/S/2/Target_Operating_Mode
  - platform: mqtt
    topic: P1P2/P/125/S/2/Actual_Operating_Mode
  - platform: mqtt
    topic: P1P2/P/125/S/2/Fan_Speed_Cooling
  - platform: mqtt
    topic: P1P2/P/125/S/2/Fan_Speed_Heating
  - platform: mqtt
    topic: P1P2/P/125/T/2/Target_Temperature_Cooling
  - platform: mqtt
    topic: P1P2/P/125/T/2/Target_Temperature_Heating
  - platform: state
    entity_id:
      - automation.ac_mqtt_middleman
    attribute: last_triggered
condition: []
  - delay:
      hours: 0
      minutes: 0
      seconds: 1
      milliseconds: 0
  - service: mqtt.publish
      topic: AC/State/Mode
      payload_template: >
        {% set values = { '97':'heat', '98':'cool', '99':'auto', '103':'dry',
        '96':'fan_only'} %}   {% if states('sensor.s2_power_off_on') == '1' %}
        {{ values[states('sensor.s2_target_operating_mode')] if
        states('sensor.s2_target_operating_mode') in values.keys() else
        'unknown' }}  {% else %}  off  {% endif %}
      topic: AC/State/Action
      payload_template: >
        {% set values = { '0':'fan', '1':'heating', '2':'cooling'} %}  {% if
        states('sensor.s2_power_off_on') == '1' %} {{
        values[states('sensor.s2_actual_operating_mode')] if
        states('sensor.s2_actual_operating_mode') in values.keys() else
      topic: AC/State/Fan
      payload_template: >
        {% set values = { '17':'low', '81':'high'} %}  {% if
        states('sensor.s2_actual_operating_mode') == '1' %}
        {{values[states('sensor.s2_fan_speed_heating')] if
        states('sensor.s2_fan_speed_heating') in values.keys() else 'off' }} {%
        else %} {{values[states('sensor.s2_fan_speed_cooling')] if
        states('sensor.s2_fan_speed_cooling') in values.keys() else 'off' }} {%
        endif %}
      topic: AC/State/Temp
      payload_template: >
        {% if states('sensor.s2_actual_operating_mode') == '1' %}
        {{states('sensor.t2_target_temperature_heating') }} {% else %}
        {{states('sensor.t2_target_temperature_cooling') }} {% endif %}
mode: queued
max: 10
description: ""
  - platform: mqtt
    topic: AC/Command/Mode
  - platform: mqtt
    topic: AC/Command/Fan
  - platform: mqtt
    topic: AC/Command/Temp
condition: []
  - choose:
      - conditions:
          - condition: trigger
        sequence:
              topic: P1P2/W
              payload_template: >
                {% if (trigger.payload != 'off') and
                (states('sensor.s2_power_off_on') == '0') %} F 38 0 1 {% endif
          - delay:
              hours: 0
              minutes: 0
              seconds: 5
              milliseconds: 0
              topic: P1P2/W
              payload_template: >
                {% set values = { 'heat':'F 38 1 61', 'cool':'F 38 1
                62','auto':'F 38 1 63', 'dry':'F 38 1 67', 'fan_only':'F 38 1
                60','off':'F 38 0 0'} %} {{ values[trigger.payload] if
                trigger.payload in values.keys() else '' }}
          - delay:
              hours: 0
              minutes: 0
              seconds: 5
              milliseconds: 0
      - conditions:
          - condition: state
            entity_id: sensor.s2_actual_operating_mode
            state: "1"
        sequence:
              topic: P1P2/W
              payload_template: >
                {% set values = { 'high':'F 38 8 51', 'low':'F 38 8 11' } %}  {{
                values[trigger.payload] if trigger.payload in values.keys() else
          - delay:
              hours: 0
              minutes: 0
              seconds: 5
              milliseconds: 0
      - conditions:
        sequence:
              topic: P1P2/W
              payload_template: >
                {% if states('sensor.s2_actual_operating_mode') == '1' %} {% set
                values = { 'high':'F 38 8 51', 'low':'F 38 8 11' } %}     {%
                else %} {% set values = { 'high':'F 38 4 51', 'low':'F 38 4 11'
                } %}  {% endif %} {{ values[trigger.payload] if trigger.payload
          - delay:
              hours: 0
              minutes: 0
              seconds: 5
              milliseconds: 0
      - conditions:
        sequence:
              topic: P1P2/W
              payload_template: >
                {% if states('sensor.s2_actual_operating_mode') == '1' %} {{"f
                38 6 " + ("%0x" | format(trigger.payload | int ) | string )
                }}     {% else %} {{"f 38 2 " + ("%0x" | format(trigger.payload
                | int ) | string ) }}  {% endif %}
          - delay:
              hours: 0
              minutes: 0
              seconds: 5
              milliseconds: 0
mode: queued
max: 10
And adding the entity to HA (under MQTT: in config.yaml)
climate:
  - name: aircon
    modes:
      - "off"
      - "auto"
      - "heat"
      - "dry"
      - "fan_only"
      - "cool"
    fan_modes:
      - "high"
      - "low"
    power_command_topic: "AC/Command/Power"
    power_state_topic: "AC/State/Power"
    mode_command_topic: "AC/Command/Mode"
    mode_state_topic: "AC/State/Mode"
    temperature_command_topic: "AC/Command/Temp"
    temperature_state_topic: "AC/State/Temp"
    fan_mode_command_topic: "AC/Command/Fan"
    fan_mode_state_topic: "AC/State/Fan"
    precision: 1.0
    min_temp: 16
    max_temp: 32
    current_temperature_topic: "P1P2/P/125/T/0/Temperature_main_controller"
and a pretty card to show it all off, and dramatically improve the WAF!
