Perfect Heating Automation with Sonoff TRVZB
Hello everyone,
To keep this post concise, I’ll focus on practical solutions without diving into excessive details. Recently, I purchased a Sonoff TRVZB. This is not my first experience with TRVs; I’ve already been using seven Moes BRT-100 TRVs in my home. Let me tell you right away: Moes TRVs are the worst TRVs ever produced. After some time, they released newer versions to address their shortcomings.
I integrated the Sonoff TRVZB into Home Assistant via Zigbee2MQTT (Z2M) without any issues. After the installation, I examined the features provided by the Z2M panel. One feature that caught my attention was the “external temperature sensor integration”, introduced in a recent firmware update. Unfortunately, this feature wasn’t available in Z2M yet. This update is currently exclusive to Sonoff Zigbee Bridge Pro devices, and firmware updates can only be performed via this hub. Sonoff has announced that it will be available for other hubs by Q4 2024.
Step 1: Inaccurate Temperature Sensor
The first problem I encountered was the inaccurate temperature readings from the built-in sensor on the TRV. Since the offset values kept changing, manual calibration wasn’t a viable option. My initial step was to disable temperature reporting from the TRV in Z2M and create an automation that pulls temperature data from an external sensor.
  • How to disable reporting:
    I disabled all reporting fields in Z2M to ensure the TRV doesn’t send inaccurate temperature data
  • External sensor selection:
    For the living room, I used a Sonoff SNZB-02D temperature sensor. However, even though these sensors were connected via Z2M, their reporting frequency wasn’t sufficient. For precise climate control, the sensor needs to update temperature data frequently. The Sonoff sensors, unfortunately, updated data every 5–10 minutes, which was inadequate.
  • Solution for faster updates:
    I adjusted the Z2M reporting settings to ensure quicker updates. Here are the settings I used:
Edit: Now that we’ve shortened the reporting intervals, it’s time to start using the data from the external sensor together with the TRVs. Fortunately, a new update has made this process much easier. In Zigbee2MQTT, open the TRV settings and select the external option. It’s important that external is selected. I recommend exiting the screen after selecting it and then returning immediately to make sure that the external option is still checked.
Below, you’ll find a simple automation that allows your TRVs to receive temperature data directly from an external sensor. Once you’ve adjusted the reporting intervals and selected the external option, this automation will ensure that your TRVs use the temperature readings from your external sensor.
alias: TRV Calibration - SalonTRV3_Calibration New
description: Xiaomi sıcaklığını external input olarak TRV'ye gönderir
triggers:
  - entity_id:
      - sensor.xiaomi_salon_temperature
    for:
      hours: 0
      minutes: 0
      seconds: 1
    trigger: state
conditions: []
actions:
  - target:
      entity_id: number.salon_trv_3_external_temperature_input
      value: "{{ states('sensor.xiaomi_salon_temperature') | float }}"
    action: number.set_value
mode: single
As you can see, the automation is very simple. You just need to enter the entity of your external temperature sensor, and then go to the MQTT section under Integrations, find your TRV’s number.salon_trv_3_external_temperature_input entity, and enter it here.
Alternatively, @photomoose also has a blueprint that performs this task. If you prefer a simpler setup, you can use that instead.
Sonoff TRVZB External Temperature Sensor Calibration
Step 2: Integrating Better Thermostat
With accurate temperature readings, the next step was to use Better Thermostat in Home Assistant. I created thermostat cards for each TRV in my home, assigning external temperature sensors, door/window sensors, and other inputs where applicable.
  • Key settings:
    • Target Base Temperature: Configured for optimal comfort.
    • Calibration: Disabled the app’s internal calibration to avoid errors, as I had already set accurate calibration through Z2M.
However, now a new issue emerged: Hysteresis values.
Step 3: Hysteresis Handling
The hysteresis setting on Sonoff TRVs used to be set to an odd fixed value like 1°C. So when you set the temperature to, say, 23°C, the TRV would stop heating once it reached that value. However, even if the temperature later dropped to 22.5°C, the valve would not reopen. The valve would only reopen if the temperature dropped below 22°C, which, as I mentioned earlier, was due to the fixed 1°C hysteresis value.
What made this worse was that, in Better Thermostat, the valve would appear to be open, but when you checked via MQTT, you’d see that the valve was actually closed.
