HA Solar Tracker
In collaboration with @Homeotte41 I have been working on a solar tracker project for Home Assistant. Since the technical details could be useful for other projects that involve tracking the sun (see my post here: Incident Angle of Sunlight) I share them here below.
@Homeotte41 made a nice video to showcase the mechanical design he made to change the tilt angle of the panels:
https://www.youtube.com/shorts/CI7dLNPx9DM
More pictures of the PV installation can be found at the bottom of this post.
Here is a graph showing the power output over a whole day, can you guess which graph has implemented the tracking system? :smiley:
Horizontal single axis trackers (HSAT)
There are many types of single and dual axis solar trackers, and if you look online you can find several projects that use them. The principle is simple, you want to maximize the amount of solar energy that you collect, and the best way to do that is to point your solar panels directly at the sun to maximize the direct beam radiation.
Typically this is done by fitting a set of sensors to the panel that try to 'find' the sun in the sky, but with the HA sun platform we have exact knowledge of solar azimuth and elevation angles based on our position and time of day. Therefore we will control the tracker via the elevation and azimuth HA calculates for us based on our latitude, longitude and time of day.
(in mathematical terms, we will align the normal vector of the panel with the sun's rays)
Horizontal single axis trackers are nice because they are relatively simple to build and therefore cheap. You can find more information about them at [1].
[1] HSAT Trackers: Design and Application
Optimizing the incident angle θ
The math is largely based on this paper by the National Renewable Energy Laboratory:
[2] Rotation Angle for the Optimum Tracking of One-Axis Trackers
The math is a bit tedious to explain but in principle it only involves trigonometry and some basic derivative calculus. In general, we try to minimize the Angle of Incidence (AOI) θ between the sun's rays and the panel's normal vector by setting the panel's rotation angle R such that the AOI θ is minimized. The following equation describes the AOI:
cos(θ) = cos(β) cos(θz) + sin(β)sin(θz)cos(γs -γ)
Where:
  • β is the surface tilt angle
  • γ is the surface azimuth angle
  • θz is the sun's zenith angle (which we get from HA)
  • γs is the sun's azimuth angle (also get from HA)
To minimize θ we can maximize cos(θ), which reaches it's maximum for θ = 0 and then cos(θ) = 1.
Because for a horizontal axis tracker the tilt of the rotational axis is always zero and the rotational angle R has a range of [-90°, +90°] the general equation for the optimal rotation angle found in the paper can be simplified to (see section 5 of [2]):
R = arctan[tan(θz)sin(γs - γa)]
Where γa is the azimuth angle of the tracker axis, which we find by looking at google maps and measuring the angle between the rotation (tracker) axis and the north-south axis. Note that the rotational axis angle is perpendicular to the surface azimuth angle γ. In the below image our tracker mode is image (c).
solar_tracker_angle:
  friendly_name: Solar tracker angle
  unit_of_measurement: 'degrees'
  value_template: >
    {% set deg2rad = pi/180 %}
    {% set rad2deg = 180/pi %}
    {% set sun_azi = deg2rad * state_attr('sun.sun', 'azimuth') %}
    {% set sun_zen = deg2rad * (90 - state_attr('sun.sun', 'elevation')) %}
    {% set rot_azi = deg2rad * (58-90) %}
    {% set night_def_angle = states('input_number.solar_tracker_default_angle_at_night') | int(-10) %}
    {% if state_attr('sun.sun', 'elevation') < 0.1 %}
        {{ night_def_angle }}
    {% else %}
        {{ rad2deg * atan(tan(sun_zen) * sin(sun_azi - rot_azi)) }}
    {% endif %}
See above YAML code for the template sensor in HA to calculate R. First, we convert the azimuth and elevation angles from degrees to radians. Then we calculate the azimuth angle of the tracker (rotation) axis γa. The panels point 58° clockwise from north but because the rotation axis is perpendicular to the panels we subtract 90° from that, see picture above. For our calculations we require the zenith angle of the sun θz = 90° - θelev, since it's with respect to the vertical axis instead of the horizon.
Then finally we check whether the sun is below or above the horizon, since tracking in the night is not very useful. If the sun is below the horizon we simply take the default value which can be set by an input_number helper entity in HA. We choose to keep the panel flat during the night so the default angle should be equal or below the minimum angle of -4°. The final value R is given in radians and then converted to degrees. We generally work in radians because the trigonometric functions in jinja templates expect radians as input.
Converting panel tilt R to linear actuator extension d
In order to tilt the solar panels we use a linear actuator from AliExpress: VEVOR 12V Solar Tracker Linear Actuator. The actuator is mounted on the back of the panel and pushes the panel up and down. The goal now is to find a linear actuator extension d, that gives a certain tilt angle R, that minimizes the AOI θ. The actuator has a stroke length of 500mm, a minimum length dmin = 605mm when it is fully retracted and a maximum length of dmax = 1105mm when it is fully extended.
