I’m looking to expand my residential electrical monitoring to include some complete branch circuits, specifically 2 240V circuits dedicated to HVAC systems. I plan to do this with a Shelly EM and have been reading some docs/forums about it, but a couple questions remain.
This is a US power system, so it’s split-phase with 2 120V lines 180 degrees out of phase with each other (L1 and L2) along with a common neutral (N). The 240V branch circuits to be monitored are 2-wire circuits that just tie into L1 and L2 (no neutral connection), so the current on each wire should be equal. As a result, I plan to monitor only one leg of each. Here’s how I think that shakes out (blue are components to be added):
As you can see though, I’m not sure how to handle the N connection on the Shelly EM. It could go to the common neutral bar in the panel (120V power to Shelly) or it could go to L2 (240V power to Shelly). They Shelly specs say it can handle either voltage but the correct wiring may depend on whether-or-not those L/N terminals also act as voltage and phase references for the power calculations the Shelly makes. That’s where I’m seeing lots of conflicting info:
This discussion implies that the Shelly should always use 120V independent of the circuits being monitored, and that it will detect voltage directly via the CT clamps. However, it also notes that Shelly will still detect incorrect power values which have to be adjusted for in HA.
This discussion (and reference from Shelly support) seems to imply that the voltage and phase details are in fact determined by the L terminal, presumably relative to the N terminal, on the Shelly. I’ve seen a couple other similar discussions, but not conclusive.
So I was hoping someone may know if those L/N terminals on the Shelly are doing more than just supplying power and if they are also involved in phase/voltage references that have impacts on the power calculations. That would inform correct wiring and also what data adjustments may be required on the HA-side (if any).
L provides voltage and phase for measurement using both clamps.
Ok, thanks, then this implies that L is indeed used for more than just device operational power. For phase I don’t see any issue since I’ll ensure that the Shelly L connection is tied to L1 in the panel (also the same phase direction as the wires CT clamps are connected to). However, for a voltage calculation the Shelly must be looking at the difference between L and N. So, if connecting N to the neutral bar this will be 120V, which is not correct for monitoring a 240V line. I assume it would work but power calculations might then be off by a factor of 2. Would connecting the Shelly N to L2 solve for this, or is that just introducing other computation problems?
I’m not an expert, so remember that, this is my opinion from the docs…
That has CT ports that measure the load current and with that I would think phase… Could be wrong.
I would expect L and N to be the power supply for the thing’s internals only. Likely that is an internal power supply and the specs state it works with international voltages, meaning it would have to be isolated and separate. And according to the specs Shelly EM can use:
Power supply AC 110-240 V, 50/60Hz
That means it should be able to power L & N to L1 and L2
or L & N to L1(or L2) and the white neutral wire which likely comes in from the vault.
Didn’t think of that. So in that case I would treat it like EU and L & N goes to L1 & L2 to measure all the voltage and any device internals that power to ground are treated as noise, I guess.
But to be safe, ask the shelly people directly. (as maxym said)
Thanks all. My Shelly EM is still on-order so I’ll need to report back more when I have it and can test more. I believe I ordered a gen 1 Shelly EM (the only one I think is available in the US) which unfortunately does not seem to have a lot of documentation about how the L and N terminals must relate to circuits being monitored. However, I do see that there’s also a gen 3 Shelly EM that shows some additional wiring details printed directly on it:
This seems to suggest device L and N should be matched to the circuits being monitored. For a US 240V with no neutral connection I think N would have to be L2.
I’ll also see if there is a way to get more info from Shelly directly on this.
It took longer than expected to actually receive the Shelly EM I ordered, but I now have some direct experience with it. I can see that the voltage detected across the L and N terminals is most certainly being used in the power calculations across both channels. So this voltage, as well as the phase reference provided, seems fundamental to all power and power-factor calculations the monitor is making.