This behavior changed with firmware version 1.3.0, which finally introduced proper hysteresis control. If you want this functionality, make sure to update your TRVs to firmware 1.3.0.
The new setting can be found in MQTT under temperature_accuracy, where you can adjust the hysteresis value between 1°C and 0.2°C.
Daily Automation
The final step was creating a daily automation to adjust temperatures based on my schedule:
  • 8 AM – 6 PM: Lower temperatures for efficiency.
  • 6 PM – 11:30 PM: Higher temperatures for comfort.
  • 11:30 PM onwards: Reduced all TRVs to 5°C as the central heating system shuts off.
alias: TRV Oto Mod - Zaman ve Duruma Göre
description: TRV'leri belirli saat aralıklarında ve koşullara göre ayarlar.
triggers:
  - trigger: time_pattern
    minutes: /10
conditions:
  - condition: state
    entity_id: input_boolean.live_tiles_trv_auto_aqara
    state: "on"
  - condition: state
    entity_id: person.berkan
    state: home
  - condition: state
    entity_id: alarm_control_panel.ha_alarm
    state: disarmed
actions:
  - choose:
      - conditions:
          - condition: time
            after: "08:00:00"
            before: "18:00:00"
        sequence:
          - target:
              entity_id: climate.bedroom_trv_better
              temperature: 20
            action: climate.set_temperature
          - target:
              entity_id: climate.ofis_trv_better
              temperature: 23
          - target:
              entity_id: climate.giysi_trv_better
              temperature: 22
          - target:
              entity_id:
                - climate.salon_trv_1_better
                - climate.salon_trv2_better
                - climate.salon_trv3_better
                - climate.salon_trv_4_better
              temperature: 22
      - conditions:
          - condition: time
            after: "18:00:00"
            before: "23:30:00"
        sequence:
          - target:
              temperature: 22
          - target:
              temperature: 23
          - target:
              temperature: 23
          - target:
              entity_id:
              temperature: 23
      - conditions:
          - condition: time
            after: "23:30:00"
            before: "07:59:59"
        sequence:
          - target:
              entity_id:
                - climate.bedroom_trv_better
                - climate.ofis_trv_better
                - climate.giysi_trv_better
              temperature: 5
mode: single
Conclusion
By combining Zigbee2MQTT, Better Thermostat, and custom Home Assistant automations, I achieved a perfectly optimized heating system. It reacts to real-time changes, maintains accurate temperatures, and overcomes the limitations of Sonoff TRVs. Additionally, Sonoff TRVs allow you to configure the percentage at which the valves remain open or closed via MQTT. This feature enables you to create automations throughout the day based on temperature conditions. For example, even if the TRVs reach their set points after 6 PM, you can keep the valves 25% open to slow down the cooling of the room, ensuring a more comfortable environment.
I hope this helps anyone facing similar issues. Feel free to ask questions or share your thoughts!
Hi I’m also trying to use external sensors for my Sonoff TRVZB. I think it might be easier to just use external temperature sensors to adjust the TRV’s offset value. This way there’s no need to adjust the polling rate as it just need to verify the offset value every 5-10 min
Hello. Actually, I initially tried a similar solution. However, I noticed some issues when I didn’t disable the internal sensor on the Sonoff TRV itself. For example, the temperature readings were highly unstable. Let’s say the room was 23°C, the sensor would show 23.4°C at one moment, then drop to 22.8°C, and later record something like 23.3°C. In short, the readings weren’t consistent. How can you manually assign a stable value to an external sensor when the readings fluctuate like this? For instance, the offset value can go from -2.3 to +2 in a short period of time. In my opinion, at least for me, the most reliable method is to disable this reporting and use automation instead.
I have a problem with sonoff trv (zigbeetoMQTT) using better thermostat, if the temperature drops with 0.1 degrees the trv starts heating until the set temperature is reached meaning for 0.1 degrees, how can i change the tolerance to 0.5, the tolerance setting in better thermostat seems not to work. thanks
The reason for this is that the values created by the Better Thermostat do not affect the actual main valve, which is the MQTT valve. In other words, you set the tolerance value in Better, but it does not impact the actual valve in MQTT. Honestly, I don’t know if there is a way to address this. Maybe it can be achieved with a complex automation as well.
