Modbus with EW11 + QDY30A RS485 water level measure probe

I want to share how to set up a QDY30A RS485 water level measure probe that i bought on AliExpress without any documentation together with a Elfin-EW11A RS485<->Wifi bridge.

The documentation was hard to find but eventually I found it :
(due to restriction I can not add more pictures :frowning: )

function code | Data start address | Number of data | Data bytes | Data range | Command meaning
--------------+--------------------+----------------+------------+------------+-----------------------------------------------------------
0x03          | 0x0000             | 1              | 2          | 1-255      | Read the slave machine address              
0x03          | 0x0001             | 1              | 2          | 0 = 1200   | Baud rate reading
                                                                 | 1 = 2400   | 
                                                                 | 2 = 4800   | 
                                                                 | 3 = 9600   | 
                                                                 | 4 = 19200  | 
                                                                 | 5 = 38400  | 
                                                                 | 6 = 57600  | 
                                                                 | 7 = 115200 | 
0x03          | 0x0002             | 1              | 2          | 0 = unit no| Pressure unit
                                                                 | 1 = CM     | 
                                                                 | 2 = MM     | 
                                                                 | 3 = MPa    | 
                                                                 | 4 = Pa     | 
                                                                 | 5 = KPa    | 
                                                                 | 6 = MA     | 
0x03          | 0x0003             | 1              | 2          | 0 = ####   | Decimal places represent 0-3 decimal points respectively
                                                                 | 1 = ###.#  |
                                                                 | 2 = ##.##  |
                                                                 | 3 = #.###  |
0x03          | 0x0004             | 1              | 2          |-32768-32767| Measure the output value
0x03          | 0x0005             | 1              | 2          |-32768-32767| Transmitter range zero
0x03          | 0x0006             | 1              | 2          |-32768-32767| Transmitter range is full point

So we need to read the register value 0x0004
I added this to HA configuration.yaml

modbus:
  - name: "dr-tom-ew11-rs485-wp-1"
    type: tcp
    host: 10.0.6.164
    port: 502
    timeout: 3
    sensors:
      - name: "Water well level"
        slave: 1
        address: 4
        data_type: int16
        unit_of_measurement: cm
        input_type: holding
        scale: 1.0
        precision: 1
        scan_interval: 5

Than I configured the EW11, extract of my configuration backup :

<!--SYS Config-->
<SYS key='User' value='admin'>
<SYS key='Password' value='yourpwd'>
<SYS key='DHCP' value='Enable'>
<SYS key='Ip Address' value='10.10.100.10'>
<SYS key='GateWay' value='10.10.100.254'>
<SYS key='Mask' value='255.255.255.0'>
<SYS key='Host Name' value='dr-tom-ew11-rs485-wp-1'>
<SYS key='DNS' value='10.0.6.3'>
<SYS key='Telnet' value='Enable'>
<SYS key='Telnet Port' value='23'>
<SYS key='Echo' value='Enable'>
<SYS key='Web' value='Enable'>
<SYS key='Web Port' value='80'>
<SYS key='Ipv6' value='Disable'>
<SYS key='Ipv6 address' value=''>
<SYS key='Ipv6 DHCP' value='Disable'>
<SYS key='NTP' value='Enable'>
<SYS key='NTP Server' value='0.be.pool.ntp.org'>
<SYS key='NTP Port' value='123'>
<SYS key='NTP GMT' value='2'>
<SYS key='Customer ID' value='EW11'>
<SYS key='Config Version' value='0'>
<SYS key='NetworkMode' value='Router'>
<SYS key='WiFiMode' value='STA'>
<SYS key='WiFiAPSSID' value='EW11_E52C'>
<SYS key='WiFiAPKey' value=''>
<SYS key='WiFiSTASSID' value='yourwifisssid'>
<SYS key='WiFiSTAKey' value='yourwifipwd'>
<SYS key='WiFiAPCH' value='0'>
<SYS key='WiFiHideSSID' value='0'>
<SYS key='WiFiRoamingEn' value='0'>
<SYS key='ScanRSSIThreshold' value='0'>
<SYS key='ConnectRSSIThreshold' value='0'>
<SYS key='LanIpAddress' value='10.10.100.254'>
<SYS key='LanMarsk' value='255.255.255.0'>
<SYS key='LanDhcpEn' value='Enable'>
<SYS key='EthernetMode' value='WAN'>
<SYS key='Longitude' value='0.000000'>
<SYS key='Latitude' value='0.000000'>
<SYS key='SmartConfig' value='SmartLink'>
<SYS key='ModbusTime' value='0'>

