Hello,
Here below the way I integrated the NewMotion Advanced 3.0 with DPM module, version with 1 x CT, to Home assistant.
The explanation is quite long, but the hardware and integration are quite short/simple.
Note that if any damages occurs, you might lose the warranty, however, it works very fine for me for a while now.
Good to know before starting: What is a CT?
[Wikipedia] → A Current Transformer is a type of transformer that is used to reduce or multiply an alternating current. It produces a current in its secondary which is proportional to the current in its primary. Current transformers, along with voltage or potential transformers, are instrument transformers.
The Dynamic Power Module
While using the DPM option, the charging station is checking that the current going through the CT at the grid connection doesn’t exceed the Max Current (Defined by your installer or Shell based on your breakers - in my case 40A for the main breaker and 32A breaker for the charging station)
→ If the current is exceeding the Max current, the changing station current will be progressively reduced to achieve stability (Current through the CT [house current, incl. charging current] = Max current)
E.g: Charging 32A (7.4kW - 230V) + switching ON a load of 10A (2.3kW - 230V) = 42A which is higher than the 40A.
The charger will then decrease the charging current (Called “Limited now”)
→ If the Max Current is not reached, then the charging power is increased until reaching stability or its maximum. (In my case 32A)
When connected by Ethernet cable, the “Max” and “Limited now” currents can be accessed on the charging station. There are a couple of posts explaining how to reach to the data in the My New Motion topic here above.
The integration
Since I didn’t found any available software integration, nor any option on the Shell Recharge App (or official Shell solution), I tested some hardware integrations. The easier/most efficient for me was to simulate a current which will be measured by the DPM.
I’m pretty sure there is also a possibility to replace the DPM by a Ethernet to RS485 converter to make direct communication with the charger, but I didn’t explore this way.
As the CT is generating an AC current to the DPM, I made some tests with generating AC currents. I abandoned this idea when I saw that the DPM was also working with DC currents, which is easier to generate.
As Xemex is warning on Page 7/13 of the datasheet, the DPM can be burned if too much current flows through it. (Very important)
Here the datasheet (The DPM module comes from Xemex)
CSMB - Current Sense Modbus Converter | Xemex
The CT has the following spec : Current range 1A … 80A (if CT ratio = 2000)
The max current going through the DPM with the original CT would be: 80A/2000= 0,040A AC = 40mA AC
Another important thing to know is that it is not allowed to disconnect a CT when current is flowing through its primer. (First remove the CT from the cable, then disconnect the CT wires)
See explanation on the video : Why you should never disconnect current transformer from burden resistor when current is at primary - YouTube