Thanks for the answer, that is really not so god news for me. But anyone has the same problem? O jut i see it as a problem? Also i am not able to disable all the reporting
How to disable these too?
Thanks for this overview, very helpful. I took a different approach using automations. I set up two for each TRV, one for high temp and one for low temp using an external zigbee thermometer as the trigger. I set the hvac mode to on/off (high/low). This worked fine. I then tried to manually set (within zigbee2mqtt) the degree open/close % for some finer control (i.e. i did not want the valves to total close, only 50% for example). but I could not seem to get this to work. Has anyone else manage to get the degree close % for the valves to work? Any suggestions for how to test them, I tried to manually set the values but nothing seems to change with the valves. I would expect (for example) if the valve is closed, and degree is set to 100. If I then change the degree closed to say 50% the valve would then open to half way, but all my tests nothing seems to happen when I play with this attribute. I have the latest firmware so this should not be an issues. I was thinking/hoping to adjusting that value (degree open/close) directly but I think I could live with on/off with the % on/off being fixed if I could get it to work.
Thanks,
Pete.
Ok. so I am going to reply to my own post as I have had a bit of a break through. Here are my observations.
If the local temperature (i.e. TRV temp) is 20c, occupied heating setpoint is set to 30c with heating mode set to “heat”. I can then adjust the valve open degree and hear the valve changing. If the set point is below the local temperature changing the open degree has no effect.
If the local temperature (i.e. TRV temp) is 20c, occupied heating setpoint is set to 15c with heating mode set to “off”. I can then adjust the valve close degree and hear the valve changing. If the set point is above the local temperature changing the close degree has no effect.
It appears there is some interrelationship between the temperature set point, local temperature and the ability to change/adjust the open/close degree. I’m guessing this make sense is you are using the local/temperature and set point.
So, it appears if I want to have this fine control in my automations I will need to change the set point temperature on close/open to be above or below temperature as appropriate then i can adjust the close/open degree.
As mentioned above. Being able to exchange the local provided temperature for an external temperature (i.e. provided by a zigbee thermometer) would be great additional functionality.
Yet another reply to my own post. It appears the “temperature” entity is not the set point temperature but the calibration temperature. Very odd to have this exposed and an entity but not the set point temperature. I will look into updating the zigbee2mqtt description file to fix this as it is available via mqtt just not as an entity with HA. in the mean time a work around is to send an mqtt message to change the set point in my automations.
Hello. First of all, you can set the valves to open and close at specific percentages. This can be done easily with an automation since the valves appear as entities. However, instead of dealing with complex automations, I have a simpler suggestion for you.
For instance, in the example automation I shared, I divided the day into two parts. From 8:00 AM to 6:00 PM, I set different degrees, and from 6:00 PM to 11:30 PM, I set another degree. You could create an automation that, for example, adjusts the valve’s closing position to a specific percentage (like 50%) after 6:00 PM. Then, at 11:30 PM, the automation could turn itself off.
This way, in the evenings, when the setpoint is reached, the valves won’t close completely, preventing the room from cooling down quickly again.
The temperature part, as you mentioned, is the section where calibration is performed. Setpoints, on the other hand, are directly controlled via thermostat cards or service calls. These are entirely different things.
As I also mentioned in my text, unfortunately, the temperature value for Sonoff TRVs is extremely unstable. It does not remain at a constant value, which causes incorrect readings when manual calibration is performed.
You can change the set temperature values via MQTT messages, and you can also create actions. I preferred the action part.
Thanks for the feedback. Yep, I went with the mqtt approach for low and high temp. I leave the mode to heat. When my room thermostat goes over a certain value I reduce the setpoint temp low (10c) and when room thermostat drops below a certain temperature increase the setpoint (30c). When the automation runs I see the setpoint value change and the state change idle/heat. I’ll play around with the valve degree values for further fine tuning over the next few days.
mqtt action…
Topic:
zigbee2mqtt/TRV Bathroom/set
payload:
{“occupied_heating_setpoint”: 10}
It’s odd that the calibration temperature is exposed as an entity but the setpoint temperature is not, not sure if that is an oversight or if there is a technical reason for this situation.
