"Hello! As a delighted user of the Webasto “Unite” (and Webasto Next soon) Charging Station, I’ve taken the initiative to integrate the Unite Modbus table register settings into Home Assistant.
In this initial phase, I’ve successfully added these settings, paving the way for enhanced functionality. Depending on your specific needs, it’s also feasible to configure the related register to adjust the charging power. This feature proves invaluable for scenarios like PV-Surcharge charging demands or Load Management requirements, especially if you plan to utilize multiple charging stations.
Below, you’ll find the Modbus sensor table, which you can seamlessly incorporate into your configuration.yaml. Alternatively, I’ve organized this information into a dedicated modbus.yaml file. In my configuration setup, I simply reference this modbus.yaml file within my configuration.yaml, streamlining the process. Here’s how it looks:"
modbus: !include modbus.yaml
Here’s the code for the modbus.yaml file::
# Protocol requirements
# The Webasto Unite charging station acts as a slave device in Modbus TCP/IP communication.
# Charging station should be in the same network with the master device, or proper routing should be applied to provide communication between slave and master devices in different sub networks.
# Each charging station should have a different IP address. There can only be one active Modbus master connection at any time.
# Parameter Modbus TCP
# Each Wallbox Unite must be given a unique IP.
# Parameter Value
# IP-address: Any IP address; All Webasto Unite on the same subnet (e.g., xxx.xxx.xxx.xxx)
# Modbus Port: 502
# Modbus Unit ID: 255
- name: Webasto_Unite
type: tcp
timeout: 5
host: 192.168.12.212
port: 502
sensors:
- name: Webasto_Unite_Serial_Number
unique_id: Webasto_Unite_Serial_Number
slave: 255
input_type: input
address: 100
data_type: string
count: 25
- name: Webasto_Unite_Charge_Point_ID
unique_id: Webasto_Unite_Charge_Point_ID
slave: 255
input_type: input
address: 130
data_type: string
count: 50
- name: Webasto_Unite_Charge_Point_Brand
unique_id: Webasto_Unite_Charge_Point_Brand
slave: 255
input_type: input
address: 190
data_type: string
count: 10
- name: Webasto_Unite_Charge_Point_Model
unique_id: Webasto_Unite_Charge_Point_Model
slave: 255
input_type: input
address: 210
data_type: string
count: 5
- name: Webasto_Unite_Firmware_Version
unique_id: Webasto_Unite_Firmware_Version
slave: 255
input_type: input
address: 230
data_type: string
count: 50
- name: Webasto_Unite_Date
unique_id: Webasto_Unite_Date
slave: 255
input_type: input
address: 290
data_type: uint32
- name: Webasto_Unite_Time
unique_id: Webasto_Unite_Time
slave: 255
input_type: input
address: 294
data_type: uint32
- name: Webasto_Unite_Charge_Point_Power
unique_id: Webasto_Unite_Charge_Point_Power
slave: 255
input_type: input
address: 400
data_type: uint32
offset: 0
scale: 1
precision: 2
state_class: measurement
unit_of_measurement: W
- name: Webasto_Unite_Number_of_Phases
# 0:1-phase, 1:3-phases
unique_id: Webasto_Unite_Number_of_Phases
slave: 255
input_type: input
address: 404
data_type: uint16
- name: Webasto_Unite_Charge_Point_State
# 0: "Available",
# 1: "Preparing",
# 2: "Charging",
# 3: "SuspendedEVSE",
# 4: "SuspendedEV",
# 5: "Finishing",
# 6: "Reserved",
# 7: "Unavailable",
# 8: "Faulted",
unique_id: Webasto_Unite_Charge_Point_State
slave: 255
input_type: input
address: 1000
data_type: uint16
- name: Webasto_Unite_Charging_State
# 0: Not Charging, State Ax, Bx, Dx or C1 1: Charging, state C2
unique_id: Webasto_Unite_Charging_State
slave: 255
input_type: input
address: 1001
data_type: uint16
- name: Webasto_Unite_Equipment_State
# 0: Initializing
# 1: Running
# 2: Fault
# 3: Disabled
# 4: Updating
unique_id: Webasto_Unite_Equipment_State
slave: 255
input_type: input
address: 1002
data_type: uint16
- name: Webasto_Unite_Cable_State
# 0: Cable not connected 1: Cable connected, vehicle not connected 2: Cable connected, vehicle connected 3: Cable connected, vehicle connected, cable locked
unique_id: Webasto_Cable_State
slave: 255
input_type: input
address: 1004
data_type: uint16
