KNX Climate hysteresis

Hello to everyone, I’m new on this platform, and I’m asking you help in order to solve this issue: I’m using HA with KNX bus, I’ve implemented the home thermoregulation using the KNX climate device but I’m not able to change the hysteresis on this controller so if I put 20 °C as temperature set point the valve doesn’t turn off until the real temperature rises over 21 °C so according to the temperature inertia the real temperature reach 22,5 °C. Does anyone know if it is possible to decrease the hysteresis from 1°C to 0.3 °C?

Hi :wave:!
If your climate controller is KNX then you would probably set this via ETS.

Yes, but I think the temperature control is made by Home Assistant, isn’t it?

If you mean a KNX Climate entity, then no - this is just an interface to set values (target temp or mode) for a KNX controller. It is not a controller itself.

Thank you very much, so I’ll try to have a look on ETS.

I changed the hysteresis parameters on ETS and now it’s ok. Thank you very much for your suggestion.

1 Like