<!--UART Config-->
<UART key='Baudrate' value='115200'>
<UART key='Databits' value='8'>
<UART key='Stopbits' value='1'>
<UART key='Parity' value='NONE'>
<UART key='FlowCtrl' value='Disable'>
<UART key='Software FlowCtrl' value='Disable'>
<UART key='Xon' value='11'>
<UART key='Xoff' value='13'>
<UART key='Protocol' value='Modbus'>
<UART key='Frame Length' value='16'>
<UART key='Frame Time' value='100'>
<UART key='Tag Enable' value='Disable'>
<UART key='Tag Head' value='00'>
<UART key='Tag Tail' value='00'>
<UART key='Buffer Size' value='512'>
<UART key='gapTime Size' value='50'>
<UART key='cliGetin' value='1'>
<UART key='serialStr' value='+++'>
<UART key='waitTime' value='300'>

<!--SOCK Config-->
<SOCK name='netp' key='Name' value='netp'>
<SOCK name='netp' key='Protocol' value='TCP-SERVER'>
<SOCK name='netp' key='Local Port' value='502'>
<SOCK name='netp' key='Buffer Size' value='512'>
<SOCK name='netp' key='KeepAlive' value='60'>
<SOCK name='netp' key='Timeout' value='0'>
<SOCK name='netp' key='Security' value='NONE'>
<SOCK name='netp' key='Connect Mode' value='Always'>
<SOCK name='netp' key='VcomEn' value='0'>
<SOCK name='netp' key='Rout' value='uart'>
<SOCK name='netp' key='maxAccept' value='3'>

The sensor is connected to the EW11 in this way :

[u]Sensor        <------->    Elfin EW11[/u]   <------>   24V power supply
BLUE                           A               
RED                            +                          +
GREEN                          -                          -
YELLOW                         B

Of course not everything worked from the first time :frowning:
First I used a USB to RS485 converter and connected the probe to it.
By using a trial version of ModBusPoll I was able to connect to it (9600 baud, 8data, no parity, 1 stop bit, mode RTU) and read the registers.
Then I wrote (adapted) a python script that can read the 7 registers available over TCP via EW11.

#!/usr/bin/env python3

# TDV 11/02/2024 : sudo pip3 install pyModbusTCP

# function code | Data start address | Number of data | Data bytes | Data range | Command meaning
# --------------+--------------------+----------------+------------+------------+-----------------------------------------------------------
# 0x03          | 0x0000             | 1              | 2          | 1-255      | Read the slave machine address
# 0x03          | 0x0001             | 1              | 2          | 0 = 1200   | Baud rate reading
#                                                                  | 1 = 2400   |
#                                                                  | 2 = 4800   |
#                                                                  | 3 = 9600   |
#                                                                  | 4 = 19200  |
#                                                                  | 5 = 38400  |
#                                                                  | 6 = 57600  |
#                                                                  | 7 = 115200 |
# 0x03          | 0x0002             | 1              | 2          | 0 = unit no| Pressure unit
#                                                                  | 1 = CM     |
#                                                                  | 2 = MM     |
#                                                                  | 3 = MPa    |
#                                                                  | 4 = Pa     |
#                                                                  | 5 = KPa    |
#                                                                  | 6 = MA     |
# 0x03          | 0x0003             | 1              | 2          | 0 = ####   | Decimal places represent 0-3 decimal points respectively
#                                                                  | 1 = ###.#  |
#                                                                  | 2 = ##.##  |
#                                                                  | 3 = #.###  |
# 0x03          | 0x0004             | 1              | 2          |-32768-32767| Measure the output value
# 0x03          | 0x0005             | 1              | 2          |-32768-32767| Transmitter range zero
# 0x03          | 0x0006             | 1              | 2          |-32768-32767| Transmitter range is full point

""" Read 10 holding registers and print result on stdout. """

import time
from pyModbusTCP.client import ModbusClient


# init modbus client
c = ModbusClient(host='10.0.6.164', port=502, debug=True, auto_open=True)

# main read loop
while True:
    # read 7 registers at address 0, store result in regs list
    regs_l = c.read_holding_registers(0, 7)

    # if success display registers
    if regs_l:
        print('reg ad #0 to 7: %s' % regs_l)
    else:
        print('unable to read registers')

    # sleep 2s before next polling
    #time.sleep(2)

When that succeeded, I was able to eventually after reading and tweaking to do the HA integration. Using the elevated logging helped :slight_smile:

# Logger config
logger:
  default: warning
  logs:
    homeassistant.components.modbus: debug
    pymodbus: debug

This gives us the following logging, once working. On every retrieval the sequence is augmented.