- name: Webasto_Unite_EVSE_Fault_Code
# 0: No fault
# Other: Fault code
unique_id: Webasto_Unite_EVSE_Fault_Code
slave: 255
input_type: input
address: 1006
data_type: uint16
- name: Webasto_Unite_Charging_Current_L1
unique_id: Webasto_Unite_Charging_Current_L1
slave: 255
input_type: input
address: 1008
data_type: uint16
device_class: current
offset: 0
scale: 0.001
precision: 0
unit_of_measurement: A
- name: Webasto_Unite_Charging_Current_L2
unique_id: Webasto_Unite_Charging_Current_L2
slave: 255
input_type: input
address: 1010
data_type: uint16
offset: 0
scale: 0.001
precision: 0
- name: Webasto_Unite_Charging_Current_L3
unique_id: Webasto_Unite_Charging_Current_L3
slave: 255
input_type: input
address: 1012
data_type: uint16
offset: 0
scale: 0.001
precision: 0
- name: Webasto_Unite_Charging_Voltage_L1
unique_id: Webasto_Unite_Charging_Voltage_L1
slave: 255
input_type: input
address: 1014
data_type: uint16
device_class: voltage
unit_of_measurement: V
- name: Webasto_Unite_Charging_Voltage_L2
unique_id: Webasto_Unite_Charging_Voltage_L2
slave: 255
input_type: input
address: 1016
data_type: uint16
- name: Webasto_Unite_Charging_Voltage_L3
unique_id: Webasto_Unite_Charging_Voltage_L3
slave: 255
input_type: input
address: 1018
data_type: uint16
- name: Webasto_Unite_Active_Power_Total
unique_id: Webasto_Unite_Active_Power_Total
slave: 255
input_type: input
address: 1020
data_type: uint32
device_class: power
- name: Webasto_Unite_Active_Power_L1
unique_id: Webasto_Unite_Active_Power_L1
slave: 255
input_type: input
address: 1024
data_type: uint32
device_class: power
- name: Webasto_Unite_Active_Power_L2
unique_id: Webasto_Unite_Active_Power_L2
slave: 255
input_type: input
address: 1028
data_type: uint32
device_class: power
- name: Webasto_Unite_Active_Power_L3
unique_id: Webasto_Unite_Active_Power_L3
slave: 255
input_type: input
address: 1032
data_type: uint32
device_class: power
- name: Webasto_Unite_Meter_Reading
unique_id: Webasto_Unite_Meter_Reading
slave: 255
input_type: input
address: 1036
data_type: uint32
device_class: energy
state_class: total_increasing
offset: 0
scale: 0.001
precision: 3
unit_of_measurement: kWh
- name: Webasto_Unite_Session_Max_Current
unique_id: Webasto_Unite_Session_Max_Current
slave: 255
input_type: input
address: 1100
data_type: uint16
- name: Webasto_Unite_EVSE_Min_Current
unique_id: Webasto_Unite_EVSE_Min_Current
slave: 255
input_type: input
address: 1102
data_type: uint16
- name: Webasto_Unite_EVSE_Max_Current
unique_id: Webasto_Unite_EVSE_Max_Current
slave: 255
input_type: input
address: 1104
data_type: uint16
- name: Webasto_Unite_Cable_Max_Current
unique_id: Webasto_Unite_Cable_Max_Current
slave: 255
input_type: input
address: 1106
data_type: uint16
- name: Webasto_Unite_Charged_Energy
unique_id: Webasto_Unite_Charged_Energy
slave: 255
input_type: input
address: 1502
data_type: uint32
state_class: total
offset: 0
scale: 0.001
precision: 3
- name: Webasto_Unite_Session_Start_Time
unique_id: Webasto_Unite_Session_Start_Time
slave: 255
input_type: input
address: 1504
data_type: uint32
- name: Webasto_Unite_Session_Duration
unique_id: Webasto_Unite_Session_Duration
slave: 255
input_type: input
address: 1508
data_type: uint32
device_class: duration
unit_of_measurement: s
- name: Webasto_Unite_Session_End_Time
unique_id: Webasto_Unite_Session_End_Time
slave: 255
input_type: input
address: 1512
data_type: uint32
- name: Webasto_Unite_Failsafe_Current
# R/W: Can be set in the Unite WebUI (Standard:6A)
# Charging power will fall back to 6A, if ALive Register 6000 not triggered with 1 within each 20 seconds
unique_id: Webasto_Unite_Failsafe_Current
slave: 255
input_type: holding
address: 2000
data_type: uint16
# Failsafe charging current during communication failure
- name: Webasto_Unite_Failsafe_Timeout
# R/W: No need to change (Standard: 20 seconds)
unique_id: Webasto_Unite_Failsafe_Timeout
slave: 255
input_type: holding
address: 2002
data_type: uint16
# Communication timeout for switching to Failsafe charging current. If the timeout has occurred and the TCP socket is still active, TCP socket restarts. If set, Failsafe period is timeout/2, otherwise 20 sec.
