I’m facing an issue where a cover is configured to work with KNX. When i move the cover up from the GUI it goes up but randomly stops at 38%. In the log from KNX i can see that a “Down” command is sent from the hassio but this has not been done by the user.
Not entirely sure. Here are some things you can try:
configure travelling_time_down and -up
configure position_address
maybe it helps.
That said MDTs “Single Object Control” is not supported and may lead to problems. If this is the cause of your issue reconfigure your actuators or maybe try removing move_long_address and only configure position_* for %-movement.
Thanks! the shutter doesn’t stop randomly anymore. The only issue that i still see is that the status bar moves twice as fast as the status that comes from the bus. (see attached video in wetransfer link)
Yes, and I think it does.
Most actuators don’t send percentages when moving - or at least not that often. So xknx interpolates the position until a new one is received to enable a smoothly moving slider in HA.