024-02-12 02:03:17.493 DEBUG (SyncWorker_11) [pymodbus.logging] Current transaction state - IDLE
2024-02-12 02:03:17.493 DEBUG (SyncWorker_11) [pymodbus.logging] Running transaction 1
2024-02-12 02:03:17.493 DEBUG (SyncWorker_11) [pymodbus.logging] SEND: 0x0 0x1 0x0 0x0 0x0 0x6 0x1 0x3 0x0 0x4 0x0 0x1
2024-02-12 02:03:17.493 DEBUG (SyncWorker_11) [pymodbus.logging] New Transaction state "SENDING"
2024-02-12 02:03:17.493 DEBUG (SyncWorker_11) [pymodbus.logging] Changing transaction state from "SENDING" to "WAITING FOR REPLY"
2024-02-12 02:03:17.606 DEBUG (SyncWorker_11) [pymodbus.logging] Changing transaction state from "WAITING FOR REPLY" to "PROCESSING REPLY"
2024-02-12 02:03:17.606 DEBUG (SyncWorker_11) [pymodbus.logging] RECV: 0x0 0x1 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x0
2024-02-12 02:03:17.606 DEBUG (SyncWorker_11) [pymodbus.logging] Processing: 0x0 0x1 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x0
2024-02-12 02:03:17.606 DEBUG (SyncWorker_11) [pymodbus.logging] Factory Response[ReadHoldingRegistersResponse': 3]
2024-02-12 02:03:17.606 DEBUG (SyncWorker_11) [pymodbus.logging] Adding transaction 1
2024-02-12 02:03:17.606 DEBUG (SyncWorker_11) [pymodbus.logging] Getting transaction 1
2024-02-12 02:03:17.606 DEBUG (SyncWorker_11) [pymodbus.logging] Changing transaction state from "PROCESSING REPLY" to "TRANSACTION_COMPLETE"
2024-02-12 02:03:21.996 DEBUG (SyncWorker_3) [pymodbus.logging] Current transaction state - TRANSACTION_COMPLETE
2024-02-12 02:03:21.996 DEBUG (SyncWorker_3) [pymodbus.logging] Running transaction 2
2024-02-12 02:03:21.996 DEBUG (SyncWorker_3) [pymodbus.logging] SEND: 0x0 0x2 0x0 0x0 0x0 0x6 0x1 0x3 0x0 0x4 0x0 0x1
2024-02-12 02:03:21.996 DEBUG (SyncWorker_3) [pymodbus.logging] New Transaction state "SENDING"
2024-02-12 02:03:21.996 DEBUG (SyncWorker_3) [pymodbus.logging] Changing transaction state from "SENDING" to "WAITING FOR REPLY"
2024-02-12 02:03:22.087 DEBUG (SyncWorker_3) [pymodbus.logging] Changing transaction state from "WAITING FOR REPLY" to "PROCESSING REPLY"
2024-02-12 02:03:22.087 DEBUG (SyncWorker_3) [pymodbus.logging] RECV: 0x0 0x2 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x0
2024-02-12 02:03:22.087 DEBUG (SyncWorker_3) [pymodbus.logging] Processing: 0x0 0x2 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x0
2024-02-12 02:03:22.087 DEBUG (SyncWorker_3) [pymodbus.logging] Factory Response[ReadHoldingRegistersResponse': 3]
2024-02-12 02:03:22.087 DEBUG (SyncWorker_3) [pymodbus.logging] Adding transaction 2
2024-02-12 02:03:22.087 DEBUG (SyncWorker_3) [pymodbus.logging] Getting transaction 2
2024-02-12 02:03:22.087 DEBUG (SyncWorker_3) [pymodbus.logging] Changing transaction state from "PROCESSING REPLY" to "TRANSACTION_COMPLETE"
2024-02-12 02:03:26.996 DEBUG (SyncWorker_11) [pymodbus.logging] Current transaction state - TRANSACTION_COMPLETE
2024-02-12 02:03:26.996 DEBUG (SyncWorker_11) [pymodbus.logging] Running transaction 3
2024-02-12 02:03:26.996 DEBUG (SyncWorker_11) [pymodbus.logging] SEND: 0x0 0x3 0x0 0x0 0x0 0x6 0x1 0x3 0x0 0x4 0x0 0x1
2024-02-12 02:03:26.996 DEBUG (SyncWorker_11) [pymodbus.logging] New Transaction state "SENDING"
2024-02-12 02:03:26.998 DEBUG (SyncWorker_11) [pymodbus.logging] Changing transaction state from "SENDING" to "WAITING FOR REPLY"
2024-02-12 02:03:27.083 DEBUG (SyncWorker_11) [pymodbus.logging] Changing transaction state from "WAITING FOR REPLY" to "PROCESSING REPLY"
2024-02-12 02:03:27.083 DEBUG (SyncWorker_11) [pymodbus.logging] RECV: 0x0 0x3 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x0
2024-02-12 02:03:27.083 DEBUG (SyncWorker_11) [pymodbus.logging] Processing: 0x0 0x3 0x0 0x0 0x0 0x5 0x1 0x3 0x2 0x0 0x0
2024-02-12 02:03:27.083 DEBUG (SyncWorker_11) [pymodbus.logging] Factory Response[ReadHoldingRegistersResponse': 3]
2024-02-12 02:03:27.083 DEBUG (SyncWorker_11) [pymodbus.logging] Adding transaction 3
2024-02-12 02:03:27.083 DEBUG (SyncWorker_11) [pymodbus.logging] Getting transaction 3
2024-02-12 02:03:27.083 DEBUG (SyncWorker_11) [pymodbus.logging] Changing transaction state from "PROCESSING REPLY" to "TRANSACTION_COMPLETE"