So, if monitoring 240V circuits without a neutral (as per initial schematic), connecting Shelly N to L2 was required to get the expected power values. On the other hand, if monitoring 120V circuits, connecting Shelly N to the neutral bus was required. The phase used for the L connection also clearly influences the orientation of the clamps in order to get the correct sign on the power value. I can also see how full-house monitoring on a split-phase system could be done with one of these things, assuming L1 and L2 were monitored as separate 120V channels. I know that’s be specifically discussed in other threads.
So I think the main issue here is that the gen1 Shelly EM docs simply do not provide enough information. The gen3 Shelly EM device, as well as the EM Pro have more detailed wiring diagrams. While those are different devices they do make good references.
To summarize:
to monitor 240 split phase, one clamp (IA) and L both connected to L1 (0 deg phase) load wire off one pole of the breaker, the second clamp (IB) and N both connected to L2 (180 deg phase) load wire off the second pole.
What I dont like about this is no path to ground or bonded neutral for the EM gen 3
Neutral is connected to N. This is also part of how the EM is powered. It is also the reference point for phase. You will need to rotate one clamp or the readings will cancel each other. There is a arrow on each coil.
In the U.S. Neutral and Ground are usually joined (connected together) in the electrical load center (breaker box). That is how it is in my breaker box. Check with your power company and/or electrician.
Yeah that’s problematic for me too. The Shelly 1PM Gen 4 technical specifications explicitly say “Neutral not needed: No”.
If any of these basic products were rated for 240V split-phase, I believe they’d mark the terminals as L1 and N/L2. Just having L and N means to me that you can use it on single-phase 240V international power which includes a neutral.
Sure it’ll function fine as noted in this post. But there are safety concerns as it is going outside of the product design specifications.
Shelly doesn’t care if you give it L/N or two split phases (180deg oop). Only safety issue comes from the fact that shelly only switches on/off L while in split phase system both phases should should be switched, otherwise the circuit remains hot.
Shelly doesn’t care because they aren’t liable. They don’t say you can use (most) of their EM and PM products without a neutral, so if there’s an issue it’s not their fault.
But beyond that, Shelly EM which is the primary product under discussion in this thread is monitoring-only anyway. No relay unless you get Shelly PM to. Without Shelly explicitly saying a specific product is rated for split phase with a connection to the N terminal, I am personally concerned about safety.
Shelly does show split phase is OK with the Shelly Pro EM 50 at Shelly Pro EM-50. They show LA and LB labeled as split-phase wires connected to terminals L and N. If this is OK on all their products, why not copy paste that for all their products? And why have the explicit specification that neutral is required on the Shelly 1PM Gen 4, if you don’t actually need a neutral and a second split phase is fine?
I’m guessing it’s 95% likely to be fine. But without Shelly explicitly saying it’s fine, the small risk is just not worth it to me.
Because there are products that can work on a single phase without neutral wire. This is specifically about that, not about split phase.
But sure, it does seem this Shelly is not specifically designed to be used on a split phase. If you are concerned for safety, just contact their support and ask about it.
I mean Shelly device doesn’t care (not the company).
And EM has relay as well.
If you are looking for certified installation, you need to stick with approved wiring schemes. Shelly Pro EM-50 on 240V split can be certified, Shelly EM can not.
These products are listed as being for a single phase only, but they are essentially software restricted to only working on the same half of that single phase, and you would have to correct the resulting inverted signs outside of the data feed provided by these units if the CT connect to a different half of that same single-phase. If you stay within the same half of that phase, though (ex. clamps on L1 only), you can wire it up L1 to N, and those will work.
In the pure 240V case, it’s simple. Despite the product label, you don’t have a neutral, and you use L1 and L2, just like the wiring would be in Europe. You won’t get completely correct readings on any split-phase 240V loads though, like ranges, dryers, etc. Portions of those loads flow back on the nuetral and would be present on L1 or L2, and not the other. To fully capture this, you would need two Shelly EM each connected to different halves of the phase (L1 and L2), and then summing those two externally. It’s probably not worth it for something like an oven that may have a 12W steady electronics draw that you could address with powercalc, but the 120V dryer drum motor can be a signfiicant imbalance.