have a knx aktor. but, the actual temperature does not come from the knx bus, it comes from a mqtt sensor.
- name: Bad
temperature_address: “4/2/2”
target_temperature_address: “4/2/3”
target_temperature_state_address: ???
setpoint_shift_address: “4/2/78”
setpoint_shift_state_address: “4/2/78”
operation_mode_address: “5/1/6”
operation_mode_state_address: “5/1/6”
min_temp: 7.0
max_temp: 32.0
entitie id sensor.xiaomi_htp_bad_eg_temperature
how should the configuration look like here?
farmio
(Matthias Alphart)
2
Hi
The knx Integration can only handle values seen on the knx bus.
- Create a dummy-group-address and assign it to the temperature.
- Use knx expose to send the HA (mqtt) value to the bus.
-
target_temperature_state_address
is not the current room temperature, temperature_address
is.
- when you use setpoint shift better use
setpoint_shift_min
and Max instead of min_temp
(maybe both together can work too)
Mario_H
3
Hello, thanks for your reply. i will give them an try.