I hope this guide is helpfull for someone :slight_smile:
When I get enough posts, I will add some screenshots.

Cheers,
Tom

2 Likes

Hello Tom,

I have the same probe I think, but with the modbuspoll tool and with the parameters you suggested it seems my USB rs485 adapter (sh-u11h) cannot talk to the probe/find its address.

I tried a 24v PSU and a 18v one, I am pretty sure the A and B terminals are correctly connected, but the led on the adapter for the reception never lights up, even when you power up the probe.

Do you think could be a DOA or am I doing something wrong? Is there a gnd that should be used somewhere?

Thanks for your post anyway!

Cheers
Raimondo

Hello Raimondo,

The sensor needs to be connected to the 24V.
As the EW11 also needs 24v the positive and negative are connected.

When using an SH-U11H you need to connect the following

SH-U11H → RS485 PIN: TXD+(A+), TXD-(B-) AND probably the GROUND
It could be that you need to connect a 120 ohm resistor between A+ en B+ (documentation : there is no 120 ohm resistor between A+ and B-)

So sensor → SH-U11H wiring should be like

TX (blue) -> TXD+(A+) (pin 1)
RX (yellow) -> TXD-(B-) (pin 2)
GND (green) -> GND AND power supply GND (pin 5)
+24V (red) -> power supply +24V

Let us know if it works.

Thank you so much. This also works with a QDW90A from AliExpress.
I read 5 modbus words using function 3 at 9600 baud, 8 data bits, 1 stop bit, no parity.

  1. slave address
  2. baud reading
  3. pressure unit
  4. decimal point position (i.e. scale factor)
  5. value
    Precisely as the table in your python code.

Thanks again, that really saved me some time :slight_smile: .

Best regards,

Victor

Thanks a lot tomdv !
This greatly helped me to get my QDY30A working.
I used a cheap RS485-to-USBserial adapter:
https://www.amazon.de/dp/B0BV7DVKR5?ref=ppx_yo2ov_dt_b_product_details&th=1

and the great open source tool:
https://pymodbus.readthedocs.io/en/latest/source/repl.html
After installation with:
pip3 install “git+https://github.com/pymodbus-dev/repl”
started with: pymodbus.console serial --port /dev/cu.usbserial-A50285BI --baudrate 9600 --bytesize 8
Then within the running console:

client.read_holding_registers address=0 count=7 slave=1
which delivered:
{
“registers”: [
1,
3,
1,
1,
629,
0,
2000
]
}
which delivers correct pressure readings.
However the sensor reported some minor false infos:
Pressure unit as “1 = cmH2O”, but in fact uses “2 = mmH2O”
Decimal places as “1 = ###.#” but in fact uses “0 = ####”
Eventually realized to integrate in ESPhome for use in HomeAssistant:
Water level sensor QDY30A modbus RS485 with ESP32 S2 mini

Hi, would like to add my case: cheap modbus relay (relay controls output) and pressure sensor QDW90A.

configuration.yaml
modbus:

  • name: modbus_hub
    type: rtuovertcp
    host: 192.168.31.222
    port: 502

    delay: 0
    message_wait_milliseconds: 30
    timeout: 5

    sensors:

    • name: “Pressure”
      slave: 1
      address: 4
      input_type: holding
      data_type: int16
      unit_of_measurement: “Bar”
      scale: 0.001
      precision: 3
      scan_interval: 5



изображение