Getting
z2m: Request 'zigbee2mqtt/bridge/request/device/configure_reporting' failed with error: 'Bind 0x0ceff6fffe6799d4/1 msTemperatureMeasurement from '0x00124b001ccdfe83/1' failed (AREQ - ZDO - bindRsp after 10000ms)'
when I try to modify any reporting intervals for my SNZB-02Ds.
Update: Fixed by re-connecting the sensors.
Update. My method for using an external thermometer with TRVZB seems to be working well so far.
Recap:
set mode to heat
Create automation triggered by max temperature required in room
action mqtt:
Topic:
payload:
Similar for the low temp. But set heating temp to something like 30c
I have also adjusted the open/close degree for finer control.
I see on the official Sonoff website for these devices it says
 You can select a SONOFF Zigbee temp. sensor as the external sensor
Anyone know if this capability will be added to HA/zigbee2mqtt?
There may be certain reasons why the reporting feature of your device cannot be disabled. Below are potential causes and solutions based on my experience:
  1. USB Dongle Issue:
    The problem might be related to the USB dongle you are using. I managed to disable this reporting feature successfully with a Sonoff Dongle Plus.
  2. Firmware Updates:
    Ensure that all your devices are running the latest firmware. Outdated firmware can cause unexpected issues.
  3. Device-Specific Issues:
    There might be a problem specific to the device itself, affecting its behavior.
  4. Coordinator Limitations:
    Check if the Zigbee coordinator you are using is nearing its capacity limit. Overloading the coordinator can lead to performance issues.
Maybe in a future update but not for now.
Hi Berkan,
Great work! I am trying to replicate this for my sonoff TRV and aquara room sensors. I am having difficulty with your automation for updating the TRV offset. and wondered if you could possibly review my code please?
First time for me writing such automations with MQTT
I get the error
Error: ValueError: Template error: float got invalid input 'unknown' when rendering template '{{ states('number.0x08ddebfffea87a36_local_temperature_calibration') | float }}' but no default was specified
Here is my code (slightly different format to yours as enforced by my HA)
alias: TRV UPdate Master Bed
description: ""
  - platform: state
    entity_id:
      - climate.master_bedroom_bed_trv
    attribute: current_temperature
  - platform: state
    entity_id:
      - sensor.master_bedroom_aquara_temperature
condition:
  - condition: template
    value_template: >
      {{ state_attr('climate.master_bedroom_bed_trv', 'current_temperature') |
      float != states('sensor.master_bedroom_aquara_temperature') | float }}
  - variables:
      trvtemp: >-
        float }}
      trvcalib: >-
        float }}
      roomtemp: "{{ states('sensor.master_bedroom_aquara_temperature') | float }}"
      calibration: "{{ (trvcalib - (trvtemp - roomtemp)) | round(2) }}"
      vpayload: |
          "local_temperature_calibration": {{ calibration }}
  - service: mqtt.publish
    metadata: {}
      qos: 0
      retain: false
      topic: zigbee2mqtt/0x08ddebfffea87a36/set
      payload: "{{ vpayload }}"
mode: single
I’ve pasted the same question to AI, and got this reply:
actions:
  - variables:
      trvtemp: "{{ state_attr('climate.stiralnia_trv', 'current_temperature') | float(0) }}"
      trvcalib: >-
        {{ states('number.0x08ddebfffea9946c_local_temperature_calibration') | float(0) }}
      roomtemp: "{{ states('sensor.stiralnia_sensor_temperature') | float(0) }}"
By adding | float(0) to each template, you ensure that if the value is ‘unknown’, it will default to 0 instead of causing an error
This is awesome! Thank you so much.
I now have this largely working, although the temperature reporting from the TRV seems to fluctuate. If i view the sensor value on my dashboard it flicks between 23.5 (which is the temp the TRV will be reading) and 20 (which is the temp my external sensor is writing back. I can see this too under Z2M for the TRV under the exposes tab. The offset keps moving and changing.
Is this expected behaviour? I have turned off local temperature reporting under the reporting tab of Z2M for the TRV.
Many Thanks
Mike
Room temperatures do not fluctuate sharply between values like 20 and 23 degrees. It’s likely that your TRV is still trying to read from its built-in thermometer. Are you sure you’ve completely disabled it in the reporting section? To test this, first disable it in the reporting section and avoid running the automation immediately. Instead, observe the calibration value on the expose page for a while. Once you’re certain that the value remains stable, then you can run the automation.