type: custom:simple-thermostat
entity: climate.aircon
step_size: 1
sensors:
  - entity: sensor.office_temperature
    decimals: 0
  - entity: sensor.t0_temperature_main_controller
    decimals: 0
  - entity: sensor.doubleview_temp_max_0
  - entity: sensor.a8_write_budget
header:
control:
  hvac:
    'off':
      icon: mdi:power
    fan_only:
      icon: mdi:fan
  fan:
    high:
      icon: mdi:fan-speed-3
    low:
      icon: mdi:fan-speed-1
I cant take credit for much of this, Arnold and others have been working on this project for a long time and the documentation and reverse engineering information is incredible. The forums here have helped me create a cheap smart home where things are local and exactly the way I want them. Hopefully this post will get the project some light, and with a few more devices in the wild they may learn more about the protocol and allow even more control or gathering of more information. Arnold expects to have more devices ready in October and likely another batch in January. He is also actively working on a rewrite of the software, which should simplify things and hopefully in the future cover a lot more models of Altherma heat pumps and VRV Air Conditioners.
Just want to say a big thanks to Arnold and his support in getting this working on such and old and unusual system, his support during the setup was incredible! with no less than 100 email between us over the last 2 weeks.
My next project will be replacing the zone controller pictured next to the original controller with a ESP based relay module, and a current sensor to upgrade the normally binary zones to positional dampers so I can better control airflow to individual rooms, and even use presence sensors to switch off rooms when unoccupied.
hello,
I’m new in the home automation world and I am in a very similar situation as you were.
I am so happy that you made this post, it enlighten me a lot on how to do it in my house.
For information do you know the model of the inside unit of your system ? mine is a FBQ-C series model.
Thank you very much anyway for sharing your work
the outdoor unit is RY125LUY-1, the indoor unit is FDY125LV1 and the controller is BRC1C51/61
I havent spoken to Arnold in a while as everything is working perfect (and used everyday) but i think he had a few other VRV systems working too. worth reaching out to him on github if your interested
hello,
sorry for the time since your answer !!
It is nice of you to have take the the time to answer me, I will look at our respective units specifications and make some tests.
I will tell you if I managed to do something as robust as you did
Thank you again
The hardware include two microcontroller? As I know it include an ATMEGA and a ESP8266, but from the image I just see the ESP.
yeah there is two micro’s the esp and the atmega,
Its a two sided board, on the back side there is quite a few components, all the SMD stuff - rectifiers, diodes, LED’s, resistors and caps. On the side you see in the photos is the esp module and the through hole components
its been a long time since I’ve had to look at the device since it just works, and it gets used very regularly.
During the initial testing and development i did need to make quite a few updates to both, but it was simple enough… just plug in the programmer that he supplied with the unit and load the binaries he compiled.
Thank you for the info. With me it is over engineering. An ESP32 and the P1P2 converter more than enough for the application. So I think the author not opensource all the code, like the code to control your device.
I have to disagree, its not over engineered. its complexity arises from the powering via the bus and also decoding the information, and re-injecting.
from what i understand, the atmega handles the timing for decoding and encoding and streams out the data for the esp. it also takes the data from the esp and injects it at specifically the right time on the bus, this timing is critical and why its a separate micro.
the esp has a serial interface to the atmega and the buffer eliminates the need for precise timing, allowing the esp to handle its wifi connection, mqtt and telnet server etc.
i haven’t looked to see what’s open source, i had my updates precompiled for me, as i didn’t have the software environments setup to compile. however there is full instructions in the how-to of his github
what are you trying to achieve? are you going to build your own device?
I have build my own software for Mitsubishi Electric, it is public on github, and plan to build the Daikin P1P2 for friend. I say it is over engineering because just the P1P2 converter and an ESP32/ESP8266 can archive the purpose. The reason why he using 2 ones may be the first version running on the UNO, then later he add WiFi adapter but does not want to spend time to covert the code.
just had a look at your github, love the look of the software!
i think there is quite a big difference in the communication, the P1P2 has all the comm’s to and from the controller, the condenser and evaporator, and there is very tight timing on the bus. i think every message from the master needs a response otherwise it causes a bus fault
have you reached out to Arnold?