We make a graphical model of the actuator and the panel, and then we can use the model to find the extension d that gives tilt angle R. The math might look at bit daunting at first but it's actually just the cosine rule and some applications of Pythagoras, most people will have had both in high school. First L1, L2, L4 and L5 were measured, and then L3 and L6 can be computed using Pythagoras. We also have to compute a few fixed angles using atan. Everything is explained quite well in [3] so I highly recommend to read if you are looking to built this yourself.
YAML template sensor code to calculate d from R:
solar_tracker_act_perc:
  friendly_name: Solar tracker linear actuator percentage
  unit_of_measurement: '%'
  value_template: >
    {% set L1 = 740 %}
    {% set L2 = 1185 %}
    {% set L4 = 1290 %}
    {% set L3 = sqrt(L1**2 + L4**2) %}
    {% set L5 = 75 %}
    {% set L6 = sqrt(L5**2 + L2**2) %}
    {% set d_max = 1105 %}
    {% set d_min = 605 %}
    {% set alpha_k = atan(L1/L4) %}
    {% set alpha_c = atan(L5/L2) %}
    {% set alpha_max = acos((L3**2 + L6**2 - d_max**2) / (2*L3*L6)) + alpha_c - alpha_k %}
    {% set alpha_min = acos((L3**2 + L6**2 - d_min**2) / (2*L3*L6)) + alpha_c - alpha_k %}
    {% set alpha = deg2rad*(states('sensor.solar_tracker_angle')|float(0)) %}
    {% set alpha_lim = max(min(alpha, alpha_max), alpha_min) %}
    {% set alpha_d = alpha_lim - alpha_c + alpha_k %}
    {% set d = sqrt(L6**2 + L3**2 - 2*L6*L3*cos(alpha_d)) %}
    {% set d_lim = max(min(d, d_max), d_min) %}
    {% set d_perc = 100*(d_lim - d_min) / (d_max - d_min) %}
    {{ d_perc | round(0) | int }}
To compute the maximum and minimum angles αmax and αmin that the panel can rotate we can use the cosine rule with the maximum and minimum length of the actuator as input. We then clamp the desired angle α to be between αmax and αmin. To compute the actuator length d that achieves the desired angle θ we can use the cosine rule again. Finally we convert the length d to a percentage of the total length of the actuator. So if the actuator is fully retracted the percentage is 0% and if it is fully extended the percentage is 100%, with a step size of 1%. Note that d is clamped to be between dmin and dmax again but this is technically not necessary due to the clamping of α, it's just a precaution.
[3] A simplified calculation method of electric linear actuators for single-axis sun tracker
Control electronics and ESPHome YAML
The control electronics consist of a relay board with an ESP8266 that runs ESPHome. The relay board switches the polarity of the 12V output to either extend or retract the linear actuator a certain distance. The distance depends on the on time duration of the relay. To find the time it takes to fully retract or extend the actuator we used a stopwatch, these values can be found in the below YAML as open_duration and close_duration. We also measured the stroke length in steps of 10% from 0% to 100%. We found this to be approximately linear (p/m a few mm) and thus accurate enough. See below picture for the box that houses the relays. The ESP8266 addon module is not present in this picture, but it is placed left of the relays on the 8-pin header.
button:
    on_press:
      - switch.turn_on: relay1
    on_press:
      - switch.turn_on: relay2
switch:
  - platform: gpio
    pin:
      number: GPIO0
      inverted: true
      mode: OUTPUT_OPEN_DRAIN
    restore_mode: RESTORE_DEFAULT_OFF
    interlock: [relay1]
  - platform: gpio
    pin:
      number: GPIO2
      inverted: true
    interlock: [relay2]
cover:
  - platform: time_based
    open_action:
      - switch.turn_off: relay2
    open_duration: 65s
    close_action:
      - switch.turn_off: relay1
    close_duration: 61s
    stop_action:
    assumed_state: false
Since the relay board has active low inputs our ESPHome YAML has to invert the outputs. The interlock option ensures that only one of the two relays can be on at the same time. The mode: OUTPUT_OPEN_DRAIN option ensures that the GPIO can only assume a high impedance (hi-z) state or low state which works great with active-low inputs. The restore_mode: RESTORE_DEFAULT_OFF option attempts to restore the ESP state when it boots and if it can't ensures that the relays are off. The linear actuator is modelled as a cover entity in HA.
Actuator control automation
The cover entity gives us a very convenient way to control the actuator, to set a certain actuator length d we simply call the service cover.set_cover_position with the stroke length d as a % in the range [dmin, dmax] as the position argument. The automation is triggered anytime the input sensor entity sensor.solar_tracker_act_perc changes. The automation then calls the service cover.set_cover_position with the input number as the position argument. You can find the automation YAML code below. It's pretty simple but could always be improved if needed, for example you could close the panels during a storm based on the wind speed.
alias: test_solar_angle
description: ""
  - platform: state
    entity_id:
      - sensor.solar_tracker_act_perc
condition: []
  - service: cover.set_cover_position
      entity_id: cover.scherm_control
      position: "{{ states('sensor.solar_tracker_act_perc') | int(0) }}"
mode: single
PV installation images
Some nice images taken by @Homeotte41 to give you a better idea of what it looks like:
PVLib simulation
In order to estimate the energy gain of the solar tracker we can use the PVLib python library to run a small simulation. Special thanks to Kevin from PVLib google group for help setting this up.