# R/W: 0-5A=Charging paused, 6-32A=Charging with set Amps
slave: 255
input_type: holding
address: 5004
data_type: uint16
# Dynamic charging current
switches:
- name: Webasto_Unite_Alive_Register
# R/W
unique_id: Webasto_Unite_Alive_Register
slave: 255
write_type: holding
address: 6000
command_on: 1
command_off: 0
verify:
delay: 5
# EMS (Master) writes 1 EVSE (Slave) writes 0 (EVSE checks this register at a period of (Failsafe Timeout)/2 for a value of 1, and sets it to 0. Period cannot go less than 3 seconds)
I’ve included explanatory notes for the sensor statuses in the file. These explanations can prove beneficial if you plan to translate them into more user-friendly status messages using helper sensors, although I haven’t implemented this feature yet.
For instance, regarding the “charge point” state with register “1000,” a value of “2” signifies “charging.”
If you’re considering dynamically adjusting the charging power (the sole writable register “5004,” apart from the keep-alive register “6000”), you can incorporate a current value slider in your configuration.yaml:
webasto_unite_current_value_slider:
initial: 16
min: 5
max: 32
step: 1
Moreover, alongside integrating the current slider, you’ll need to implement corresponding automation to ensure the seamless updating of register “5004”:
alias: Set Webasto Unite Current Limit
description: Set Webasto Unite Current Limit
- platform: state
entity_id:
- input_number.webasto_unite_current_value_slider
condition: []
- service: modbus.write_register
hub: Webasto_Unite
address: 5004
slave: 255
value:
- "{{ (states.input_number.webasto_unite_current_value_slider.state) }}"
mode: single
Please Note: Every Amp value set below 6A (e.g. 5A) will not halt a charging session but rather pause it (this is wanted and normal!). This is indicated by the Webasto Unite LED indicator ring, which will shine purple.
To ensure this integration operates smoothly, you must activate Modbus in the Unite WebUI:
Additionally, for safety purposes, if Modbus register “6000” (Keep Alive Register) is not frequently triggered with a value of “1”, the wallbox will terminate the Modbus connection to Home Assistant.
Consequently, you need to implement an additional automation. The following setup has proven effective for me:
alias: Webasto Unite Keep Alive
description: Webasto Unite Keep Alive
- platform: time_pattern
seconds: /5
condition: []
- service: switch.turn_on
data: {}
entity_id: switch.webasto_unite_alive_register
mode: single
Some general notes: This code may potentially be compatible with certain Vestel Charging Stations, although I haven’t personally tested it.
However, the primary advantage and unique selling point that led me to choose the Webasto Unite was its robust integration with a powerful OCPP backend—the Webasto Charge Connect Backend and accompanying app— which perfectly fulfills all my requirements. For instance, within the backend, I can effortlessly set up various automated charging reports, tailored to my specific needs. For instance, as a household with multiple EVs and a company car, it was crucial for me to have detailed charging reports segregated between private and company vehicle sessions. With the Webasto Charge Connect Backend, I can easily generate a report based on the RFID tag assigned to my company car.
As I’m planning to install the Webasto “Next” alongside the Unite in the near future, I’m also considering integrating it into Home Assistant.
I’m curious to know if there are others who own a Webasto Charging Station and have explored integrating it with Home Assistant. Any experiences or insights to share?