He say same as you said :). I will try to rewrite the lib it and use UI like the Mitsubishi one.
i think if you are building a device with the components for powering off the bus and also getting the comms modulated to/from the bus, the cost of the atmega is negligible anyway. having said that it would be nice to just have the one micro that does it all, it would make updates easier for sure.
keep us in the loop with your progress
hello, great project i have 2 heat pump to add to 2 HA system (not on the same house and with 2 separate HA)
1 - ekhbrd016acy1
2 - ekcbx008 v3
when i’m looking at the sheme each of them have P1P2 entry
1 - so i wonder if this project could be used for both heat pump ?
2 - if so where could i buy the package to wired with my heat pumps
3 - i follow the GitHub - Arnold-n/P1P2Serial: Monitor and control Daikin/Rotex (hybrid/Altherma) heat pumps via the 2-wire P1/P2 thermostat interface with an ATmega328P, ESP8266, and electronics. The P1P2Serial library and P1P2Monitor program perform low-level bus operation, the P1P2-bridge-esp8266 program interprets data from/to MQTT supporting Home Assistant MQTT discovery. P1P2Serial may also be used for other Japanese Home Bus System based standards: DIII-NET (F1/F2) bus, Mitsubishi M-Net bus, Toshiba TCC-Link, Hitachi H-link, Panasonic/Sanyo SIII-Net, Haier, York, and others. project but i don’t understand how to make this project running - Is there a tuto which show how to built all the project step by step ?
thank you a lot for your thread
if you email Arnold he can advise if similar unit have been tested with his devices. he also sells them pre assembled, when i bought mine he gave me a PDF with all the information i needed to get started.
his email is on line 3 of this file https://github.com/Arnold-n/P1P2Serial/blob/03f53dc752166231369eb8cdedb86b0f0fb4c85f/P1P2Serial.cpp
thanks chris, i have email arnold yesterday and i’m waiting for a response, still now no answser.
Thanks for this thread! I’d all but given up on integrating my Daikin units into HA, but this has given me hope!
I emailed Arnold today and let’s hope he is in an amicable mood😅.
Thank you so much for this, I have copied your work and then adapted to fit my VRV unit
For everyone elses reference my configuration.yaml has:
mqtt:
  climate:
    - name: living_ac
      unique_id: living_ac
      modes:
        - "off"
        - "auto"
        - "heat"
        - "dry"
        - "fan_only"
        - "cool"
      fan_modes:
        - "high"
        - "medium"
        - "low"
      power_command_topic: "ACLiving/Command/Power"
#      power_state_topic: "AC/State/Power"
      mode_command_topic: "ACLiving/Command/Mode"
      mode_state_topic: "ACLiving/State/Mode"
      temperature_command_topic: "ACLiving/Command/Temp"
      temperature_state_topic: "ACLiving/State/Temp"
      fan_mode_command_topic: "ACLiving/Command/Fan"
      fan_mode_state_topic: "ACLiving/State/Fan"
      precision: 1.0
      min_temp: 23
      max_temp: 32
      action_topic:  "ACLiving/State/Mode"
      current_temperature_topic: "P1P2/P/141/T/1/Temperature_inside_air_intake"
Key changes:
  1. Added a unique ID
  2. Added medium fan speed
  3. power_state_topic is depreciated, so added action_topic
  4. Changed the MQTT topic to ACLiving as I will need to have multiple
I also needed to change the automations to the correct items for my VRV aircons as they are different.
I have finished the project, but it is commercial so will not public the source code or hardware design (Closed source firmware, I am thinking about open source the P1P2 driver, use to communication with the bus, the hardware base on Max22088 design.). The hardware include a Max22088, an ESP32/ESP32C3 and some passive components. In pictures below is a thin version using ESP32C3, single side PCB, you can install it it in the case of the wall remote, complete invisible.
Another option for controlling the Daikin heat pumps is getting a Modbus controller for it. I went this route with mine (FDYAN125AV1).
There are a couple of controller options, some by RTD and some by Intesis. The latter is more up to date and has better support, including a virtual temp sensor which would allow you to feed a temperature sensor from HA to the controller that can be used to feed the temperature back to the heat pump.
FYI for those who are interested found this on taobao, it’s a pretty cheapish plug and play solution got it for $37 a pop
Works pretty well to control my daikin ducted air connected via P1P2 terminal either on the wall remote or the main unit. Only downside is you need to add the device using the chinese server on mihome app, but it has local control and works great using HACS miot auto integration
it is advertised to work with many other brands aswell since it has quite a few different type of connectors