With all default parameters the AC power plot on a clear day in june, with a 1kW system, looks like this:
From the plot it's visible the tracker collects more energy, especially during the morning and late afternoon. The total energy gain is about 20% for this day. In reality the energy gain will be quite a bit lower, because in reality the tilt angle is limited to about -4° towards south-west which limits the efficiency in the afternoon. But we still see we are able to improve efficiency during the morning and early afternoon compared to a fixed system.
Nice project!
Maybe interesting to stimulate the performance increase in spring as well as in mid winter? In summer the gain maybe limited because the sun rises very high, whereas in winter the sun stays low and thus benefits from the angle. Based on that result you may want to expand the simulation over the complete year to see the extra gain.
Hi langestefan,
Great Project first of all!
I am trying your code, if i understand well, shoud the panels during the days, going max-up during the sunrise, the move almost to flat position at noon, and the going up again until sunrise?
That is correct. The sun rises in the east, and goes down in the west. We can visualize this with a plot from sunearthtools (the yellow digits are the hours):
So to maximize incoming sunlight in the morning we want the panels fully upright. Ofcourse in an urban environment like this there are many houses blocking direct sunlight so the gain of going fully upright would be minimal. Note that the optimal angle is also dependent on the azimuth of the rotational axis (see the images in my post above).
Thank you! because using your code the solar sensor anglr gives me positive value in the morning and negative ones afternoon, so the actuator adjuster does not work in the afternoon, i corrected the template using absolute value of the sensor,and it seems to work,do you think it is correct?
Well yes that makes sense, if the sun is on the horizon due east the tracker must be at tilt 90 degrees (fully upright pointing east) and when the sun goes down due west the tracker must be at tilt -90 degrees. Fully flat would be 0 degrees.
In my situation that wouldn’t make any sense, so no.
but the tilt in your case is case c , on the zenit,isn’t it? n-s axe and and the rotation is on w-e axe.
The azimuth of the PV panel is 58 degrees. The rotational axis is at 58-90+360 = 328 degrees, or 58+90 = 148 degrees. They are equivalent. So you could say the rotational axis is pointing south east, or somewhere in between c and d. If the rotational axis was exactly (c) then yes, its movement would be symmetric with respect to astronomical noon (it would go upright → flat → upright)
you are right, i am in case d and i need to find tilt angle of the panel so beta in your case,so different case.
Could you monitor the output of one panel and adjust the linear actuator until the maximum output is reached?
That doesn’t matter, the formula is the same. I think the problem is with the atan function, I should have used atan2. atan only gives the correct angle in the 1st and 4th quadrants, atan2 gives the correct angle in all quadrants.
That would require some kind of control algorithm, similar to what an MPPT is doing. It could be done, but the cost would probably be too high to make it worthwhile. Additionally you would have increased usage of the actuator in order to find the right set point, which would also change during the day and may be unreliable during cloudy weather. An alternative is to use the conventional sensor based tracking method, which uses LDR sensors to ‘find’ the sun in the sky. There are plenty of resources online that cover this method, but I prefer my method because it is deterministic :slight_smile:
You can get a controller on Ebay for $50. SZMWKJ Single Axis Solar Panel Tracker Tracking Electronic Controller 602463254787 | eBay
That’s using the light sensor method. I doubt it’s very efficient
Ok, do you think you can change it?
I don’t need it, as my usable range falls in quadrant 1 and 4. I have no time to modify and test it at the moment, but it shouldn’t be that hard to make it work.
@langestefan OMG! You are a genius! :star_struck:
I sadly don’t understand your formula, but can I ask you to provide me with a formula?
I just like to know the angle the sun shines on my solar panels. (in HA)
As in your formula: I am getting the sun’s angles (elevation and direction) from home assistant.
And for the formular I like to put in the static parameters
  1. direction the solar panels are facing to (285 deg.) and
  2. angle/tilt of the solar panels (15 deg.)
Would you be able to provide a formula to calculate the angle the sun is shining on my solar panels?
(I am living south of the equator in Brisbane! → But if I am correct this should not influence the formula?)
Can you please help a stupid MBA here? :frowning:
Hi, I gave a formula for the angle of incidence θ here:
Hi Stefan,
Love the sound of this project, i’ve built an east-west frame and i am just trying your templates but can’t really see it working for me.
I have copied and pasted the templates into HA and the solar tracker seems to be producing angles currently -48.13 but the Solar tracker linear actuator percentage always produces 0 with negative numbers…
What am i doing wrong ?
I think that’s correct. Sun comes up in the east and goes down in the west. You need to calibrate the template so that 0% of the linear actuator is the minimum elevation and 100% is the maximum elevation.
As you can see my angle tracker covers the full -90 degrees to 90 degrees range, but the range of the linear actuator is much smaller.